QUOTE(Xploit Machine @ Oct 9 2013, 02:49 PM)
varies on electrical appliances, lights usually fitted with 6 ~ 10A, airconditioner and fridge to 30A ...
*
Common is 6, 10, and 15.

30A make sure you have thick cables minimal 4mm.
weikee
post Oct 9 2013, 06:29 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Actually, why do you post this question?
weikee
post Oct 9 2013, 10:54 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 9 2013, 10:32 PM)
My house MCB most of it harden already, stuck, so difficult to pull down or push up. My electrician advised me to change all even though some are still good. And he suggested all change to 32A. I have 10, 20 and 32A. I am worry about his advice to change all to 32a and if the cable/wire can take load and what is the danger of doing so.

It is time to get some advice from others like you and be sure and if I can diy or just let him do it. See picture of my DB and the 3 types of MCB.

[attachmentid=3668036]

[attachmentid=3668038]  [attachmentid=3668040]
*
Your electrician want you to change house is it? All 32Amp, if wires are 1.5mm, use until wires burn the MCB won't trip. Usually they will put 20A for socket, and some will use 32A for a/c and heater, but 20A is good enough because 2.5mm can't supply 32A load for long period, and now a/c don't have such high spike.

Light, use back 6A or 10A.

Best check the old MCB, and do direct replace.
weikee
post Oct 10 2013, 07:58 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 9 2013, 11:03 PM)
This is not the original, he changed it 12 yrs ago when i reno my house so direct replace also may not be correct. rclxub.gif

I will test out all how it is all connected how the MCB are shared and post the table here for your further advice. Now at night cannot test, cannot see in the dark. sad.gif

Also, that is why i am asking about the wire, how to identify the wire rating.
*
Not easy to guide you identify wire type. Best go to the electric shop ask sample. Alternative, take out your power point faceplate see the wire, hope your contractor use the correct wire size.
weikee
post Oct 10 2013, 08:27 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
If you share few load into one MCB and use over 15amp load, long run if the 2.5mm cable don't burn it will get harden and trip frequent because cable can be crack.
weikee
post Oct 10 2013, 02:24 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Not many use ring circuit.
weikee
post Oct 10 2013, 04:04 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 10 2013, 03:50 PM)
Thanks....but how this thing look like? What is cable radial or ring circuit?
*
You can't see it by visual inspection. Ring circuit is from MCB to socket/power point and back to MCB. This is good design circuit but not common practice here.
weikee
post Oct 10 2013, 09:01 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 10 2013, 08:07 PM)
Cost is not so much of a problem. The problem is under the existing box below are a row of switches sure got wire running in the wall.

Also, the wires now terminated at the DB box and how to connect to another place without major re-wiring? Even next to it still need to connect and lengthen the wire one by one?  rclxub.gif

This time i want to make sure i know what is to be done before getting electrician to do what he wants or easy cincai job.
*
Cost really depend on the aesthetic, it need to be hack and conceal again. When I renovate my house, I insist minimal looping, and identify every single point that go direct. I have 2 DB Box, one per floor, even separate the ELCB.

My ground floor
user posted image


My first floor
user posted image


weikee
post Oct 10 2013, 09:34 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 10 2013, 09:25 PM)
Can't understand the table. mine showing me which are for 10A, 20A and 32A from the table?
*
It show the cable thickness and its properties. A more layman site http://www.epanorama.net/index.php?index=calc_cable It give you very general guideline if room temperature are 20c, if you have bad quality cable or long run cable the guideline won't apply.

This post has been edited by weikee: Oct 10 2013, 09:35 PM
weikee
post Oct 11 2013, 11:14 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Yes, but 10 is way too much. If the circuit break for whatever reason you lost 10 points. And if got flyback say from lighting strik to one equipment you may loose all the connected equipment.

QUOTE(stevie8 @ Oct 11 2013, 10:23 AM)
Just to confirm one more question.

Diagram below refers:
[attachmentid=3670054]

In the radial circuit as circled in red. The circuit is protected by a 20a CB.

Question:

Am I right to say the amperage of the wire(denoted in red) it carries in the radial circuit is the sum of all the 10 power points? If each point consuming 1a, the total amperage of the "red" wire is 10a?

Similarly, The "green colour" wire is the sum of 7,8,9 and 10?
*
weikee
post Oct 11 2013, 02:21 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Add on to that; How sure the existing cables not tap to other place? If it was tapped you risk sending live current to unknown place.

QUOTE(Sydneguy @ Oct 11 2013, 01:45 PM)
You could but its not really the right way to do it for a few reasons.

1) after cutting the old wires probably be to short by a few inches to go from Main DB to sub-Db. remember you want to cut the upstairs wires from sockets a bit longer so its easy to connect into Sub-DB and you are not trying to stretch wires.

2) joined parallel wires don't really have the same capacity in practice as they do in theory. Also its easy for 1 or 2 wires of a twisted set to come loose from the crew point, then youve got loose wires and reduced capacity and remaining wires are now free to come loose also.

3) It will be very hard to join those several wires into the DB and sub Db.

4) its just plain messy.

5) AFAIK its probably against the wiring rules/codes.

6) the 2-3 mtrs of big wire from sub to main will only cost less than RM50, so its not a bifg cost

the only real reason to do what you suggested is to save $ and time inconvenience on hacking and plaster back, but this is easly out voted by reasons 1-5 above.
Cheers
*
weikee
post Oct 11 2013, 02:57 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 11 2013, 02:53 PM)
Thanks for the input. You got me, "the only real reason to do what you suggested is to save $ and time inconvenience on hacking and plaster back"

Anyway, hacking is unavoidable for the installation of sub DB where I need to hack out the cable long enough to get all of them one by one into the MCBs in the sub DB. The problem is to hack thru the slab and beam. I do not want another hole thru the beam which is at the middle of the house, it only weaken the beam.

I just need to find two 4mm wires each and twist them together which will support 60A, right? Below is the potential load up-stair:

1 x 2 1/2 hp aircond
2 x 1 hp aircond
1 x iron
5 x fans (not on when use aircond)
30 x downlight, wall light and table lamp.
1 x vacuum cleaner (not use when ironing), my wife cannot be doing 2 things at a time
Many power sockets but seldom use other than mentioned above for ironing, vacuuming, also for charging handphone, hair dryer, no water heater (I use solar heater), TV, Audio, PS2 games.

Therefore, one 4mm for 32A could be enough, but 2 x 4mm definitely more than enough. Then need to connect 2 x 4mm wire to one 8mm wire to the sub-DB.

What do you think if I use lead soldering to join the 2 4mm wire together instead of twisting them together for terminating at the sub-DB and the down stair DB? How good is the lead joint conducting electricity compare to bear copper wire?

Cheers
*
You old house wiring come with 4mm wiring too?
weikee
post Oct 11 2013, 03:48 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(stevie8 @ Oct 11 2013, 03:05 PM)
Not sure, I did not take notice of the old DB before the reno if there was any 32A MCB.  But during reno the electrician could have use 4 mm since he put so many 32A MCBs.
*
Don't assume, need to confirm. Put 32amp some can put 2.5mm because then amps for starting load only.
weikee
post May 6 2017, 02:10 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 6 2017, 12:38 AM)
I spoke to a friend and it appears that there is more to just the amperage on the MCB vs the amount of current you need to size an MCB. If the amount of current is below the MCB's rating multiplied by the value of its type, there'll no trip. In an overcurrent situation, most likely your electrical/electronic device will get fried (it's gotta be already faulty to draw excessive current) before your wire if you're lucky.

To size it, you'll need to know all the resistance involved (wire, devices, earth loop, inrush current). Not sure how many have the equipment to perform these tests?

Anyway, just to share.

http://www.studyelectrical.com/2014/07/min...tic-curves.html
http://www.theiet.org/forums/forum/message...&threadid=32143
The reason I'm researching this is because I have a neighbor who had his concealed wire shorted permanently, something I'd rather avoid.
*
To avoid that, any long term high current usages better direct from MCB with 4mm2 cables. And reduce tapping for extra points.
weikee
post May 8 2017, 01:57 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 8 2017, 05:08 AM)
wise words, bro weikee. I think that's why the developer gave 4mm2 wires for room aircond despite room airconds are likely 1HP.

My neighbor's house was rented out. No one really knew how that socket was used as he only got back his house recently. It was looped alright. From MCB to 3 sockets. The last point was the one that fried.

I'm installing some new points for my own house. Will be using 4mm2 to minimize the melting problem, regardless of how long I use the current. Price does not differ a lot vs 2.5mm2 when I buy in rolls. The last time I paid for wiring, I was "convinced" that their 1.0mm2 (yes, I read it on the wire several times because I thought I misread it) 3cores is good enough for 2HP aircond. 1 month warranty woh.

BTW, I've read a lot of your useful responses here when I was searching for RCCB. Pleased to meet you, finally. Speaking of RCCB, another neighbor insisted that MCB will trip when there is a current leak when I tipped him about the 10mA RCCB for heater. I guess it would, if the leakage goes beyond the MCB rating x Type.
*
1mm2 should be ban from using as outlet point. Maybe just a single light point is ok.

Wires problem usually won't happen so fast. Maybe only 1-2 years after usages. Unless of course it was intended overload.

ELCB/RCCB will trip only beyond the threshold level, more sensitive will be more expensive. If you have 10mA RCCB, and DB installed with 30mA. In scenario when leaking say is 15mA, the water heater RCCD will trip but not the DB side RCCD.
weikee
post May 8 2017, 05:06 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 8 2017, 03:53 PM)
That's why he confidently gave 1 month warranty. I always consult my friend before agreeing to all the deals offered by contractors. When problem occurs, can make money pulling new wires again.

Referring to RCCB, yes, after so much research, that's what I learned. Also read that some will trip at 50% of the value. Didn't drill too much into that.

Let me ask you this, since you're a 高人. Which is better? 10mA RCCB between MCB and water heater, or MCB between RCCB and water heater? My friend recommended the latter, but I went for the former after some research. It's sort of whether I want the MCB to protect RCCB from potential overcurrent damages, or RCCB to protect MCB from leakages. I'm protecting the RCCB because it's much more expensive. He said RCCB will not break, though I wonder what will happen when 100A flows through a 25A RCCB.
*
Don't look me so up. I just speak from my general knowledge.

If you plan to do "MCB between RCCB and water heater", unless you can identify the water heater neutral wires at the DB box if can't you will not have a balance current and it will always trip.
weikee
post May 11 2017, 09:07 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 11 2017, 02:26 AM)
hmmmm that's where my concern is. Or probably it's unwarranted.

Type C will only trip at 5x its rated current. If my understanding is correct, there'll be no trips below 5x. On a 20A Type C MCB, it means that 99.9999A can flow through the cable without it tripping. If it heats up the cables long enough, fire or short circuit.

Of course, knowledgeable people know not to overload any particular circuit, but we can't stop anyone from doing so.

This was the reason why my friend said there's no point protecting the RCCB with an MCB. I guess there's no harm trying though smile.gif
I don't think I've much choice. Seems like it's our norm in this country to compromise safety for convenience. When I goto shops for 10mA-30mA RCCB, they'll always tell me "don't buy this, always trip". I guess the same applies to MCB, so no Type B for the wicked.
*
Some of the rare or hard to find items, i usually pay a bit more and buy at element14, The B curved should be available there

http://my.element14.com/abb/s201mb16/mcb-1...urve/dp/1775068
weikee
post May 11 2017, 02:15 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 11 2017, 10:49 AM)
Thanks bro weikee.

Yes, I found it there and my friend is using element14 exactly as you - for rare items. These are made in Europe too smile.gif Costs 8x more though.

http://my.rs-online.com/web/c/automation-c...archTerm=S201b2 seems cheaper than element14. I don't know who will do the customs clearance and not sure if SIRIM approval is needed.

Edit : Ok, my friend say all the clearance will be handled by element14.
*
Some items selling in element14 is not expensive. I got the velcro tape same price as Ace, and they have stock. 7AH Battery RM 63+ and i can at least sure the quality are better. Raspberry Pi + Camera much cheaper than outside price.

 

Change to:
| Lo-Fi Version
0.0184sec    0.36    7 queries    GZIP Disabled
Time is now: 25th November 2025 - 07:00 AM