QUOTE(slimey @ Oct 17 2018, 09:58 AM)
Your water heater runs on single phase right? Then 2 pole it is.
You need to find out which mcb is for the heater currently, and which neutral wire it is using if you plan to install it at the distribution box.
If too much hassle doing that, just install a 4 way distribution box next to the water heater switch with a single rcd, 20amp, 10ma tripping value. Wiring diagram is on the rcd.
Thank you for your
slimey prompt response. I understand based on what you explained just now. Could you also enlighten me on questions below?
1) If I have extra space in DB and I choose to install the RCD at DB, will it be less effective compared to RCD nearer to water heater?
2) If I have to install at nearer to water heater, the RCD should be installed before the 20A switch as per sequence below?
(Main RCD (30Amp) - Water Heater MCB- RCD(10Amp)-20A Switch-Water Heater Power Inlet)
3) I found Hager 2 Pole RCD only has 16A and 25A rating with 10mA tripping value, which one should I get for my 20A water heater? (See attached photo)
Cheers!