QUOTE(cyberkoh88 @ Dec 22 2016, 07:05 PM)
actually not an expert in electrical, so correct me if i am wrong...actually if i change the cutoff fuse to 100A, RSD to 100A and DP Insulator to 100A, isit it means that i change this for the purpose if on the same times if i use my electrical appliance, total combines can tahan until 100A. why actually still need to check the wire. each individual wire already protected by MCB (20A) where each individual wire cannot exceed 20A, if exceed will cause trip in MCB. actually i did plan upgrade for 1 MCB to maybe 40A (coz my water heater and aircon sharing wire by looling). only need to check this wire whether can tahan 40A or not rite?
or actually bro here mean need to check cable from tnb box to DB box only bcoz maybe the wire from tnb meter to DB box last time not support for 100A electricity? not the whole house wiring rite?
and one more things, i check thru internet, actually single phase max can support until 100A based on internatioanl standard. isit because of TNB we only can be max 63A?
sorry if my question look dumb coz i am not expert in electical, so hope all sifu here can enlighten me.
actually already pay deposit to that electrician (told me need it to buy electical part) and he will come to install it on saturday, if really got problem, i think i need to consult another electrician. actually i already call them to issue my worry, he just say no problem one and my wiring can support blah blah....not an expert in electical, so not argue with him a lot coz that electrician a little cocky one.....
thanks....
You're right..
A HRC fuse protects the immediate wiring subcircuit..
Based on this logic..
100A single phase requires wire size to be 2x25mm2 copper cable or bigger for Live & Neutral .. means from 100A HRC fuse to TNB Kwh meter to 100A Distribution Board (DB)..
So this means your inside your DB must have a 100A Double pole (DP) to 100A RCD (to outgoing SP mcb Live busbar and to Neutral Bar) all still using 25mm2 wire ..
The only problem to this is the normal wire size that can fit inside a residential DB is only 10mm2.. which is only rated to 40A
If you know what your wireman is doing and he is indeed replacing the wire it is all good..
I am saying it is very hard and almost impossible to fit a 25mm2 pvc copper wire within a residential DB and I think your wireman is taking you for a fool..
Another thing is the combined (maximum demand) load which can trip a 40A mcb will not blow a 100A HRC fuse..
What usually happens if a fault happens is a high fault inrush current(usually from AC motors) will melt fuse the 40A mcb contacts making it unable to trip heat up the 10mm2 copper cable and start to burn ..
This fault current will not trip a 100A HRC fuse (which is a slow thermal response high rupturing capacity type and not a magnetic type tripping device)..
A fuse blows open and mcb (miniature circuit breaker) magnetically trips (and a bimetallic thermal trip but the primary trip function is magnetic)..
The decision is yours to make but if you do it wrong it is a safety issue ..
Edit * If you refer to the Suruhanjaya Tenaga tables for current carrying capacity the minimum cable size for 100A (enclosed in conduit) is 35mm2..
You must tighten the cables to make good contact if you know you have high loads or the connection points will heat up, start to arc and loosen in time..
This post has been edited by Richard: Dec 23 2016, 12:41 AM