QUOTE(robert82 @ Oct 18 2018, 04:26 PM)
"Usually the 20A switch is serve directly by a single 20A MCB. "
Does this means if i check in DB i can confirm it?
" Usually the fan even probably loop through lighting N wire."
Sorry, in layman terms, if the fan and light loop through the lighting N wire, then i connect it to the side 20AMP ac neutral, not an issue?
Just make sure your two AP channels are not overlapping each other. Both 2.4GHz? If they are and if you are setting them for 802.11n, then use channel 3 and 11.
Sounds doable, I'll leave this to the last, i have tinkered with them previously, not per my expectations.
Yes. Find which MCB that cut the power off to the 20A switch. Most likely one of the one labelled 20A.
Standard wiring usually like this:
1 x 16A MCB > 1 x 3-pin socket
1 x 20A MCB > 2 x 3-pin socket
1 x 32A MCB > 4 x 3-pin socket
1 x 32A MCB > 6 x 3-pin socket (if using ring configuration)
1 x 20A MCB > 1 heater point through 20A DPDT switch
1 x 20A MCB > 1 air-con point through 20A DPDT switch
1 x 6A MCB > 6 x light
1 x 6A MCB > 6 x light point/fan
As for the light and fan switches, the N wire is looped at ceiling level. That is why only L wire go to switches.
In single phase wiring, all N wire go back to same point at DB. So, you can tap any nearby N wire. Normally this will not trip RCD.
If 3-phase wiring, most likely the N for each phase go back to separate RCD. So, if there is any imbalance is current return compare to current to devices, the RCD will trip because RCD assume there is short or leakage.
For me, it is safe to tap N from any wire though certified electrician will say cannot. So, take note on this. This is my word only though I'm confident with it
You can refer TNB wiring practice here
https://www.scribd.com/doc/125868342/Suruha...ing-Residential