 Home Electrical MCB, How to size Miniature Circuit Breaker

views
     
TSstevie8
post Oct 9 2013, 02:02 PM, updated 13y ago

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
Anyone knows how to size MCB of our home?

Got B,C,D type and different Amperage. How and what to choose?

Attached Image Attached Image
Xccess
post Oct 9 2013, 02:39 PM

Twinkle lil Stars
*******
Senior Member
2,768 posts

Joined: Feb 2012


QUOTE(stevie8 @ Oct 9 2013, 02:02 PM)
Anyone knows how to size MCB of our home?

Got B,C,D type and different Amperage. How and what to choose?

Attached Image Attached Image
*
Bro, if you are not sure please get engage the help from a professional electrician. In the event of overload, fire may occur thus handle with care.

This post has been edited by Xccess: Oct 9 2013, 02:40 PM
SUSXploit Machine
post Oct 9 2013, 02:49 PM

❤️ 孤独な旅行者 ❤️​
*******
Senior Member
7,247 posts

Joined: Nov 2008
From: SINGAPORE💃

QUOTE(stevie8 @ Oct 9 2013, 02:02 PM)
Anyone knows how to size MCB of our home?

Got B,C,D type and different Amperage. How and what to choose?

Attached Image Attached Image
*
varies on electrical appliances, lights usually fitted with 6 ~ 10A, airconditioner and fridge to 30A ...
weikee
post Oct 9 2013, 02:51 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(Xploit Machine @ Oct 9 2013, 02:49 PM)
varies on electrical appliances, lights usually fitted with 6 ~ 10A, airconditioner and fridge to 30A ...
*
Common is 6, 10, and 15.

30A make sure you have thick cables minimal 4mm.
TSstevie8
post Oct 9 2013, 04:17 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(weikee @ Oct 9 2013, 02:51 PM)
Common is 6, 10, and 15.

30A make sure you have thick cables minimal 4mm.
*
How to know 4mm, xmm? Some cable got 3 wires, some 1 wire, etc.

What mm for which Am rating?

Thanks
weikee
post Oct 9 2013, 06:29 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Actually, why do you post this question?
TSstevie8
post Oct 9 2013, 10:32 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(weikee @ Oct 9 2013, 06:29 PM)
Actually, why do you post this question?
*
My house MCB most of it harden already, stuck, so difficult to pull down or push up. My electrician advised me to change all even though some are still good. And he suggested all change to 32A. I have 10, 20 and 32A. I am worry about his advice to change all to 32a and if the cable/wire can take load and what is the danger of doing so.

It is time to get some advice from others like you and be sure and if I can diy or just let him do it. See picture of my DB and the 3 types of MCB.

Attached Image

Attached Image Attached Image
Saton666
post Oct 9 2013, 10:43 PM

Getting Started
**
Junior Member
117 posts

Joined: Jan 2012
all change to 32? what for

if the device only suppose to run 5A, and connect to a 8A breaker. anything more than 8 it will trip to protect the device

unless you expect it to shoot up to 32, no point to up the amp by so much. 100 percent still reasonable, few hundred sweat.gif


ezzone
post Oct 9 2013, 10:48 PM

Getting Started
**
Junior Member
54 posts

Joined: Jan 2003
First thing you need to do is terminate your electrician....change all to 32A??? doh.gif


The big one with black handle is the Main Switch - If you ON/OFF this, it will ON/OFF whole house
The blue handle is the ELCB (Earth Leakage Circuit Breaker) - This is the protective device to protect your electrical system if there is a current leakage.
The other are MCB (Miniature Circuit Breaker) - This is the circuit breaker of each wiring circuit.

My suggestion....replace according to existing rating.....


This post has been edited by ezzone: Oct 9 2013, 10:58 PM
weikee
post Oct 9 2013, 10:54 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 9 2013, 10:32 PM)
My house MCB most of it harden already, stuck, so difficult to pull down or push up. My electrician advised me to change all even though some are still good. And he suggested all change to 32A. I have 10, 20 and 32A. I am worry about his advice to change all to 32a and if the cable/wire can take load and what is the danger of doing so.

It is time to get some advice from others like you and be sure and if I can diy or just let him do it. See picture of my DB and the 3 types of MCB.

Attached Image

Attached Image   Attached Image
*
Your electrician want you to change house is it? All 32Amp, if wires are 1.5mm, use until wires burn the MCB won't trip. Usually they will put 20A for socket, and some will use 32A for a/c and heater, but 20A is good enough because 2.5mm can't supply 32A load for long period, and now a/c don't have such high spike.

Light, use back 6A or 10A.

Best check the old MCB, and do direct replace.
TSstevie8
post Oct 9 2013, 10:58 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
Thanks for the replies.

But the problem is few socket/power point to one MCB. So, if on all together total load could be more than 20A.

Let me check one by one and post here again.
TSstevie8
post Oct 9 2013, 11:03 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(weikee @ Oct 9 2013, 10:54 PM)
Your electrician want you to change house is it? All 32Amp, if wires are 1.5mm, use until wires burn the MCB won't trip. Usually they will put 20A for socket, and some will use 32A for a/c and heater, but 20A is good enough because 2.5mm can't supply 32A load for long period, and now a/c don't have such high spike.

Light, use back 6A or 10A.

Best check the old MCB, and do direct replace.
*
This is not the original, he changed it 12 yrs ago when i reno my house so direct replace also may not be correct. rclxub.gif

I will test out all how it is all connected how the MCB are shared and post the table here for your further advice. Now at night cannot test, cannot see in the dark. sad.gif

Also, that is why i am asking about the wire, how to identify the wire rating.

This post has been edited by stevie8: Oct 9 2013, 11:04 PM
Sydneguy
post Oct 10 2013, 12:44 AM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


QUOTE(stevie8 @ Oct 9 2013, 10:58 PM)
Thanks for the replies.

But the problem is few socket/power point to one MCB. So, if on all together total load could be more than 20A.

Let me check one by one and post here again.
*
1) The solution to this particular problem is to add more MCB and split some of the socket to the extra MCB.

2) As others have mentioned using 32A MCB with writing only meant for 10, 15 or 20A MCB will lead to fire when there is an overload.

3) fire you electrician and get one that gives good advice.
weikee
post Oct 10 2013, 07:58 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 9 2013, 11:03 PM)
This is not the original, he changed it 12 yrs ago when i reno my house so direct replace also may not be correct. rclxub.gif

I will test out all how it is all connected how the MCB are shared and post the table here for your further advice. Now at night cannot test, cannot see in the dark. sad.gif

Also, that is why i am asking about the wire, how to identify the wire rating.
*
Not easy to guide you identify wire type. Best go to the electric shop ask sample. Alternative, take out your power point faceplate see the wire, hope your contractor use the correct wire size.
weikee
post Oct 10 2013, 08:27 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
If you share few load into one MCB and use over 15amp load, long run if the 2.5mm cable don't burn it will get harden and trip frequent because cable can be crack.
amberglow
post Oct 10 2013, 10:37 AM

Getting Started
**
Junior Member
103 posts

Joined: Jan 2003
From: PJ


QUOTE(weikee @ Oct 10 2013, 07:58 AM)
Not easy to guide you identify wire type. Best go to the electric shop ask sample. Alternative, take out your power point faceplate see the wire, hope your contractor use the correct wire size.
*
You better get a qualified electrician - make sure he is registered with TNB before you engage. Wire-cable thickness is very important ... if the load more than wire can handle then it will overload which leads to wire becomes heated up which leads to electrical fire.

Each wall power socket should not be more than 13A which means your fuse should be 15A. And depending on how your electrician wired up your sockets previously ... some electricians do short cut ... they put multiple wall socket on one wire example one room you ask 3 sockets ... that may be shared with 1 wire 1 MCB ... thus it is no better than an extension bar ... maximum load combined is only 13A.

Kitchen appliances such fridge, washing machines, microwave, electric stove, etc. usually will require its own dedicated socket and MCB ... that would be around 20A each. This especially true if you use very old appliances. New modern appliances nowadays use a lot smaller amps - so a standard 13A can support.

You better check your appliance power draw requirements and count ... to be safe make sure total amp to 1 wall socket is no more than 13A. If you are overloading ... you have inefficient electric wiring which leads to high power loss which leads to a higher power bill.

So when it comes to electric wiring ... don't play-play ... be penny wise pound foolish.

Hope that helps.

This post has been edited by amberglow: Oct 10 2013, 10:41 AM
TSstevie8
post Oct 10 2013, 10:38 AM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(weikee @ Oct 10 2013, 07:58 AM)
Not easy to guide you identify wire type. Best go to the electric shop ask sample. Alternative, take out your power point faceplate see the wire, hope your contractor use the correct wire size.
*
Can you advise what mm wire is for what amp MCB?
TSstevie8
post Oct 10 2013, 10:56 AM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
Guys,

This is the power table of my house (see attached files).

As you can see from the picture post earlier, there is no more space for MCB, how to add?

Attached Image Attached Image
Xccess
post Oct 10 2013, 01:39 PM

Twinkle lil Stars
*******
Senior Member
2,768 posts

Joined: Feb 2012


Bro, a word of advice, please get the help of a certified electrician. I used to work as a electrician many years ago when I was much younger, even with a certain level of experience, I won't touch the electrical box let alone changing of ELCB and ECB.

Please take note there's live wire in it unless you shut off from the main electrical board outside your unit. Stay safe.
shadowofevil
post Oct 10 2013, 01:44 PM

Regular
******
Senior Member
1,763 posts

Joined: Nov 2004
From: GrAVe YArd


Lighting Load
6-10A (cable use 1.5mm)

Power Load
20A -30A (cable radial or ring circuit)
weikee
post Oct 10 2013, 02:24 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Not many use ring circuit.
TSstevie8
post Oct 10 2013, 03:49 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Xccess @ Oct 10 2013, 01:39 PM)
Bro, a word of advice, please get the help of a certified electrician. I used to work as a electrician many years ago when I was much younger, even with a certain level of experience, I won't touch the electrical box let alone changing of ELCB and ECB.

Please take note there's live wire in it unless you shut off from the main electrical board outside your unit. Stay safe.
*
Thanks for your advise, this thing cannot DIY, too dangerous, evenh though I know got to pull out the big black fuse from outside at the meter. There are just too many wires in the DB, once take out the MCB got to mark which pair in the circuit. And if cannot finish work in one day, whole house got no light. Fridge has to be empty otherwise foods go bad.
TSstevie8
post Oct 10 2013, 03:50 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(shadowofevil @ Oct 10 2013, 01:44 PM)
Lighting Load
6-10A (cable use 1.5mm)

Power Load
20A -30A (cable radial or ring circuit)
*
Thanks....but how this thing look like? What is cable radial or ring circuit?
weikee
post Oct 10 2013, 04:04 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 10 2013, 03:50 PM)
Thanks....but how this thing look like? What is cable radial or ring circuit?
*
You can't see it by visual inspection. Ring circuit is from MCB to socket/power point and back to MCB. This is good design circuit but not common practice here.
TSstevie8
post Oct 10 2013, 07:40 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Sydneguy @ Oct 10 2013, 12:44 AM)
1) The solution to this particular problem is to add more MCB and split some of the socket to the extra MCB.

2) As others have mentioned using 32A MCB with writing only meant for 10, 15 or 20A MCB will lead to fire when there is an overload.

3) fire you electrician and get one that gives good advice.
*
Any electrician real good and qualified one to recommend?
TSstevie8
post Oct 10 2013, 07:44 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(amberglow @ Oct 10 2013, 10:37 AM)
You better get a qualified electrician - make sure he is registered with TNB before you engage.    Wire-cable thickness is very important ... if the load more than wire can handle then it will overload which leads to wire becomes heated up which leads to electrical fire.

Each wall power socket should not be more than 13A which means your fuse should be 15A.  And depending on how your electrician wired up your sockets previously ... some electricians do short cut ... they put multiple wall socket on one wire example one room you ask 3 sockets ... that may be shared with 1 wire 1 MCB ... thus it is no better than an extension bar ... maximum load combined is only 13A.

Kitchen appliances such fridge, washing machines, microwave, electric stove, etc. usually will require its own dedicated socket and MCB ... that would be around 20A each. This especially true if you use very old appliances.  New modern appliances nowadays use a lot smaller amps - so a standard 13A can support. 

You better check your appliance power draw requirements and count ... to be safe make sure total amp to 1 wall socket is no more than 13A.  If you are overloading ... you have inefficient electric wiring which leads to high power loss which leads to a higher power bill.

So when it comes to electric wiring ... don't play-play ... be penny wise pound foolish.

Hope that helps.
*
How man? The existing DB Box is full and I have so many power points and dont know how it was connected if one wire shares many points. rclxub.gif
Sydneguy
post Oct 10 2013, 07:51 PM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


QUOTE(stevie8 @ Oct 10 2013, 07:40 PM)
Any electrician real good and qualified one to recommend?
*
Sorry I don't. I'm also looking for one .
Sydneguy
post Oct 10 2013, 07:54 PM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


QUOTE(stevie8 @ Oct 10 2013, 07:44 PM)
How man? The existing DB Box is full and I have so many power points and dont know how it was connected if one wire shares many points.  rclxub.gif
*
You can get electrician to add an extra sub-board, either next to the existing one or some other place in your house then run 60A or 100A cable from that sub-DB back to your main DB.

But I expect that will cost something like RM1-2k including hardware (RM700-1200).

Cheers.
Xccess
post Oct 10 2013, 08:01 PM

Twinkle lil Stars
*******
Senior Member
2,768 posts

Joined: Feb 2012


QUOTE(stevie8 @ Oct 10 2013, 07:40 PM)
Any electrician real good and qualified one to recommend?
*
Bro, please check your PM.

TSstevie8
post Oct 10 2013, 08:07 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Sydneguy @ Oct 10 2013, 07:54 PM)
You can get electrician to add an extra sub-board, either next to the existing one or some other place in your house then run 60A or 100A cable from that sub-DB back to your main DB.

But I expect that will cost something like RM1-2k including hardware (RM700-1200).

Cheers.
*
Cost is not so much of a problem. The problem is under the existing box below are a row of switches sure got wire running in the wall.

Also, the wires now terminated at the DB box and how to connect to another place without major re-wiring? Even next to it still need to connect and lengthen the wire one by one? rclxub.gif

This time i want to make sure i know what is to be done before getting electrician to do what he wants or easy cincai job.
TSstevie8
post Oct 10 2013, 08:10 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Xccess @ Oct 10 2013, 08:01 PM)
Bro, please check your PM.
*
Thanks. Can show a picture of your DB kah? Just want to know how many MCB you have and how complicated it is.
Xccess
post Oct 10 2013, 08:11 PM

Twinkle lil Stars
*******
Senior Member
2,768 posts

Joined: Feb 2012


QUOTE(stevie8 @ Oct 10 2013, 08:10 PM)
Thanks. Can show a picture of your DB kah? Just want to know how many MCB you have and how complicated it is.
*
Ok wait, I try to take a photo then post it here.

Xccess
post Oct 10 2013, 08:23 PM

Twinkle lil Stars
*******
Senior Member
2,768 posts

Joined: Feb 2012


QUOTE(stevie8 @ Oct 10 2013, 08:10 PM)
Thanks. Can show a picture of your DB kah? Just want to know how many MCB you have and how complicated it is.
*
Here you go.


user posted image
Sydneguy
post Oct 10 2013, 08:37 PM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


QUOTE(stevie8 @ Oct 10 2013, 08:07 PM)
l.

Also, the wires now terminated at the DB box and how to connect to another place without major re-wiring?

*
Yeap, sorry to say it wont be a simple job.

If you have usstairs and downstairs then most of the wires will run from upstairs to downstairs at the same place, somewhere near the DB, most likeley just above it.

Then the easiest solution is to put a sub-BD upstairs near that common location and connect all those wires from upstairs into that DB, then run one big wire downstairs to the main DB. now your upstairs sub-DB should have several spare CB slot, and you will have freed up several CB slot in the downstairs DB. then can add in extra DB as required.

In Australia most of our internal and even most external walls are cavity walls, so its very easy to run extra wires.

Here in Malaysia the wires usually plastered into the brick wall so have to hack the wall to run new wires. If your super lucky the electrician will have placed some conduit in the birck/concrete wall and you can pull a new wire through that without hacking the wall, but from what ive seen that is very very very rare case in Malaysia.

Cheers
TSstevie8
post Oct 10 2013, 08:47 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Xccess @ Oct 10 2013, 08:23 PM)
Here you go.
user posted image
*
Thanks bro.

Look like you got no 32A. Mine many of it and I think the wire cannot take load of 32A. Before it trips the wire burned first.

By the way your RCCB is 0.3A (300mA). Mine is 0.1A more sensitive.
weikee
post Oct 10 2013, 09:01 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 10 2013, 08:07 PM)
Cost is not so much of a problem. The problem is under the existing box below are a row of switches sure got wire running in the wall.

Also, the wires now terminated at the DB box and how to connect to another place without major re-wiring? Even next to it still need to connect and lengthen the wire one by one?  rclxub.gif

This time i want to make sure i know what is to be done before getting electrician to do what he wants or easy cincai job.
*
Cost really depend on the aesthetic, it need to be hack and conceal again. When I renovate my house, I insist minimal looping, and identify every single point that go direct. I have 2 DB Box, one per floor, even separate the ELCB.

My ground floor
user posted image


My first floor
user posted image


TSstevie8
post Oct 10 2013, 09:02 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Sydneguy @ Oct 10 2013, 08:37 PM)
Yeap, sorry to say it wont be a simple job.

If you have usstairs and downstairs then most of the wires will run from upstairs to downstairs at the same place, somewhere near the DB, most likeley just above it.

Then the easiest solution is to put a sub-BD upstairs near that common location and connect all those wires from upstairs into that DB, then run one big wire downstairs to the main DB. now your upstairs sub-DB should have several spare CB slot, and you will have freed up several CB slot in the downstairs DB. then can add in extra DB as required.

In Australia most of our internal and even most external walls are cavity walls, so its very easy to run extra wires.

Here in Malaysia the wires usually plastered into the brick wall so have to hack the wall to run new wires. If your super lucky the electrician will have placed some conduit in the birck/concrete wall and you can pull a new wire through that without hacking the wall, but from what ive seen that is very very very rare case in Malaysia.

Cheers
*
Good idea to have the sub DB upstairs. But I have to find from photos taken last time. Below pic is the massive wires at DB photo taken during reno 12 yrs ago.
Attached Image

This is where the wire from G floor to 1st floor and up to ceiling, i think. Got to go up to ceiling to check this week end.
Attached Image

As you can see no conduit in wall. Conduit only on those above plaster ceiling. So have to drill a hole thru the 1st flr slap down to plaster ceiling for the thick cable
Attached Image
kickent
post Oct 10 2013, 09:10 PM

Casual
***
Junior Member
477 posts

Joined: Jan 2009


http://en.wikipedia.org/wiki/American_wire_gauge
TSstevie8
post Oct 10 2013, 09:11 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
Here is the photo taken from ground floor. The wire from DB far end near door, drilled thru the beam and up to 1st floor. But only for new cable. The old cable not sure how it goes up.
Attached Image

This post has been edited by stevie8: Oct 10 2013, 09:12 PM
Sydneguy
post Oct 10 2013, 09:19 PM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


Just for comparison purposes here is my current DB. Its quite small, but its only for a 3 bedroom 1200sqft Condo with only 4 AC, 3 of which are hardly ever used.

There are 12 CB.

5 pcs 32 A
4 pcs 20A
and
3 pcs 6 A

the RCB is 0.3A

and the Main CB is only 32A.

I once tried to map out which lights and power sockets got to which CB but i gave up after only a few as it didnt make much sense. In particular some CB had both Lights and power socket on the the same CB, which is a big NO-NO is Oz but not sure about the wiring rules here.

My the power sockets for the Kitchen, laundry and common bathroom also also seem to be on one CB, since i have tripped it a few times when I have I had the washing machine, kettle, rice cooker and someone showering at the same time.


Cheers


Attached thumbnail(s)
Attached Image
TSstevie8
post Oct 10 2013, 09:23 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(weikee @ Oct 10 2013, 09:01 PM)
Cost really depend on the aesthetic, it need to be hack and conceal again. When I renovate my house, I insist minimal looping, and identify every single point that go direct. I have 2 DB Box, one per floor, even separate the ELCB.

My ground floor
user posted image
My first floor
user posted image
*
Wow...nice.
TSstevie8
post Oct 10 2013, 09:25 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(kickent @ Oct 10 2013, 09:10 PM)
Can't understand the table. mine showing me which are for 10A, 20A and 32A from the table?
TSstevie8
post Oct 10 2013, 09:30 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Sydneguy @ Oct 10 2013, 09:19 PM)
Just for comparison purposes here is my current DB. Its quite small, but its only for a 3 bedroom 1200sqft Condo with only 4 AC, 3 of which are hardly ever used.

There are 12 CB.

5 pcs 32 A
4 pcs 20A
and
3 pcs 6 A

the RCB is 0.3A

and the Main CB is only 32A.

I once tried to map out which lights and power sockets got to which CB but i gave up after only a few as it didnt make much sense. In particular some CB had both Lights and power socket on the the same CB, which is a big NO-NO is Oz but not sure about the wiring rules here.

My the power sockets for the  Kitchen, laundry and common bathroom also also seem to be on one CB, since i have tripped it a few times when I have I had the washing machine, kettle, rice cooker and someone showering at the same time.
Cheers
*
My original DB also look like this.
weikee
post Oct 10 2013, 09:34 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 10 2013, 09:25 PM)
Can't understand the table. mine showing me which are for 10A, 20A and 32A from the table?
*
It show the cable thickness and its properties. A more layman site http://www.epanorama.net/index.php?index=calc_cable It give you very general guideline if room temperature are 20c, if you have bad quality cable or long run cable the guideline won't apply.

This post has been edited by weikee: Oct 10 2013, 09:35 PM
Sydneguy
post Oct 10 2013, 09:48 PM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


QUOTE(stevie8 @ Oct 10 2013, 09:25 PM)
Can't understand the table. mine showing me which are for 10A, 20A and 32A from the table?
*
Look at the Column called "NEC copper wire ampacity with 60/75/90 °C insulation (A)[7]"

NEC in USA means National Electrical Code which is the rules for wiring etc.

This Column has 3 numbers which correspond respectively to whether the wire has 60 or 75 or 90 Deg C insulation.

In that column find the maximum Amps you need to carry, and then look across to the the Wire Diameter in mm2.

BTW unless you are sure best to always assume your wire is the lowest rated insulation ie 60degC

eg Lets say you want to caryy 32A, there is no 32 A for 60degC, only 30 or 40 A, so select 40A then look across and you will see you need 8.37mm2 wire.

Now 8.37mm2 wire sounds a little bit big to me for 32 A, which I seem to recall (assuming my memory is working correctly) 32A usually needs about 4mm2. Now from the table you can see that 4.17mm2 wire can carry something between 30 and 40 A if it is 90deg C insulated (but like i said always better to oversize wires and be safe than sorry).

BTW I'm an Aerospace, Mechanical and Industrial Engineer, NOT an Electrical Engineer so take the about as friendly advice only. Best to consult an Electrical Engineer or licensed Electrician.

Cheers
TSstevie8
post Oct 10 2013, 10:14 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
Weikee, Sydneguy,

Tq very much. Now I am somewhere to it already.

I am not trying to master. Just want to know if the existing wire is safe and use the right CB for the circuit when I get my electrician to replace and add the CBs. Not just blindly follow what he says. I should have that many CBs as what Weikee has with 2 DBs.

The idea of having 2 DBs is great. I just need to locate where the original developer wires supply to 1st floor. I think it should be somewhere at the ceiling where there is a bunch of wire out from one of a side wall. There will be some hacking but it is ok.
Sydneguy
post Oct 11 2013, 12:49 AM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


rclxms.gif rclxms.gif rclxms.gif rclxms.gif 1 Lowyat forumer problem solved, 23,494,985 to go tongue.gif
TSstevie8
post Oct 11 2013, 10:23 AM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
Just to confirm one more question.

Diagram below refers:
Attached Image

In the radial circuit as circled in red. The circuit is protected by a 20a CB.

Question:

Am I right to say the amperage of the wire(denoted in red) it carries in the radial circuit is the sum of all the 10 power points? If each point consuming 1a, the total amperage of the "red" wire is 10a?

Similarly, The "green colour" wire is the sum of 7,8,9 and 10?
weikee
post Oct 11 2013, 11:14 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Yes, but 10 is way too much. If the circuit break for whatever reason you lost 10 points. And if got flyback say from lighting strik to one equipment you may loose all the connected equipment.

QUOTE(stevie8 @ Oct 11 2013, 10:23 AM)
Just to confirm one more question.

Diagram below refers:
Attached Image

In the radial circuit as circled in red. The circuit is protected by a 20a CB.

Question:

Am I right to say the amperage of the wire(denoted in red) it carries in the radial circuit is the sum of all the 10 power points? If each point consuming 1a, the total amperage of the "red" wire is 10a?

Similarly, The "green colour" wire is the sum of 7,8,9 and 10?
*
TSstevie8
post Oct 11 2013, 12:35 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
One more question comes to mind. Look like never ending...

If I get to locate the bunch of wires run up to the first floor and cut them and fix a new DB at the 1st floor, I then need to run a thick cable from the new DB to the main DB at the ground floor right?

Question:

Instead of pulling a new thick cable (live, neutral and earth), can I twist a few or all of the existing "cut" cables (become a big thick cable) that I cut (for making the new DB) which connect down to the ground floor DB, same twist them together? See drawing below:

Attached Image

This post has been edited by stevie8: Oct 11 2013, 12:37 PM
amberglow
post Oct 11 2013, 12:37 PM

Getting Started
**
Junior Member
103 posts

Joined: Jan 2003
From: PJ


QUOTE(stevie8 @ Oct 11 2013, 10:23 AM)
Just to confirm one more question.

Diagram below refers:
Attached Image

In the radial circuit as circled in red. The circuit is protected by a 20a CB.

Question:

Am I right to say the amperage of the wire(denoted in red) it carries in the radial circuit is the sum of all the 10 power points? If each point consuming 1a, the total amperage of the "red" wire is 10a?

Similarly, The "green colour" wire is the sum of 7,8,9 and 10?
*
Ewwww ... really bad design .. your power sockets are no better than a RM30 extension bar since they all share the same fuse. One blow all blow ... and you have a high chance of overloading unless you are consciously remembering how many devices you are putting on that circuit.
TSstevie8
post Oct 11 2013, 01:21 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(amberglow @ Oct 11 2013, 12:37 PM)
Ewwww ... really bad design .. your power sockets are no better than a RM30 extension bar since they all share the same fuse.  One blow all blow ... and you have a high chance of overloading unless you are consciously remembering how many devices you are putting on that circuit.
*
This is not my house wiring la. This is from wikipedia just use it to illustrating and asking a question.
Sydneguy
post Oct 11 2013, 01:45 PM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


QUOTE(stevie8 @ Oct 11 2013, 12:35 PM)
One more question comes to mind. Look like never ending...

If I get to locate the bunch of wires run up to the first floor and cut them and fix a new DB at the 1st floor, I then need to run a thick cable from the new DB to the main DB at the ground floor right?

Question:

Instead of pulling a new thick cable (live, neutral and earth), can I twist a few or all of the existing "cut" cables (become a big thick cable) that I cut (for making the new DB) which connect down to the ground floor DB, same twist them together? See drawing below:

Attached Image
*
You could but its not really the right way to do it for a few reasons.

1) after cutting the old wires probably be to short by a few inches to go from Main DB to sub-Db. remember you want to cut the upstairs wires from sockets a bit longer so its easy to connect into Sub-DB and you are not trying to stretch wires.

2) joined parallel wires don't really have the same capacity in practice as they do in theory. Also its easy for 1 or 2 wires of a twisted set to come loose from the crew point, then youve got loose wires and reduced capacity and remaining wires are now free to come loose also.

3) It will be very hard to join those several wires into the DB and sub Db.

4) its just plain messy.

5) AFAIK its probably against the wiring rules/codes.

6) the 2-3 mtrs of big wire from sub to main will only cost less than RM50, so its not a bifg cost

the only real reason to do what you suggested is to save $ and time inconvenience on hacking and plaster back, but this is easly out voted by reasons 1-5 above.


Cheers
weikee
post Oct 11 2013, 02:21 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Add on to that; How sure the existing cables not tap to other place? If it was tapped you risk sending live current to unknown place.

QUOTE(Sydneguy @ Oct 11 2013, 01:45 PM)
You could but its not really the right way to do it for a few reasons.

1) after cutting the old wires probably be to short by a few inches to go from Main DB to sub-Db. remember you want to cut the upstairs wires from sockets a bit longer so its easy to connect into Sub-DB and you are not trying to stretch wires.

2) joined parallel wires don't really have the same capacity in practice as they do in theory. Also its easy for 1 or 2 wires of a twisted set to come loose from the crew point, then youve got loose wires and reduced capacity and remaining wires are now free to come loose also.

3) It will be very hard to join those several wires into the DB and sub Db.

4) its just plain messy.

5) AFAIK its probably against the wiring rules/codes.

6) the 2-3 mtrs of big wire from sub to main will only cost less than RM50, so its not a bifg cost

the only real reason to do what you suggested is to save $ and time inconvenience on hacking and plaster back, but this is easly out voted by reasons 1-5 above.
Cheers
*
TSstevie8
post Oct 11 2013, 02:53 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Sydneguy @ Oct 11 2013, 01:45 PM)
You could but its not really the right way to do it for a few reasons.

1) after cutting the old wires probably be to short by a few inches to go from Main DB to sub-Db. remember you want to cut the upstairs wires from sockets a bit longer so its easy to connect into Sub-DB and you are not trying to stretch wires.

2) joined parallel wires don't really have the same capacity in practice as they do in theory. Also its easy for 1 or 2 wires of a twisted set to come loose from the crew point, then youve got loose wires and reduced capacity and remaining wires are now free to come loose also.

3) It will be very hard to join those several wires into the DB and sub Db.

4) its just plain messy.

5) AFAIK its probably against the wiring rules/codes.

6) the 2-3 mtrs of big wire from sub to main will only cost less than RM50, so its not a bifg cost

the only real reason to do what you suggested is to save $ and time inconvenience on hacking and plaster back, but this is easly out voted by reasons 1-5 above.
Cheers
*
Thanks for the input. You got me, "the only real reason to do what you suggested is to save $ and time inconvenience on hacking and plaster back"

Anyway, hacking is unavoidable for the installation of sub DB where I need to hack out the cable long enough to get all of them one by one into the MCBs in the sub DB. The problem is to hack thru the slab and beam. I do not want another hole thru the beam which is at the middle of the house, it only weaken the beam.

I just need to find two 4mm wires each and twist them together which will support 60A, right? Below is the potential load up-stair:

1 x 2 1/2 hp aircond
2 x 1 hp aircond
1 x iron
5 x fans (not on when use aircond)
30 x downlight, wall light and table lamp.
1 x vacuum cleaner (not use when ironing), my wife cannot be doing 2 things at a time
Many power sockets but seldom use other than mentioned above for ironing, vacuuming, also for charging handphone, hair dryer, no water heater (I use solar heater), TV, Audio, PS2 games.

Therefore, one 4mm for 32A could be enough, but 2 x 4mm definitely more than enough. Then need to connect 2 x 4mm wire to one 8mm wire to the sub-DB.

What do you think if I use lead soldering to join the 2 4mm wire together instead of twisting them together for terminating at the sub-DB and the down stair DB? How good is the lead joint conducting electricity compare to bear copper wire?

Cheers
weikee
post Oct 11 2013, 02:57 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 11 2013, 02:53 PM)
Thanks for the input. You got me, "the only real reason to do what you suggested is to save $ and time inconvenience on hacking and plaster back"

Anyway, hacking is unavoidable for the installation of sub DB where I need to hack out the cable long enough to get all of them one by one into the MCBs in the sub DB. The problem is to hack thru the slab and beam. I do not want another hole thru the beam which is at the middle of the house, it only weaken the beam.

I just need to find two 4mm wires each and twist them together which will support 60A, right? Below is the potential load up-stair:

1 x 2 1/2 hp aircond
2 x 1 hp aircond
1 x iron
5 x fans (not on when use aircond)
30 x downlight, wall light and table lamp.
1 x vacuum cleaner (not use when ironing), my wife cannot be doing 2 things at a time
Many power sockets but seldom use other than mentioned above for ironing, vacuuming, also for charging handphone, hair dryer, no water heater (I use solar heater), TV, Audio, PS2 games.

Therefore, one 4mm for 32A could be enough, but 2 x 4mm definitely more than enough. Then need to connect 2 x 4mm wire to one 8mm wire to the sub-DB.

What do you think if I use lead soldering to join the 2 4mm wire together instead of twisting them together for terminating at the sub-DB and the down stair DB? How good is the lead joint conducting electricity compare to bear copper wire?

Cheers
*
You old house wiring come with 4mm wiring too?
TSstevie8
post Oct 11 2013, 03:03 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(weikee @ Oct 11 2013, 02:21 PM)
Add on to that; How sure the existing cables not tap to other place? If it was tapped you risk sending live current to unknown place.
*
hmmm.... thanks, have to be super careful. I think the way to find out is to switch off the MCB how it is linked and double check.
TSstevie8
post Oct 11 2013, 03:05 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(weikee @ Oct 11 2013, 02:57 PM)
You old house wiring come with 4mm wiring too?
*
Not sure, I did not take notice of the old DB before the reno if there was any 32A MCB. But during reno the electrician could have use 4 mm since he put so many 32A MCBs.

This post has been edited by stevie8: Oct 11 2013, 03:06 PM
TSstevie8
post Oct 11 2013, 03:15 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(weikee @ Oct 11 2013, 02:21 PM)
Add on to that; How sure the existing cables not tap to other place? If it was tapped you risk sending live current to unknown place.
*
OK, found it. Of the 32A MCBs, the no. 4,5 and 6 are used only for 1st floor. These could be 4mm wires not shared else where with down stair.
Attached Image
weikee
post Oct 11 2013, 03:48 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 11 2013, 03:05 PM)
Not sure, I did not take notice of the old DB before the reno if there was any 32A MCB.  But during reno the electrician could have use 4 mm since he put so many 32A MCBs.
*
Don't assume, need to confirm. Put 32amp some can put 2.5mm because then amps for starting load only.
Sydneguy
post Oct 11 2013, 04:41 PM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


QUOTE(stevie8 @ Oct 11 2013, 02:53 PM)
Thanks for the input. You got me, "the only real reason to do what you suggested is to save $ and time inconvenience on hacking and plaster back"

Anyway, hacking is unavoidable for the installation of sub DB where I need to hack out the cable long enough to get all of them one by one into the MCBs in the sub DB. The problem is to hack thru the slab and beam. I do not want another hole thru the beam which is at the middle of the house, it only weaken the beam.

I just need to find two 4mm wires each and twist them together which will support 60A, right? Below is the potential load up-stair:

1 x 2 1/2 hp aircond
2 x 1 hp aircond
1 x iron
5 x fans (not on when use aircond)
30 x downlight, wall light and table lamp.
1 x vacuum cleaner (not use when ironing), my wife cannot be doing 2 things at a time
Many power sockets but seldom use other than mentioned above for ironing, vacuuming, also for charging handphone, hair dryer, no water heater (I use solar heater), TV, Audio, PS2 games.

Therefore, one 4mm for 32A could be enough, but 2 x 4mm definitely more than enough. Then need to connect 2 x 4mm wire to one 8mm wire to the sub-DB.

What do you think if I use lead soldering to join the 2 4mm wire together instead of twisting them together for terminating at the sub-DB and the down stair DB? How good is the lead joint conducting electricity compare to bear copper wire?

Cheers
*
Once you pull all the old wires that went upstairs out there will be a big hole in the floor/beam for you to put the new thick wire through , Problem Solved. thumbup.gif
TSstevie8
post Oct 11 2013, 08:40 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Sydneguy @ Oct 11 2013, 04:41 PM)
Once you pull all the old wires that went upstairs out there will be a big hole in the floor/beam for you to put the new thick wire through , Problem Solved.  thumbup.gif
*
1. There are floor tiles at first floor, the hole could have been sealed during tiling.
2. Plaster ceiling at ground ceiling where the cables going thru the beam except that the hole at the beam was not sealed.
3. Then on top of the main DB where the new thick cable coming down from plaster ceiling the wall is concealed with many wires from all over the house, cannot hack but to run externally with plastic casing.

3 obstacles that is why am considering using the existing cables, otherwise, I will not hesitate using one thick cable. Anyway got to consult electrician and plaster ceiling guy and tile rclxub.gif I do not think can find same pattern tile. 12 yrs already.

This post has been edited by stevie8: Oct 11 2013, 08:42 PM
firdaruddin
post May 9 2016, 01:57 PM

Getting Started
**
Junior Member
76 posts

Joined: Nov 2005
From: KL


Hello. I have a situation where a fuse keep kicking back. The pic of the db is attached. The one that always kicking back is the 20A one. So the question is, can I change the fuse directly or i should change the wire first to 4mm?


Current wire size is 1.5mm. I think.


Attached thumbnail(s)
Attached Image
Richard
post May 9 2016, 05:43 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(stevie8 @ Oct 9 2013, 02:02 PM)
Anyone knows how to size MCB of our home?

Got B,C,D type and different Amperage. How and what to choose?

Attached Image Attached Image
*
B, C, D types are for the inrush current.. Domestic uses type B

Ampere rating are for current overload protection of the cable. Size the amps according to the cabl's current carrying capacity..

Scroll to the btm of the page, the link at the btm.. Read it.
Suruhanjaya Tenaga - Guidelines for Electrical Wiring in Residential Building 2008
Richard
post May 9 2016, 05:55 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(firdaruddin @ May 9 2016, 01:57 PM)
Hello. I have a situation where a fuse keep kicking back. The pic of the db is attached.  The one that always kicking back is the 20A one.  So the question is, can I change the fuse directly or i should change the wire first to 4mm?
Current wire size is 1.5mm. I think.
*
Is this a new installation and is it a new mcb?
If yes then its probably this circuit is overloaded causing a thermal trip.. Get a clamp ammeter and cheack the load and compare it to the mcb's rating.. If overloaded then remove part of the load to another circuit (If it's more that one load on the circuit)

If no (meaning it was working well previously) then listen carefully to this particular mcb.. If you hear small crackling sounds before tripping then replace the mcb. The mcb has pitted contacts, that means the contact area has reduced to the point where it itself causes the thermal overload.. The device is faulty..

You only replace wiring if the insulation is damaged and you test with an insulation tester (Meggar).. Hire an electrician for this.. He has the equipment and competency to use it.. You cannot use a multimeter..
Richard
post May 9 2016, 06:07 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Xccess @ Oct 10 2013, 08:23 PM)
Here you go.
user posted image
*
This picture shows a Three phase Distribution board (DB)..

It's protection device ia a 4 pole Residual Current device (the one with the yellow trip button)

QUOTE(stevie8 @ Oct 10 2013, 08:47 PM)
By the way your RCCB is 0.3A (300mA). Mine is 0.1A more sensitive.
*
The RCD is for 3 phases that's 100mA trip per phase..

Whether yours (0.1A) more sensitive depends if you have 3 Phase supply ..

meaning is your RCCB 2P or 4P?

If 2P then i think it is not more sensitive..
firdaruddin
post May 9 2016, 10:33 PM

Getting Started
**
Junior Member
76 posts

Joined: Nov 2005
From: KL


QUOTE(Richard @ May 9 2016, 05:55 PM)
Is this a new installation and is it a new mcb?
If yes then its probably this circuit is overloaded causing a thermal trip.. Get a clamp ammeter and cheack the load and compare it to the mcb's rating.. If overloaded then remove part of the load to another circuit (If it's more that one load on the circuit)

If no (meaning it was working well previously) then listen carefully to this particular mcb.. If you hear small crackling sounds before tripping then replace the mcb. The mcb has pitted contacts, that means the contact area has reduced to the point where it itself causes the thermal overload.. The device is faulty..

You only replace wiring if the insulation is damaged and you test with an insulation tester (Meggar).. Hire an electrician  for this.. He has the equipment and competency to use it.. You cannot use a multimeter..
*
Hi. It was an old thing. It happened whether i switch on my computer or nothing while I'm not switch anything at all. It kicked back like ikut suka dia. So my plan maybe upgrading the 20A fuse by changing it to 32A fuse. Is it possible the problem will still occur after changing the fuse directly? Also that fuse goes to one 3-pin point and then loop for two more 3 pin point outside the room for washing machine use.
fireballs
post May 9 2016, 10:36 PM

10101
*******
Senior Member
5,646 posts

Joined: Mar 2012
QUOTE(firdaruddin @ May 9 2016, 01:57 PM)
Hello. I have a situation where a fuse keep kicking back. The pic of the db is attached.  The one that always kicking back is the 20A one.  So the question is, can I change the fuse directly or i should change the wire first to 4mm?
Current wire size is 1.5mm. I think.
*
get a new one. this time dun buy fanban multi9

fireballs
post May 9 2016, 10:38 PM

10101
*******
Senior Member
5,646 posts

Joined: Mar 2012
QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
Hi. It was an old thing.  It happened whether i switch on my computer or nothing while I'm not switch anything at all. It kicked back like ikut suka dia. So my plan maybe upgrading the 20A fuse by changing it to 32A fuse. Is it possible the problem will still occur after changing the fuse directly?  Also that fuse goes to one 3-pin point and then loop for two more 3 pin point outside the room for washing machine use.
*
the normal washing machine should be fine, as long as you dont use iron and hairdryer all at the same time.
as said, most likely its a busted mcb. just change but change to better brand.
Richard
post May 10 2016, 03:16 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
Hi. It was an old thing.  It happened whether i switch on my computer or nothing while I'm not switch anything at all. It kicked back like ikut suka dia.
*
Firstly, use the correct terms for the components, it helps avoid confusion..

A fuse cannot kick back.. It is a fusible link.. It blows (meaning gets hot, melts thus disconnect) when over rated current flows through..
A miniature circuit breaker (mcb) trips (meaning there's a bimetal contact which trips a spring) when over rated current flows ..
You replace a fuse.. You reset an mcb (only replace if faulty)..


QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
So my plan maybe upgrading the 20A fuse by changing it to 32A fuse. Is it possible the problem will still occur after changing the fuse directly?
*
Yes, it is possible.. This is a forum and I'm just giving my opinion. You need an actual competent person to repair it.. (An electrician)

However the fuse or mcb function is to protect the wire.. It blows/trips before the wire gets hot.. A 1.5mm wire is rated at 23Amps..

QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
Current wire size is 1.5mm. I think.
*
A 32A fuse/mcb cannot protect a 1.5mm wire.. The wire will melt and burn anything combustible close to it..
It might burn down your house.. Pls understand your risk..

Hire an electrician if you don't know what I'm talking about.. It will save you more..

QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
Also that fuse goes to one 3-pin point and then loop for two more 3 pin point outside the room for washing machine use.
*
ok..

Standard domestic wiring regulation requires you use 2.5mm2 or higher size wire for sockets..

When new the metal within the wire is pure .. An older wire oxidizes and its insulation degrades.. It cannot carry rated current and heats up when over current..

Regulation states you must completely rewire after 30 years.. I rewired my house after 20 years.. It's my insurance..

Good luck..

This post has been edited by Richard: May 10 2016, 03:42 AM
firdaruddin
post May 10 2016, 02:12 PM

Getting Started
**
Junior Member
76 posts

Joined: Nov 2005
From: KL


Another question. Is there any way for me to determine which wire go to that particular point etc.? I mean if i want to change the whole box with the fuse everything. So that i can reconnect the wire to the box correctly. 1 seperate fuse for a/c etc.
Richard
post May 10 2016, 10:05 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(firdaruddin @ May 10 2016, 02:12 PM)
Another question. Is there any way for me to determine which wire go to that particular point etc.? I mean if i want to change the whole box with the fuse everything.
*
Yes.. Switch off all your miniature circuit breakers (mcb)..

Standard wiring mcb's all type B's except motor (if nuisance tripping then use type C or D for higher inrush(start) current)
-------------------------------------------------------------------------------------
6A & 10A are lighting mcb's
16A & 20A are socket/aircon/water heater mcb's
32A are cooker/large freezer/3HP & above motor mcb's

- Switch on only one mcb
- Visually check which one has power and record on the mcb
- Switch off
- Repeat next mcb..

QUOTE(firdaruddin @ May 10 2016, 02:12 PM)
So that i can reconnect the wire to the box correctly. 1 seperate fuse for a/c etc.
*
Seriously..? I myself am certified with ST but i get an electrician to do the work.. For me it's a matter of cost and speed.. I can talk the talk but crawl the walk if you get what I mean..

For you I think it will be an additional safety issue.. Wiring a whole house with 20-40 points is not an amateur DIY..
One point is ok.. Not whole house.. you're crazy to think you can do it..

beLIEve
post May 6 2017, 12:38 AM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


I spoke to a friend and it appears that there is more to just the amperage on the MCB vs the amount of current you need to size an MCB. If the amount of current is below the MCB's rating multiplied by the value of its type, there'll no trip. In an overcurrent situation, most likely your electrical/electronic device will get fried (it's gotta be already faulty to draw excessive current) before your wire if you're lucky.

To size it, you'll need to know all the resistance involved (wire, devices, earth loop, inrush current). Not sure how many have the equipment to perform these tests?

Anyway, just to share.

http://www.studyelectrical.com/2014/07/min...tic-curves.html

QUOTE
MCBs are classified according to tripping over range of fault current as follows:

    Type B MCB
    Type C MCB
    Type D MCB


Type B MCB:

This type of MCB trips between 3 and 5 times full load current. Type B devices are mainly used in residential applications or light commercial applications where connected loads are primarily lighting fixtures, domestic appliances with mainly resistive elements. The surge current levels in such cases are relatively low.

Type C MCB:

This type of MCB trips between 5 and 10 times full load current. This is used in commercial or industrial type of applications where there could be chances of higher values of short circuit currents in the circuit. The connected loads are mainly inductive in nature (e.g. induction motors) or fluorescent lighting.

Type D MCB:

This type of MCB trips between 10 and 20 times full load current. These MCBs are use in specialty industrial / commercial uses where current inrush can be very high. Examples include transformers or X-ray machines, large winding motors etc.

All the above three types of MCBs provide tripping protection within one tenth of a second.


http://www.theiet.org/forums/forum/message...&threadid=32143

QUOTE
*Standard ranges of instantaneous tripping:

Type B - Above 3 In up to and including 5 In
Type C - Above 5 In up to and including 10 In
Type D - Above 10 In up to and including 20 In*

To be classed as a BS EN 60898-1 circuit breaker the following tests must be satisfied (you must remember these are tests carried out in a controlled environment):

*Type B

A current equal to 3 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:

- 45 s for rated currents up to and including 32 A,

- 90 s for rated currents above 32 A.

A current equal to 5 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.


Type C

A current equal to 5 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:

- 15 s for rated currents up to and including 32 A,

- 30 s for rated currents above 32 A.

A current equal to 10 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.

Type D

A current equal to 10 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:

- 4 s for rated currents above 10A up to and including 32 A,

- 8 s for rated currents up to an including 10 A and above 32 A.

A current equal to 20 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.*

*Source: BS EN 60898-1:2003+A1:2004 - Circuit Breakers for overcurrent protection for household and similar installations - Part 1: Circuit-breakers for a.c. operation


The reason I'm researching this is because I have a neighbor who had his concealed wire shorted permanently, something I'd rather avoid.

This post has been edited by beLIEve: May 6 2017, 12:40 AM
beLIEve
post May 6 2017, 12:15 PM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


Very detailed explanation : http://www.kevinboone.net/cableselection_web.html
weikee
post May 6 2017, 02:10 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 6 2017, 12:38 AM)
I spoke to a friend and it appears that there is more to just the amperage on the MCB vs the amount of current you need to size an MCB. If the amount of current is below the MCB's rating multiplied by the value of its type, there'll no trip. In an overcurrent situation, most likely your electrical/electronic device will get fried (it's gotta be already faulty to draw excessive current) before your wire if you're lucky.

To size it, you'll need to know all the resistance involved (wire, devices, earth loop, inrush current). Not sure how many have the equipment to perform these tests?

Anyway, just to share.

http://www.studyelectrical.com/2014/07/min...tic-curves.html
http://www.theiet.org/forums/forum/message...&threadid=32143
The reason I'm researching this is because I have a neighbor who had his concealed wire shorted permanently, something I'd rather avoid.
*
To avoid that, any long term high current usages better direct from MCB with 4mm2 cables. And reduce tapping for extra points.
beLIEve
post May 8 2017, 05:08 AM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


wise words, bro weikee. I think that's why the developer gave 4mm2 wires for room aircond despite room airconds are likely 1HP.

My neighbor's house was rented out. No one really knew how that socket was used as he only got back his house recently. It was looped alright. From MCB to 3 sockets. The last point was the one that fried.

I'm installing some new points for my own house. Will be using 4mm2 to minimize the melting problem, regardless of how long I use the current. Price does not differ a lot vs 2.5mm2 when I buy in rolls. The last time I paid for wiring, I was "convinced" that their 1.0mm2 (yes, I read it on the wire several times because I thought I misread it) 3cores is good enough for 2HP aircond. 1 month warranty woh.

BTW, I've read a lot of your useful responses here when I was searching for RCCB. Pleased to meet you, finally. Speaking of RCCB, another neighbor insisted that MCB will trip when there is a current leak when I tipped him about the 10mA RCCB for heater. I guess it would, if the leakage goes beyond the MCB rating x Type.

This post has been edited by beLIEve: May 8 2017, 05:10 AM
weikee
post May 8 2017, 01:57 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 8 2017, 05:08 AM)
wise words, bro weikee. I think that's why the developer gave 4mm2 wires for room aircond despite room airconds are likely 1HP.

My neighbor's house was rented out. No one really knew how that socket was used as he only got back his house recently. It was looped alright. From MCB to 3 sockets. The last point was the one that fried.

I'm installing some new points for my own house. Will be using 4mm2 to minimize the melting problem, regardless of how long I use the current. Price does not differ a lot vs 2.5mm2 when I buy in rolls. The last time I paid for wiring, I was "convinced" that their 1.0mm2 (yes, I read it on the wire several times because I thought I misread it) 3cores is good enough for 2HP aircond. 1 month warranty woh.

BTW, I've read a lot of your useful responses here when I was searching for RCCB. Pleased to meet you, finally. Speaking of RCCB, another neighbor insisted that MCB will trip when there is a current leak when I tipped him about the 10mA RCCB for heater. I guess it would, if the leakage goes beyond the MCB rating x Type.
*
1mm2 should be ban from using as outlet point. Maybe just a single light point is ok.

Wires problem usually won't happen so fast. Maybe only 1-2 years after usages. Unless of course it was intended overload.

ELCB/RCCB will trip only beyond the threshold level, more sensitive will be more expensive. If you have 10mA RCCB, and DB installed with 30mA. In scenario when leaking say is 15mA, the water heater RCCD will trip but not the DB side RCCD.
beLIEve
post May 8 2017, 03:53 PM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


That's why he confidently gave 1 month warranty. I always consult my friend before agreeing to all the deals offered by contractors. When problem occurs, can make money pulling new wires again.

Referring to RCCB, yes, after so much research, that's what I learned. Also read that some will trip at 50% of the value. Didn't drill too much into that.

Let me ask you this, since you're a 高人. Which is better? 10mA RCCB between MCB and water heater, or MCB between RCCB and water heater? My friend recommended the latter, but I went for the former after some research. It's sort of whether I want the MCB to protect RCCB from potential overcurrent damages, or RCCB to protect MCB from leakages. I'm protecting the RCCB because it's much more expensive. He said RCCB will not break, though I wonder what will happen when 100A flows through a 25A RCCB.
weikee
post May 8 2017, 05:06 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 8 2017, 03:53 PM)
That's why he confidently gave 1 month warranty. I always consult my friend before agreeing to all the deals offered by contractors. When problem occurs, can make money pulling new wires again.

Referring to RCCB, yes, after so much research, that's what I learned. Also read that some will trip at 50% of the value. Didn't drill too much into that.

Let me ask you this, since you're a 高人. Which is better? 10mA RCCB between MCB and water heater, or MCB between RCCB and water heater? My friend recommended the latter, but I went for the former after some research. It's sort of whether I want the MCB to protect RCCB from potential overcurrent damages, or RCCB to protect MCB from leakages. I'm protecting the RCCB because it's much more expensive. He said RCCB will not break, though I wonder what will happen when 100A flows through a 25A RCCB.
*
Don't look me so up. I just speak from my general knowledge.

If you plan to do "MCB between RCCB and water heater", unless you can identify the water heater neutral wires at the DB box if can't you will not have a balance current and it will always trip.
Richard
post May 8 2017, 09:51 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(beLIEve @ May 8 2017, 03:53 PM)
That's why he confidently gave 1 month warranty. I always consult my friend before agreeing to all the deals offered by contractors. When problem occurs, can make money pulling new wires again.

Referring to RCCB, yes, after so much research, that's what I learned. Also read that some will trip at 50% of the value. Didn't drill too much into that.

Let me ask you this, since you're a 高人. Which is better? 10mA RCCB between MCB and water heater, or MCB between RCCB and water heater? My friend recommended the latter, but I went for the former after some research. It's sort of whether I want the MCB to protect RCCB from potential overcurrent damages, or RCCB to protect MCB from leakages. I'm protecting the RCCB because it's much more expensive. He said RCCB will not break, though I wonder what will happen when 100A flows through a 25A RCCB.
*
You use a water heater for hot water..

You use a 10mA RCD to protect your life from electrocution from the water heater..

Why would you value a 10mA RCD higher than life?

Edit * Watch this youtube video.. It is good .. https://www.youtube.com/watch?v=A5HuPol99sU

I also find it pretty funny ..

This post has been edited by Richard: May 8 2017, 09:58 PM
beLIEve
post May 8 2017, 11:18 PM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


QUOTE(weikee @ May 8 2017, 05:06 PM)
Don't look me so up. I just speak from my general knowledge.

If you plan to do "MCB between RCCB and water heater", unless you can identify the water heater neutral wires at the DB box if can't you will not have a balance current and it will always trip.
*
I'm very short only. That's why have to look up on you smile.gif

Actually, I thought as long as I add an RCCB, I need to identify the neutral wire no?

My original setup based on my friend's advice :
Live busbar --- wire --- RCCB Live Top --- RCCB Live Bottom --- MCB Bottom --- MCB Top --- Water Heater Live
Water Heater Neutral --- RCCB Neutral Bottom --- RCCB Neutral Top --- Neutral bar

New setup :
Live busbar --- wire --- MCB bottom --- MCB Top --- RCCB Live Top --- RCCB Live Bottom --- Water Heater Live
Water Heater Neutral --- RCCB Neutral Bottom --- RCCB Neutral Top --- Neutral bar

Yes I managed to identify the neutral wire. Small apartment, and developer was generous enough to use a 4mm. Only 2 of these.


QUOTE(Richard @ May 8 2017, 09:51 PM)
Why would you value a 10mA RCD higher than life?
Bro, did you misunderstand my posts? Or you see something wrong with my setup having MCB before RCCB?

Thanks for your responses.
Richard
post May 10 2017, 12:32 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(beLIEve @ May 8 2017, 11:18 PM)
Bro, did you misunderstand my posts? Or you see something wrong with my setup having MCB before RCCB?

Thanks for your responses.
*
I might have actually ... when you typed " I'm protecting the RCCB because it's much more expensive." ..

My mistake..

Your setup is a standard arrangement i.e. The RCCB (or RCD) doing the protection of life, while the MCB protection for the property (cable, RCD & load)..

It's good..


beLIEve
post May 10 2017, 12:42 AM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


thanks bro Richard
beLIEve
post May 10 2017, 03:06 PM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


Back to the original topic.

Anyone here use MCB Type B at home? Seems like everyone is using Type C, but of course, most were probably installed by developers. Forgotten to find out if Pasar Road is selling Type B. The last time I bought, I didn't know the existence of Types B C D, they just gave me a Type C.
Richard
post May 10 2017, 07:52 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(beLIEve @ May 10 2017, 03:06 PM)
Back to the original topic.

Anyone here use MCB Type B at home? Seems like everyone is using Type C, but of course, most were probably installed by developers. Forgotten to find out if Pasar Road is selling Type B. The last time I bought, I didn't know the existence of Types B C D, they just gave me a Type C.
*
I only experience seeing type C in the market..

Physically the difference is nominal (I.e. in name only), as it deals with the breaking capacity of the breaker.. thus the physical characteristics of the spring.. you would need a department like SIRIM to be able to tell the difference..

You and me, we take and accept what is available..

beLIEve
post May 11 2017, 02:26 AM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


hmmmm that's where my concern is. Or probably it's unwarranted.

Type C will only trip at 5x its rated current. If my understanding is correct, there'll be no trips below 5x. On a 20A Type C MCB, it means that 99.9999A can flow through the cable without it tripping. If it heats up the cables long enough, fire or short circuit.

Of course, knowledgeable people know not to overload any particular circuit, but we can't stop anyone from doing so.

This was the reason why my friend said there's no point protecting the RCCB with an MCB. I guess there's no harm trying though smile.gif

QUOTE(Richard @ May 10 2017, 07:52 PM)
You and me, we take and accept what is available..
I don't think I've much choice. Seems like it's our norm in this country to compromise safety for convenience. When I goto shops for 10mA-30mA RCCB, they'll always tell me "don't buy this, always trip". I guess the same applies to MCB, so no Type B for the wicked.
weikee
post May 11 2017, 09:07 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 11 2017, 02:26 AM)
hmmmm that's where my concern is. Or probably it's unwarranted.

Type C will only trip at 5x its rated current. If my understanding is correct, there'll be no trips below 5x. On a 20A Type C MCB, it means that 99.9999A can flow through the cable without it tripping. If it heats up the cables long enough, fire or short circuit.

Of course, knowledgeable people know not to overload any particular circuit, but we can't stop anyone from doing so.

This was the reason why my friend said there's no point protecting the RCCB with an MCB. I guess there's no harm trying though smile.gif
I don't think I've much choice. Seems like it's our norm in this country to compromise safety for convenience. When I goto shops for 10mA-30mA RCCB, they'll always tell me "don't buy this, always trip". I guess the same applies to MCB, so no Type B for the wicked.
*
Some of the rare or hard to find items, i usually pay a bit more and buy at element14, The B curved should be available there

http://my.element14.com/abb/s201mb16/mcb-1...urve/dp/1775068
beLIEve
post May 11 2017, 10:49 AM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


Thanks bro weikee.

Yes, I found it there and my friend is using element14 exactly as you - for rare items. These are made in Europe too smile.gif Costs 8x more though.

http://my.rs-online.com/web/c/automation-c...archTerm=S201b2 seems cheaper than element14. I don't know who will do the customs clearance and not sure if SIRIM approval is needed.

Edit : Ok, my friend say all the clearance will be handled by element14.

This post has been edited by beLIEve: May 11 2017, 12:13 PM
Richard
post May 11 2017, 12:59 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(beLIEve @ May 11 2017, 02:26 AM)
hmmmm that's where my concern is. Or probably it's unwarranted.

Type C will only trip at 5x its rated current. If my understanding is correct, there'll be no trips below 5x. On a 20A Type C MCB, it means that 99.9999A can flow through the cable without it tripping. If it heats up the cables long enough, fire or short circuit.

Of course, knowledgeable people know not to overload any particular circuit, but we can't stop anyone from doing so.

This was the reason why my friend said there's no point protecting the RCCB with an MCB. I guess there's no harm trying though smile.gif
I don't think I've much choice. Seems like it's our norm in this country to compromise safety for convenience. When I goto shops for 10mA-30mA RCCB, they'll always tell me "don't buy this, always trip". I guess the same applies to MCB, so no Type B for the wicked.
*
Correction..

On a 20A Type C MCB, Once there is an overload current meaning more than 20A the breaker will trip .. There's a coil within which pulls in a metal piece (an electromagnet) which trips out the breaker..

Type B, C and D only refers to the inrush current .. produced by inductive lighting and motors.. The 5x is a transient (momentary or short time only) current during the start to enable starting torque(of a motor) or to jump a spark (of lights)..

Once the motor is running or the lamp is lit, the current goes back to rated normal..

A continuous flow of overload current (beyond 20A) will heat up a secondary part of the breaker (a bimetal strip)..

Your friend is misinformed .. A MCB protects against an overload (both magnetic and thermal type), a RCD protects against leakage current (below the rated) but will kill a person..

You need both devices in your DB, one to protect property, the other to protect life.. It is a mandatory (MUST HAVE) requirement..

For the secondary RCD at the water heater I believe it is only recommended not yet enforced by our Suruhanjaya Tenaga..

If you read the news then you know that people have died due to faulty electric water heaters .. 50mA AC Voltage over 5 secs will kill a fully grown 60kG human male..

You can google, read it up or ask any medically trained person.. The symptom is similar to a heart attack with burns at the contact areas..

Edit*

If the device keeps tripping then there is a leakage current, dirty equipment in a high humidity environment is the usual cause...

The dust settles on the live or Neutral wire and when wet will leak to a conductive cover tripping out the RCD..

You need to clean the electrical devices.. Wet dust can conduct electricity..

Edit**

Correction For the secondary 10mA trip RCD at the water heater.. It is a mandatory requirement by Suruhanjaya Tenaga..

This post has been edited by Richard: May 20 2017, 08:43 AM
weikee
post May 11 2017, 02:15 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 11 2017, 10:49 AM)
Thanks bro weikee.

Yes, I found it there and my friend is using element14 exactly as you - for rare items. These are made in Europe too smile.gif Costs 8x more though.

http://my.rs-online.com/web/c/automation-c...archTerm=S201b2 seems cheaper than element14. I don't know who will do the customs clearance and not sure if SIRIM approval is needed.

Edit : Ok, my friend say all the clearance will be handled by element14.
*
Some items selling in element14 is not expensive. I got the velcro tape same price as Ace, and they have stock. 7AH Battery RM 63+ and i can at least sure the quality are better. Raspberry Pi + Camera much cheaper than outside price.
beLIEve
post May 12 2017, 02:33 AM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


QUOTE
A continuous flow of overload current (beyond 20A) will heat up a secondary part of the breaker (a bimetal strip)..

Thanks bro Richard. You just answered my question! I did some further research based on your answer and found out that it's available on Wikipedia. All other sites just explain the magnetic trigger, which is 5x-10x the rating for our Type C. That explains the line curve to the left of the 5x-10x "rectangle".

This also explained what I observed with my neighbor's MCB. When I first reset the MCB that goes to the faulty line, it took a few seconds to trip. Subsequent resets are almost instant. So it's the thermal effect - it hadn't cool down. I disconnected the faulty link which is last in the loop and no more trips. There was already a partially (say, 10%) melted plug when he got back the house, so I think it's beyond dirt. Not within my skill to fix that smile.gif

For the RCD, yes, I've searched and read before, just for reading pleasure. I tumpang my friend to buy the 10mA and 30mA RCCBs when he bought his before all the readings. So my house is fully secured, at least, to what is within my knowledge. I'm still using a stack of Type 2 MCBs from the developers though, need to research how much they differ with Type C. I briefly read the other day, Type 2 is old standard.

My friend got everything right minus the thermal tripping part. He was the one who told me about the 10mA and 30mA RCCB. So yes, it's not enforced yet. By the time it gets enforced, there'll be a shortage in supplies smile.gif

And yes, ventricular fibrillation.

QUOTE
The dust settles on the live or Neutral wire and when wet will leak to a conductive cover tripping out the RCD..

Thanks for the tips. Long story short, my old 100mA used to trip on lightnings while neighbors' houses aren't. Now the new Hager 30mA (I use as main RCCB) survived many lightnings. It tripped once without lightning. At that time, only the fridge and fan is running (2 different circuits). So I think I'll have to clean some wires. I noticed many of my wires have paints on them. Contractors must've painted before they install the sockets. We're the second owner, apartment is 20 years old now.

bro weikee :
Ahhhh ok, thanks for the info. I just briefly browsed that site. Friend told me there are wires better than Mega. So I just searched for the wires, for the sake of knowing, and the MCBs. Both are much more expensive than Pasar Road. I'll check out element14 next time.

This post has been edited by beLIEve: May 12 2017, 02:41 AM
heloooo
post May 19 2017, 10:04 PM

New Member
*
Junior Member
6 posts

Joined: Aug 2010
1 aircond draw 3.91 Amp, and we know 2.5mm cable can safely carry current up to 15Amp, so can i install 2 aircond using same cable?
Cyberbullies
post Jul 1 2018, 08:48 PM

Getting Started
**
Junior Member
121 posts

Joined: Nov 2017
Hi guys, have some questions due to disagreement with my electrician:

1) I asked to put 10mA 63A RCD for water heater + electric water closet + 2 power socket but he said it's better to do 1-to-1, meaning 1 RCD for 1 water heater instead, which does not make sense to me. Is 10mA too sensitive to be practical for what i am planning to use for? If not, i am planning to use only single 10mA RCD for 2 bathrooms lol.

2) He asked me to only use 1 RCD for all the lighting, fans and power sockets for the whole second floor, which i disagree with because it would mean total blackout when it trips.

3) I have asked for 30mA RCD for the lighting, fans and power sockets but he said to use 100mA RCD, which i again disagree with as anything over 30mA would be meaningless as it would greatly increase the fatality rate.

Having said that, i am concerned with nuisance tripping so would like to ask if there is anyone who changed 30mA for the house and 10mA for the water heater and experienced constant nuisance tripping?

4) Is it wise to use 30mA RCD for aircon? Or should i use 100mA or higher? Heard inverter aircon often causes nuisance tripping. But seems like no point when we go over 30mA.

Thanks!


SUSslimey
post Jul 1 2018, 09:39 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(Cyberbullies @ Jul 1 2018, 08:48 PM)
Hi guys, have some questions due to disagreement with my electrician:

1) I asked to put 10mA 63A RCD for water heater + electric water closet + 2 power socket but he said it's better to do 1-to-1, meaning 1 RCD for 1 water heater instead, which does not make sense to me. Is 10mA too sensitive to be practical for what i am planning to use for? If not, i am planning to use only single 10mA RCD for 2 bathrooms lol.

2) He asked me to only use 1 RCD for all the lighting, fans and power sockets for the whole second floor, which i disagree with because it would mean total blackout when it trips.

3) I have asked for 30mA RCD for the lighting, fans and power sockets but he said to use 100mA RCD, which i again disagree with as anything over 30mA would be meaningless as it would greatly increase the fatality rate.

Having said that, i am concerned with nuisance tripping so would like to ask if there is anyone who changed 30mA for the house and 10mA for the water heater and experienced constant nuisance tripping?

4) Is it wise to use 30mA RCD for aircon? Or should i use 100mA or higher? Heard inverter aircon often causes nuisance tripping. But seems like no point when we go over 30mA.

Thanks!
*
1. your electrition is right.
2. that's up to you.
3. if you use 30 you will need more RCD than 2.
don't worry about nuisance tripping for water heater. for house you can get those with high immunity and protected by SPD.
4. same as 3.
SUSslimey
post Jul 1 2018, 09:40 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(heloooo @ May 19 2017, 10:04 PM)
1 aircond draw 3.91 Amp, and we know 2.5mm cable can safely carry current up to 15Amp, so can i install 2 aircond using same cable?
*
technically yes.
also need to take into effect the distance of wires of course.
Richard
post Jul 2 2018, 12:08 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(slimey @ Jul 1 2018, 09:40 PM)
technically yes.
also need to take into effect the distance of wires of course.
*
No. An Aircon compressor motor starts/stops multiple times acting on thermostat sensor

The starting amps will be 6x or higher and will burn out the mcb or connectors contacts. There will be arc damages initially slowly continuosly damaging the contacts and burn.

Any 4 Ampere Aircon compressor motor must have a dedicated circuit protected by a 20A mcb.

Only a single 1hp Aircon to one circuit. No more.
Cyberbullies
post Jul 9 2018, 01:00 AM

Getting Started
**
Junior Member
121 posts

Joined: Nov 2017
QUOTE(slimey @ Jul 1 2018, 09:39 PM)
1. your electrition is right.
2. that's up to you.
3. if you use 30 you will need more RCD than 2.
don't worry about nuisance tripping for water heater. for house you can get those with high immunity and protected by SPD.
4. same as 3.
*
QUOTE(Richard @ Jul 2 2018, 12:08 PM)
No. An Aircon compressor motor starts/stops multiple times acting on thermostat sensor

The starting amps will be 6x or higher and will burn out the mcb or connectors contacts. There will be arc damages initially slowly continuosly damaging the contacts and burn.

Any 4 Ampere Aircon compressor motor must have a dedicated circuit protected by a 20A mcb.

Only a single 1hp Aircon to one circuit. No more.
*
Dear sifus, is it weird that both Hager and Schneider do not have RCCB type A for 10mA or even 10mA RCBO with 20A or 25A rating?

Reason being is that some water heaters come with pump (mine does), so naturally the RCCB has to be type A (protects against pulsating DC current) instead of type AC isn't it?

And then there's the issue of RCBO being 16A, which barely exceeds the max wattage of some water heater. I know water heater does not usually run at full load but i am not willing to buy one to test if it will trip and end up not being able to use it.

Maxguard does produce type A for 10mA RCCB and 10mA 20A for RCBO but mixing with Hager MCB is a no no for me. Plus Hager has better build with better anti-nuisance features.

Also what SPD do you guys recommend? Type 2 that is installed after the main switch? Mine is a single phase DB. For Hager, there is this medium protection, fine protection, with reserve, without reserve and monobloc series, don't even know how to decide lol.

Installing SPD to reduce nuisance tripping during lightning as i will be using majority 30mA for sockets/lighting.

Lastly, is isolator needed and how does one arrange the DB sequence? And should RCCB be installed first before MCB or vice versa? Sockets>RCCB>MCB?

Thanks in advance.

This post has been edited by Cyberbullies: Jul 9 2018, 01:02 AM
FrankieSiow
post Oct 17 2018, 09:40 AM

Getting Started
**
Junior Member
51 posts

Joined: May 2012
Hello, I have read through few threads including this thread, I have some questions on RCCB for water heater. My house is using 3-phase power, and currently I have 2x 4-pole RCCB (100mA & 30mA) installed in my DB. Let's say I want to install additional 10mA RCCB for each water heater that I have, what type of RCCB to be used? 2-pole? How will be the wiring diagram looks nice? Appreciate your kind advise, TIA.
SUSslimey
post Oct 17 2018, 09:58 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(FrankieSiow @ Oct 17 2018, 09:40 AM)
Hello, I have read through few threads including this thread, I have some questions on RCCB for water heater. My house is using 3-phase power, and currently I have 2x 4-pole RCCB (100mA & 30mA) installed in my DB. Let's say I want to install additional 10mA RCCB for each water heater that I have, what type of RCCB to be used? 2-pole? How will be the wiring diagram looks nice? Appreciate your kind advise, TIA.
*
Your water heater runs on single phase right? Then 2 pole it is.

You need to find out which mcb is for the heater currently, and which neutral wire it is using if you plan to install it at the distribution box.

If too much hassle doing that, just install a 4 way distribution box next to the water heater switch with a single rcd, 20amp, 10ma tripping value. Wiring diagram is on the rcd.
FrankieSiow
post Oct 17 2018, 10:24 AM

Getting Started
**
Junior Member
51 posts

Joined: May 2012
QUOTE(slimey @ Oct 17 2018, 09:58 AM)
Your water heater runs on single phase right? Then 2 pole it is.

You need to find out which mcb is for the heater currently, and which neutral wire it is using if you plan to install it at the distribution box.

If too much hassle doing that, just install a 4 way distribution box next to the water heater switch with a single rcd, 20amp, 10ma tripping value. Wiring diagram is on the rcd.
*
Thank you for your slimey prompt response. I understand based on what you explained just now. Could you also enlighten me on questions below?

1) If I have extra space in DB and I choose to install the RCD at DB, will it be less effective compared to RCD nearer to water heater?
2) If I have to install at nearer to water heater, the RCD should be installed before the 20A switch as per sequence below?
(Main RCD (30Amp) - Water Heater MCB- RCD(10Amp)-20A Switch-Water Heater Power Inlet)
3) I found Hager 2 Pole RCD only has 16A and 25A rating with 10mA tripping value, which one should I get for my 20A water heater? (See attached photo)

Cheers! smile.gif

This post has been edited by FrankieSiow: Oct 17 2018, 10:57 AM


Attached thumbnail(s)
Attached Image
SUSslimey
post Oct 17 2018, 01:18 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(FrankieSiow @ Oct 17 2018, 10:24 AM)
Thank you for your slimey prompt response. I understand based on what you explained just now. Could you also enlighten me on questions below?

1) If I have extra space in DB and I choose to install the RCD at DB, will it be less effective compared to RCD nearer to water heater?
2) If I have to install at nearer to water heater, the RCD should be installed before the 20A switch as per sequence below?
    (Main RCD (30Amp) - Water Heater MCB- RCD(10Amp)-20A Switch-Water Heater Power Inlet)
3) I found Hager 2 Pole RCD only has 16A and 25A rating with 10mA tripping value, which one should I get for my 20A water heater? (See attached photo)

Cheers!  smile.gif
*
1. Negligible difference. But if the neutral to the water heater switch is shared with other stuff then it is rather troublesome or inconvenient. Either need to pull new neutral line or if not the rcd trip will cause other stuff shared on the neutral line to trip together.
2. No real difference before or after.
3. Erm....check the wire size going into the water heater. If less than 4mmsq do not use 25a unless it is already protected by a 20a mcb in the distribution board.
16a i think will trip if use full power of water heater.
FrankieSiow
post Oct 17 2018, 01:36 PM

Getting Started
**
Junior Member
51 posts

Joined: May 2012
QUOTE(slimey @ Oct 17 2018, 01:18 PM)
1.  Negligible difference. But if the neutral to the water heater switch is shared with other stuff then it is rather troublesome or inconvenient. Either need to pull new neutral line or if not the rcd trip will cause other stuff shared on the neutral line to trip together.
2. No real difference before or after.
3. Erm....check the wire size going into the water heater. If less than 4mmsq do not use 25a unless it is already protected by a 20a mcb in the distribution board.
16a i think will trip if use full power of water heater.
*
Really thanks for your explanation. I understand the whole concept already. I will discuss this with my electrician on this matter. smile.gif
SUSslimey
post Oct 17 2018, 01:39 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(FrankieSiow @ Oct 17 2018, 01:36 PM)
Really thanks for your explanation. I understand the whole concept already. I will discuss this with my electrician on this matter.  smile.gif
*
To add on. If trip the neutral without tripping the live of the appliance that share the neutral is dangerous.

All the neutral that share it will actually become live which is more dangerous than before.

And since you have 3 phase electric supply , kaboom if different phase mix into neutral line which lost the link to the main neutral link.

This post has been edited by slimey: Oct 17 2018, 01:43 PM
FrankieSiow
post Oct 17 2018, 02:05 PM

Getting Started
**
Junior Member
51 posts

Joined: May 2012
QUOTE(slimey @ Oct 17 2018, 01:39 PM)
To add on. If trip the neutral without tripping the live of the appliance that share the neutral is dangerous.

All the neutral that share it will actually become live which is more dangerous than before.

And since you have 3 phase electric supply , kaboom if different phase mix into neutral line which lost the link to the main neutral link.
*
Duly noted Sir! smile.gif
dv7.sun
post Jan 17 2019, 01:10 PM

New Member
*
Junior Member
7 posts

Joined: Nov 2015
QUOTE(stevie8 @ Oct 9 2013, 10:32 PM)
My house MCB most of it harden already, stuck, so difficult to pull down or push up. My electrician advised me to change all even though some are still good. And he suggested all change to 32A. I have 10, 20 and 32A. I am worry about his advice to change all to 32a and if the cable/wire can take load and what is the danger of doing so.

It is time to get some advice from others like you and be sure and if I can diy or just let him do it. See picture of my DB and the 3 types of MCB.

Attached Image

Attached Image   Attached Image
*
please report to ST about this action from your electrician...

https://aduan.st.gov.my

mcb need calculation before installation... it depends your load and cable size selection... purpose for the mcb is safety... overload and shock... please do not consult the decision if you not confident with your electrician... it might kill you.. safy first

IceBikers
post Jan 17 2019, 01:59 PM

Enthusiast
*****
Senior Member
960 posts

Joined: Jan 2003


32A not suitable for residence, unless for known high power electrical device
20A for aircond (max 2 HP im not sure bout this) / water heater
16A for plug
10A for light n fan
( I may be wrong, but it is close, however c32 really not fit)

32A mayb hardly trip if anything happen.

example using 16A, if the device overload more than 16A, it will trip for safety. but if using 32A, it won;t trip and perhaps situation may gone bad like Device explode or fire.

This post has been edited by IceBikers: Jan 17 2019, 10:26 PM
tlcm5229
post Mar 22 2020, 11:07 PM

Getting Started
**
Junior Member
56 posts

Joined: Jan 2017
Any experience and trustable electrical technician? One of water heater breaker trip? My house in Puchong.
Please PM me if you have any recommendation.
dv7.sun
post Dec 31 2020, 04:50 PM

New Member
*
Junior Member
7 posts

Joined: Nov 2015
QUOTE(weikee @ Oct 9 2013, 10:54 PM)
Your electrician want you to change house is it? All 32Amp, if wires are 1.5mm, use until wires burn the MCB won't trip. Usually they will put 20A for socket, and some will use 32A for a/c and heater, but 20A is good enough because 2.5mm can't supply 32A load for long period, and now a/c don't have such high spike.

Light, use back 6A or 10A.

Best check the old MCB, and do direct replace.
*
please report this technician to https://www.st.gov.my/


https://www.st.gov.my/en/microsites/index/4/8


this technician not follow IEC
Momo33
post Dec 31 2020, 05:03 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(dv7.sun @ Dec 31 2020, 05:50 PM)
please report this technician to https://www.st.gov.my/
https://www.st.gov.my/en/microsites/index/4/8
this technician not follow IEC
*
yes...
i have seen too many electrician screwing up your house with wrong replacement devices and
wrong advise...
just read and follow ST recommendations is best and advise by K experts here ... thumbsup.gif




kirlcheah
post Dec 31 2020, 11:07 PM

Getting Started
**
Junior Member
63 posts

Joined: Apr 2005


QUOTE(beLIEve @ May 11 2017, 02:26 AM)
hmmmm that's where my concern is. Or probably it's unwarranted.

Type C will only trip at 5x its rated current. If my understanding is correct, there'll be no trips below 5x. On a 20A Type C MCB, it means that 99.9999A can flow through the cable without it tripping. If it heats up the cables long enough, fire or short circuit.

Of course, knowledgeable people know not to overload any particular circuit, but we can't stop anyone from doing so.

This was the reason why my friend said there's no point protecting the RCCB with an MCB. I guess there's no harm trying though smile.gif
I don't think I've much choice. Seems like it's our norm in this country to compromise safety for convenience. When I goto shops for 10mA-30mA RCCB, they'll always tell me "don't buy this, always trip". I guess the same applies to MCB, so no Type B for the wicked.
*
When you go to the shop to buy the 10mA to 30mA RCCB, this is designed for water heater. A single jolt of up to 50mA can actually kill us when there's a leakage from the water heater. When the 10mA or 30mA trip, it's designed to check for residual current so that anything over 10mA / 30mA will trip it to save your life.
Hence why only 10mA will be used for heater in case of water heater leakage. Mind you, installing a good RCCB would not save you if your house grounding wire is not good. You must remove the grounding cable from the electrode / grounding rod and test to get less than 10 ohm. This is dictated by ST. Less or equal to zero is the best and this is done for factories. This can be tested with a grounding meter. Please make sure to connect the cable back to grounding rod after opening it. Also, grounding cable must be at least 10mm cable or best is 16mm cable. Why this is needed to be this thick is because the grounding cable will have lower resistance and all voltage when hits your house during a lightning will travel via this cable to the grounding rod to be absorbed by earth. If you have a 1.5mm or 2.5mm or even 4mm, it will not work as good as a 10mm cable as the resistance is high thus the voltage will not use it as the main cable to travel to earth and will flow elsewhere into your house circuit.
A lot of people don't understand and says that this will trip easily is because they do not know what it's designed for. If your house grounding is good and the 10mA RCCB trips, means there's issue with the circuit and require your attention. Either there's a lightning strike or the cable been damaged by mouse etc. You have to test the cables to make sure it's good.
For house, the main RCCB should be at 100mA. Not 300mA. Those electrician who tells you your house need a 300mA, you better ask them to go and fly kite. 100mA is the maximum dictated by ST. Best is 30mA but it will always trip if there's lightning but if you have a 65kV Surge Arrestor installed, you should be alright without any RCCB trip cause the surge arrestor will absorb the voltage from the lightning. 45k is around RM500 plus. 65kV is around RM1000. Go figure. Buy only good MCB or RCCB with Sirim. There's a lot of fakes out there. EPS is low cost range. Buy Hager / Schneider. Hager is around RM8 for a MCB while Schneider is around RM 13 each. More expensive means it's more sensitive. EPS only cost RM4 dollars. I won't put my life in danger by using a MCB costing dollars....

This post has been edited by kirlcheah: Dec 31 2020, 11:09 PM
beLIEve
post Jan 1 2021, 08:44 AM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


QUOTE(kirlcheah @ Dec 31 2020, 11:07 PM)
Best is 30mA but it will always trip if there's lightning but if you have a 65kV Surge Arrestor installed, you should be alright without any RCCB trip cause the surge arrestor will absorb the voltage from the lightning. 45k is around RM500 plus. 65kV is around RM1000. Go figure. Buy only good MCB or RCCB with Sirim. There's a lot of fakes out there. EPS is low cost range. Buy Hager / Schneider. Hager is around RM8 for a MCB while Schneider is around RM 13 each. More expensive means it's more sensitive. EPS only cost RM4 dollars. I won't put my life in danger by using a MCB costing dollars....
*
My Hager 30mA never trip on lightning, without arrestors. Perhaps a good brand makes a difference? Besides, shouldn't an RCCB trip on Amp leak rather than Voltage surge?

Sometimes don't get to choose. Most people rely on contractors.
SUSceo684
post Jan 1 2021, 10:56 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(kirlcheah @ Dec 31 2020, 11:07 PM)
When you go to the shop to buy the 10mA to 30mA RCCB, this is designed for water heater. A single jolt of up to 50mA can actually kill us when there's a leakage from the water heater. When the 10mA or 30mA trip, it's designed to check for residual current so that anything over 10mA / 30mA will trip it to save your life.
Hence why only 10mA will be used for heater in case of water heater leakage. Mind you, installing a good RCCB would not save you if your house grounding wire is not good. You must remove the grounding cable from the electrode / grounding rod and  test to get less than 10 ohm. This is dictated by ST. Less or equal to zero is the best and this is done for factories. This can be tested with a grounding meter. Please make sure to connect the cable back to grounding rod after opening it. Also, grounding cable must be at least 10mm cable or best is 16mm cable. Why this is needed to be this thick is because the grounding cable will have lower resistance and all voltage when hits your house during a lightning will travel via this cable to the grounding rod to be absorbed by earth. If you have a 1.5mm or 2.5mm or even 4mm, it will not work as good as a 10mm cable as the resistance is high thus the voltage will not use it as the main cable to travel to earth and will flow elsewhere into your house circuit.
A lot of people don't understand and says that this will trip easily is because they do not know what it's designed for. If your house grounding is good and the 10mA RCCB trips, means there's issue with the circuit and require your attention. Either there's a lightning strike or the cable been damaged by mouse etc. You have to test the cables to make sure it's good.
For house, the main RCCB should be at 100mA. Not 300mA. Those electrician who tells you your house need a 300mA, you better ask them to go and fly kite. 100mA is the maximum dictated by ST. Best is 30mA but it will always trip if there's lightning but if you have a 65kV Surge Arrestor installed, you should be alright without any RCCB trip cause the surge arrestor will absorb the voltage from the lightning. 45k is around RM500 plus. 65kV is around RM1000. Go figure. Buy only good MCB or RCCB with Sirim. There's a lot of fakes out there. EPS is low cost range. Buy Hager / Schneider. Hager is around RM8 for a MCB while Schneider is around RM 13 each. More expensive means it's more sensitive. EPS only cost RM4 dollars. I won't put my life in danger by using a MCB costing dollars....
*
RCD doesn't need earth to operate. 10A in must have >9.97A out for a 30mA RCD.
ELCB needs earth to operate. This is why it has gone to the dinosaur age because a lousy ground will render ELCB useless.

MCB wise

I don't trust those ciplak brand MCB etc. There are a lot out there. Commonly available top-tier brands in MY are ABB Hager Schneider for around RM8 each (shopee online from electrical supply shop). I've a whole bag of Himel crap that the developer installed in my new apartment and I ripped whole thing out and replaced with metal DB box + top tier internals. Generally when top tier MCB is available for RM8 ea.. there is no point in buying crap for half the price. Most MCB are made in China even from top tier places.

In angmoh countries.. B curve MCB is used typically as the general use MCB (resistive loads such as water heater), C curve is for bigger induction load (special use/motors). Yes there's D curve (extreme heavy use for factory with huge motor).
Here general use is C curve rclxub.gif and I had to "special order" B curve siemens B16 MCB from RS components for my water heater (it being a resistive load doesn't require such high tripping characteristics of C curve.. B curve more than enough) cos its near to impossible to find a B curve MCB here in MY. Everything is C curve rclxub.gif

RCD wise

10mA for WH will not work well with shared neutral. Too much "interference with other circuit neutrals" (assume the faux electrician from previous owner time using shared neutral for WH) there. Whole hse using 30mA so its not leaking improperly. When I connect the WH in DOL (direct online) mode with my own 3 direct cables it works perfectly. For top tier brands some are still made in EU (France/Italy/Bulgaria).

For house use follow the angmoh countries..just use 30mA for whole house main RCD will give complete protection for each and any circuit downstream as 30mA will not kill you.
School requirement is 30mA in case student poke pens or pencils inside the SSO. Above 50mA, a leakage of 100mA or 300mA also doesnt matter, both also end up in coffin.

Attached Image

My personal opinion is that here our ST spec too "outdated for life preservation w.r.t. whole house RCD" as the risk is still the same whether u are using lights (change bulb) or 13A SSO (plug unplug stuff) whereby they use 100mA for lights and 30mA for 13A SSO rclxub.gif seems like they just wanna sell you another piece of RCD rclxub.gif The ST spec for Water Heater requiring 10mA RCD is the only good part. thumbup.gif

30mA RCD does not always trip - only during severe thunderstorm.
I replaced my main RCD last year (2020) with a 2019 made 30mA RCD from ABB (got anti-nuisance trip) - actually the new one (even being 30mA) trips less during thunderstorms than the 1995 era 300mA which is only suitable for commercial/light industry usage.

This post has been edited by ceo684: Jan 1 2021, 11:16 PM
SUSceo684
post Jan 1 2021, 11:04 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(beLIEve @ Jan 1 2021, 08:44 AM)
My Hager 30mA never trip on lightning, without arrestors. Perhaps a good brand makes a difference? Besides, shouldn't an RCCB trip on Amp leak rather than Voltage surge?

Sometimes don't get to choose. Most people rely on contractors.
*
RCD/RCCB is measuring current delta (difference between in and out).
Voltage doesn't cause it to trip. The current IN on live must equal the current OUT up to the specified delta allowed (10mA or 30mA or 100mA or 300mA).
Not good to have >30mA for residential application if you value your life.
100/300mA only for commercial/light industrial use with big motor/heavy machinery.

Voltage wise we're talking about SPD (lightning surge protection) Type2.. where there are ciplak MOV types sold for 20-30 bucks made in china unknown brands to about 2xx for a single phase Hager/Schneider, and about 400-500 for 3ph+N for ABB/Hager/Schneider. It is easier to find the 3P+N type than the single phase 1P+N SPD.
SUSceo684
post Jan 1 2021, 11:19 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(beLIEve @ May 10 2017, 03:06 PM)
Back to the original topic.

Anyone here use MCB Type B at home? Seems like everyone is using Type C, but of course, most were probably installed by developers. Forgotten to find out if Pasar Road is selling Type B. The last time I bought, I didn't know the existence of Types B C D, they just gave me a Type C.
*
Due to the prohibitive cost of purchasing other B curve MCB (from RS) I just use B16 x2 for my WH circuits on Siemens 5SJ series cos they were relatively affordable at 15 bucks each. The rest cost one extra digit per MCB :x
cfc
post Jun 4 2022, 11:24 PM

Casual
***
Junior Member
440 posts

Joined: Apr 2005
QUOTE(ceo684 @ Jan 1 2021, 11:19 PM)
Due to the prohibitive cost of purchasing other B curve MCB (from RS) I just use B16 x2 for my WH circuits on Siemens 5SJ series cos they were relatively affordable at 15 bucks each. The rest cost one extra digit per MCB :x
*
Hi ceo64, mind share where to get the 5sj .. seems Google malaysia search didn't give much result
SUSceo684
post Jun 5 2022, 08:08 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(cfc @ Jun 4 2022, 11:24 PM)
Hi ceo64, mind share where to get the 5sj .. seems Google malaysia search didn't give much result
*
RS component/element14
Or import from SG lah, in SG whole DB box use B curve
cfc
post Jun 5 2022, 09:47 AM

Casual
***
Junior Member
440 posts

Joined: Apr 2005
Thanks ceo684
One question , for old house with old wiring , will it have frequent trip if I use 30mA RCD ? I know will have voltage drop for old wiring but for current , total In=total Out + some minor leakge current right , it should not matter if use 30mA for old house right.

Just check, my old house has really old stuff, don even know what the black color stuff is.
The DB box just have mcb, does not have any rcd, any idea which type (40A,63A) i should buy ?
my intention is to improve the house electrical safety , probably need to have a enclose case for that rccb too
any recommendation
» Click to show Spoiler - click again to hide... «


and also planning to replace the elcb for the WH to mcb + rccb
just buy 3 way DB that fit + 20A MCB + ABB F202 RCCB 25A 10mA will do right
need to make sure technician use 4mm2 cable during installation too ?
» Click to show Spoiler - click again to hide... «


This post has been edited by cfc: Jun 5 2022, 01:08 PM
mushigen
post Apr 11 2023, 11:00 AM

Look at all my stars!!
*******
Senior Member
4,949 posts

Joined: Jul 2010


Apologies for necroing this old but useful thread.

My existing WH is only protected by 18mm-width C20 MCB.

May I know:
1) this 18mm MCB is 1P+N, correct?
2) is this 1P+N mcb safe compared to 2P MCB?
3) if I add RCCB, do I use 1P+N or 2P RCCB?

TQVM
Ichighost
post Apr 12 2023, 11:07 AM

Casual
***
Junior Member
358 posts

Joined: Aug 2008
From: Oxpod



guys help take a look.

red-C10, blue C-20 and bottom most row C-32

C-32 i use for AC, Water Heater and Oven..using 4mm wire for all C-32.

user posted image
SUSceo684
post Apr 13 2023, 12:07 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(Ichighost @ Apr 12 2023, 11:07 AM)
guys help take a look.

red-C10, blue C-20 and bottom most row C-32

C-32 i use for AC, Water Heater and Oven..using 4mm wire for all C-32.

user posted image
*
where is the 10mA RCD for WH?
PowerGadget
post Apr 14 2023, 09:55 AM

Enthusiast
*****
Junior Member
821 posts

Joined: Apr 2012
Hello all the kind souls and sifu, wondering whether anybody could give me good advise accordingly? My double storey house is about 30+ years old and the db is rather due to upgrade I think.

some of the mcb is not able to push it down anymore, the lever stuck at the position ON which is rather dangerous I think. Currently, I am thinking of adding more sockets to three of my rooms. two sockets to each room and total of 6 sockets.

Then, pulling 1 socket for kitchen hood and 2 for general sockets for kitchen usage.

Wondering what are the good steps for me to do as of my situation. I wanted to buy parts myself and ask electrician to do as I worry they might cheap out the part but I am not familiar with electric stuffs.

So I really appreciate any input from any sifus. thanks a lot in advanced.


» Click to show Spoiler - click again to hide... «


SUSceo684
post Apr 24 2023, 12:10 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(PowerGadget @ Apr 14 2023, 09:55 AM)
Hello all the kind souls and sifu, wondering whether anybody could give me good advise accordingly? My double storey house is about 30+ years old and the db is rather due to upgrade I think.

some of the mcb is not able to push it down anymore, the lever stuck at the position ON which is rather dangerous I think. Currently, I am thinking of adding more sockets to three of my rooms. two sockets to each room and total of 6 sockets.

Then, pulling 1 socket for kitchen hood and 2 for general sockets for kitchen usage.

Wondering what are the good steps for me to do as of my situation. I wanted to buy parts myself and ask electrician to do as I worry they might cheap out the part but I am not familiar with electric stuffs.

So I really appreciate any input from any sifus. thanks a lot in advanced.
» Click to show Spoiler - click again to hide... «

*
Mullti9 macam fake breakers sia. Never heard of them. Even google images don’t seem to have mullti9

Plus the RCD 63A 0.01A sensitivity from Hager can't find anything on that P/N CB2642, for the fun of it I contacted Hager to see if they ever made it. I highly suspect it is fake.

For the parts u can buy from Official Store on shopee x
For replacement of existing MCB - U just need to buy 4pcs MCB each i.e.
4x 6A
4x 20A
4x 32A

https://shopee.com.my/ABB-6kA-MCB-SH201-6A-...113.12706623208

For existing RCD [suspect fake part]
1x 2P 63A 30mA
https://shopee.com.my/ABB-RCCB-ELCB-FH202-AC-63-0.03-(30mA)-2-POLE-(2P)-i.403384113.11846935209

Then, pulling 1 socket for kitchen hood and 2 for general sockets for kitchen usage.
--The "suck hot air" hood is only 300W or so at most so not a problem to tap on existing socket "looping"
--If its the "electric cooker top u cook on" this one pull a new line from DB box and add a 20A MCB

This post has been edited by ceo684: Apr 24 2023, 12:53 PM
lcloon
post Apr 25 2023, 09:33 AM

New Member
*
Junior Member
28 posts

Joined: Apr 2005
Hi everyone. I have a strange problem with my water heater MCB. It always trip off, at random timing. Even when the water heater switch is off, that particular MCB will trip off at random time. May I know what is the problem? MCB (15 years old) became too sensitive or faulty? Or maybe wiring problem? I’m staying in a condominium.

This post has been edited by lcloon: Apr 25 2023, 09:34 AM
PowerGadget
post Apr 26 2023, 05:57 PM

Enthusiast
*****
Junior Member
821 posts

Joined: Apr 2012
QUOTE(ceo684 @ Apr 24 2023, 12:10 PM)
Mullti9 macam fake breakers sia. Never heard of them. Even google images don’t seem to have mullti9

Plus the RCD 63A 0.01A sensitivity from Hager can't find anything on that P/N CB2642, for the fun of it I contacted Hager to see if they ever made it. I highly suspect it is fake.

For the parts u can buy from Official Store on shopee x
For replacement of existing MCB - U just need to buy 4pcs MCB each i.e.
4x 6A
4x 20A
4x 32A

https://shopee.com.my/ABB-6kA-MCB-SH201-6A-...113.12706623208

For existing RCD [suspect fake part]
1x 2P 63A 30mA
https://shopee.com.my/ABB-RCCB-ELCB-FH202-AC-63-0.03-(30mA)-2-POLE-(2P)-i.403384113.11846935209

Then, pulling 1 socket for kitchen hood and 2 for general sockets for kitchen usage.
--The "suck hot air" hood is only 300W or so at most so not a problem to tap on existing socket "looping"
--If its the "electric cooker top u cook on" this one pull a new line from DB box and add a 20A MCB
*
Thanks for your help, ceo684! Really appreciate it.

I had called to my local store to inquiry about the parts availability. They came back to me with these price, wondering whether is reasonable as I am located in East Malaysia.

» Click to show Spoiler - click again to hide... «


I also contacted two electricians for this job as I am not confident enough to do it myself.

First Electrician #1

» Click to show Spoiler - click again to hide... «


Second Electrician #2 (ONLY LABOUR FEE, NO MATERIALS INCLUDE)

» Click to show Spoiler - click again to hide... «


Which one would be a better option for me? Anything that I need to be pay more attention?

This post has been edited by PowerGadget: Apr 26 2023, 06:09 PM
Moogle Stiltzkin
post May 5 2025, 04:24 PM

Look at all my stars!!
*******
Senior Member
4,451 posts

Joined: Jan 2003
QUOTE(kirlcheah @ Dec 31 2020, 11:07 PM)
When you go to the shop to buy the 10mA to 30mA RCCB, this is designed for water heater. A single jolt of up to 50mA can actually kill us when there's a leakage from the water heater. When the 10mA or 30mA trip, it's designed to check for residual current so that anything over 10mA / 30mA will trip it to save your life.
Hence why only 10mA will be used for heater in case of water heater leakage. Mind you, installing a good RCCB would not save you if your house grounding wire is not good. You must remove the grounding cable from the electrode / grounding rod and  test to get less than 10 ohm. This is dictated by ST. Less or equal to zero is the best and this is done for factories. This can be tested with a grounding meter. Please make sure to connect the cable back to grounding rod after opening it. Also, grounding cable must be at least 10mm cable or best is 16mm cable. Why this is needed to be this thick is because the grounding cable will have lower resistance and all voltage when hits your house during a lightning will travel via this cable to the grounding rod to be absorbed by earth. If you have a 1.5mm or 2.5mm or even 4mm, it will not work as good as a 10mm cable as the resistance is high thus the voltage will not use it as the main cable to travel to earth and will flow elsewhere into your house circuit.
A lot of people don't understand and says that this will trip easily is because they do not know what it's designed for. If your house grounding is good and the 10mA RCCB trips, means there's issue with the circuit and require your attention. Either there's a lightning strike or the cable been damaged by mouse etc. You have to test the cables to make sure it's good.
For house, the main RCCB should be at 100mA. Not 300mA. Those electrician who tells you your house need a 300mA, you better ask them to go and fly kite. 100mA is the maximum dictated by ST. Best is 30mA but it will always trip if there's lightning but if you have a 65kV Surge Arrestor installed, you should be alright without any RCCB trip cause the surge arrestor will absorb the voltage from the lightning. 45k is around RM500 plus. 65kV is around RM1000. Go figure. Buy only good MCB or RCCB with Sirim. There's a lot of fakes out there. EPS is low cost range. Buy Hager / Schneider. Hager is around RM8 for a MCB while Schneider is around RM 13 each. More expensive means it's more sensitive. EPS only cost RM4 dollars. I won't put my life in danger by using a MCB costing dollars....
*
the electrician who came install EPS. how bad is this brand? hmm.gif i check shopee reviews not much bad reviews or not expert reviews anyway to say why downvoted.

This post has been edited by Moogle Stiltzkin: May 5 2025, 05:53 PM

 