WHOLE HOUSE
Recommend 30mA as little use to put an insensitive RCD unless you run huge motors (industrial) use.
According to Hager, shock exceeding 50mA is lethal.
Refer page 2 -
Technical_Handbook_10x15cm_English.pdf ( 3.41mb )
Number of downloads: 324WH 10mA RCD
RCD 10ma need to be combined with the MCB 16A or 20A depending on your load amps of water heater.
There is no requirement to position the RCD outside WH. In DB box also same protection as the RCD work on differential L-N. If 13.000A incoming on L, at least 12.990A must return otherwise it will trip (current loss = fault somewhere).
You can choose either to add on RCD 10ma + combine with MCB,
or
RCBO (all in one) device - RCD+MCB in one slot (eg Schneider)
They cost about the same..
EU made ABB or Hager RCD 17x-19x bucks
CN made SE RCD is about 105
CN made SE RCBO 175
Recommend match back the brand you have in your DB box unless its some local made/CN stuff that doesn't get international certification.
Do note 2P RCD 10ma usually take up 2 more slot in DB box. Whereas for the RCBO you can just replace MCB with it directly.
Also need to identify which is the neutral wire dedicated for WH circuit.
In my new place built 2018 no problem they actually put in some china brand RCD but it is combined 40A 10ma for two WH circuits (which even ABB, Hager unable to produce such model). I replace with ABB 10ma RCD and split to two circuits/two RCD 10ma (i.e. dedicated RCD to one circuit) as they should be.
For my old place built 1995 i add in RCD 10ma keep on tripping when on WH. WH no issue with 30ma main RCD. Suspect wiring problem with original 1995 wiring so I run dedicated line to WH from the RCD 10ma in DB box then it was OK, since its MCO I only have 2.5mm cable but it works fine for temporary solution.
Aircon load 4-7A only for 1-1.5hp typical operating load.
WH is the one that heat up wires as typical load is 13.7-16A depending on power rating.