Lightning strike your house is very very rare. But install the rod ontop the house is increase the percentage. Our house here is not a big house. And all the wire is conceal in the wall. If the rod it not enough to take the strong lightning, it will travel all over the house wiring.
The conventional design for a building lightning protection system is a rolling sphere approach with Franklin rods. The lightning rods at the highest points of the structure connection via 25x3mm2 copper tape straight down the structure to an 16mm dia min earth copper rod to an earth impedance of below 50 Ohm. Sometimes your electrical supplier can advise you as these are standard JKR building design.
The minimum earth conductor is 10mm2 for a 40 Amp main incoming and 16mm2 for 63Amp mains. For residential design.
You can refer to the attached guidelines or to Malaysian Building By-Law 1984 for confirmation as for me this all was a long time ago.
Hopefully I've uploaded the right attachement but note the Bahasa Malaysia version is the latest and my copy is an old code but should still be applicable.
Best wishes.