 Home Electrical MCB, How to size Miniature Circuit Breaker

views
     
SUSceo684
post Jan 1 2021, 10:56 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(kirlcheah @ Dec 31 2020, 11:07 PM)
When you go to the shop to buy the 10mA to 30mA RCCB, this is designed for water heater. A single jolt of up to 50mA can actually kill us when there's a leakage from the water heater. When the 10mA or 30mA trip, it's designed to check for residual current so that anything over 10mA / 30mA will trip it to save your life.
Hence why only 10mA will be used for heater in case of water heater leakage. Mind you, installing a good RCCB would not save you if your house grounding wire is not good. You must remove the grounding cable from the electrode / grounding rod and  test to get less than 10 ohm. This is dictated by ST. Less or equal to zero is the best and this is done for factories. This can be tested with a grounding meter. Please make sure to connect the cable back to grounding rod after opening it. Also, grounding cable must be at least 10mm cable or best is 16mm cable. Why this is needed to be this thick is because the grounding cable will have lower resistance and all voltage when hits your house during a lightning will travel via this cable to the grounding rod to be absorbed by earth. If you have a 1.5mm or 2.5mm or even 4mm, it will not work as good as a 10mm cable as the resistance is high thus the voltage will not use it as the main cable to travel to earth and will flow elsewhere into your house circuit.
A lot of people don't understand and says that this will trip easily is because they do not know what it's designed for. If your house grounding is good and the 10mA RCCB trips, means there's issue with the circuit and require your attention. Either there's a lightning strike or the cable been damaged by mouse etc. You have to test the cables to make sure it's good.
For house, the main RCCB should be at 100mA. Not 300mA. Those electrician who tells you your house need a 300mA, you better ask them to go and fly kite. 100mA is the maximum dictated by ST. Best is 30mA but it will always trip if there's lightning but if you have a 65kV Surge Arrestor installed, you should be alright without any RCCB trip cause the surge arrestor will absorb the voltage from the lightning. 45k is around RM500 plus. 65kV is around RM1000. Go figure. Buy only good MCB or RCCB with Sirim. There's a lot of fakes out there. EPS is low cost range. Buy Hager / Schneider. Hager is around RM8 for a MCB while Schneider is around RM 13 each. More expensive means it's more sensitive. EPS only cost RM4 dollars. I won't put my life in danger by using a MCB costing dollars....
*
RCD doesn't need earth to operate. 10A in must have >9.97A out for a 30mA RCD.
ELCB needs earth to operate. This is why it has gone to the dinosaur age because a lousy ground will render ELCB useless.

MCB wise

I don't trust those ciplak brand MCB etc. There are a lot out there. Commonly available top-tier brands in MY are ABB Hager Schneider for around RM8 each (shopee online from electrical supply shop). I've a whole bag of Himel crap that the developer installed in my new apartment and I ripped whole thing out and replaced with metal DB box + top tier internals. Generally when top tier MCB is available for RM8 ea.. there is no point in buying crap for half the price. Most MCB are made in China even from top tier places.

In angmoh countries.. B curve MCB is used typically as the general use MCB (resistive loads such as water heater), C curve is for bigger induction load (special use/motors). Yes there's D curve (extreme heavy use for factory with huge motor).
Here general use is C curve rclxub.gif and I had to "special order" B curve siemens B16 MCB from RS components for my water heater (it being a resistive load doesn't require such high tripping characteristics of C curve.. B curve more than enough) cos its near to impossible to find a B curve MCB here in MY. Everything is C curve rclxub.gif

RCD wise

10mA for WH will not work well with shared neutral. Too much "interference with other circuit neutrals" (assume the faux electrician from previous owner time using shared neutral for WH) there. Whole hse using 30mA so its not leaking improperly. When I connect the WH in DOL (direct online) mode with my own 3 direct cables it works perfectly. For top tier brands some are still made in EU (France/Italy/Bulgaria).

For house use follow the angmoh countries..just use 30mA for whole house main RCD will give complete protection for each and any circuit downstream as 30mA will not kill you.
School requirement is 30mA in case student poke pens or pencils inside the SSO. Above 50mA, a leakage of 100mA or 300mA also doesnt matter, both also end up in coffin.

Attached Image

My personal opinion is that here our ST spec too "outdated for life preservation w.r.t. whole house RCD" as the risk is still the same whether u are using lights (change bulb) or 13A SSO (plug unplug stuff) whereby they use 100mA for lights and 30mA for 13A SSO rclxub.gif seems like they just wanna sell you another piece of RCD rclxub.gif The ST spec for Water Heater requiring 10mA RCD is the only good part. thumbup.gif

30mA RCD does not always trip - only during severe thunderstorm.
I replaced my main RCD last year (2020) with a 2019 made 30mA RCD from ABB (got anti-nuisance trip) - actually the new one (even being 30mA) trips less during thunderstorms than the 1995 era 300mA which is only suitable for commercial/light industry usage.

This post has been edited by ceo684: Jan 1 2021, 11:16 PM
SUSceo684
post Jan 1 2021, 11:04 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(beLIEve @ Jan 1 2021, 08:44 AM)
My Hager 30mA never trip on lightning, without arrestors. Perhaps a good brand makes a difference? Besides, shouldn't an RCCB trip on Amp leak rather than Voltage surge?

Sometimes don't get to choose. Most people rely on contractors.
*
RCD/RCCB is measuring current delta (difference between in and out).
Voltage doesn't cause it to trip. The current IN on live must equal the current OUT up to the specified delta allowed (10mA or 30mA or 100mA or 300mA).
Not good to have >30mA for residential application if you value your life.
100/300mA only for commercial/light industrial use with big motor/heavy machinery.

Voltage wise we're talking about SPD (lightning surge protection) Type2.. where there are ciplak MOV types sold for 20-30 bucks made in china unknown brands to about 2xx for a single phase Hager/Schneider, and about 400-500 for 3ph+N for ABB/Hager/Schneider. It is easier to find the 3P+N type than the single phase 1P+N SPD.
SUSceo684
post Jan 1 2021, 11:19 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(beLIEve @ May 10 2017, 03:06 PM)
Back to the original topic.

Anyone here use MCB Type B at home? Seems like everyone is using Type C, but of course, most were probably installed by developers. Forgotten to find out if Pasar Road is selling Type B. The last time I bought, I didn't know the existence of Types B C D, they just gave me a Type C.
*
Due to the prohibitive cost of purchasing other B curve MCB (from RS) I just use B16 x2 for my WH circuits on Siemens 5SJ series cos they were relatively affordable at 15 bucks each. The rest cost one extra digit per MCB :x
SUSceo684
post Jun 5 2022, 08:08 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(cfc @ Jun 4 2022, 11:24 PM)
Hi ceo64, mind share where to get the 5sj .. seems Google malaysia search didn't give much result
*
RS component/element14
Or import from SG lah, in SG whole DB box use B curve
SUSceo684
post Apr 13 2023, 12:07 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(Ichighost @ Apr 12 2023, 11:07 AM)
guys help take a look.

red-C10, blue C-20 and bottom most row C-32

C-32 i use for AC, Water Heater and Oven..using 4mm wire for all C-32.

user posted image
*
where is the 10mA RCD for WH?
SUSceo684
post Apr 24 2023, 12:10 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(PowerGadget @ Apr 14 2023, 09:55 AM)
Hello all the kind souls and sifu, wondering whether anybody could give me good advise accordingly? My double storey house is about 30+ years old and the db is rather due to upgrade I think.

some of the mcb is not able to push it down anymore, the lever stuck at the position ON which is rather dangerous I think. Currently, I am thinking of adding more sockets to three of my rooms. two sockets to each room and total of 6 sockets.

Then, pulling 1 socket for kitchen hood and 2 for general sockets for kitchen usage.

Wondering what are the good steps for me to do as of my situation. I wanted to buy parts myself and ask electrician to do as I worry they might cheap out the part but I am not familiar with electric stuffs.

So I really appreciate any input from any sifus. thanks a lot in advanced.
» Click to show Spoiler - click again to hide... «

*
Mullti9 macam fake breakers sia. Never heard of them. Even google images don’t seem to have mullti9

Plus the RCD 63A 0.01A sensitivity from Hager can't find anything on that P/N CB2642, for the fun of it I contacted Hager to see if they ever made it. I highly suspect it is fake.

For the parts u can buy from Official Store on shopee x
For replacement of existing MCB - U just need to buy 4pcs MCB each i.e.
4x 6A
4x 20A
4x 32A

https://shopee.com.my/ABB-6kA-MCB-SH201-6A-...113.12706623208

For existing RCD [suspect fake part]
1x 2P 63A 30mA
https://shopee.com.my/ABB-RCCB-ELCB-FH202-AC-63-0.03-(30mA)-2-POLE-(2P)-i.403384113.11846935209

Then, pulling 1 socket for kitchen hood and 2 for general sockets for kitchen usage.
--The "suck hot air" hood is only 300W or so at most so not a problem to tap on existing socket "looping"
--If its the "electric cooker top u cook on" this one pull a new line from DB box and add a 20A MCB

This post has been edited by ceo684: Apr 24 2023, 12:53 PM

 