QUOTE(okuribito @ Oct 14 2021, 09:52 PM)
thanks... would you know what test it is that need to
check current Amps in the DB? I read that to prove DB is dead, NCV and Voltage is sufficient (haha dangerous to DIY work on live db)
Do NOT work on the live DB if you don't have any idea what you are doing in there.Current MeasurementYou can carefully position the clamp not to disturb the wires in the DB and be 100% mindful don't simply poke here poke there.
It is used in residential to troubleshoot AC that die off.. WH load amps.. getting a feel of 3 phase balanced or totally imba circuit assignment.
Usually I used them for commercial work/inverter load monitoring upon commissioning
NCV sufficient, follow with a 2nd test on voltage just to be sure.
You need to understand the concept of LDL (live dead live), prove the equipment works to measure, prove the dead circuit is truly dead reading, prove the measurement is repeatable on live again.
https://www.fluke.com/en-my/learn/blog/elec...voltage-testingQUOTE(okuribito @ Oct 14 2021, 07:13 PM)
Can I ask why measure AC amps at DB box? Is it a normal test for troubleshooting? Curious to learn
The other thing is, I notice the regular residential DB is really crammed with wires, especially at the E & N bars; I'm curious how the clamps can be used. Perhaps only on the big wires in & out of the ELCB & main breaker?
LOL iinm I understand the clamp is really to measure current by inductance (also non-contact safety iinm). But I see many youtubers (some probably working electricians) use the clamp to hang up and free the hands (good idea

). On the other hand, I notice Fluke DMMs have a magnetic strap accessory to do the same thing.
Can I have your opinion on the Fluke 101 for basic troubleshooting residential wiring - light switches, power sockets, aircon/water heater switches? Is it sufficient? Not going to use for troubleshooting appliances that have capacitors ... just wiring (with the mains OFF)
Thanks in advance
PS: I guess key criteria would be reliability & safety which everyone would expect from Fluke. Not so much features. Suggestions for other affordable brands/models most appreciated

Clamps are for measuring
AC amps under load safely. It is NOT a test by itself. It is a measurement.
Why usually at DB? Because its easy to access all the live wire.
There is no better spot (logically) as:
1. concealed wiring = need to tear down the whole wall
2. device on the other end is fixed in nicely = meaning there won't be enough space to slip in a clamp.
3. flexicord L and N cancel each other out = meaning forever 0A reading
4. Fundamental of Clamps = can only work for AC amps measurement when you can isolate only one leg.
Theoretically, you can use a clamp to check full load amps before the compressor motor jams up or sth along those lines.
Other than that, the fluke 101 is kinda like an overpriced A-class.. you get to check voltage and continuity with it. Cannot read current.
If you want to poke around AC.. I'd recommend the Kyoritsu clamp (KEW 2117) over it. Autoranging so lesser chance to blow up.
There you can see.. ahh WH take up 16A..
got voltage checks
got continuity test to see whether fuse blow
Coz voltage will be 230V all over the house unless something is wrong.
Magnetic straps are accessories but not needed.
The CAT III or better rating is the one to be concerned about. Just in case butterfingers.
This post has been edited by ceo684: Oct 14 2021, 11:21 PM