 RCCB for Water Heater

views
     
SUSceo684
post Apr 9 2020, 12:24 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




WHOLE HOUSE
Recommend 30mA as little use to put an insensitive RCD unless you run huge motors (industrial) use.
According to Hager, shock exceeding 50mA is lethal.

Refer page 2 - Attached File  Technical_Handbook_10x15cm_English.pdf ( 3.41mb ) Number of downloads: 324


WH 10mA RCD
RCD 10ma need to be combined with the MCB 16A or 20A depending on your load amps of water heater.
There is no requirement to position the RCD outside WH. In DB box also same protection as the RCD work on differential L-N. If 13.000A incoming on L, at least 12.990A must return otherwise it will trip (current loss = fault somewhere).

You can choose either to add on RCD 10ma + combine with MCB,
or
RCBO (all in one) device - RCD+MCB in one slot (eg Schneider)

They cost about the same..
EU made ABB or Hager RCD 17x-19x bucks
CN made SE RCD is about 105
CN made SE RCBO 175

Recommend match back the brand you have in your DB box unless its some local made/CN stuff that doesn't get international certification.

Do note 2P RCD 10ma usually take up 2 more slot in DB box. Whereas for the RCBO you can just replace MCB with it directly.

Also need to identify which is the neutral wire dedicated for WH circuit.
In my new place built 2018 no problem they actually put in some china brand RCD but it is combined 40A 10ma for two WH circuits (which even ABB, Hager unable to produce such model). I replace with ABB 10ma RCD and split to two circuits/two RCD 10ma (i.e. dedicated RCD to one circuit) as they should be.

For my old place built 1995 i add in RCD 10ma keep on tripping when on WH. WH no issue with 30ma main RCD. Suspect wiring problem with original 1995 wiring so I run dedicated line to WH from the RCD 10ma in DB box then it was OK, since its MCO I only have 2.5mm cable but it works fine for temporary solution.

Aircon load 4-7A only for 1-1.5hp typical operating load.
WH is the one that heat up wires as typical load is 13.7-16A depending on power rating.

This post has been edited by ceo684: Apr 9 2020, 04:24 PM
SUSceo684
post Aug 4 2020, 07:21 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(Chengi @ Aug 4 2020, 12:16 PM)
i have RCBO just before my storage heater. But honestly, how many times you would test it in 1 year if you were to put it just before heater?
*
Maybe once a year should suffice if it's a good brand and not some kind of questionable CN brand..
SUSceo684
post Aug 6 2020, 06:53 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(iSean @ Aug 6 2020, 01:30 AM)
What does WH means  hmm.gif
*
water heater bruce.gif
SUSceo684
post Aug 29 2020, 03:46 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(amco @ Aug 29 2020, 03:00 AM)
Good idea, but it's troublesome to change to bigger DB Box and find the neutral wire dedicated for the water heater and need also separate the neutral bar for just water heater.
For simplicity i just change the socket or plug with built-in RCBO according to usage amphere. All of my water heaters and air conditioners are with RCBO either with socket or plug. Much easier

I have this 10mA but only 13A for water heater.

user posted image
*
That may work for aircon but WH at 3300W / 230V = 14.3A, 3600W = 15.6A which is a fire hazard to knowingly overload the 13A socket.

Schneider 1-DIN module RCBO is available so it is just direct replacement of the WH MCB in DB box.

This post has been edited by ceo684: Aug 29 2020, 03:48 AM
SUSceo684
post Aug 31 2020, 10:49 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(amco @ Aug 29 2020, 04:32 AM)
Actually, I am using China's plug & socket which is 16A for water heater with tank. That 13A is suitable for AC and tankless water heater.
*
I don't think it's suitable for water heater since normal running already exceeded 13A.
Attached Image

The correct one should use 30mA for whole house RCD, and 10mA RCD specific for each WH circuit as per ST guidelines.

Attached Image
SUSceo684
post Apr 19 2021, 10:45 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Apr 19 2021, 09:55 PM)
can anyone recommend an installer for external rccb ?
*
Well, it is supposed to be inside the DB box.
Any qualified electrician will be able to handle the installation of 10mA RCD.

Generally if theres enough space in the DB box for 2 modules ("fat RCD") then no problem to add it in, else may need to consider using slim 1 module RCBO instead. U can take a pic of the DB box and show us for better commentary. No need to open until can see wires. Just the user accesible portion will do.

There may be false tripping if your WH circuit is not dedicated circuit but running on looped (shared) neutral as the 10mA RCD is a highly sensitive device.

This post has been edited by ceo684: Apr 19 2021, 11:03 PM
SUSceo684
post Apr 19 2021, 11:39 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Apr 19 2021, 11:26 PM)
attached is my current box, its messy as i requested my electrician to change all fuse mcb to trip mcb, but somehow my autogate and bell stop working and he cant seems to figure out how.

So i asked him to stop work and tmr another electrician will come.

So i told this new electrician i want RCCB outside toilet and i am not sure he understand what i want so he said he will come and see first
*
Oh dear. Best to get the new electrician to do complete overhaul change all the MCBs to one brand (ABB/Hager). The MCBs around RM7-8 bucks each only at the electrical store.

As you can see, between the taller ones and the shorter ones there are physical differences. This is a very dangerous situation as it is a loose connection (can catch fire) for the top row of short Hager fuse boxes.

Judging from the age of the whole setup, it is likely that the wires has broke internally for the one that powers your autogate (internal injury of the cable).

Normally we will advise user to turn off the questionable circuit until the electrician comes - but in this case there are alot of LIVE WIRES hanging around with masking tape as insulation puke.gif - so please do NOT touch it at all

This post has been edited by ceo684: Apr 19 2021, 11:49 PM


Attached thumbnail(s)
Attached Image
SUSceo684
post Apr 20 2021, 10:56 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(stormer.lyn @ Apr 20 2021, 08:30 AM)
You absolutely cannot use a shared neutral through a RCCB/RCBO.
*
Yup, as this 10mA is for WH circuit only.

Whole house one still return to neutral common link so no issue for the whole house RCD.

QUOTE(Zot @ Apr 20 2021, 08:45 AM)
I believe if the N is shared before the RCCB, it is still okay. Not between RCCB and device being protected.
*
Prev owner contractors did funny things for connecting the WH. I pulled new dedicated cables for the WH and all good smile.gif
SUSceo684
post Apr 20 2021, 06:34 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Apr 20 2021, 02:50 PM)
Thanks ceo684, finally got someone to fix back everything and change the mcb.

I plan to pull new wires from dbbox since i have shared heater and ac on all three bedrooms upstairs.

always have to off ac before use heater. so far no issue, just troublesome.

Any electrician whom u can recommend or u able to do?
*
Your new electrician should be able to handle?
Since new wiring (new set of LNE cables) being pulled it may make sense to procure the material yourself and ask him to come to install as labour only if agreeable and also it will save some cost lah.

Ideally, following ST guidelines, core scope of work will be
Pull a new set of 2.5mm² LNE cables for each AC unit
Pull a new set of 4.0mm² LNE for each WH unit
Add in C20 MCB for all the above circuits
Add in 10mA RCD to the DB box, one RCD for each WH circuit
Add in 20A double pole WH switch for each WH circuit outside bathroom
Add in 20A double pole switch for each aircon

Additional nice to haves:
Whether to conceal (need extensive hacking) or just run surface mounted PVC conduit (no need extensive hacking, minor hacking required) will be a price+aesthetic consideration.

Replace whole hse main incomer from switch fuse and old 100mA RCD - to new whole hse RCD 30mA + new whole house MCB (40/63A depending on existing cable size)

This post has been edited by ceo684: Apr 20 2021, 06:36 PM
SUSceo684
post Apr 22 2021, 11:30 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Apr 21 2021, 07:55 PM)
Cos he doesnt do hack/conceal, only do casing sweat.gif  sweat.gif

But i manage to find another electrician already, also prefer not to do hacking so i said will have to find some contractor to do hacking first

So i got quoted 3550RM without hacking for:-

a) install second DB at second floor 500
b) pull 3 wires for AC & switch 180*3 540
c) pull 3 wires for WH & switch 180*3 540 or 250*3 750 dep on 4mm² follow spec or 2.5mm²
d) pull 1 wire for water pump & switch 130
e) pull 3 wires for socket 130*3 390

reasonable?
*
roughly circa 2100 for the electricals; and the rest will be the hacking work.
Sounds about right.
SUSceo684
post Jun 9 2021, 08:27 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Jun 9 2021, 05:51 PM)
btw can we change the neutral and live for rccb?

The electrician already changed the whole DB Box and mcb but didnt change the RCCB cos he said still can use but still charged me full sum cry.gif  .

I just ok that time, but now i bought another hager RCCD and think just install myself.

The new RCCB stated that top left no. 1 is live but my old RCCB the top right is live instead and the wire not long enough if wanna switch.
*
You need to plan out how to reposition it. When there is limitation of wire length, this becomes tricky.
I've done replacement of DB for such hangmen tight wires that it may require some creative placement (to ensure everything can be connected).
For the wiring that came with the house.. that one no comment la can't do much; but for new wiring enough slack inside the DB box is important so you can configure accordingly.

Not sure how the NEW DB (current condition) look like but from the OLD BOX you can isolate the whole house off by disabling the fuse marked with Danger High Voltage (pull out the fuse and put it safely away on a table).
The incomer will be a problem to shut off but if you can shut off the whole house using the fuse (pull out) then you can work on the downstream components AFTER it.

Your new RCCB (30mA) can replace the existing one (i.e. second module) of the OLD BOX pic AFTER you have isolated the power.

Ref OLDBOX2 pic:
Busbar and 16mm² mega kabel pigtailsin the correct RED/BLACK colours can be purchased as loose cut (by meter).. LINK (Loose cut 16mm)

This post has been edited by ceo684: Jun 9 2021, 08:43 PM


Attached thumbnail(s)
Attached Image Attached Image
SUSceo684
post Jun 10 2021, 12:13 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Jun 9 2021, 09:06 PM)
Oh looks like my old setup the live is on RCCB top left, in my new setup (see attached pic), its on top right, so it means no issue to switch from left to right?
*
Whoever did this should be banned from working with electricity. bruce.gif
The original (OLD FUSE) is 40A (sized for 10mmsq cable). Cannot suka suka replace with 63A breaker without changing ALL the wire to 16mmsq.
Should be fitted with C40 (NOT C63). 🔥🔥🔥🔥🔥 risk - cable all burn but the master MCB will not trip.."haven't overload >63A mah!" shocking.gif

Attached Image

You can park the new RCD at the far right and just extend with new pigtails.
Attached Image
Attached Image
I see the new one also 100mA whistling.gif Should return it and request to change it to a 30mA RCD instead as 100mA whole house is NOT up to code.
A single phase 40A 30mA RCD is not expensive. It make a world of difference between a 30mA or 100mA if there is a fault situation passing thru a human.

QUOTE
The nominal rating of 30mA has thus become the internationally accepted norm for RCDs intended to provide additional protection against the risk of electrocution.

For further reading can see BEAMA (UK/BS standards) on RCDs. Attached File  BEAMA_RCD_Handbook__Dec_2010_.pdf ( 4.78mb ) Number of downloads: 51


Only in Msia lives are cheap- we still sell 100mA and 300mA openly shakehead.gif






Unmodified file rotated for easier viewing
Attached Image

This post has been edited by ceo684: Jun 10 2021, 12:14 AM
SUSceo684
post Jun 11 2021, 01:21 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Jun 11 2021, 12:42 AM)
Hmm already buried all the wires into wall can the electrician uncle just pull the cable out without hacking?

I was thinking about 30mA RCD too but when he tried to install a 10mA RCD at the water heater plug downstairs, it keeps tripping. The plug point has looping (to another 4 sockets which i am not using except for a socket for a hood) which causes the tripping according to him. So to be safe i thought just used back the original 100mA since no tripping issue.

The electrician also install new DB upstairs (as attached). Anything i should ask him to change besides to change the 10mm to 16mm? The water heater cable he is using 2.5mm instead and he said trust him no issue one even after i show him the ST guidelines, i suppose should be ok right since my water heater is only 15amp. Not an easy uncle to deal with, even after i bought 10mA RCD and asked him to install, he refuses saying ppl will laugh at me. Only agreed after i showed him the Electricity Regulations.  shakehead.gif  shakehead.gif
*
Personally 30mA whole house will be fine since total amps IN = total amps OUT regardless how it is looped after that.
Attached Image
I run 30mA whole house myself no issue.
My parent's place also had this same problem where the WH circuit was shared with other things and its NOT dedicated. 10mA always trip. Resolved by running dedicated LNE circuit to the WH.
The difference is that the SINGLE circuit 10mA RCD had "unexplainable and unaccounted for amps from other devices" that the 10mA cannot account for = trip first talk later, save life more important.
Whereas for WHOLE HOUSE 30mA.. as long as total amps IN = total amps OUT (since there's only one IN and one OUT cable back to TNB meter) it will be fine, even high sensitivity 30mA also OK.

Anyway, congrats for putting in the 10mA RCDs for better electrical safety. thumbup.gif

The difference is in 10mA WH circuit:
Even in cases where the WH circuit is actually shared neutral and trips the 10mA (because the neutral also contain other appliances' return so its imbalance with the incoming amp), this will not affect the whole house RCD.


This one can be solved by (a) correct way i.e. running a dedicated LNE circuit to that WH itself, as per code, without looping or
(b) use dirty trick (not so code compliant but likely to work without extensive hacking all over) is to install RCD as a spur i.e. AFTER the 20A switch (load side) and BEFORE the WH, so only that particular line going to the WH is balanced amps between incoming and outgoing.

Regarding the 63A MCB used on 10mm wire..
Changing the 10mm to 16mm will be expensive. In this situation, since your 63A will never trip before the 10mm cable is overloaded, the TNB cutout fuse will be your Plan Z overcurrent protection (between TNB meter to DB box) since that should still be on original 40A fuse.
The difference with MCB vs fuse, one can be reset in case of overload (just flip the MCB back on) whereas a fuse once blow already it need someone to buy a replacement, and that replacement fuse will not be available fast if the electrical supply store is closed.

Regarding 2.5mm cable used for WH circuits;
Should be OK-lah with 2.5mm for WH if its just 15-16A load, within spec of the cable, as long as its all 3kW class heater (3xxx W). You cannot install those highlands model with 4800W using 2.5mm cable.
2.5mm can withstand 21A safely.

That uncle cannot explain why these happened leh.. nobody is laughing

QUOTE
September 2013 – Japanese man electrocuted while holding shower head of water heater. Wife electrocuted trying to save husband.
https://www.thestar.com.my/news/nation/2013...death-apartment

August 2014 – Pharmacist (lady) found electrocuted while still clutching shower head of water heater.
https://www.thestar.com.my/news/nation/2014...-clutching-show

July 2016 - https://www.straitstimes.com/asia/se-asia/m...e-having-shower

August 2020 https://www.thestar.com.my/news/nation/2020...ted-in-bathroom

Singapore- using plug to connect WH
https://www.straitstimes.com/singapore/impr...while-showering

Since 2009; seven reported cases of death by electrocution on heated appliances, safety for electrical household appliances, SIRIM) (as of 2015)

7 Examples of WH Failure (Malaysia) https://www.st.gov.my/en/contents/presentat...er%20Heater.pdf
on heated appliances, safety for electrical household appliances, SIRIM):
-- Four cases involved water heaters
-- Three cases involved storage water heaters
-- Most cases RCCB (main) not working
-- In one case earth and live cables melted (found to be undersized).
-- In ALL cases, victim died while still holding onto metallic shower head.


This post has been edited by ceo684: Jun 11 2021, 01:33 AM
SUSceo684
post Jun 11 2021, 03:39 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Jun 11 2021, 03:07 PM)
» Click to show Spoiler - click again to hide... «


The cutout fuse already blown once when I tried to plug in a old computer, so TNB came and changed to new one at 63A

So i should just use back 40A should be enough ? Change everything to 40A since my wiring all is 10mm to the second DB also
*
Normally, a fuse is sacrificial i.e. rated lower than the cable to protect the cable from burning up.
The other way, cable will burn up first to protect a higher rated fuse from blowing.

The TNB to main DB (incomer) is 10mm also?

Having four water heaters on at the same time is 16Ax4, without adding on anything else. Upsizing fuse need the cable to be upsized accordingly as well.
SUSceo684
post Jun 19 2021, 02:35 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Jun 19 2021, 02:13 PM)
Tnb to main is 16mm at least I think.

Anyway I asked my electrician to change to 40a main switch and 40a rccb 0.03A. But even with full load of 51a tested using clamp meter, the thing doesnt trip? Something wrong ah? But the cable very hot though, almost 45 degree celcius compared to ambient of just 28 degree
*
The main switch need to be C40 MCB for it to trip on OVERCURRENT FAULT exceeding 40A.
Note: Just plain switch (isolator) without OVERCURRENT protection (ie No MCB function) does nothing to protect for OVERCURRENT.

When will MCB Slow Trip
In this case 51A > 40A its a sustained overload (MINOR OVERCURRENT FAULT) and it should "slow trip" using thermal trip within few mins.

QUOTE
In case of sustained overload more than the rated safe current of the MCB thermal bimetal tripping will operate in 2 secs to 10000 secs depending on the overload and not overcurrent or transients.


I'm assuming you got a hager C40 P/N MU240A installed.
According to datasheet, https://www.hager-me.com/products/energy-di...u240a/30368.htm
min/maxi threshold value of the AC thermal operation 1,13/1,45 In (meaning between 1.13x40A and 1.45x40A)
for the 51A (divided by 40A rating) is around 1.27 In
this means a time to trip about 500 seconds based on Hager MU datasheet
Attached Image
‐-----
When will MCB Fast/instant Trip
(It will do a "fast trip" on the magnetic trip only if there is a SHORT CIRCUIT/MAJOR OVERCURRENT FAULT).

-----
RCD working principle is DIFF from MCB

For the 0.03A RCD yes this will be instant trip for CURRENT IMBALANCE (LEAKAGE PROTECTION).
The 40A on this unit is an indicator on how much total current can be safely monitored..but this RCD does NOT & will NOT trip in case of OVERCURRENT (which is MCB job).

RCD only measure "I-in = I-out + (tolerance of loss x up to 0.03A)". If the loss x higher than 0.03 (eg 0.032A) it will trip because "something is missing somewhere".

This post has been edited by ceo684: Jun 19 2021, 03:11 PM
SUSceo684
post Jun 19 2021, 03:26 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(babybaby1988 @ Jun 19 2021, 03:12 PM)
Ahh no wonder.
Urmm lets say now my current usage now is 50A and then there is a leakage of 0.1A somewhere, will this 40A 0.03A RCCB trip?
*
For RCD it will trip.
Main RCD max current rating (40A part of that 40A 0.03) should match or exceed the main MCB rating (40A).
SUSceo684
post Oct 17 2021, 10:23 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(empoleon @ Oct 17 2021, 08:51 PM)
Please help me to check if my house wiring is correct.

My 3600W water heater shares a 16A MCB with the lights/fan in the kitchen, bathroom and 3rd bedroom. From what I understand light points use 1.5mm wires, so are the wires being overloaded now?
So far no problem. The heater was fixed 5 years ago by the shop people.

Another thing, all my light points use 16A MCB, while sockets use 20A. Should I change the 16A MCBs to something lower or it doesn't matter?
*
Lights should be C6 (6A) for safety. I don't think the installer would ever use 2.5mm for light circuits.

MCB must be rated lower than the cable safe load.
I suspect the WH is running on 1.5mm if its tapping into the light circuit if the WH circuit was not originally built in (wrong).

Shop ppl wont care.."not my house syndrome"

This post has been edited by ceo684: Oct 17 2021, 10:23 PM
SUSceo684
post Oct 17 2021, 11:53 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(empoleon @ Oct 17 2021, 10:57 PM)
This confirms my doubts. I wanted to DIY replace the heater but saw all these mistakes.

One more thing. I have another water heater, this one has its own circuit and is using a 16A MCB. Everytime the heater is used there's a buzz coming from the MCB. This has been going on for over 7 years. 2 years ago I changed the water heater to a new one and the buzz still happens. The installer said it's normal. Is this really normal? I suppose I can get the MCB replaced as the next troubleshooting step but keen to hear your experience on this.
*
Weird sounds are indicative of overload (close to redline) or loose connection.

What MCB brand are you using? It'll be good to check your cable sizing whether 1.5mm or 2.5mm...the former looks very thin. You can off the whole DB to check safely. The cable going out from MCB controlling WH should look like the sockets one..NOT like light circuits.
SUSceo684
post Nov 5 2021, 11:09 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hcmalaya @ Nov 5 2021, 08:14 PM)
Tumpang tanya
House rccb trip few times lately thunder
Notice the plastic part cracked
How much normally is the charge to replace it ah?
*
Depending on you're 1ph or 3ph supply, and how many amps. Take a pix and post lah.
SUSceo684
post Nov 5 2021, 11:59 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(hcmalaya @ Nov 5 2021, 11:10 PM)
Residential not all single phase ka?
*
I use 3 phase at home. whistling.gif The pricing of the device also depend on rated current. Hence if you're talking about single phase RCD, e.g. from ABB.os its 77 for 40A 30mA and 127 for 63A 30mA materials only

This post has been edited by ceo684: Nov 6 2021, 12:13 AM