QUOTE(wailing81 @ Feb 17 2020, 01:31 PM)
Teral Ab25x254tpc. Now headache want to add the additional buffer tank or not.Water pump
Water pump
|
|
Feb 17 2020, 01:35 PM
|
![]()
Newbie
39 posts Joined: Aug 2013 |
|
|
|
|
|
|
Feb 19 2020, 02:21 AM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
785 posts Joined: Jan 2003 |
QUOTE(bowl @ Feb 17 2020, 01:33 PM) Dear All i would like to ask that water pump have buffer tank. The water pump i purchase is normal without a small water buffer tank attach on top of it. My supplier advice me to add another RM150 to attach a small 8 Liter small water buffer tank to attach on it. He claim that this can reduce the pump working frequency (example open water tap wash hand pump won't run) hence less maintenance and longer life span. https://item.taobao.com/item.htm?spm=a1z09...._u=j2qli4at83ddMay i know what he say it is true? It really a lot benefit to add the water buffer tank and RM150 is fair price for the tank? Thank you RM150 is too expensive. I am using 4L for corner terrace house. |
|
|
Feb 19 2020, 02:25 AM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
785 posts Joined: Jan 2003 |
QUOTE(Peppa_Pig @ Jan 27 2020, 09:40 AM) Get 370w is suffice. Buy Pressure Reducing Valve with meter around RM 25-40 to control pressure. For old house, start with 1.5bar. Maximum 2.2 bar for old house. From a DIY with experience in installing, modify piping, service pump (rewinding coil, change m.seal & bearing), repair PS... |
|
|
Feb 19 2020, 09:57 AM
|
![]()
Newbie
39 posts Joined: Aug 2013 |
QUOTE(amco @ Feb 19 2020, 02:21 AM) https://item.taobao.com/item.htm?spm=a1z09...._u=j2qli4at83dd Tq for your feedback. I think will not install the water buffer tank. Just share with you all, i use to work at KL. Now i relocate back to Ipoh i found that in Ipoh all this home appliance la, car spare part la, computer la if buy at here really expensive a lot compare to KL due to very less competitive here. RM150 is too expensive. I am using 4L for corner terrace house. |
|
|
Feb 26 2020, 01:25 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,797 posts Joined: Jan 2003 |
Hello Guys,
Is this diagram correct? For kitchen sink and washing machine will be use direct water from main source. Bathroom will use water from tank. I am not sure either use ball valve/butterfly valve/stockoff. Can use water from tank for kitchen sink and washing machine? Is it safe? If i am not mistaken, i have read from this thread/somewhere for kitchen sink/washing machine is advisable to use water direct from main. UPDATE: My contractor said building by-law not allow to use water from tank. Thanks. This post has been edited by xphr3ak: Feb 26 2020, 04:57 PM |
|
|
Mar 19 2020, 01:12 PM
Show posts by this member only | IPv6 | Post
#186
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,519 posts Joined: Aug 2007 From: Somewhere in the distant galaxy.... |
I'm looking for water pump recommendation for my parent's house. Its a single storey and have 5 bathroom with rain shower. Is cm3-5pm1 sufficient or any other recommendation?
|
|
|
|
|
|
Apr 2 2020, 01:34 AM
|
![]() ![]()
Junior Member
191 posts Joined: Oct 2007 |
QUOTE(xphr3ak @ Feb 26 2020, 01:25 PM) » Click to show Spoiler - click again to hide... « You need a check valve (one way valve) at your bypass line after ball valve 1. This is to prevent your pump from pumping backwards i.e (pumping after ball valve 3 into the bypass line) and creating a pumping loop. Hope it makes sense. |
|
|
Aug 16 2020, 10:04 AM
|
![]() ![]()
Junior Member
65 posts Joined: Nov 2004 From: Bukit Jelutong |
Hi, i just installed scala 2 and they did a bypass from main also.. i though they gonna do bypass after water tank.. now without using pump the pressure quite good already haha.. Im just afraid that the pipe cannot tahan from the pressure from main. Also im in new taman new house and not many people yet.. issit ok to just leave it like that or change the bypass after water tank?
|
|
|
Aug 24 2020, 11:16 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,152 posts Joined: Jul 2011 |
QUOTE(matrism @ Aug 16 2020, 10:04 AM) Hi, i just installed scala 2 and they did a bypass from main also.. i though they gonna do bypass after water tank.. now without using pump the pressure quite good already haha.. Im just afraid that the pipe cannot tahan from the pressure from main. Also im in new taman new house and not many people yet.. issit ok to just leave it like that or change the bypass after water tank? Quickly change it! Your conceal pvc pipes will burst soon! |
|
|
Aug 25 2020, 12:26 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,184 posts Joined: Jan 2008 From: Builders Hardware Enterprise 0362572412 |
standard main water supply ard 2 - 3 bar only, max i seen 4bar. cant burst PVC pipe.
Grundfos CM3-5pm1 rated 4.6 - 4.7bar even stronger, PVC pipe no problem |
|
|
Aug 25 2020, 02:47 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,152 posts Joined: Jul 2011 |
QUOTE(zheilwane @ Aug 25 2020, 12:26 PM) standard main water supply ard 2 - 3 bar only, max i seen 4bar. cant burst PVC pipe. It is not the PVC pipe that burst, it's the PVC elbow joints I'm talking about.Grundfos CM3-5pm1 rated 4.6 - 4.7bar even stronger, PVC pipe no problem It couldn't hold the pressure. |
|
|
Sep 22 2020, 11:21 AM
Show posts by this member only | IPv6 | Post
#192
|
![]() ![]() ![]()
Junior Member
361 posts Joined: Mar 2010 |
Hi guys
I have a question and hope to hear from you if you have any idea to help me solve this problem. ![]() My water tank is on the 5th floor and my unit is on the 3rd. Problem is the water outlet from the water tank to my unit needs to climb over the wall and according to the plumber, there is a risk of air trap when the water level in the tank runs lower than the outlet. The 'climbing' can cost a lot of problems. He asked me to instal water pump which costs RM1800. Is this true? Thanks! |
|
|
Sep 22 2020, 12:24 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,941 posts Joined: Jan 2003 |
Would like to ask a question - Recently due to the water cut, I faced airlock issues for most of the pipes that goes through tangki...
Luckily most of them are resolved maybe because water heater draw the air out quickly? Issue - My washing machine and one of the hand wash kitchen basin goes through tangki as well and the airlock does not seems be resolved. Tried every method to draw the Air out but still, water pressure is too small... Any idea getting this pump will help to draw the air out? https://www.lazada.com.my/products/50-offdc...s445463966.html Thanks... This post has been edited by thankyou: Sep 22 2020, 12:24 PM |
|
|
|
|
|
Sep 22 2020, 12:37 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,006 posts Joined: Mar 2005 From: Truly Malaise |
Hi, I'd like to ask if it's normal to have low water pressure at high rise?
|
|
|
Sep 22 2020, 08:49 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(lyt25_1234 @ Aug 25 2020, 02:47 PM) It is not the PVC pipe that burst, it's the PVC elbow joints I'm talking about. Can use class 7 pipe + inline ball valve to regulate the pressure so it will be good pressure and not excessively high.It couldn't hold the pressure. QUOTE(Skydrop @ Sep 22 2020, 11:21 AM) Hi guys RM1800 seems on the steep side. I would say the risk of having the water running out on the main tank is rather low but good pump will have overheat protection. Your situation where by the water tank is higher than the unit is easy to pump so a small 150-200W pump will suffice as your water doesnt need to fight against gravity that much.I have a question and hope to hear from you if you have any idea to help me solve this problem. ![]() My water tank is on the 5th floor and my unit is on the 3rd. Problem is the water outlet from the water tank to my unit needs to climb over the wall and according to the plumber, there is a risk of air trap when the water level in the tank runs lower than the outlet. The 'climbing' can cost a lot of problems. He asked me to instal water pump which costs RM1800. Is this true? Thanks! The entire surface area of the upstairs tank is easily 1-2 sq meters (if small tangki) is enough to push down the water into the 1" pipe. A "150W HITACHI WM-P150 XS AUTOMATIC CONSTANT PRESSURE WATER PUMP" should run you around 660 for the pump only. Key is automatic pump so no need to turn on turn off. QUOTE(thankyou @ Sep 22 2020, 12:24 PM) Would like to ask a question - Recently due to the water cut, I faced airlock issues for most of the pipes that goes through tangki... You can backflow it from another outlet using water hose (tap to tap)?Luckily most of them are resolved maybe because water heater draw the air out quickly? Issue - My washing machine and one of the hand wash kitchen basin goes through tangki as well and the airlock does not seems be resolved. Tried every method to draw the Air out but still, water pressure is too small... Any idea getting this pump will help to draw the air out? https://www.lazada.com.my/products/50-offdc...s445463966.html Thanks... QUOTE(iamsobloodysick @ Sep 22 2020, 12:37 PM) Old high rise >15 years yes, iron pipes corroded and from 1" become 0.2" diameter left for water to pass thru. It could also be the WH filter clogged/flexi pipes clogged. Usually management will replace with new piping.New high rise within past couple years no.. water pressure is so good I need to max out the WH to have enough heat to take bath. This post has been edited by ceo684: Sep 22 2020, 08:51 PM |
|
|
Sep 22 2020, 09:08 PM
Show posts by this member only | IPv6 | Post
#196
|
![]() ![]() ![]()
Junior Member
361 posts Joined: Mar 2010 |
QUOTE(ceo684 @ Sep 22 2020, 08:49 PM) Can use class 7 pipe + inline ball valve to regulate the pressure so it will be good pressure and not excessively high. Thanks Bro. I actually shared similar thought on the possibility of the tank running empty but the risk is still there. Suppose the tank is empty and the pipe is filled with air, when the water tank is refilled with water again, the water flow will be blocked by air in the pipe. That's why I was told to install pump to help draw out air trap in the pipe so water can flow again. Is this true? RM1800 is unreasonable to me! I am still trying to survey what is in the market. RM1800 seems on the steep side. I would say the risk of having the water running out on the main tank is rather low but good pump will have overheat protection. Your situation where by the water tank is higher than the unit is easy to pump so a small 150-200W pump will suffice as your water doesnt need to fight against gravity that much. The entire surface area of the upstairs tank is easily 1-2 sq meters (if small tangki) is enough to push down the water into the 1" pipe. A "150W HITACHI WM-P150 XS AUTOMATIC CONSTANT PRESSURE WATER PUMP" should run you around 660 for the pump only. Key is automatic pump so no need to turn on turn off. You can backflow it from another outlet using water hose (tap to tap)? Old high rise >15 years yes, iron pipes corroded and from 1" become 0.2" diameter left for water to pass thru. It could also be the WH filter clogged/flexi pipes clogged. Usually management will replace with new piping. New high rise within past couple years no.. water pressure is so good I need to max out the WH to have enough heat to take bath. What is the difference between class 6 and class 7 pipe btw? Which one is more suitable and durable for apartment/home use? @Zheilwane, any comments/recommendations from you? |
|
|
Sep 24 2020, 02:26 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(Skydrop @ Sep 22 2020, 09:08 PM) Thanks Bro. I actually shared similar thought on the possibility of the tank running empty but the risk is still there. Suppose the tank is empty and the pipe is filled with air, when the water tank is refilled with water again, the water flow will be blocked by air in the pipe. That's why I was told to install pump to help draw out air trap in the pipe so water can flow again. Is this true? RM1800 is unreasonable to me! I am still trying to survey what is in the market. Grey PVC pipe the higher the class the tougher the pipe due to thicker material. Class 0 is low class and should only be used for light duty (aka aircon drain pipe). If wanna bury in concrete use class 7 direct, its not that expensive but will save a lot of headache later on.What is the difference between class 6 and class 7 pipe btw? Which one is more suitable and durable for apartment/home use? @Zheilwane, any comments/recommendations from you? |
|
|
Sep 24 2020, 10:46 AM
|
![]() ![]() ![]()
Junior Member
456 posts Joined: Oct 2019 |
For new house, does bypass or installing pump void the defect / warranty ?
|
|
|
Sep 24 2020, 11:11 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
7,938 posts Joined: Mar 2014 |
QUOTE(Skydrop @ Sep 22 2020, 09:08 PM) Thanks Bro. I actually shared similar thought on the possibility of the tank running empty but the risk is still there. Suppose the tank is empty and the pipe is filled with air, when the water tank is refilled with water again, the water flow will be blocked by air in the pipe. That's why I was told to install pump to help draw out air trap in the pipe so water can flow again. Is this true? RM1800 is unreasonable to me! I am still trying to survey what is in the market. Depends on the pump type. Cheap pump will get water jetting when pump automatically switch on and off. it is because the pressure switch turn motor on and off abruptly. When motor is turned on the pressure build up in pipe but then the water out is less casing pump to switch off and when pressure low again the pump on and so on, causing water jetting. More expensive one have bigger bladder tank thus less water jetting effect.What is the difference between class 6 and class 7 pipe btw? Which one is more suitable and durable for apartment/home use? @Zheilwane, any comments/recommendations from you? Nowadays, high end pump is using inverter to vary motor speed, thus the pressure in pipe is consistant. This will let water flow smoothly. The inverter type even no need to have bladder tank. The RM1800 probably this high end type. You need to ask. I know that Grundfos Scala2 is around RM1700~1800. This is real constant pressure pump. |
|
|
Sep 24 2020, 11:12 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
7,938 posts Joined: Mar 2014 |
|