QUOTE(clickNsnap @ Apr 5 2019, 07:55 PM)
I think my house's wires are connected to the DB with ELCB and attached to one earth rod, the rod is about 3-4 meters from the DB

Follow that wire from DB to electrode. For example, if it goes up over a foundation and down to an earthing electrode, then protection is compromised. It is unnecessary too long. It has sharp bends over the foundation. And it is best routed away from other non-grounding wires.

Better would also put another electrode maybe somewhere before the original one. Since those are cheap and it would expand and make more conductive that earth ground.

Whether that is necessary is a function of neighborhood history. For example, a transient typically happens once every seven years. Ten or twenty years of neighborhood history would better quantify risk.

Even the ELCB must be protected. Better is to connect an incoming transient to earth so that it does not go through the ELCB. An electrician can better determine what local codes also require.
ozak
post Apr 6 2019, 02:36 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(clickNsnap @ Apr 5 2019, 01:56 PM)
Thanks Ozak.

My house installed grounding rod...about 10-12 feet below the ground, it was near the DB area in my last renovation in 2015. But not sure how good is the grounding reading? How can we check ourself?

I received a quote to install a SPD (class 1) and grounding check at about RM1k, SPD (class 2) + groundimg check at around RM500.

I wish I can do DIY like you...cost saving smile.gif
*
Every new house has a ground rod which is a must state in the country electrical rule.

What we do is add an additional ground rod around the house to get fully (or more) protect. An advantage if the developer doesn't do a good job on the ground rod.

I see a very poor job in my house ground rod when I get the house. They just wrap the copper wire around the steel rebar which is not a proper grounding rod. And the wire is 4mm size which is not a proper size.

If your house ground is landfill, the deep might not be enough. It has a high resistance. Plung as deep as possible. The contractor has the earth meter to check the proper grounding. And not in the rainy day to test. Dry earth have higher resistance.

I don't have the equipment to check. Costly. What I can do and check is the resistance wire to the rod by multimeter. Makesure low enough ohm. And a min of 6mm wire size. Rod deep as possible and connection. I solder weld the wire to the rod. The only way to confirm my grounding DIY done a good job is by the 2pcs Belkin surge protector Led light. Now it always light up to tell me the earthing is good.

That RCCB I mention above have a nuisance trip prevention which causes by lightning. It will not easily trip by lightning even it has a sensitivity of 100mA.

SPD doesn't function at all (or limited) without the shortest earth wire to the grounding rod. It has a limited radius length of protection. I forget the wire limited length. Something like 10m-20m. Any wire that longer than this range will require another SPD and nearer earth wire to another grounding rod to get protected.

SPD job is to get the lightning energy (surge voltage) as fast as possible to the grounding rod. If the surge is from the Live and neutral wire. (From TNB if you put in the class 1 SPD). MCB, RCCB or fuse in the DB box don't have the earth wire connection. So if the lightning surge coming from TNB, where will it go to unable it travel to the ground? It have to go through your equipment which have earthing protection. And from your equipment earthing body, travel to the earth wire and last to the ground rod. Which might already damage the equipment.

So don't complain if you put a bunch of SPD and cannot protect. Grounding is still important.
ozak
post Apr 6 2019, 03:01 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(westom @ Apr 5 2019, 08:58 PM)
Anyone who understands what Ben Franklin did can understand what works.  The electric current goes from a cloud (ie 3 kilometers up) to earth borne charges (ie 4 kilometers distant).  Why is that complicated?  Either that electric current makes that 7 kilometer connection inside a building.  Or it makes the same connection outside via that earth ground rod.  It was always that layman simple - as first explained in primary school science.

Now, how good is that connection.  If lightning wants to use the building, then a lightning rod connects it to earth on a path that remains outside the structure.  No damage to a structure.

If lightning wants to use appliances inside a building, then a 'whole house' protector connects it to earth on a path that remains outside the structure.  No damage to appliances.  Why is that so hard?

If a protector's earth ground is not single point earth ground, then one has invited lightning to be inside - destructively via appliances.  Multiple earth grounds (ie plung another grounding rod at the garden side) makes appliance damage likely.  A surge, incoming on AC utility wires will use the other ground rod to connect to distant earthborne charges.  That connection will be destructively through appliances.

No protector does protection.  Without a good grounding in earth, the device will not work; will not be effective.  Because no protector does protection.  This is very hard for people educated by advertising.  A plug-in protector does not have that low impedance (ie less than 3 meter) connection to earth.  So it does significantly less or no effective protection.  And can even make appliance damage easier.  A protector must connect low impedance (ie hardwire has no sharp bends) to single point earth ground.  To the one and only earth ground electrode that all incoming utility cables connect to.

If any incoming utility cable does not first connect to that same earth ground (ie directly or via a protector), then appliance protection is compromised.

Lightning rods never make lightning strikes more likely.  That has always been an urban myth promoted by scammers who promote useless products such as ESE devices.  Lightning rods are always implemented everywhere that lightning damage cannot harm a building. That direct strike is going to happen with or without that lightning rod.  A building owner decides to let it strike the building or to connect to earth harmlessly via a lightning rod.    Only ESE scams and other outright lies deny what lightning rods have done successfully for over 250 years.  Connect the inevitable direct lightning strike to earthborne charges on a path that is not destructive.

If any of this is complex, then 1) it is new, and 2) one has not yet read it at least three times.  Even a genius never understand something new until after, at least, three rereads.  It may take more rereads if one was educated by lies from plug-in protectors, ESE manufacturers, advertising, wild speculation, or hearsay.

Why do we teach what Ben Franklin demonstrated in primary school science?  Concepts of lightning protection have alwaus been that simple.  However, if educated by lies (ie plug-in protectors), then comprehension is harder.  Unlearning those lies (from plug-in protectors or ESE manufacturers) makes learning challenging.

Protection is always about the path a current will take from cloud to earthborne charges.  Only a human makes that decision - to either have damage or to connect that current on a path that causes no damage.  We know this for both lightning rods and for protectors.  Both are only as effective as its earth ground electrode.  Facilities that cannot have damage routinely earth hardwire connections or protectors on a low impedance (ie hardwire must not be inside metallic conduit) path to single point earth ground.  Anything that does not connect that transient low impedance (ie less than 3 meters) to single point earth ground will never answer the relevant question.  Where do hundreds of thousands of joules harmlessly dissipate?  It is only hard when one has been scammed by advertising and myths that promote scams (ie plug-in protectors).

Wall 'power point' safety ground is not, cannot be, and never will be earth ground.  Difficult for many to grasp.  That wall receptacle safety ground is not and will never be an earth ground.  Better is even more electrodes at the same common point.  Protectors must have a low impedance (ie less than 3 meter) connection to single point earth ground.  Otherwise a protector does nothing useful.
*
Lightning strike your house is very very rare. But install the rod ontop the house is increase the percentage. Our house here is not a big house. And all the wire is conceal in the wall. If the rod it not enough to take the strong lightning, it will travel all over the house wiring.

If want to install the lightning rod, install a safe distance away from the house. It will like the rod than the house if it prefer to strike.

I have see this problem from a developer container office before. Thing still fried even the rod ontop take the lightning surge to the ground.

My nearer housing area high ground which is all is a banglo house have a very high chance for strike. They place few lightning pole around the area. Not ontop the house roof.
Richard
post Apr 6 2019, 03:54 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(ozak @ Apr 6 2019, 03:01 PM)
Lightning strike your house is very very rare. But install the rod ontop the house is increase the percentage. Our house here is not a big house. And all the wire is conceal in the wall. If the rod it not enough to take the strong lightning, it will travel all over the house wiring.

*
The conventional design for a building lightning protection system is a rolling sphere approach with Franklin rods. The lightning rods at the highest points of the structure connection via 25x3mm2 copper tape straight down the structure to an 16mm dia min earth copper rod to an earth impedance of below 50 Ohm.
Sometimes your electrical supplier can advise you as these are standard JKR building design.

The minimum earth conductor is 10mm2 for a 40 Amp main incoming and 16mm2 for 63Amp mains. For residential design.

You can refer to the attached guidelines or to Malaysian Building By-Law 1984 for confirmation as for me this all was a long time ago.

Hopefully I've uploaded the right attachement but note the Bahasa Malaysia version is the latest and my copy is an old code but should still be applicable.

Best wishes.

This post has been edited by Richard: Apr 6 2019, 04:48 PM


Attached File(s)
Attached File  guidelines_for_electrical_wiring_in_residential_buildings_.pdf ( 427.2k ) Number of downloads: 63
ozak
post Apr 6 2019, 04:11 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(Richard @ Apr 6 2019, 03:54 PM)
The conventional design for a building lightning protection system is a rolling sphere approach with Franklin rods. The lightning rods at the highest points of the structure connection via 25x3mm2 copper tape straight down the structure to an 16mm dia min earth copper rod to an earth impedance of below 10 Ohm.
Sometimes your electrical supplier can advise you as these are standard JKR building design.

The minimum earth conductor is 10mm2 for a 40 Amp main incoming and 16mm2 for 63Amp mains. For residential design.

You can refer to the attached guidelines or to Malaysian Building By-Law 1988 for confirmation as  for me this all was a long time ago.

Hopefully I've uploaded the right attachement but note the Bahasa Malaysia version is the latest and my copy is an old code but should still be applicable.

Best wishes.
*
Thanks Richard.

What we want to know is, it is advisable to install the lightning rod ontop of your house roof? Or better away from the house.

A 10mm size earth wire to the grounding rod you mean ? I think many developer failed to do that.
Richard
post Apr 6 2019, 04:29 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(ozak @ Apr 6 2019, 04:11 PM)
Thanks Richard.

What we want to know is, it is advisable to install the lightning rod ontop of your house roof?  Or better away from the house.

A 10mm size earth wire to the grounding rod you mean ? I think many developer failed to do that.
*
Yes, at the highest point and usually the TV and Radio antenna s are directly grounded. You will notice the tape around any government high structures or poles

Lightning protection is via copper tape is 25mnX3mm not 10mm2. The larger size to cater for lightning strike

DB home earthing can be a minimum 10mm2 pvc green wire
The sizing is calculated for the short circuit current
It's an estimate actually

Yes many housing development do not bother as there isn't too many people aware of this code and how to check the DB earth's impedance.

Maybe it's all old school.

Nice to see brother Westom still around. Hahaha

This post has been edited by Richard: Apr 6 2019, 04:42 PM
ozak
post Apr 6 2019, 06:10 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(Richard @ Apr 6 2019, 04:29 PM)
Yes, at the highest point and usually the TV and Radio antenna s are directly grounded. You will notice the tape around any government high structures or poles

Lightning protection is via copper tape is 25mnX3mm not 10mm2. The larger size to cater for lightning strike

DB home earthing can be a minimum 10mm2 pvc green wire
The sizing is calculated for the short circuit current
It's an estimate actually 

Yes many housing development do not bother as there isn't too many people aware of this code and how to check the DB earth's impedance.

Maybe it's all old school.

Nice to see brother Westom still around. Hahaha
*
Yup. My parent apartment outside end lot wall have this copper tape running down the building. With a pvc pipe cover at the ground floor wall.

Still fried many equipment during storm.
Richard
post Apr 6 2019, 06:40 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(ozak @ Apr 6 2019, 06:10 PM)
Yup. My parent apartment outside end lot wall have this copper tape running down the building. With a pvc pipe cover at the ground floor wall.

Still fried many equipment during storm.
*
Conventional wisdom is to install an SPD (per DB rated kA or higher) before the DB to dissipate to mass of earth the lightning surge current. However I'm no expert so get a second opinion if you can.

The home DB's earth pit impedance must be as low as possible to maintain shortest path to earth mass. For landed properties only.

I would suspect your parents building earth pits are too high impedance thus the lightning surge randomly hit so many equipment

I would suggest you get a certified electrical contractor to check the structure electrical earthing pit (preferably 10 Ohm or better) system.

Edit* Anyway here's an easy way to check whether your home has good earthing.

Use your multimeter to measure the Voltage between Phase/Earth, if you get the same(or about 5V diff) voltage as between Phase/Neutral then you have good earthing. Fluctuates according to current weather/ground conditions.

Otherwise have your earthing checked by a certified electrician
If only you continually experience damaged equipment due to lightning strikes.
My house earthing is bad (I've checked) but no lightning damaged so I don't bother.

This post has been edited by Richard: Apr 7 2019, 06:47 AM
westom
post Apr 6 2019, 09:13 PM

Getting Started
**
Junior Member
228 posts

Joined: Mar 2009
QUOTE(ozak @ Apr 6 2019, 12:11 PM)
What we want to know is, it is advisable to install the lightning rod ontop of your house roof?  Or better away from the house.
A FL house suffered repeat lightning strikes to one wall. So they installed lightning rods. And suffered another strike to that wall.

Lightning is a connection from cloud to distant earthborne charges. That wall contained bathroom (plumbing) pipes that connected to deeper limestone. Lightning rods were connected to 2.4 meter electrodes only in sand. An inferior connection.

Solution. Longer electrodes were driven into that deeper limestone. That lightning rod made a better connection to those distant earthborne charges. That bathroom wall suffered no more strikes.


For protection of appliances or for protection of a structure. It is always defined and about the connection to and quality of earth ground.

BTW, many only use specuation to assume lightning rods with sharp points are better. Research was clear. Blunt rods are more effective than pointed ones.

RoyalGaston
post Apr 8 2019, 07:38 AM

New Member
*
Newbie
17 posts

Joined: Jan 2019
Too much technical terms for an idiot layman like me. Not sure if this is still LYN or what.

Anyway;

1. Check grounding first (cost +/- RM500)
2. Solve your grounding issue if any. (Don’t know the cost)
3. Install SPD if the grounding is OK for secondary protection. (cost +/- RM500)

That’s all my brain could take.
Hopefully this is correct.
westom
post Apr 8 2019, 08:06 AM

Getting Started
**
Junior Member
228 posts

Joined: Mar 2009
QUOTE(RoyalGaston @ Apr 8 2019, 03:38 AM)
1. Check grounding first (cost +/- RM500)
2. Solve your grounding issue if any. (Don’t know the cost)
Which ground? That was a major point. Motherboard ground, floating ground, mains ground, receptacle safety ground, chassis ground, virtual ground, analog ground, or static electric ground beneath shoes? All are different.

A relevant ground has at least two words - earth ground. All incoming wires must make a low impedance (ie less than 3 meter) connection to that one and only ground. Why is that hard? (A question that expects an answer because I just do not get it.) A homeowner is responsible for inspecting and maintaining that ground. Just another reason why that ground should not be complex ... if you are the homeowner.

Apparently this is all new. So it will not begin to make sense without at least three rereads. It really is quite simple. How does that current connect to earthborne charges maybe 4 kilometers away without going through any appliance or the structure?

clickNsnap
post Apr 8 2019, 05:22 PM

On my way
****
Junior Member
540 posts

Joined: Jun 2006


QUOTE(westom @ Apr 6 2019, 09:13 AM)
Follow that wire from DB to electrode.  For example, if it goes up over a foundation and down to an earthing electrode, then protection is compromised.  It is unnecessary too long.  It has sharp bends over the foundation.  And it is best routed away from other non-grounding wires.

Better would also put another electrode maybe somewhere before the original one.  Since those are cheap and it would expand and make more conductive that earth ground.

Whether that is necessary is a function of neighborhood history.  For example, a transient typically happens once every seven years.  Ten or twenty years of neighborhood history would better quantify risk.

Even the ELCB must be protected.  Better is to connect an incoming transient to earth so that it does not go through the ELCB.  An electrician can better determine what local codes also require.
*
QUOTE(ozak @ Apr 6 2019, 03:36 PM)
Every new house has a ground rod which is a must state in the country electrical rule.

What we do is add an additional ground rod around the house to get fully (or more) protect. An advantage if the developer doesn't do a good job on the ground rod.

I see a very poor job in my house ground rod when I get the house. They just wrap the copper wire around the steel rebar which is not a proper grounding rod. And the wire is 4mm size which is not a proper size.

If your house ground is landfill, the deep might not be enough. It has a high resistance. Plung as deep as possible. The contractor has the earth meter to check the proper grounding. And not in the rainy day to test. Dry earth have higher resistance.

I don't have the equipment to check. Costly. What I can do and check is the resistance wire to the rod by multimeter. Makesure low enough ohm. And a min of 6mm wire size. Rod deep as possible and connection. I solder weld the wire to the rod. The only way to confirm my grounding DIY done a good job is by the 2pcs Belkin surge protector Led light. Now it always light up to tell me the earthing is good.   

That RCCB I mention above have a nuisance trip prevention which causes by lightning. It will not easily trip by lightning even it has a sensitivity of 100mA.

SPD doesn't function at all (or limited) without the shortest earth wire to the grounding rod. It has a limited radius length of protection. I forget the wire limited length. Something like 10m-20m. Any wire that longer than this range will require another SPD and nearer earth wire to another grounding rod to get protected.

SPD job is to get the lightning energy (surge voltage) as fast as possible to the grounding rod. If the surge is from the Live and neutral wire. (From TNB if you put in the class 1 SPD). MCB, RCCB or fuse in the DB box don't have the earth wire connection. So if the lightning surge coming from TNB, where will it go to unable it travel to the ground? It have to go through your equipment which have earthing protection. And from your equipment earthing body, travel to the earth wire and last to the ground rod. Which might already damage the equipment.

So don't complain if you put a bunch of SPD and cannot protect. Grounding is still important.
*
QUOTE(Richard @ Apr 6 2019, 07:40 PM)
Conventional wisdom is to install an SPD (per DB rated kA or higher) before the DB to dissipate to mass of earth the lightning surge current. However I'm no expert so get a second opinion if you can.

The home DB's earth pit impedance must be as low as possible to maintain shortest path to earth mass. For landed properties only.

I would suspect your parents building earth pits are too high impedance thus the lightning surge randomly hit so many equipment

I would suggest you get a certified electrical contractor to check the structure electrical earthing pit (preferably 10 Ohm or better) system.

Edit* Anyway here's an easy way to check whether your home has good earthing.

Use your multimeter to measure the Voltage between Phase/Earth, if you get the same(or about 5V diff) voltage as between Phase/Neutral then you have good earthing. Fluctuates according to current weather/ground conditions.

Otherwise have your earthing checked by a certified electrician
If only you continually experience damaged equipment due to lightning strikes.
My house earthing is bad (I've checked) but no lightning damaged so I don't bother.
*
Thanks for sharing. My electrician is coming to inspect the earth grounding and install SPD tomorrow. Hope all goes well smile.gif

Btw, the earth ground reading should be 10 Ohm or lower, right?

Richard
post Apr 8 2019, 05:41 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(clickNsnap @ Apr 8 2019, 05:22 PM)
Thanks for sharing. My electrician is coming to inspect the earth grounding and install SPD tomorrow. Hope all goes well smile.gif

Btw, the earth ground reading should be 10 Ohm or lower, right?
*
Yes

Ask to witness his earth testing method. He must use an earth tester to test your earth rod with a result of 10 Ohm or below

Let him setup his earth tester with a clamp to your earth rod. The remainder voltage/current spikes will be a few metres away.

Witness the 10 Ohm reading on his tester. Done.
.
Easiest way I know to get that reading is to locate your rod next to drain so it's wet most of the time. Anyway that is where I put in my earth rod and chamber. Just sharing.

Edit* Refer 8.2.4 the earth resistance testing method in the ST guidelines.

Attached JKR specs for lightning protection system


This post has been edited by Richard: Apr 9 2019, 06:39 AM


Attached File(s)
Attached File  guidelines_for_electrical_wiring_in_residential_buildings_.pdf ( 427.2k ) Number of downloads: 83
Attached File  JKR_LPS_Chap17.pdf ( 885.55k ) Number of downloads: 97
Richard
post Apr 9 2019, 06:55 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


Earth impedance value

Transformer Neutral (star) pt and body - 1 Ohm or below

Residential electrical DB earthing pit - 10 Ohm or below

Residential Lightning protection system pit - between 5 to 50 Ohm or below
depending on soil conditions and consultant design.

Problem was some areas almost impossible to get the earth reading due to budget constraints. Needed to explain to the client and design engineer.

This post has been edited by Richard: Apr 9 2019, 07:34 AM


Attached File(s)
Attached File  4346628a_en_EarthGround_tutorial_e__1_.pdf ( 6.88mb ) Number of downloads: 79
westom
post Apr 9 2019, 09:31 AM

Getting Started
**
Junior Member
228 posts

Joined: Mar 2009
QUOTE(clickNsnap @ Apr 8 2019, 01:22 PM)
  Btw, the earth ground reading should be 10 Ohm or lower, right?
Earth ground would be low ohm resistance. The connection to earth ground must be low ohm impedance. Electrician would not have any equipment to measure impedance. And most probablly do not know what impedance is.

But we make it simple. A low impedance connection is short (ie less than 3 meters), has no sharp bends, is not inside metallic conduit, and has no splices.

Generally, many electrician cannot measure earth ground resistance. So most simply install two electrodes. One is more than sufficient to protect human life. More (sufficiently spaced apart) are necessary to protect appliances.

Rather than measure ground resistance, a decision for earth ground may be determined by geology. Sandy soil needs an enhanced ground. Earth of fine particles that stays moist (therefore is more electrically conductive) means one or two electrodes are probably sufficient.

This post has been edited by westom: Apr 9 2019, 10:58 AM
clickNsnap
post Apr 9 2019, 05:42 PM

On my way
****
Junior Member
540 posts

Joined: Jun 2006


QUOTE(Richard @ Apr 9 2019, 07:55 AM)
Earth impedance value

Transformer Neutral (star) pt and body - 1 Ohm or below

Residential electrical DB earthing pit - 10 Ohm or below

Residential Lightning protection system pit - between 5 to 50 Ohm or below
depending on soil conditions and consultant design.

Problem was some areas almost impossible to get the earth reading due to budget constraints. Needed to explain to the client and design engineer.
*
QUOTE(westom @ Apr 9 2019, 10:31 AM)
Earth ground would be low ohm resistance.  The connection to earth ground must be low ohm impedance.  Electrician would not have any equipment to measure impedance.  And most probablly do not know what impedance is.

But we make it simple.  A low impedance connection is short (ie less than 3 meters), has no sharp bends, is not inside metallic conduit, and has no splices.

Generally, many electrician cannot measure earth ground resistance.  So most simply install two electrodes.  One is more than sufficient to protect human life.  More (sufficiently spaced apart) are necessary to protect appliances.

Rather than measure ground resistance, a decision for earth ground may be determined by geology.  Sandy soil needs an enhanced ground.  Earth of fine particles that stays moist (therefore is more electrically conductive) means one or two electrodes are probably sufficient.
*
Thanks Richard & Westom.

My house installed the SPD and inspect earth grounding today, the SPD is an unknown brand (electrician replace with own company logo), it comes with 3 years warranty. The boss provides prompt reply on my enquiries, the installer did a nice job, the earth grounding reading is 1.3 Ohm... hope all goes well thumbup.gif

This post has been edited by clickNsnap: Apr 11 2019, 12:15 AM


Attached thumbnail(s)
Attached Image
Momo33
post Jul 27 2020, 01:32 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(ozak @ Apr 6 2019, 07:10 PM)
Yup. My parent apartment outside end lot wall have this copper tape running down the building. With a pvc pipe cover at the ground floor wall.

Still fried many equipment during storm.
*
Need some advice here..on SPD .

I am lookin to install a SPD surge device at the DB box /single phase /63A for my landed house.

What kA rating shall i chose ?

i see in shopee there is 20kA to 120kA choice.
is chosing a 100kA SPD better than 40kA

Thanks..


ozak
post Jul 27 2020, 01:40 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(Momo33 @ Jul 27 2020, 01:32 PM)
Need some advice here..on SPD . 

I am lookin to install a SPD  surge device  at the DB box /single phase /63A    for  my landed house.

What kA  rating  shall  i chose ? 

i see in shopee  there is  20kA to 120kA  choice.
is chosing a 100kA  SPD better than  40kA

Thanks..
*
Std is 20ka to 40ka.

It's capacity current it can absorb.

It's better with additional earth rod.
Momo33
post Jul 27 2020, 02:36 PM

Regular
******
Senior Member
1,448 posts

Joined: Oct 2019
QUOTE(ozak @ Jul 27 2020, 02:40 PM)
Std is 20ka to 40ka.

It's capacity current it can absorb.

It's better with additional earth rod.
*
thanks ..
the price for 60kA and 100kA is about 98rm to 108 rm .
Any issues if i go for higher current capacity .

https://www.lazada.com.my/products/schneide...3660056082.html?


ozak
post Jul 27 2020, 02:58 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(Momo33 @ Jul 27 2020, 02:36 PM)
thanks  ..
the price  for 60kA  and 100kA  is about  98rm to 108 rm .
Any issues if i go for higher current capacity . 

https://www.lazada.com.my/products/schneide...3660056082.html?
*
Forget already.

It got to do with sensitivity and the placement of the SPDA. Either the type protect the incoming (External) before the MB or protect the internal (after the MB).