 RCCB for Water Heater

views
     
amco
post Jun 11 2023, 01:13 AM

Enthusiast
*****
Senior Member
785 posts

Joined: Jan 2003
QUOTE(mushigen @ May 17 2023, 01:22 PM)
I don't understand this statement.
*
This is untrue. ST requires 10ma RCCB for all type of water heater. Plug and socket for water heater inside toilet is banned. I know why it's banned.


Latest Guideline for water heater
xkaizoku
post Aug 3 2023, 11:47 AM

Getting Started
**
Junior Member
220 posts

Joined: Sep 2021
QUOTE(ceo684 @ Mar 20 2023, 12:20 AM)
Use 30mA, no developed country use 100mA for homes one.
*
i just checked my single phase db beside the lever have 63a 100mA rccd, so it is suggested to replace with 63a 30mA 2P? my house quite old already 20+ years

ABB https://shopee.com.my/ABB-RCCB-ELCB-FH202-A...93-457ea2c660fb
Hager https://shopee.com.my/HAGER-CD263B-63AMP-2-...e1-9498152d9ef1

This post has been edited by xkaizoku: Aug 3 2023, 01:46 PM
thinkgoodpositive
post Aug 25 2023, 04:49 PM

Getting Started
**
Junior Member
196 posts

Joined: Sep 2015
QUOTE(xkaizoku @ Aug 3 2023, 11:47 AM)
i just checked my single phase db beside the lever have 63a 100mA rccd, so it is suggested to replace with 63a 30mA 2P? my house quite old already 20+ years

ABB https://shopee.com.my/ABB-RCCB-ELCB-FH202-A...93-457ea2c660fb
Hager https://shopee.com.my/HAGER-CD263B-63AMP-2-...e1-9498152d9ef1
*
This ABB model I think without anti-nuisance tripping function. Hager model stated with anti-nuisance tripping function, fyi.

em_on
post Aug 25 2023, 04:53 PM

On My Way
****
Junior Member
612 posts

Joined: Jan 2011
QUOTE(thinkgoodpositive @ Aug 25 2023, 04:49 PM)
This ABB model I think without anti-nuisance tripping function. Hager model stated with anti-nuisance tripping function, fyi.
*
nope, ABB does have


https://library.e.abb.com/public/7115a45a1e...421002B0201.pdf
thinkgoodpositive
post Aug 28 2023, 10:09 AM

Getting Started
**
Junior Member
196 posts

Joined: Sep 2015
QUOTE(em_on @ Aug 25 2023, 04:53 PM)
Ya I know this model got. What I meant was the one ABB model FH202 quoted by him earlier in the shopee link.
xkaizoku
post Aug 29 2023, 10:35 PM

Getting Started
**
Junior Member
220 posts

Joined: Sep 2021
QUOTE(thinkgoodpositive @ Aug 28 2023, 10:09 AM)
Ya I know this model got. What I meant was the one ABB model FH202 quoted by him earlier in the shopee link.
*
which ABB model have?
thinkgoodpositive
post Aug 30 2023, 09:40 AM

Getting Started
**
Junior Member
196 posts

Joined: Sep 2015
QUOTE(xkaizoku @ Aug 29 2023, 10:35 PM)
which ABB model have?
*
https://library.e.abb.com/public/7115a45a1e...421002B0201.pdf

This AP range but not sure is commonly available online in Malaysia or not.
jio
post Aug 30 2023, 09:33 PM

Casual
***
Junior Member
383 posts

Joined: May 2005
Actually ABB FH202 AC-63/0.03 does has anti nuisance tripping. You can search using its SKU at ABB website where it does list 250A max surge current. AP-R range is their high immunity model and usually hard to find ready stock. If you have excessive tripping during lightning that not even close by, it is usually due leakage/short from neutral to earth that high resistance enough preventing it from tripping the RCCB on normal days. Only the lowest end consumer RCCB (for 30ma/100ma) don't have anti nuisance tripping.

This post has been edited by jio: Aug 30 2023, 09:34 PM
Richard Walter
post Oct 3 2023, 12:25 PM

New Member
*
Junior Member
15 posts

Joined: Jan 2022
QUOTE(ceo684 @ May 12 2023, 07:40 AM)
Didn't see my own place blackout every 2-3days laugh.gif its a myth
*
Is this DB ok? Need some advice before proceeding. Thanks in advance!




Attached thumbnail(s)
Attached Image
SUSceo684
post Oct 3 2023, 07:00 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(Richard Walter @ Oct 3 2023, 12:25 PM)
Is this DB ok? Need some advice before proceeding. Thanks in advance!
*
Ok except the last one use 40A 0.03A


Attached thumbnail(s)
Attached Image
Richard Walter
post Oct 3 2023, 08:45 PM

New Member
*
Junior Member
15 posts

Joined: Jan 2022
QUOTE(ceo684 @ Oct 3 2023, 07:00 PM)
Ok except the last one use 40A 0.03A
*
Ok.Will get it replaced. Thanks a lot notworthy.gif
stormer.lyn
post Oct 3 2023, 08:57 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(Richard Walter @ Oct 3 2023, 12:25 PM)
Is this DB ok? Need some advice before proceeding. Thanks in advance!
*
I believe you will have unnecessary tripping faults. You have made a common Neutral busbar for both the top RCCB (Marked "40A 30mA" - Let's call this RCCB1) and the bottom RCCB (Marked "63A 100mA or 40A 30mA" - Let's call this RCCB2)

This may happen : Current flows through RCCB1 live > MCB 16A > socket in room > appliance > Neutral wire back to DB > Neutral busbar > RCCB2 Neutral.
Your RCCBs will trip. You have to split the Neutral busbar for RCCB1 and RCCB2.

The WH Neutrals must be connected to the RCCB2 Neutral busbar, as the current to the WH originated from RCCB2.

Also, physically, when I am making the connections, I would connect the 10 mm² wires together. This is for the WH Live. In the drawing it is connected through the Live busbar at each end. Potentially the Live busbar will heat up.

This post has been edited by stormer.lyn: Oct 3 2023, 09:08 PM
Richard Walter
post Oct 4 2023, 11:49 AM

New Member
*
Junior Member
15 posts

Joined: Jan 2022
QUOTE(stormer.lyn @ Oct 3 2023, 08:57 PM)
I believe you will have unnecessary tripping faults. You have made a common Neutral busbar for both the top RCCB (Marked "40A 30mA" - Let's call this RCCB1) and the bottom RCCB (Marked "63A 100mA or 40A 30mA" - Let's call this RCCB2)

This may happen : Current flows through RCCB1 live > MCB 16A > socket in room > appliance > Neutral wire back to DB > Neutral busbar > RCCB2 Neutral.
Your RCCBs will trip. You have to split the Neutral busbar for RCCB1 and RCCB2.

The WH Neutrals must be connected to the RCCB2 Neutral busbar, as the current to the WH originated from RCCB2.

Also, physically, when I am making the connections, I would connect the 10 mm² wires together. This is for the WH Live. In the drawing it is connected through the Live busbar at each end. Potentially the Live busbar will heat up.
*
Oh no, The DB box only has 1 neutral busbar. Need to change DB box or can add another neutral busbar?

For the WH live you mean replace the busbar to 10mm wire instead?

Thanks ya
lankorn
post Oct 5 2023, 01:05 AM

Getting Started
**
Junior Member
125 posts

Joined: Mar 2009


QUOTE(stormer.lyn @ Oct 3 2023, 08:57 PM)
I believe you will have unnecessary tripping faults. You have made a common Neutral busbar for both the top RCCB (Marked "40A 30mA" - Let's call this RCCB1) and the bottom RCCB (Marked "63A 100mA or 40A 30mA" - Let's call this RCCB2)

This may happen : Current flows through RCCB1 live > MCB 16A > socket in room > appliance > Neutral wire back to DB > Neutral busbar > [b]RCCB2 Neutral.
Your RCCBs will trip. You have to split the Neutral busbar for RCCB1 and RCCB2.

The WH Neutrals must be connected to the RCCB2 Neutral busbar, as the current to the WH originated from RCCB2.

Also, physically, when I am making the connections, I would connect the 10 mm² wires together. This is for the WH Live. In the drawing it is connected through the Live busbar at each end. Potentially the Live busbar will heat up.
*
May i know why you say so?Do you mean to have 2 separate Neutral busbar?
Eventually all the Neutral will be connect back to incoming(main) Neutral right?

This post has been edited by lankorn: Oct 5 2023, 01:07 AM
SUSceo684
post Oct 5 2023, 01:20 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(lankorn @ Oct 5 2023, 01:05 AM)
May i know why you say so?Do you mean to have 2 separate Neutral busbar?
Eventually all the Neutral will be connect back to incoming(main) Neutral right?
*
Actually on second thought. Why not just use a single 63 0.03 RCD since it’s on single phase. There is no need to split DB.

It’s because the neutral group of circuits on RCCB A should not be mixed with neutral group of circuits on RCCB B before passing the “checkpoint”.
lankorn
post Oct 5 2023, 01:30 AM

Getting Started
**
Junior Member
125 posts

Joined: Mar 2009


QUOTE(ceo684 @ Oct 5 2023, 01:20 AM)
Actually on second thought. Why not just use a single 63 0.03 RCD since it’s on single phase. There is no need to split DB.

It’s because the neutral group of circuits on RCCB A should not be mixed with neutral group of circuits on RCCB B before passing the “checkpoint”.
*
I cannot understand biggrin.gif .Can you draw?

This post has been edited by lankorn: Oct 5 2023, 01:30 AM
SUSceo684
post Oct 5 2023, 01:49 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(lankorn @ Oct 5 2023, 01:30 AM)
I cannot understand  biggrin.gif .Can you draw?
*
Mixing your neutrals BEFORE the RCD "checkpoint" has different implications.

U know how shops like genki sushi and sushi king charge for per-plate kaiten belt sushi?
RCD operates like u eat, u pay for your plate tower.
Now let's say I eat, I don't know you, but I put my plates into your table.

This post has been edited by ceo684: Oct 5 2023, 01:52 AM


Attached thumbnail(s)
Attached Image
Richard Walter
post Oct 5 2023, 07:49 AM

New Member
*
Junior Member
15 posts

Joined: Jan 2022
QUOTE(ceo684 @ Oct 3 2023, 07:00 PM)
Ok except the last one use 40A 0.03A
*
Done changed the RCCB & DB box to the one with double neutral bars. smile.gif

Should be good to go right? Waiting for the wireman to fix on weekend.


Attached thumbnail(s)
Attached Image
stormer.lyn
post Oct 5 2023, 08:37 AM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(Richard Walter @ Oct 5 2023, 07:49 AM)
Done changed the RCCB & DB box to the one with double neutral bars. smile.gif

Should be good to go right? Waiting for the wireman to fix on weekend.
*
Yes, this diagram looks good. What I meant about the water heater live wire is in the picture below.

user posted image

This is the physical connection of the wires. This way the Current to the WH doesn't go through the busbar, but goes wire-to-wire. If you look at a busbar, the bar is rated for 120A (example) but the tines are rated for the Current to an MCB only. They way wiremen stuff the incoming wire into the MCB and get it to distribute is dangerous in my opinion.

Sorry, a bit busy to get on LYN. In the marine line, many ships right now. But I'll try to get back to you asap if you have any further questions.
Richard Walter
post Oct 5 2023, 10:49 AM

New Member
*
Junior Member
15 posts

Joined: Jan 2022
QUOTE(stormer.lyn @ Oct 5 2023, 08:37 AM)
Yes, this diagram looks good. What I meant about the water heater live wire is in the picture below.

user posted image

This is the physical connection of the wires. This way the Current to the WH doesn't go through the busbar, but goes wire-to-wire. If you look at a busbar, the bar is rated for 120A (example) but the tines are rated for the Current to an MCB only. They way wiremen stuff the incoming wire into the MCB and get it to distribute is dangerous in my opinion.

Sorry, a bit busy to get on LYN. In the marine line, many ships right now. But I'll try to get back to you asap if you have any further questions.
*
I see. True also. Possible to slot 2 10mm cables & busbar tines into the same mcb . I mean does it fit?
Thanks for everyones input on this. Really appreciate it.