 Waterproofing Water Leaking Problem, Ask Me Water Leaking, Waterproofing

views
     
brapa?
post Oct 16 2018, 12:12 AM

Getting Started
**
Junior Member
154 posts

Joined: Mar 2015
There is a leak somewhere at the toilet.
Contractor 1 - inject pu from above (ie tiled floor)
Contractor 2 - inject pu from below (ie neighbour ceiling below)

Which is the better way ?

SUSslimey
post Oct 16 2018, 01:09 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(brapa? @ Oct 16 2018, 12:12 AM)
There is a leak somewhere at the toilet.
Contractor 1 - inject pu from above (ie tiled floor)
Contractor 2 - inject pu from below (ie neighbour ceiling below)

Which is the better way ?
*
from the source aka from above.


crusher
post Oct 28 2018, 04:32 PM

Regular
******
Senior Member
1,345 posts

Joined: Jun 2006


Guys,

I have been facing this car pouch leaking issue near the beam. Currently the issue have been "rectified" by developer sub contractor under warranty. However, after PU injection still have water leakage stain as per photos below. Not sure is it water or the PU injection leaked out and touched plaster ceiling that causes yellowish

» Click to show Spoiler - click again to hide... «


Any kind input would be much appreciated.

Thank you
SUSslimey
post Oct 28 2018, 04:50 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(crusher @ Oct 28 2018, 04:32 PM)
Guys,

I have been facing this car pouch leaking issue near the beam. Currently the issue have been "rectified" by developer sub contractor under warranty. However, after PU injection still have water leakage stain as per photos below. Not sure is it water or the PU injection leaked out and touched plaster ceiling that causes yellowish

» Click to show Spoiler - click again to hide... «


Any kind input would be much appreciated.

Thank you
*
What type of roof above the car porch?
Also, does the position of the water mark coincide with the water drainage of the roof for the upper floor?
crusher
post Oct 28 2018, 05:17 PM

Regular
******
Senior Member
1,345 posts

Joined: Jun 2006


QUOTE(slimey @ Oct 28 2018, 04:50 PM)
What type of roof above the car porch?
Also, does the position of the water mark coincide with the water drainage of the roof for the upper floor?
*
Concrete slab.

Suspect the leakage leaked down from the beam. Unfortunately the water mark does not coincide with water drainage of the roof
SUSslimey
post Oct 28 2018, 06:13 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(crusher @ Oct 28 2018, 05:17 PM)
Concrete slab.

Suspect the leakage leaked down from the beam. Unfortunately the water mark does not coincide with water drainage of the roof
*
i suspect they PU injection the wrong place.

for concrete slab roof need to make sure :
1. level.......make sure there is declining level towards the drainage. no pooling of water.
2. water proofing. can paint with elastomeric paint(got various brand like nippon, pye, sika etc etc) after making sure the level is done properly. as usual, paint from above aka the source of water.
3. make sure the edges(where 2 section of concrete meet like a horizontal slab with a vertical wall for example) are properly waterproofed as these are the usual places where waterproofing failed.

This post has been edited by slimey: Oct 28 2018, 06:15 PM
crusher
post Oct 28 2018, 09:23 PM

Regular
******
Senior Member
1,345 posts

Joined: Jun 2006


QUOTE(slimey @ Oct 28 2018, 06:13 PM)
i suspect they PU injection the wrong place.

for concrete slab roof need to make sure :
1. level.......make sure there is declining level towards the drainage. no pooling of water.
2. water proofing. can paint with elastomeric paint(got various brand like nippon, pye, sika etc etc) after making sure the level is done properly. as usual, paint from above aka the source of water.
3. make sure the edges(where 2 section of concrete meet like a horizontal slab with a vertical wall for example) are properly waterproofed as these are the usual places where waterproofing failed.
*
Any recommendation for the contractor? Maybe I can engage a proper one to resolve my problem
Richard
post Oct 28 2018, 10:27 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


Try getting access to a contractor with a thermal imaging camera like a Flir mr176 or a fluke so you can see exactly where the water leak is from.

I've been watching a few YouTube videos on how those equipment are used but have no idea if anyone here has actual experience using one and making sense of the images. So maybe try asking around.

If you goggle Flir thermal camera you can find a rental company so maybe see if they provide a service(maybe a building inspector) to detect the leak/provide a report before then engage a contractor do the pressure injection repair.

This post has been edited by Richard: Oct 28 2018, 10:40 PM
SUSslimey
post Oct 28 2018, 10:50 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(crusher @ Oct 28 2018, 09:23 PM)
Any recommendation for the contractor? Maybe I can engage a proper one to resolve my problem
*
No recommendation. I would diy it anyway
cherroy
post Oct 29 2018, 11:44 AM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(brapa? @ Oct 16 2018, 12:12 AM)
There is a leak somewhere at the toilet.
Contractor 1 - inject pu from above (ie tiled floor)
Contractor 2 - inject pu from below (ie neighbour ceiling below)

Which is the better way ?
*
QUOTE(slimey @ Oct 16 2018, 01:09 AM)
from the source aka from above.
*
Normally it is done from below.
Reason:
As from below, the source of crack that lead to leaking can be found via the water dripping point, whereby PU can be injected from there and let the PU find its way to fill up the crack during pressuring.

If from above, then it is difficult to find the source of leak, so no way to start for the PU injection.


lucifah
post Oct 30 2018, 09:32 AM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(slimey @ Oct 28 2018, 06:13 PM)
i suspect they PU injection the wrong place.

for concrete slab roof need to make sure :
1. level.......make sure there is declining level towards the drainage. no pooling of water.
2. water proofing. can paint with elastomeric paint(got various brand like nippon, pye, sika etc etc) after making sure the level is done properly. as usual, paint from above aka the source of water.
3. make sure the edges(where 2 section of concrete meet like a horizontal slab with a vertical wall for example) are properly waterproofed as these are the usual places where waterproofing failed.
*
this. one time i see liao i know they injected at wrong place

should have injected it on the beam near the slab (topmost) or on the slab nearest to the beam

what i see is they inject in the MIDDLE of the beam, which does nothing
lucifah
post Oct 30 2018, 09:40 AM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(Richard @ Oct 28 2018, 10:27 PM)
Try getting access to a contractor with a thermal imaging camera like a Flir mr176 or a fluke so you can see exactly where the water leak is from.

I've been watching a few YouTube videos on how those equipment are used but have no idea if anyone here has actual experience using one and making sense of the images. So maybe try asking around.

If you goggle Flir thermal camera you can find a rental company so maybe see if they provide a service(maybe a building inspector) to detect the leak/provide a report before then engage a contractor do the pressure injection repair.
*
LOL... the thermal camera is very very expensive

and you cant see where the leak is from because the temperature difference between the liquid and concrete is very minimal if there is any

what you need is a moisture meter and u can check the "wettest" part of the beam / slab / column , which you can assume is the entry point of the water leakage
SUSslimey
post Oct 30 2018, 11:59 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(lucifah @ Oct 30 2018, 09:32 AM)
this. one time i see liao i know they injected at wrong place

should have injected it on the beam near the slab (topmost) or on the slab nearest to the beam

what i see is they inject in the MIDDLE of the beam, which does nothing
*
May have weaken the beam lol
crusher
post Oct 30 2018, 12:05 PM

Regular
******
Senior Member
1,345 posts

Joined: Jun 2006


QUOTE(slimey @ Oct 30 2018, 11:59 AM)
May have weaken the beam lol
*
You mean weaken the beam by injecting the middle or topmost?
crusher
post Nov 3 2018, 11:05 AM

Regular
******
Senior Member
1,345 posts

Joined: Jun 2006


Apparently the leaking after PU Injection has become worst. Water has been dripping down onto floor.

» Click to show Spoiler - click again to hide... «


Any good contractors can recommend to fix this issue? Afraid by the time contractor from developer come is too late
xAmdx
post Nov 3 2018, 11:10 AM

Casual
***
Junior Member
487 posts

Joined: Oct 2004


QUOTE(crusher @ Nov 3 2018, 11:05 AM)
Apparently the leaking after PU Injection has become worst. Water has been dripping down onto floor.

» Click to show Spoiler - click again to hide... «


Any good contractors can recommend to fix this issue? Afraid by the time contractor from developer come is too late
*
I had pm you the contractor which I engage previously to solve my bathroom leaking.
crusher
post Nov 3 2018, 01:27 PM

Regular
******
Senior Member
1,345 posts

Joined: Jun 2006


QUOTE(xAmdx @ Nov 3 2018, 11:10 AM)
I had pm you the contractor which I engage previously to solve my bathroom leaking.
*
Thanks for the contacts.

Guys heard of torch membrane water proofing?
lucifah
post Nov 3 2018, 03:12 PM

St. Fu
Group Icon
Staff
7,948 posts

Joined: Jan 2005
From: Soviet Sarawak


QUOTE(crusher @ Nov 3 2018, 01:27 PM)
Thanks for the contacts.

Guys heard of torch membrane water proofing?
*
yes, expensive and only suitable for large exposed area like flat roof or balcony

plus this one u need to make sure u do it properly the first time since its pretty difficult to find the leaking point after u install the membrane
crusher
post Nov 3 2018, 07:04 PM

Regular
******
Senior Member
1,345 posts

Joined: Jun 2006


QUOTE(lucifah @ Nov 3 2018, 03:12 PM)
yes, expensive and only suitable for large exposed area like flat roof or balcony

plus this one u need to make sure u do it properly the first time since its pretty difficult to find the leaking point after u install the membrane
*
Yes aiming to do at roof. However developer most likely wont opt for this
xAmdx
post Nov 4 2018, 10:44 AM

Casual
***
Junior Member
487 posts

Joined: Oct 2004


QUOTE(crusher @ Nov 3 2018, 07:04 PM)
Yes aiming to do at roof. However developer most likely wont opt for this
*
My boss project we are using this application to do. However the mixture of the concrete also had waterproofing capabilities.


Attached thumbnail(s)