QUOTE(westom @ Apr 6 2019, 09:13 AM)
Follow that wire from DB to electrode. For example, if it goes up over a foundation and down to an earthing electrode, then protection is compromised. It is unnecessary too long. It has sharp bends over the foundation. And it is best routed away from other non-grounding wires.
Better would also put another electrode maybe somewhere before the original one. Since those are cheap and it would expand and make more conductive that earth ground.
Whether that is necessary is a function of neighborhood history. For example, a transient typically happens once every seven years. Ten or twenty years of neighborhood history would better quantify risk.
Even the ELCB must be protected. Better is to connect an incoming transient to earth so that it does not go through the ELCB. An electrician can better determine what local codes also require.
QUOTE(ozak @ Apr 6 2019, 03:36 PM)
Every new house has a ground rod which is a must state in the country electrical rule.
What we do is add an additional ground rod around the house to get fully (or more) protect. An advantage if the developer doesn't do a good job on the ground rod.
I see a very poor job in my house ground rod when I get the house. They just wrap the copper wire around the steel rebar which is not a proper grounding rod. And the wire is 4mm size which is not a proper size.
If your house ground is landfill, the deep might not be enough. It has a high resistance. Plung as deep as possible. The contractor has the earth meter to check the proper grounding. And not in the rainy day to test. Dry earth have higher resistance.
I don't have the equipment to check. Costly. What I can do and check is the resistance wire to the rod by multimeter. Makesure low enough ohm. And a min of 6mm wire size. Rod deep as possible and connection. I solder weld the wire to the rod. The only way to confirm my grounding DIY done a good job is by the 2pcs Belkin surge protector Led light. Now it always light up to tell me the earthing is good.
That RCCB I mention above have a nuisance trip prevention which causes by lightning. It will not easily trip by lightning even it has a sensitivity of 100mA.
SPD doesn't function at all (or limited) without the shortest earth wire to the grounding rod. It has a limited radius length of protection. I forget the wire limited length. Something like 10m-20m. Any wire that longer than this range will require another SPD and nearer earth wire to another grounding rod to get protected.
SPD job is to get the lightning energy (surge voltage) as fast as possible to the grounding rod. If the surge is from the Live and neutral wire. (From TNB if you put in the class 1 SPD). MCB, RCCB or fuse in the DB box don't have the earth wire connection. So if the lightning surge coming from TNB, where will it go to unable it travel to the ground? It have to go through your equipment which have earthing protection. And from your equipment earthing body, travel to the earth wire and last to the ground rod. Which might already damage the equipment.
So don't complain if you put a bunch of SPD and cannot protect. Grounding is still important.
QUOTE(Richard @ Apr 6 2019, 07:40 PM)
Conventional wisdom is to install an SPD (per DB rated kA or higher) before the DB to dissipate to mass of earth the lightning surge current. However I'm no expert so get a second opinion if you can.
The home DB's earth pit impedance must be as low as possible to maintain shortest path to earth mass. For landed properties only.
I would suspect your parents building earth pits are too high impedance thus the lightning surge randomly hit so many equipment
I would suggest you get a certified electrical contractor to check the structure electrical earthing pit
(preferably 10 Ohm or better) system.
Edit* Anyway here's an easy way to check whether your home has good earthing.
Use your multimeter to measure the Voltage between Phase/Earth, if you get the same(or about 5V diff) voltage as between Phase/Neutral then you have good earthing. Fluctuates according to current weather/ground conditions.
Otherwise have your earthing checked by a certified electrician
If only you continually experience damaged equipment due to lightning strikes.
My house earthing is bad (I've checked) but no lightning damaged so I don't bother.
Thanks for sharing. My electrician is coming to inspect the earth grounding and install SPD tomorrow. Hope all goes well

Btw, the earth ground reading should be 10 Ohm or lower, right?