To size it, you'll need to know all the resistance involved (wire, devices, earth loop, inrush current). Not sure how many have the equipment to perform these tests?
Anyway, just to share.
http://www.studyelectrical.com/2014/07/min...tic-curves.html
QUOTE
MCBs are classified according to tripping over range of fault current as follows:
Type B MCB
Type C MCB
Type D MCB
Type B MCB:
This type of MCB trips between 3 and 5 times full load current. Type B devices are mainly used in residential applications or light commercial applications where connected loads are primarily lighting fixtures, domestic appliances with mainly resistive elements. The surge current levels in such cases are relatively low.
Type C MCB:
This type of MCB trips between 5 and 10 times full load current. This is used in commercial or industrial type of applications where there could be chances of higher values of short circuit currents in the circuit. The connected loads are mainly inductive in nature (e.g. induction motors) or fluorescent lighting.
Type D MCB:
This type of MCB trips between 10 and 20 times full load current. These MCBs are use in specialty industrial / commercial uses where current inrush can be very high. Examples include transformers or X-ray machines, large winding motors etc.
All the above three types of MCBs provide tripping protection within one tenth of a second.
Type B MCB
Type C MCB
Type D MCB
Type B MCB:
This type of MCB trips between 3 and 5 times full load current. Type B devices are mainly used in residential applications or light commercial applications where connected loads are primarily lighting fixtures, domestic appliances with mainly resistive elements. The surge current levels in such cases are relatively low.
Type C MCB:
This type of MCB trips between 5 and 10 times full load current. This is used in commercial or industrial type of applications where there could be chances of higher values of short circuit currents in the circuit. The connected loads are mainly inductive in nature (e.g. induction motors) or fluorescent lighting.
Type D MCB:
This type of MCB trips between 10 and 20 times full load current. These MCBs are use in specialty industrial / commercial uses where current inrush can be very high. Examples include transformers or X-ray machines, large winding motors etc.
All the above three types of MCBs provide tripping protection within one tenth of a second.
http://www.theiet.org/forums/forum/message...&threadid=32143
QUOTE
*Standard ranges of instantaneous tripping:
Type B - Above 3 In up to and including 5 In
Type C - Above 5 In up to and including 10 In
Type D - Above 10 In up to and including 20 In*
To be classed as a BS EN 60898-1 circuit breaker the following tests must be satisfied (you must remember these are tests carried out in a controlled environment):
*Type B
A current equal to 3 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:
- 45 s for rated currents up to and including 32 A,
- 90 s for rated currents above 32 A.
A current equal to 5 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.
Type C
A current equal to 5 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:
- 15 s for rated currents up to and including 32 A,
- 30 s for rated currents above 32 A.
A current equal to 10 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.
Type D
A current equal to 10 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:
- 4 s for rated currents above 10A up to and including 32 A,
- 8 s for rated currents up to an including 10 A and above 32 A.
A current equal to 20 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.*
*Source: BS EN 60898-1:2003+A1:2004 - Circuit Breakers for overcurrent protection for household and similar installations - Part 1: Circuit-breakers for a.c. operation
Type B - Above 3 In up to and including 5 In
Type C - Above 5 In up to and including 10 In
Type D - Above 10 In up to and including 20 In*
To be classed as a BS EN 60898-1 circuit breaker the following tests must be satisfied (you must remember these are tests carried out in a controlled environment):
*Type B
A current equal to 3 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:
- 45 s for rated currents up to and including 32 A,
- 90 s for rated currents above 32 A.
A current equal to 5 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.
Type C
A current equal to 5 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:
- 15 s for rated currents up to and including 32 A,
- 30 s for rated currents above 32 A.
A current equal to 10 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.
Type D
A current equal to 10 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:
- 4 s for rated currents above 10A up to and including 32 A,
- 8 s for rated currents up to an including 10 A and above 32 A.
A current equal to 20 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.*
*Source: BS EN 60898-1:2003+A1:2004 - Circuit Breakers for overcurrent protection for household and similar installations - Part 1: Circuit-breakers for a.c. operation
The reason I'm researching this is because I have a neighbor who had his concealed wire shorted permanently, something I'd rather avoid.