This is untrue. ST requires 10ma RCCB for all type of water heater. Plug and socket for water heater inside toilet is banned. I know why it's banned.Latest Guideline for water heater
RCCB for Water Heater
|
|
Jun 11 2023, 01:13 AM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
785 posts Joined: Jan 2003 |
QUOTE(mushigen @ May 17 2023, 01:22 PM) This is untrue. ST requires 10ma RCCB for all type of water heater. Plug and socket for water heater inside toilet is banned. I know why it's banned.Latest Guideline for water heater |
|
|
|
|
|
Aug 3 2023, 11:47 AM
Show posts by this member only | IPv6 | Post
#122
|
![]() ![]()
Junior Member
220 posts Joined: Sep 2021 |
QUOTE(ceo684 @ Mar 20 2023, 12:20 AM) i just checked my single phase db beside the lever have 63a 100mA rccd, so it is suggested to replace with 63a 30mA 2P? my house quite old already 20+ yearsABB https://shopee.com.my/ABB-RCCB-ELCB-FH202-A...93-457ea2c660fb Hager https://shopee.com.my/HAGER-CD263B-63AMP-2-...e1-9498152d9ef1 This post has been edited by xkaizoku: Aug 3 2023, 01:46 PM ceo684 liked this post
|
|
|
Aug 25 2023, 04:49 PM
|
![]() ![]()
Junior Member
196 posts Joined: Sep 2015 |
QUOTE(xkaizoku @ Aug 3 2023, 11:47 AM) i just checked my single phase db beside the lever have 63a 100mA rccd, so it is suggested to replace with 63a 30mA 2P? my house quite old already 20+ years This ABB model I think without anti-nuisance tripping function. Hager model stated with anti-nuisance tripping function, fyi. ABB https://shopee.com.my/ABB-RCCB-ELCB-FH202-A...93-457ea2c660fb Hager https://shopee.com.my/HAGER-CD263B-63AMP-2-...e1-9498152d9ef1 |
|
|
Aug 25 2023, 04:53 PM
|
![]() ![]() ![]() ![]()
Junior Member
612 posts Joined: Jan 2011 |
QUOTE(thinkgoodpositive @ Aug 25 2023, 04:49 PM) This ABB model I think without anti-nuisance tripping function. Hager model stated with anti-nuisance tripping function, fyi. nope, ABB does have https://library.e.abb.com/public/7115a45a1e...421002B0201.pdf |
|
|
Aug 28 2023, 10:09 AM
|
![]() ![]()
Junior Member
196 posts Joined: Sep 2015 |
QUOTE(em_on @ Aug 25 2023, 04:53 PM) Ya I know this model got. What I meant was the one ABB model FH202 quoted by him earlier in the shopee link. |
|
|
Aug 29 2023, 10:35 PM
Show posts by this member only | IPv6 | Post
#126
|
![]() ![]()
Junior Member
220 posts Joined: Sep 2021 |
|
|
|
|
|
|
Aug 30 2023, 09:40 AM
|
![]() ![]()
Junior Member
196 posts Joined: Sep 2015 |
QUOTE(xkaizoku @ Aug 29 2023, 10:35 PM) https://library.e.abb.com/public/7115a45a1e...421002B0201.pdfThis AP range but not sure is commonly available online in Malaysia or not. |
|
|
Aug 30 2023, 09:33 PM
|
![]() ![]() ![]()
Junior Member
383 posts Joined: May 2005 |
Actually ABB FH202 AC-63/0.03 does has anti nuisance tripping. You can search using its SKU at ABB website where it does list 250A max surge current. AP-R range is their high immunity model and usually hard to find ready stock. If you have excessive tripping during lightning that not even close by, it is usually due leakage/short from neutral to earth that high resistance enough preventing it from tripping the RCCB on normal days. Only the lowest end consumer RCCB (for 30ma/100ma) don't have anti nuisance tripping.
This post has been edited by jio: Aug 30 2023, 09:34 PM |
|
|
Oct 3 2023, 12:25 PM
|
![]()
Junior Member
15 posts Joined: Jan 2022 |
|
|
|
Oct 3 2023, 07:00 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
|
|
|
Oct 3 2023, 08:45 PM
|
![]()
Junior Member
15 posts Joined: Jan 2022 |
|
|
|
Oct 3 2023, 08:57 PM
Show posts by this member only | IPv6 | Post
#132
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,132 posts Joined: Apr 2014 From: Shah Alam, Selangor |
QUOTE(Richard Walter @ Oct 3 2023, 12:25 PM) I believe you will have unnecessary tripping faults. You have made a common Neutral busbar for both the top RCCB (Marked "40A 30mA" - Let's call this RCCB1) and the bottom RCCB (Marked "63A 100mA or 40A 30mA" - Let's call this RCCB2)This may happen : Current flows through RCCB1 live > MCB 16A > socket in room > appliance > Neutral wire back to DB > Neutral busbar > RCCB2 Neutral. Your RCCBs will trip. You have to split the Neutral busbar for RCCB1 and RCCB2. The WH Neutrals must be connected to the RCCB2 Neutral busbar, as the current to the WH originated from RCCB2. Also, physically, when I am making the connections, I would connect the 10 mm² wires together. This is for the WH Live. In the drawing it is connected through the Live busbar at each end. Potentially the Live busbar will heat up. This post has been edited by stormer.lyn: Oct 3 2023, 09:08 PM |
|
|
Oct 4 2023, 11:49 AM
|
![]()
Junior Member
15 posts Joined: Jan 2022 |
QUOTE(stormer.lyn @ Oct 3 2023, 08:57 PM) I believe you will have unnecessary tripping faults. You have made a common Neutral busbar for both the top RCCB (Marked "40A 30mA" - Let's call this RCCB1) and the bottom RCCB (Marked "63A 100mA or 40A 30mA" - Let's call this RCCB2) Oh no, The DB box only has 1 neutral busbar. Need to change DB box or can add another neutral busbar?This may happen : Current flows through RCCB1 live > MCB 16A > socket in room > appliance > Neutral wire back to DB > Neutral busbar > RCCB2 Neutral. Your RCCBs will trip. You have to split the Neutral busbar for RCCB1 and RCCB2. The WH Neutrals must be connected to the RCCB2 Neutral busbar, as the current to the WH originated from RCCB2. Also, physically, when I am making the connections, I would connect the 10 mm² wires together. This is for the WH Live. In the drawing it is connected through the Live busbar at each end. Potentially the Live busbar will heat up. For the WH live you mean replace the busbar to 10mm wire instead? Thanks ya |
|
|
|
|
|
Oct 5 2023, 01:05 AM
|
![]() ![]()
Junior Member
125 posts Joined: Mar 2009 |
QUOTE(stormer.lyn @ Oct 3 2023, 08:57 PM) I believe you will have unnecessary tripping faults. You have made a common Neutral busbar for both the top RCCB (Marked "40A 30mA" - Let's call this RCCB1) and the bottom RCCB (Marked "63A 100mA or 40A 30mA" - Let's call this RCCB2) May i know why you say so?Do you mean to have 2 separate Neutral busbar?This may happen : Current flows through RCCB1 live > MCB 16A > socket in room > appliance > Neutral wire back to DB > Neutral busbar > [b]RCCB2 Neutral. Your RCCBs will trip. You have to split the Neutral busbar for RCCB1 and RCCB2. The WH Neutrals must be connected to the RCCB2 Neutral busbar, as the current to the WH originated from RCCB2. Also, physically, when I am making the connections, I would connect the 10 mm² wires together. This is for the WH Live. In the drawing it is connected through the Live busbar at each end. Potentially the Live busbar will heat up. Eventually all the Neutral will be connect back to incoming(main) Neutral right? This post has been edited by lankorn: Oct 5 2023, 01:07 AM |
|
|
Oct 5 2023, 01:20 AM
Show posts by this member only | IPv6 | Post
#135
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(lankorn @ Oct 5 2023, 01:05 AM) May i know why you say so?Do you mean to have 2 separate Neutral busbar? Actually on second thought. Why not just use a single 63 0.03 RCD since it’s on single phase. There is no need to split DB.Eventually all the Neutral will be connect back to incoming(main) Neutral right? It’s because the neutral group of circuits on RCCB A should not be mixed with neutral group of circuits on RCCB B before passing the “checkpoint”. |
|
|
Oct 5 2023, 01:30 AM
|
![]() ![]()
Junior Member
125 posts Joined: Mar 2009 |
QUOTE(ceo684 @ Oct 5 2023, 01:20 AM) Actually on second thought. Why not just use a single 63 0.03 RCD since it’s on single phase. There is no need to split DB. I cannot understand It’s because the neutral group of circuits on RCCB A should not be mixed with neutral group of circuits on RCCB B before passing the “checkpoint”. This post has been edited by lankorn: Oct 5 2023, 01:30 AM |
|
|
Oct 5 2023, 01:49 AM
Show posts by this member only | IPv6 | Post
#137
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(lankorn @ Oct 5 2023, 01:30 AM) Mixing your neutrals BEFORE the RCD "checkpoint" has different implications.U know how shops like genki sushi and sushi king charge for per-plate kaiten belt sushi? RCD operates like u eat, u pay for your plate tower. Now let's say I eat, I don't know you, but I put my plates into your table. This post has been edited by ceo684: Oct 5 2023, 01:52 AM Attached thumbnail(s) lankorn liked this post
|
|
|
Oct 5 2023, 07:49 AM
|
![]()
Junior Member
15 posts Joined: Jan 2022 |
|
|
|
Oct 5 2023, 08:37 AM
Show posts by this member only | IPv6 | Post
#139
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,132 posts Joined: Apr 2014 From: Shah Alam, Selangor |
QUOTE(Richard Walter @ Oct 5 2023, 07:49 AM) Done changed the RCCB & DB box to the one with double neutral bars. Yes, this diagram looks good. What I meant about the water heater live wire is in the picture below.Should be good to go right? Waiting for the wireman to fix on weekend. ![]() This is the physical connection of the wires. This way the Current to the WH doesn't go through the busbar, but goes wire-to-wire. If you look at a busbar, the bar is rated for 120A (example) but the tines are rated for the Current to an MCB only. They way wiremen stuff the incoming wire into the MCB and get it to distribute is dangerous in my opinion. Sorry, a bit busy to get on LYN. In the marine line, many ships right now. But I'll try to get back to you asap if you have any further questions. |
|
|
Oct 5 2023, 10:49 AM
|
![]()
Junior Member
15 posts Joined: Jan 2022 |
QUOTE(stormer.lyn @ Oct 5 2023, 08:37 AM) Yes, this diagram looks good. What I meant about the water heater live wire is in the picture below. I see. True also. Possible to slot 2 10mm cables & busbar tines into the same mcb . I mean does it fit?![]() This is the physical connection of the wires. This way the Current to the WH doesn't go through the busbar, but goes wire-to-wire. If you look at a busbar, the bar is rated for 120A (example) but the tines are rated for the Current to an MCB only. They way wiremen stuff the incoming wire into the MCB and get it to distribute is dangerous in my opinion. Sorry, a bit busy to get on LYN. In the marine line, many ships right now. But I'll try to get back to you asap if you have any further questions. Thanks for everyones input on this. Really appreciate it. |