SUSkimsim
post Jul 1 2015, 03:31 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(coolkwc @ Jul 1 2015, 02:49 PM)
My ME inverter 1HP used 800W leh... whistling.gif
*
Your new ME has been cutting cost and they bring Indonesia model for M'sia, unless you go with premium inverter just 485w only
coolkwc
post Jul 1 2015, 04:17 PM

Fall in love with audio again.
*******
Senior Member
3,112 posts

Joined: Jul 2006
QUOTE(kimsim @ Jul 1 2015, 03:31 PM)
Your new ME has been cutting cost and they bring Indonesia model for M'sia, unless you go with premium inverter just 485w only
*
Then why u still recommend ME everywhere. whistling.gif ME = cheapskate cut cost, period. whistling.gif

I consider RM1.5k for 1HP unit already premium, anything above it, sorry, no go for me.
SUSkimsim
post Jul 1 2015, 04:21 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(coolkwc @ Jul 1 2015, 04:17 PM)
Then why u still recommend ME everywhere. whistling.gif ME = cheapskate cut cost, period. whistling.gif

I consider RM1.5k for 1HP unit already premium, anything above it, sorry, no go for me.
*
I had sometime ago never recommended on ME for 1hp to 1.5hp & 2hp and excepted for 2.5Hp ME inverter.

You can read my replied sometime ago has push on Daikin GA inverter
coolkwc
post Jul 1 2015, 04:47 PM

Fall in love with audio again.
*******
Senior Member
3,112 posts

Joined: Jul 2006
QUOTE(kimsim @ Jul 1 2015, 04:21 PM)
I had sometime ago never recommended on ME for 1hp to 1.5hp & 2hp and excepted for 2.5Hp ME inverter.

You can read my replied sometime ago has push on Daikin GA inverter
*
Daikin GA inverter? u sure or not? I saw the 1HP inverter model power min-max is 280-920W (rated 780W), i dun think is outstanding power saving, more or less same as my ME only.

This post has been edited by coolkwc: Jul 1 2015, 04:49 PM
SUSkimsim
post Jul 1 2015, 04:54 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(coolkwc @ Jul 1 2015, 04:47 PM)
Daikin GA inverter? u sure or not? I saw the 1HP inverter model power min-max is 280-920W, i dun think is outstanding power saving, more or less same as my ME only.
*
Ya how is ur ME 1hp inverter any feedback from you?

Just sharing here, since u r the user.
SUSleonhart88
post Jul 1 2015, 04:59 PM

Regular
******
Senior Member
1,686 posts

Joined: May 2012
kimsim why made in thailand one better than made in malaysia or china? we know rm> baht. we are more develop than thai
SUSkimsim
post Jul 1 2015, 05:05 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(leonhart88 @ Jul 1 2015, 04:59 PM)
kimsim why made in thailand one better than made in malaysia or china? we know rm> baht. we are more develop than thai
*
Just tells u on Daikin made in Thailand really worst design than made in MY.

You see how dusty there are, but the fan blower can't remove out or difficult to take out

user posted image

user posted image

For York design at least the blower still can able to remove out and spray with water n brush.
coolkwc
post Jul 1 2015, 05:29 PM

Fall in love with audio again.
*******
Senior Member
3,112 posts

Joined: Jul 2006
QUOTE(kimsim @ Jul 1 2015, 04:54 PM)
Ya how is ur ME 1hp inverter any feedback from you?

Just sharing here, since u r the user.
*
I normally set 26'C-27'C only, the temp set was quite accurate la, i measure using thermometer same as the temp i set. But don't know why, sometimes it takes long time to reach my desired temp, sometimes faster, but the outside temp and room temp is more or less same everyday.

I switch ON 10 hours every night, i monitor my TNB meter, sometimes consume 5kW/night, sometimes can reach 8-9kW...not that kind of power saving that i expected.

Anyway, i noticed the outer copper pipe is not ice up during operation, i thought it should be ice up. hmm.gif The direct air blow from the blower is not as cold as expected too. The compressor is not working at its full capacity even on startup, which i think is suspicious. I suspect gas overfill or what.

This post has been edited by coolkwc: Jul 1 2015, 05:41 PM
coolkwc
post Jul 1 2015, 05:51 PM

Fall in love with audio again.
*******
Senior Member
3,112 posts

Joined: Jul 2006
I just called ME to ask about my problem. He told me the temp delta of inlet vs outlet air temp during turn ON before it reach my desired temp should be around 15'C, and he said during normal operation the small copper pipe shouldn't freeze up, if not it means the refrigerant is not enough. I'm gonna to measure the temp tonight to see normal or not.
SUSkimsim
post Jul 1 2015, 05:57 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(coolkwc @ Jul 1 2015, 05:51 PM)
I just called ME to ask about my problem. He told me the temp delta of inlet vs outlet air temp during turn ON before it reach my desired temp should be around 15'C, and he said during normal operation the small copper pipe shouldn't freeze up, if not it means the refrigerant is not enough. I'm gonna to measure the temp tonight to see normal or not.
*
Freeze can see at fan coil on right hand side, then the gas pipe still not connected as well, to be confirm gas leaking again

Your Aircon man boss also cannot used too.


This post has been edited by kimsim: Jul 1 2015, 05:59 PM
cedyy
post Jul 1 2015, 06:07 PM

Regular
******
Senior Member
1,403 posts

Joined: Jun 2009


guys, appreciate it if can PM contact for reliable air cond contractor for service n repair in Klang Valley. thanks
SUSkimsim
post Jul 1 2015, 06:08 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(coolkwc @ Jul 1 2015, 05:51 PM)
I just called ME to ask about my problem. He told me the temp delta of inlet vs outlet air temp during turn ON before it reach my desired temp should be around 15'C, and he said during normal operation the small copper pipe shouldn't freeze up, if not it means the refrigerant is not enough. I'm gonna to measure the temp tonight to see normal or not.
*
You can whatsapp me lah, if you wanna know more on Aircon
SUSleonhart88
post Jul 1 2015, 06:20 PM

Regular
******
Senior Member
1,686 posts

Joined: May 2012
QUOTE(kimsim @ Jul 1 2015, 05:05 PM)
Just tells u on Daikin made in Thailand really worst design than made in MY.

You see how dusty there are, but the fan blower can't remove out or difficult to take out

user posted image

user posted image

For York design at least the blower still can able to remove out and spray with water n brush.
*
but why more durable?
SUSkimsim
post Jul 1 2015, 06:23 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(leonhart88 @ Jul 1 2015, 06:20 PM)
but why more durable?
*
Durable York is better also cheaper, even sound airflow dB much better to handle than non inverter model, much quiet from indoor also much cooler
SUSleonhart88
post Jul 1 2015, 06:29 PM

Regular
******
Senior Member
1,686 posts

Joined: May 2012
QUOTE(kimsim @ Jul 1 2015, 06:23 PM)
Durable York is better also cheaper, even sound airflow dB much better to handle than non inverter model, much quiet from indoor also much cooler
*
I will buy MHI
SUSkimsim
post Jul 1 2015, 06:31 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(leonhart88 @ Jul 1 2015, 06:29 PM)
I will buy MHI
*
MHI indoor unit design not as good, the worst part on fan blower cannot be remove n also fan coil area very smaller surface, once blocking then difficult to clean out.

Daikin GA much better than MHI lah
SUSleonhart88
post Jul 1 2015, 06:57 PM

Regular
******
Senior Member
1,686 posts

Joined: May 2012
QUOTE(kimsim @ Jul 1 2015, 06:31 PM)
MHI indoor unit design not as good, the worst part on fan blower cannot be remove n also fan coil area very smaller surface, once blocking then difficult to clean out.

Daikin GA much better than MHI lah
*
can you give me the pic of mhi indoor?
SUSkimsim
post Jul 1 2015, 07:00 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(leonhart88 @ Jul 1 2015, 06:57 PM)
can you give me the pic of mhi indoor?
*
Didn't take, cause not interested at all
SUSleonhart88
post Jul 1 2015, 08:50 PM

Regular
******
Senior Member
1,686 posts

Joined: May 2012
QUOTE(kimsim @ Jul 1 2015, 07:00 PM)
Didn't take, cause not interested at all
*
no pic means no fact at all bro. mhi claims in brochure very easy to clean and remove filter
mghong
post Jul 1 2015, 09:53 PM

Casual
***
Junior Member
450 posts

Joined: Nov 2005


i going to make my 2nd batch order.

1HP for guestroom , prefer non-inverter since noone is coming hahah
1.5hp for 1st family hall , i dont expect to open it for more than 2 hour because most time people all stay downstair.

1.5hp for living hall . this unit also backup to support my 2hp livinghall(main) ,

1) What is your suggestion which shall i take inverter or non-inverter.
2) i see Pana and MIt non-inverter also use new gas r4xxx. should i stay with new gas.
3)both living and family hall unit are for short and need quick cool , any brand to recommend for now ?