QUOTE(eddyann @ May 29 2015, 09:21 AM)
It won't trip. if you check the outside tnb fuse sometimes it rated 100 A. more than the demand that u have right now.

total hp u have 6hp. it is not even close to 30Amp
*
It depends on how we use the air cond.
That wireman are right, it won't trip.
But if we always turn on all the air cond at the same time, it will be different story. When the outdoor unit are energized, it will draw 2X of the rated current for 0.5-2 seconds.
So if we always turn on all together, it will create heat stress to the connecting points.\ which later melt them and cause fire.
Richard
post Jun 2 2015, 04:28 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


Just on the aircon alone, 1hp = 4 amps, 1.5hp = 5.2amps, 2.5hp = 11.5a,amps
Total = 20.7 Amps

Now imagine a small party in your house all aircons running and someone taking a
hot water shower.

Add Bath Water heater (hottest)= 24amps, kitchen load rice cooker = 10 amps, fridge = 5 amps, microwave, water kettle=10amps microwave - 10 amps
Total = 59amps

Add lights/fans and miscellaneous TV, sockets total another 10amps

Grand Total = 90.7 amps. Almost no more safety factor.

Prefer 20% safety factor for transient overloads and copper wiring aging.

Add another phase to balance the electrical load is good advice.
SUSkimsim
post Jun 2 2015, 08:21 AM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(supersound @ May 29 2015, 09:33 AM)
It depends on how we use the air cond.
That wireman are right, it won't trip.
But if we always turn on all the air cond at the same time, it will be different story. When the outdoor unit are energized, it will draw 2X of the rated current for 0.5-2 seconds.
So if we always turn on all together, it will create heat stress to the connecting points.\ which later melt them and cause fire.
*
If we used China wires should broken somewhere already, that is why we needs invest 100% copper wires at all.

Can imaging also electronic water cooker wire can be burned as well.



SUSsupersound
post Jun 2 2015, 08:54 AM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(kimsim @ Jun 2 2015, 08:21 AM)
If we used China wires should broken somewhere already, that is why we needs invest 100% copper wires at all.

Can imaging also electronic water cooker wire can be burned as well.
*
If you can get 100% copper wire, I'll give rm1000 per M whistling.gif
weikee
post Jun 2 2015, 09:45 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(Richard @ Jun 2 2015, 04:28 AM)
Just on the aircon alone, 1hp = 4 amps, 1.5hp = 5.2amps, 2.5hp = 11.5a,amps
Total = 20.7 Amps

Now imagine a small party in your house all aircons running and someone taking a
hot water shower.

Add Bath Water heater (hottest)= 24amps, kitchen load rice cooker = 10 amps, fridge = 5 amps, microwave, water kettle=10amps microwave - 10 amps
Total = 59amps

Add lights/fans and miscellaneous TV, sockets total another 10amps

Grand Total = 90.7 amps.  Almost no more safety factor.

Prefer 20% safety factor for transient overloads and copper wiring aging.

Add another phase to balance the electrical load is good advice.
*
What water heater take 24amps? that is 5.5KW
Rice cooker, getting for huge one? Panasonic Large rice cooker 4+L only take 7Amps, only the huge one 7L take 11Amps

Your ratting look like is for a family of 8-10 members in a big house.
SUSkimsim
post Jun 2 2015, 10:54 AM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(supersound @ Jun 2 2015, 08:54 AM)
If you can get 100% copper wire, I'll give rm1000 per M whistling.gif
*
In sg yes
SUSsupersound
post Jun 2 2015, 11:10 AM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(kimsim @ Jun 2 2015, 10:54 AM)
In sg yes
*
NVM, as long as you can get 100% copper, I will give you.
But, must be test with reliable tester to check for 100% copper that has no other impurities inside.
If the so called wire you get has impurities inside, you have to pay for the lab test whistling.gif
weikee
post Jun 2 2015, 11:14 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(kimsim @ Jun 2 2015, 10:54 AM)
In sg yes
*
Don't simply put claim. I will also want a 100% copper if you can get. Get your fact before simply tembak.
weikee
post Jun 2 2015, 11:14 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(supersound @ Jun 2 2015, 11:10 AM)
NVM, as long as you can get 100% copper, I will give you.
But, must be test with reliable tester to check for 100% copper that has no other impurities inside.
If the so called wire you get has impurities inside, you have to pay for the lab test whistling.gif
*
I also will want to pay that amount... hey maybe 2k per meter if its 100%, not even 99.99% biggrin.gif
enriquelee
post Jun 2 2015, 11:40 AM

Don't ask for more, ask for COKE
********
All Stars
10,510 posts

Joined: Jan 2003
From: Atlanta

QUOTE(Richard @ Jun 2 2015, 04:28 AM)
Just on the aircon alone, 1hp = 4 amps, 1.5hp = 5.2amps, 2.5hp = 11.5a,amps
Total = 20.7 Amps

Now imagine a small party in your house all aircons running and someone taking a
hot water shower.

Add Bath Water heater (hottest)= 24amps, kitchen load rice cooker = 10 amps, fridge = 5 amps, microwave, water kettle=10amps microwave - 10 amps
Total = 59amps

Add lights/fans and miscellaneous TV, sockets total another 10amps

Grand Total = 90.7 amps.  Almost no more safety factor.

Prefer 20% safety factor for transient overloads and copper wiring aging.

Add another phase to balance the electrical load is good advice.
*
All these on at the same time? shocking.gif
And invertor aircond calculation will be different already.
SUSsupersound
post Jun 2 2015, 02:47 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(weikee @ Jun 2 2015, 11:14 AM)
I also will want to pay that amount... hey maybe 2k per meter if its 100%, not even 99.99% biggrin.gif
*
Looks like you catch me already icon_rolleyes.gif
Iceman74
post Jun 2 2015, 03:21 PM

Regular
******
Senior Member
1,407 posts

Joined: May 2010


Hi guys,

Which brand of wire to do re-wiring is good quality and price is reasonable?
Gonna get my keys soon. Need to do planing to re-wire the whole house.
If possible, let me know where can get it and best price too. Thanks.

This post has been edited by Iceman74: Jun 2 2015, 03:29 PM
weikee
post Jun 2 2015, 03:29 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(Iceman74 @ Jun 2 2015, 03:21 PM)
Hi guys,

Which brand of wire to do re-wiring is good quality and price is reasonable?
Gonna get my keys soon. Need to do planing to re-wire the whole house.
*
New house also need to rewire? mostly if you get local brand should be good.

Some local brand I know are
Fajar Cables, Universal Cables, FEC, Megakable



Iceman74
post Jun 2 2015, 03:49 PM

Regular
******
Senior Member
1,407 posts

Joined: May 2010


QUOTE(weikee @ Jun 2 2015, 03:29 PM)
New house also need to rewire? mostly if you get local brand should be good.

Some local brand I know are
Fajar Cables, Universal Cables, FEC, Megakable
*
2nd hand house. Don't like the way previous owner done the wiring, just sambung here & there even aircond just sambung normal wall plug.

Thanks for the tip. Any idea how much per row roughly?
weikee
post Jun 2 2015, 04:08 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(Iceman74 @ Jun 2 2015, 03:49 PM)
2nd hand house. Don't like the way previous owner done the wiring, just sambung here & there even aircond just sambung normal wall plug.

Thanks for the tip. Any idea how much per row roughly?
*
Really out of this for sometime, you got to shop around and ask.
JunJun04035
post Jun 3 2015, 10:43 AM

Sir Kalahari, Duke of Autocorrect
******
Senior Member
1,167 posts

Joined: May 2009


QUOTE(Iceman74 @ Jun 2 2015, 03:49 PM)
2nd hand house. Don't like the way previous owner done the wiring, just sambung here & there even aircond just sambung normal wall plug.

Thanks for the tip. Any idea how much per row roughly?
*
3 core 40/0.016 100% copper RM40++ per roll
4 core 40/0.16 100% copper RM200++ per roll
looilk74
post Jun 3 2015, 03:26 PM

New Member
*
Junior Member
11 posts

Joined: Dec 2014
My house has got 1x2.5, 1x2.0, 1x1.5, 5x1HP (Total 8), 5 water heater, fridge, hood and oven and all the downlights and light boxes. My electrian has laid lay all the new wiring and install a 54 ways EPS Metal Switch board with all the necessary MCB and 3 Phase 63A 100Ma ELCB. Total cost RM1800 (Include supply and install this 54 ways EPS Metal Switch board). All the load balancing has been done. And my meter is located outside and ready with 3 phase wiring from developer since it is new house and no any new cables is required. What i need to do now is to apply TNB to change the 3 phase meter only. My electrician quote me additional cost as below:-

1) To apply 3 phase meter runner fees-RM 1600
2) Another 2 payment to TNB RM1700 and RM 2000
Total RM 5300

My question is it overprice since only need to apply meter ? Or is it i am still ok if stay with current setup 1 phase without upgrading to 3 phase meter.
Pls kindly advise.

looilk74
post Jun 3 2015, 03:27 PM

New Member
*
Junior Member
11 posts

Joined: Dec 2014
My house has got 1x2.5, 1x2.0, 1x1.5, 5x1HP (Total 8), 5 water heater, fridge, hood and oven and all the downlights and light boxes. My electrian has laid lay all the new wiring and install a 54 ways EPS Metal Switch board with all the necessary MCB and 3 Phase 63A 100Ma ELCB. Total cost RM1800 (Include supply and install this 54 ways EPS Metal Switch board). All the load balancing has been done. And my meter is located outside and ready with 3 phase wiring from developer since it is new house and no any new cables is required. What i need to do now is to apply TNB to change the 3 phase meter only. My electrician quote me additional cost as below:-

1) To apply 3 phase meter runner fees-RM 1600
2) Another 2 payment to TNB RM1700 and RM 2000
Total RM 5300

My question is it overprice since only need to apply meter ? Or is it i am still ok if stay with current setup 1 phase without upgrading to 3 phase meter.
Pls kindly advise.

Richard
post Jun 7 2015, 09:21 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(weikee @ Jun 2 2015, 09:45 AM)
What water heater take 24amps? that is 5.5KW
Rice cooker, getting for huge one?  Panasonic Large rice cooker  4+L only take 7Amps, only the huge one 7L take 11Amps

Your ratting look like is for a family of 8-10 members in a big house.
*
Refer Joven instant water heater http://www.joven-electric.com/product_deta...d=2&series_id=8 specifications.

On highest (hotest) setting it(instant water heater) will draw 20+ amps from your supply. I have confirmed this with a tong tester.

Also don't take the best case scenario that they are using new expensive low power high efficiency energy saving electrical appliances after one(1) year usage any 2kw/3kw rice cooker/kettle will draw near 10 Amps from your mains.


weikee
post Jun 7 2015, 09:43 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(Richard @ Jun 7 2015, 09:21 PM)
Refer Joven instant water heater http://www.joven-electric.com/product_deta...d=2&series_id=8 specifications.

On highest (hotest) setting it(instant water heater) will draw 20+ amps from your supply. I have confirmed this with a tong tester.

Also don't take the best case scenario that they are using new expensive low power high efficiency energy saving electrical appliances after one(1) year usage any 2kw/3kw rice cooker/kettle will draw near 10 Amps from your mains.
*
Malaysia unit usually 3.6kw. I doubt you can get the 5.2kw unit.