QUOTE(paskal @ Jul 24 2018, 07:39 AM)
thanks for the suggestion.
but requires the use of multiple tanks. prefer to reduce the number of tanks that i have exposed and can be seen.
Ok.but requires the use of multiple tanks. prefer to reduce the number of tanks that i have exposed and can be seen.
Anyway I already design the electric logic. Just post here.

For pump run,
1) Pressure switch high (PS) --> Pump off. (Ball valve top tank close)
2) Pressure switch low --> Pump on (Ball valve top tank open)
3) Floating Swicth high (FS) --> Pump on (Receiving tank water level high)
4) Floating Switch low --> Pump off (Receiving tank water level low)
Logic,
1) If PS high and FS high --> Pump off
2) If PS low and FS low --> Pump off
3) If PS high and FS low --> Pump off
4) If PS low and FS high --> Pump on
1) Entire system run in auto with 2 switch to detect water pressure and level. All switch at the pump side and receiving tank. No switch or any electrical ontop ceiling tank for easy maintenance and problem solving. Pump run in interval depend on water refill time and margin level set for the floating switch.
2) Indicator light for full, low level and pump error can be wired to indoor if require.
3) Timer (T) is to delay in sec for stabilize switch signal receiving. Timer (T1) is to delay in 10 over sec for flow detect error. (Incase the pump priming). Both can be adjustable timing.
4) Overload relay (TR) is to protect the motor pump incase run dry and hot. It is self reset.
5) Magnetic Contactor (MC) is for pump.
6) Last minute add on the Manual Over Ride Switch. For maintenance and priming of water pump.
The electrical logic are not perfect as it lack on safety prevention. It can be add in and modify.