QUOTE(ozak @ Jul 11 2012, 09:09 AM)
Oh my, you remember me back when I work in 1 of the aircon manufacturing. Yes the process of condenser(indoor) and evaporator (outdoor) is brazing the copper pipe together. Than pump high pressure air into it and put into the fish tank. Check for the bubble leakage. Than take back and repair again. Even we using this method of checking on the compressor.
Haha. They call it the 'pressure dip tank'. Checking compressor normally they hod pressure with bubble soap on the joints. Else, they will use more high tech machine. They call it the leakage checker.
Added on July 11, 2012, 12:41 pmQUOTE(skng03 @ Jul 11 2012, 09:32 AM)
Actually, the amount of work to install 2.5 or 3.o is the same, just the 3.o compressor may b heavier, and need to top up more gas as the piping size bigger, thus cost a little bit More
Not necessarily. 3HP might not need a bigger piping size. Check spec. Also check your AC spec to see what is the standard piping length. Within this standard piping length, there is no need to add on the refrigerant. Do not exceed the max allowable piping length. Once exceed, you will have compressor oil return problem. Installation work for all 'residential' AC is the same. Work is the same. The cost difference is because of the piping length and type, and also the location of the AC. If it is difficult to access, AC installer wants higher price. For 'residential' AC, you do not need to top up gas if your piping length does not exceed the standard piping length. Take note and dont get conned.
Added on July 11, 2012, 12:47 pmQUOTE(weikee @ Jul 11 2012, 09:45 AM)
Your piping so long, sure expensive. Have you consider losses? 1HP at that length may not get any power when reach the blower.
My previous company, need 30000btu, but the compressor is 5 level below, total length is about 90ft and the HVAC expert advise minimal 36k BTUs, we end up getting about 40k BTUs and is just nice.
Of course there is always a de-rating value which is not always available in the catalogue. 90ft = 27m. That is a long one plus outdoor unit is at the bottom. Unless you are using single split packaged unit (cassettes, ducted, ceiling exposed), there will be no single split wall mounted that can allow piping length that long. So design the location wise. Putting the compressor at the top helps in your case.
This post has been edited by lingleeyen: Jul 11 2012, 12:47 PM