 Home Electrical MCB, How to size Miniature Circuit Breaker

views
     
Sydneguy
post Oct 11 2013, 04:41 PM

Casual
***
Junior Member
383 posts

Joined: Jul 2013


QUOTE(stevie8 @ Oct 11 2013, 02:53 PM)
Thanks for the input. You got me, "the only real reason to do what you suggested is to save $ and time inconvenience on hacking and plaster back"

Anyway, hacking is unavoidable for the installation of sub DB where I need to hack out the cable long enough to get all of them one by one into the MCBs in the sub DB. The problem is to hack thru the slab and beam. I do not want another hole thru the beam which is at the middle of the house, it only weaken the beam.

I just need to find two 4mm wires each and twist them together which will support 60A, right? Below is the potential load up-stair:

1 x 2 1/2 hp aircond
2 x 1 hp aircond
1 x iron
5 x fans (not on when use aircond)
30 x downlight, wall light and table lamp.
1 x vacuum cleaner (not use when ironing), my wife cannot be doing 2 things at a time
Many power sockets but seldom use other than mentioned above for ironing, vacuuming, also for charging handphone, hair dryer, no water heater (I use solar heater), TV, Audio, PS2 games.

Therefore, one 4mm for 32A could be enough, but 2 x 4mm definitely more than enough. Then need to connect 2 x 4mm wire to one 8mm wire to the sub-DB.

What do you think if I use lead soldering to join the 2 4mm wire together instead of twisting them together for terminating at the sub-DB and the down stair DB? How good is the lead joint conducting electricity compare to bear copper wire?

Cheers
*
Once you pull all the old wires that went upstairs out there will be a big hole in the floor/beam for you to put the new thick wire through , Problem Solved. thumbup.gif
TSstevie8
post Oct 11 2013, 08:40 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(Sydneguy @ Oct 11 2013, 04:41 PM)
Once you pull all the old wires that went upstairs out there will be a big hole in the floor/beam for you to put the new thick wire through , Problem Solved.  thumbup.gif
*
1. There are floor tiles at first floor, the hole could have been sealed during tiling.
2. Plaster ceiling at ground ceiling where the cables going thru the beam except that the hole at the beam was not sealed.
3. Then on top of the main DB where the new thick cable coming down from plaster ceiling the wall is concealed with many wires from all over the house, cannot hack but to run externally with plastic casing.

3 obstacles that is why am considering using the existing cables, otherwise, I will not hesitate using one thick cable. Anyway got to consult electrician and plaster ceiling guy and tile rclxub.gif I do not think can find same pattern tile. 12 yrs already.

This post has been edited by stevie8: Oct 11 2013, 08:42 PM
firdaruddin
post May 9 2016, 01:57 PM

Getting Started
**
Junior Member
76 posts

Joined: Nov 2005
From: KL


Hello. I have a situation where a fuse keep kicking back. The pic of the db is attached. The one that always kicking back is the 20A one. So the question is, can I change the fuse directly or i should change the wire first to 4mm?


Current wire size is 1.5mm. I think.


Attached thumbnail(s)
Attached Image
Richard
post May 9 2016, 05:43 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(stevie8 @ Oct 9 2013, 02:02 PM)
Anyone knows how to size MCB of our home?

Got B,C,D type and different Amperage. How and what to choose?

[attachmentid=3667236] [attachmentid=3667238]
*
B, C, D types are for the inrush current.. Domestic uses type B

Ampere rating are for current overload protection of the cable. Size the amps according to the cabl's current carrying capacity..

Scroll to the btm of the page, the link at the btm.. Read it.
Suruhanjaya Tenaga - Guidelines for Electrical Wiring in Residential Building 2008
Richard
post May 9 2016, 05:55 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(firdaruddin @ May 9 2016, 01:57 PM)
Hello. I have a situation where a fuse keep kicking back. The pic of the db is attached.  The one that always kicking back is the 20A one.  So the question is, can I change the fuse directly or i should change the wire first to 4mm?
Current wire size is 1.5mm. I think.
*
Is this a new installation and is it a new mcb?
If yes then its probably this circuit is overloaded causing a thermal trip.. Get a clamp ammeter and cheack the load and compare it to the mcb's rating.. If overloaded then remove part of the load to another circuit (If it's more that one load on the circuit)

If no (meaning it was working well previously) then listen carefully to this particular mcb.. If you hear small crackling sounds before tripping then replace the mcb. The mcb has pitted contacts, that means the contact area has reduced to the point where it itself causes the thermal overload.. The device is faulty..

You only replace wiring if the insulation is damaged and you test with an insulation tester (Meggar).. Hire an electrician for this.. He has the equipment and competency to use it.. You cannot use a multimeter..
Richard
post May 9 2016, 06:07 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Xccess @ Oct 10 2013, 08:23 PM)
Here you go.
user posted image
*
This picture shows a Three phase Distribution board (DB)..

It's protection device ia a 4 pole Residual Current device (the one with the yellow trip button)

QUOTE(stevie8 @ Oct 10 2013, 08:47 PM)
By the way your RCCB is 0.3A (300mA). Mine is 0.1A more sensitive.
*
The RCD is for 3 phases that's 100mA trip per phase..

Whether yours (0.1A) more sensitive depends if you have 3 Phase supply ..

meaning is your RCCB 2P or 4P?

If 2P then i think it is not more sensitive..
firdaruddin
post May 9 2016, 10:33 PM

Getting Started
**
Junior Member
76 posts

Joined: Nov 2005
From: KL


QUOTE(Richard @ May 9 2016, 05:55 PM)
Is this a new installation and is it a new mcb?
If yes then its probably this circuit is overloaded causing a thermal trip.. Get a clamp ammeter and cheack the load and compare it to the mcb's rating.. If overloaded then remove part of the load to another circuit (If it's more that one load on the circuit)

If no (meaning it was working well previously) then listen carefully to this particular mcb.. If you hear small crackling sounds before tripping then replace the mcb. The mcb has pitted contacts, that means the contact area has reduced to the point where it itself causes the thermal overload.. The device is faulty..

You only replace wiring if the insulation is damaged and you test with an insulation tester (Meggar).. Hire an electrician  for this.. He has the equipment and competency to use it.. You cannot use a multimeter..
*
Hi. It was an old thing. It happened whether i switch on my computer or nothing while I'm not switch anything at all. It kicked back like ikut suka dia. So my plan maybe upgrading the 20A fuse by changing it to 32A fuse. Is it possible the problem will still occur after changing the fuse directly? Also that fuse goes to one 3-pin point and then loop for two more 3 pin point outside the room for washing machine use.
fireballs
post May 9 2016, 10:36 PM

10101
*******
Senior Member
5,646 posts

Joined: Mar 2012
QUOTE(firdaruddin @ May 9 2016, 01:57 PM)
Hello. I have a situation where a fuse keep kicking back. The pic of the db is attached.  The one that always kicking back is the 20A one.  So the question is, can I change the fuse directly or i should change the wire first to 4mm?
Current wire size is 1.5mm. I think.
*
get a new one. this time dun buy fanban multi9

fireballs
post May 9 2016, 10:38 PM

10101
*******
Senior Member
5,646 posts

Joined: Mar 2012
QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
Hi. It was an old thing.  It happened whether i switch on my computer or nothing while I'm not switch anything at all. It kicked back like ikut suka dia. So my plan maybe upgrading the 20A fuse by changing it to 32A fuse. Is it possible the problem will still occur after changing the fuse directly?  Also that fuse goes to one 3-pin point and then loop for two more 3 pin point outside the room for washing machine use.
*
the normal washing machine should be fine, as long as you dont use iron and hairdryer all at the same time.
as said, most likely its a busted mcb. just change but change to better brand.
Richard
post May 10 2016, 03:16 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
Hi. It was an old thing.  It happened whether i switch on my computer or nothing while I'm not switch anything at all. It kicked back like ikut suka dia.
*
Firstly, use the correct terms for the components, it helps avoid confusion..

A fuse cannot kick back.. It is a fusible link.. It blows (meaning gets hot, melts thus disconnect) when over rated current flows through..
A miniature circuit breaker (mcb) trips (meaning there's a bimetal contact which trips a spring) when over rated current flows ..
You replace a fuse.. You reset an mcb (only replace if faulty)..


QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
So my plan maybe upgrading the 20A fuse by changing it to 32A fuse. Is it possible the problem will still occur after changing the fuse directly?
*
Yes, it is possible.. This is a forum and I'm just giving my opinion. You need an actual competent person to repair it.. (An electrician)

However the fuse or mcb function is to protect the wire.. It blows/trips before the wire gets hot.. A 1.5mm wire is rated at 23Amps..

QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
Current wire size is 1.5mm. I think.
*
A 32A fuse/mcb cannot protect a 1.5mm wire.. The wire will melt and burn anything combustible close to it..
It might burn down your house.. Pls understand your risk..

Hire an electrician if you don't know what I'm talking about.. It will save you more..

QUOTE(firdaruddin @ May 9 2016, 10:33 PM)
Also that fuse goes to one 3-pin point and then loop for two more 3 pin point outside the room for washing machine use.
*
ok..

Standard domestic wiring regulation requires you use 2.5mm2 or higher size wire for sockets..

When new the metal within the wire is pure .. An older wire oxidizes and its insulation degrades.. It cannot carry rated current and heats up when over current..

Regulation states you must completely rewire after 30 years.. I rewired my house after 20 years.. It's my insurance..

Good luck..

This post has been edited by Richard: May 10 2016, 03:42 AM
firdaruddin
post May 10 2016, 02:12 PM

Getting Started
**
Junior Member
76 posts

Joined: Nov 2005
From: KL


Another question. Is there any way for me to determine which wire go to that particular point etc.? I mean if i want to change the whole box with the fuse everything. So that i can reconnect the wire to the box correctly. 1 seperate fuse for a/c etc.
Richard
post May 10 2016, 10:05 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(firdaruddin @ May 10 2016, 02:12 PM)
Another question. Is there any way for me to determine which wire go to that particular point etc.? I mean if i want to change the whole box with the fuse everything.
*
Yes.. Switch off all your miniature circuit breakers (mcb)..

Standard wiring mcb's all type B's except motor (if nuisance tripping then use type C or D for higher inrush(start) current)
-------------------------------------------------------------------------------------
6A & 10A are lighting mcb's
16A & 20A are socket/aircon/water heater mcb's
32A are cooker/large freezer/3HP & above motor mcb's

- Switch on only one mcb
- Visually check which one has power and record on the mcb
- Switch off
- Repeat next mcb..

QUOTE(firdaruddin @ May 10 2016, 02:12 PM)
So that i can reconnect the wire to the box correctly. 1 seperate fuse for a/c etc.
*
Seriously..? I myself am certified with ST but i get an electrician to do the work.. For me it's a matter of cost and speed.. I can talk the talk but crawl the walk if you get what I mean..

For you I think it will be an additional safety issue.. Wiring a whole house with 20-40 points is not an amateur DIY..
One point is ok.. Not whole house.. you're crazy to think you can do it..

beLIEve
post May 6 2017, 12:38 AM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


I spoke to a friend and it appears that there is more to just the amperage on the MCB vs the amount of current you need to size an MCB. If the amount of current is below the MCB's rating multiplied by the value of its type, there'll no trip. In an overcurrent situation, most likely your electrical/electronic device will get fried (it's gotta be already faulty to draw excessive current) before your wire if you're lucky.

To size it, you'll need to know all the resistance involved (wire, devices, earth loop, inrush current). Not sure how many have the equipment to perform these tests?

Anyway, just to share.

http://www.studyelectrical.com/2014/07/min...tic-curves.html

QUOTE
MCBs are classified according to tripping over range of fault current as follows:

    Type B MCB
    Type C MCB
    Type D MCB


Type B MCB:

This type of MCB trips between 3 and 5 times full load current. Type B devices are mainly used in residential applications or light commercial applications where connected loads are primarily lighting fixtures, domestic appliances with mainly resistive elements. The surge current levels in such cases are relatively low.

Type C MCB:

This type of MCB trips between 5 and 10 times full load current. This is used in commercial or industrial type of applications where there could be chances of higher values of short circuit currents in the circuit. The connected loads are mainly inductive in nature (e.g. induction motors) or fluorescent lighting.

Type D MCB:

This type of MCB trips between 10 and 20 times full load current. These MCBs are use in specialty industrial / commercial uses where current inrush can be very high. Examples include transformers or X-ray machines, large winding motors etc.

All the above three types of MCBs provide tripping protection within one tenth of a second.


http://www.theiet.org/forums/forum/message...&threadid=32143

QUOTE
*Standard ranges of instantaneous tripping:

Type B - Above 3 In up to and including 5 In
Type C - Above 5 In up to and including 10 In
Type D - Above 10 In up to and including 20 In*

To be classed as a BS EN 60898-1 circuit breaker the following tests must be satisfied (you must remember these are tests carried out in a controlled environment):

*Type B

A current equal to 3 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:

- 45 s for rated currents up to and including 32 A,

- 90 s for rated currents above 32 A.

A current equal to 5 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.


Type C

A current equal to 5 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:

- 15 s for rated currents up to and including 32 A,

- 30 s for rated currents above 32 A.

A current equal to 10 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.

Type D

A current equal to 10 In is passed through all poles starting from cold. The opening time shall be not less than 0.1 s and not more than:

- 4 s for rated currents above 10A up to and including 32 A,

- 8 s for rated currents up to an including 10 A and above 32 A.

A current equal to 20 In is then passed through all poles, again starting from cold. The circuit-breaker shall trip in a time less than 0.1 s.*

*Source: BS EN 60898-1:2003+A1:2004 - Circuit Breakers for overcurrent protection for household and similar installations - Part 1: Circuit-breakers for a.c. operation


The reason I'm researching this is because I have a neighbor who had his concealed wire shorted permanently, something I'd rather avoid.

This post has been edited by beLIEve: May 6 2017, 12:40 AM
beLIEve
post May 6 2017, 12:15 PM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


Very detailed explanation : http://www.kevinboone.net/cableselection_web.html
weikee
post May 6 2017, 02:10 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 6 2017, 12:38 AM)
I spoke to a friend and it appears that there is more to just the amperage on the MCB vs the amount of current you need to size an MCB. If the amount of current is below the MCB's rating multiplied by the value of its type, there'll no trip. In an overcurrent situation, most likely your electrical/electronic device will get fried (it's gotta be already faulty to draw excessive current) before your wire if you're lucky.

To size it, you'll need to know all the resistance involved (wire, devices, earth loop, inrush current). Not sure how many have the equipment to perform these tests?

Anyway, just to share.

http://www.studyelectrical.com/2014/07/min...tic-curves.html
http://www.theiet.org/forums/forum/message...&threadid=32143
The reason I'm researching this is because I have a neighbor who had his concealed wire shorted permanently, something I'd rather avoid.
*
To avoid that, any long term high current usages better direct from MCB with 4mm2 cables. And reduce tapping for extra points.
beLIEve
post May 8 2017, 05:08 AM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


wise words, bro weikee. I think that's why the developer gave 4mm2 wires for room aircond despite room airconds are likely 1HP.

My neighbor's house was rented out. No one really knew how that socket was used as he only got back his house recently. It was looped alright. From MCB to 3 sockets. The last point was the one that fried.

I'm installing some new points for my own house. Will be using 4mm2 to minimize the melting problem, regardless of how long I use the current. Price does not differ a lot vs 2.5mm2 when I buy in rolls. The last time I paid for wiring, I was "convinced" that their 1.0mm2 (yes, I read it on the wire several times because I thought I misread it) 3cores is good enough for 2HP aircond. 1 month warranty woh.

BTW, I've read a lot of your useful responses here when I was searching for RCCB. Pleased to meet you, finally. Speaking of RCCB, another neighbor insisted that MCB will trip when there is a current leak when I tipped him about the 10mA RCCB for heater. I guess it would, if the leakage goes beyond the MCB rating x Type.

This post has been edited by beLIEve: May 8 2017, 05:10 AM
weikee
post May 8 2017, 01:57 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 8 2017, 05:08 AM)
wise words, bro weikee. I think that's why the developer gave 4mm2 wires for room aircond despite room airconds are likely 1HP.

My neighbor's house was rented out. No one really knew how that socket was used as he only got back his house recently. It was looped alright. From MCB to 3 sockets. The last point was the one that fried.

I'm installing some new points for my own house. Will be using 4mm2 to minimize the melting problem, regardless of how long I use the current. Price does not differ a lot vs 2.5mm2 when I buy in rolls. The last time I paid for wiring, I was "convinced" that their 1.0mm2 (yes, I read it on the wire several times because I thought I misread it) 3cores is good enough for 2HP aircond. 1 month warranty woh.

BTW, I've read a lot of your useful responses here when I was searching for RCCB. Pleased to meet you, finally. Speaking of RCCB, another neighbor insisted that MCB will trip when there is a current leak when I tipped him about the 10mA RCCB for heater. I guess it would, if the leakage goes beyond the MCB rating x Type.
*
1mm2 should be ban from using as outlet point. Maybe just a single light point is ok.

Wires problem usually won't happen so fast. Maybe only 1-2 years after usages. Unless of course it was intended overload.

ELCB/RCCB will trip only beyond the threshold level, more sensitive will be more expensive. If you have 10mA RCCB, and DB installed with 30mA. In scenario when leaking say is 15mA, the water heater RCCD will trip but not the DB side RCCD.
beLIEve
post May 8 2017, 03:53 PM

三軍都督
*******
Senior Member
7,803 posts

Joined: Jan 2005


That's why he confidently gave 1 month warranty. I always consult my friend before agreeing to all the deals offered by contractors. When problem occurs, can make money pulling new wires again.

Referring to RCCB, yes, after so much research, that's what I learned. Also read that some will trip at 50% of the value. Didn't drill too much into that.

Let me ask you this, since you're a 高人. Which is better? 10mA RCCB between MCB and water heater, or MCB between RCCB and water heater? My friend recommended the latter, but I went for the former after some research. It's sort of whether I want the MCB to protect RCCB from potential overcurrent damages, or RCCB to protect MCB from leakages. I'm protecting the RCCB because it's much more expensive. He said RCCB will not break, though I wonder what will happen when 100A flows through a 25A RCCB.
weikee
post May 8 2017, 05:06 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(beLIEve @ May 8 2017, 03:53 PM)
That's why he confidently gave 1 month warranty. I always consult my friend before agreeing to all the deals offered by contractors. When problem occurs, can make money pulling new wires again.

Referring to RCCB, yes, after so much research, that's what I learned. Also read that some will trip at 50% of the value. Didn't drill too much into that.

Let me ask you this, since you're a 高人. Which is better? 10mA RCCB between MCB and water heater, or MCB between RCCB and water heater? My friend recommended the latter, but I went for the former after some research. It's sort of whether I want the MCB to protect RCCB from potential overcurrent damages, or RCCB to protect MCB from leakages. I'm protecting the RCCB because it's much more expensive. He said RCCB will not break, though I wonder what will happen when 100A flows through a 25A RCCB.
*
Don't look me so up. I just speak from my general knowledge.

If you plan to do "MCB between RCCB and water heater", unless you can identify the water heater neutral wires at the DB box if can't you will not have a balance current and it will always trip.
Richard
post May 8 2017, 09:51 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(beLIEve @ May 8 2017, 03:53 PM)
That's why he confidently gave 1 month warranty. I always consult my friend before agreeing to all the deals offered by contractors. When problem occurs, can make money pulling new wires again.

Referring to RCCB, yes, after so much research, that's what I learned. Also read that some will trip at 50% of the value. Didn't drill too much into that.

Let me ask you this, since you're a 高人. Which is better? 10mA RCCB between MCB and water heater, or MCB between RCCB and water heater? My friend recommended the latter, but I went for the former after some research. It's sort of whether I want the MCB to protect RCCB from potential overcurrent damages, or RCCB to protect MCB from leakages. I'm protecting the RCCB because it's much more expensive. He said RCCB will not break, though I wonder what will happen when 100A flows through a 25A RCCB.
*
You use a water heater for hot water..

You use a 10mA RCD to protect your life from electrocution from the water heater..

Why would you value a 10mA RCD higher than life?

Edit * Watch this youtube video.. It is good .. https://www.youtube.com/watch?v=A5HuPol99sU

I also find it pretty funny ..

This post has been edited by Richard: May 8 2017, 09:58 PM