Renovations 3-phase wiring

views
     
buncho89
post Dec 30 2019, 11:29 AM

Getting Started
**
Junior Member
282 posts

Joined: Aug 2011


Subsale condo I bought came with 3 phase wiring. Deposit pay to TNB - 1.2k ouch. Minimum electricity bill - rm3 (even with zero usage) lol.
Electric diy P
post May 23 2020, 01:08 AM

New Member
*
Probation
2 posts

Joined: Apr 2020
QUOTE(ozak @ Dec 20 2016, 11:02 AM)
Electrical have rule to follow. Not what you want 100A this and that.

Max single phase is 60A.  So everything must be content in 63A. Fuse or isolator. More than that, advise you to get 3phase.

Your single room heater and aircon share the same point is not recommend. Even you change the MB to 40A, your wire spec exceed the actual current running. Heater 3.6kw and aircon 1.5HP 1.2kw = 4.8kw. Your 2.5mm wire is running hot.

As a precaution, separate into 2 point with 2pcs MB is the proper way.
*
Yes correct, 40A mcb is irrelevant for house, i would blame the owner bcs he might not know about the danger, but definitely will blame the electrician, how stupid he is, how can he change mains switch 63A to 100A and cut out fuse too 100A,its just house, less protection, and do not share heater and aircond,most probably the cable.is 2.5mm... omg i had stroke reading this....
einoom P
post May 28 2020, 04:12 PM

New Member
*
Probation
9 posts

Joined: Apr 2020
Hi!

Anyone have TNB Runner & contractor contact for penang island side?
need for a application of shop in Tesco Penang.
Yellow lemon
post Oct 7 2020, 06:02 PM

Getting Started
**
Junior Member
165 posts

Joined: Mar 2014


QUOTE(Peppa_Pig @ Oct 21 2019, 04:52 PM)
Just sharing a 3-phase upgrade guide for everyone’s benefit since there isn’t clear instructions on what is the process and how to go about it. So I hope this will be useful for future readers.
____________________

Step 1:
Do your necessary preparation works such as (i) preparation of meter box compartment at required location; (ii) converting your distribution box to 3-phase ready; (iii) doing the required armoured cable laying from meter box to distribution box;

Tip: Hire a qualified/certified electrician to do all this. Basically, you want to be “3-phase ready”.

Step 2:
Ask your electrician to prepare the meter board and 3 phase cables wiring as per pic below. Note that this is a sample but it should look something like this depending on your requirement.
By this stage you are to called 3-phase ready.

Tip: Ask your electrician to ensure its as per TNB’s required specs. You will be able to find the spec pdf on TNB’s website.

Step 3:
Go to myTNB’s website, register and then apply to upgrade your power to 3-phase.

Step 4:
Select a TNB licensed company from the list as your contractor and to do your submission to TNB (i.e runner). At this point, you only need a runner to do the submission to TNB for you. You have no choice but to select a company from the list as your runner.

Note: they can also do all electrical works to be 3-phase ready but its your decision to hire your own contractor or use one of the panel contractors.

Tip: call up each company you have shortlisted to ask them how much are their submission fees are. You would want to let them know that you are 3-phase ready and only need to do the submission process to TNB. Runners generally charge a fee of RM600 to RM1.5k depending on which company you engage. Typically, they will charge a high fee of RM1.5k.

Step 5:
The runner will then contact you to come over to your house to take pictures of the meter compartment, wiring board and nearest pole to pull the cable for 3-phase power. This is to ensure everything is in order as per TNB’s specs before submission.

Step 6:
Once the runner has made the submission to TNB, it will take around 3 weeks for them to assess how best to pull in the cable to your house. The runner will inform you if they are putting a new pole up or digging the road.
Note: digging of road will require special permit from the local council and it might include additional cost to be estimated by TNB.

Step 7:
After the assessment period, TNB will send you a invoice to be settled prior to starting of construction works (i.e pulling the cable and installing the meter).

Typically, fees are:
1. Contribution fee – RM1,700
2. Deposit top for 3-phase – RM200

Note: Generally, the cost should be within the above figures unless special case where it includes road cutting where TNB does not want to bare or your area is really secluded.

Step 8:
At this stage, TNB should have completed the erection of the pole and installation of the meter. Further appointment will be made to install the fuse and remove your old single phase meter etc.

Step 9:
Congratulations! You now have 3-phase power. The power connection process is very simple. TNB will put in 3 fuses to complete the connection. 

Note: TNB is NOT responsible for anything that is inside your house compound so if there are any power or wiring issues then it’s up to you to rectify it hence a good electrician is important. TNB’s  scope of works is only limited to up to the meter compartment box.
*
thank you very much for this details advise.

referring to below, do you have any advise on the charges like?


Step 6:
Once the runner has made the submission to TNB, it will take around 3 weeks for them to assess how best to pull in the cable to your house. The runner will inform you if they are putting a new pole up or digging the road.
Note: digging of road will require special permit from the local council and it might include additional cost to be estimated by TNB.



Yellow lemon
post Oct 7 2020, 06:20 PM

Getting Started
**
Junior Member
165 posts

Joined: Mar 2014


QUOTE(PaterB @ Aug 5 2019, 04:02 PM)
Hi I'm trying to upgrade my house to 3phase, however the pole is not in front of my house but opposite. So they are are suggesting me to add another pole infront of my house which I dislike.

I asked them for the price of laying the cable underneath the road. They quote me RM25k!
Does it cost this much?
*
hi bro, how is your case to settle? paid 25k? omg thats a lot! sweat.gif
ComingBackSoon
post Dec 28 2020, 10:53 PM

Enthusiast
*****
Junior Member
787 posts

Joined: Oct 2010
QUOTE(Peppa_Pig @ Oct 21 2019, 04:52 PM)
Just sharing a 3-phase upgrade guide for everyone’s benefit since there isn’t clear instructions on what is the process and how to go about it. So I hope this will be useful for future readers.
____________________

Step 1:
Do your necessary preparation works such as (i) preparation of meter box compartment at required location; (ii) converting your distribution box to 3-phase ready; (iii) doing the required armoured cable laying from meter box to distribution box;

Tip: Hire a qualified/certified electrician to do all this. Basically, you want to be “3-phase ready”.

Step 2:
Ask your electrician to prepare the meter board and 3 phase cables wiring as per pic below. Note that this is a sample but it should look something like this depending on your requirement.
By this stage you are to called 3-phase ready.

Tip: Ask your electrician to ensure its as per TNB’s required specs. You will be able to find the spec pdf on TNB’s website.

Step 3:
Go to myTNB’s website, register and then apply to upgrade your power to 3-phase.

Step 4:
Select a TNB licensed company from the list as your contractor and to do your submission to TNB (i.e runner). At this point, you only need a runner to do the submission to TNB for you. You have no choice but to select a company from the list as your runner.

Note: they can also do all electrical works to be 3-phase ready but its your decision to hire your own contractor or use one of the panel contractors.

Tip: call up each company you have shortlisted to ask them how much are their submission fees are. You would want to let them know that you are 3-phase ready and only need to do the submission process to TNB. Runners generally charge a fee of RM600 to RM1.5k depending on which company you engage. Typically, they will charge a high fee of RM1.5k.

Step 5:
The runner will then contact you to come over to your house to take pictures of the meter compartment, wiring board and nearest pole to pull the cable for 3-phase power. This is to ensure everything is in order as per TNB’s specs before submission.

Step 6:
Once the runner has made the submission to TNB, it will take around 3 weeks for them to assess how best to pull in the cable to your house. The runner will inform you if they are putting a new pole up or digging the road.
Note: digging of road will require special permit from the local council and it might include additional cost to be estimated by TNB.

Step 7:
After the assessment period, TNB will send you a invoice to be settled prior to starting of construction works (i.e pulling the cable and installing the meter).

Typically, fees are:
1. Contribution fee – RM1,700
2. Deposit top for 3-phase – RM200

Note: Generally, the cost should be within the above figures unless special case where it includes road cutting where TNB does not want to bare or your area is really secluded.

Step 8:
At this stage, TNB should have completed the erection of the pole and installation of the meter. Further appointment will be made to install the fuse and remove your old single phase meter etc.

Step 9:
Congratulations! You now have 3-phase power. The power connection process is very simple. TNB will put in 3 fuses to complete the connection. 

Note: TNB is NOT responsible for anything that is inside your house compound so if there are any power or wiring issues then it’s up to you to rectify it hence a good electrician is important. TNB’s  scope of works is only limited to up to the meter compartment box.
*
Just to share with everyone. Step 6 can easily take more than 1 month even if there is no complication, depending on how busy (or lazy, I don't know) TNB is.

Runner submitted my application to TNB (step 5) on 26 November 2020.

Invoice for Step 7 was only given to me on 14 December 2020. I paid the invoice within minutes.

They only came and connect the wires on 22 December 2020, but decided to install the meter on a separate day. Since then it has been almost a week and everyday TNB just give me the "thank you for your patience, we are following up closely". Damn bloody slow.
5p3ak
post Mar 16 2021, 09:26 PM

CPE, FIG Certified Gymnastics Coach
*******
Senior Member
5,648 posts

Joined: Mar 2011
From: Jalan Tijani
Good day to all, I got noob question.

Is 3 phase = able to provide 3 x the Amp of single phase? So if single phase max is 63A so 3 phase = 3x63A?
SUSceo684
post Mar 16 2021, 09:47 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(5p3ak @ Mar 16 2021, 09:26 PM)
Good day to all,  I got noob question.

Is 3 phase = able to provide 3 x the Amp of single phase? So if single phase max is 63A so 3 phase = 3x63A?
*
Yes, correct 3*63A (for 16mm² cable) or 3*40A for 10mm² cable because of the way the phases cancel each other out in perfectly balanced system, the neutral carries very little current.
Perfect never happens but usually the electrician will position the loads to be balanced out based on typical load amps per phase or similar method.

The danger is if you lose the neutral, it becomes phase-to-phase aka 415V so the neutral connection need to be securely attached for 3ph supply.

This post has been edited by ceo684: Mar 16 2021, 09:48 PM
focusrite
post Mar 17 2021, 10:16 AM

Casual
***
Junior Member
409 posts

Joined: Apr 2019
My parents want to start a small home baking business and are planning on getting a commercial oven. Would you guys recommend that we change to three phase?

We have a lot of aircons in the house but pretty much never on them all at the same time. At most 2 on at the same time.
SUSceo684
post Mar 17 2021, 01:43 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(focusrite @ Mar 17 2021, 10:16 AM)
My parents want to start a small home baking business and are planning on getting a commercial oven. Would you guys recommend that we change to three phase?

We have a lot of aircons in the house but pretty much never on them all at the same time. At most 2 on at the same time.
*
It will depend on your typical load amps right now; this can be checked by a clamp meter on the main cable when you turn on everything that you usually use (sans aircons since normally not used but you can also conduct a check with and without all the AC).
Attached Image

and what is the supply rating ie 40A or 63A to see what is your "available capacity amps" not in use.

Then see the oven rating how many watts to calculate the oven load amps.
Depending on the oven power rating you may need to pull a new dedicated circuit from DB to the oven.

This post has been edited by ceo684: Mar 17 2021, 01:48 PM
focusrite
post Mar 17 2021, 01:46 PM

Casual
***
Junior Member
409 posts

Joined: Apr 2019
QUOTE(ceo684 @ Mar 17 2021, 01:43 PM)
It will depend on your typical load amps right now and what is the supply rating ie 40A or 63A.
*
I don't even know how to check that sweat.gif
SUSceo684
post Mar 17 2021, 01:52 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(focusrite @ Mar 17 2021, 01:46 PM)
I don't even know how to check that  sweat.gif
*
Load amps can be checked by an electrician with a clamp meter. As this is done "hot" while electricity is still running.

Generally if the oven is below 3000W then should be no problem.
But if the oven has signs saying "requires permanent installation" or the likes, OR if power exceed 3000W then you still have to pull new wiring as the standard 13A socket is NOT sufficient.

Supply rating = take a picture of the DB box, you DON'T need to open up all the way to the insides, just need to see the two largest blocks in there.

This post has been edited by ceo684: Mar 17 2021, 01:54 PM
focusrite
post Mar 17 2021, 01:53 PM

Casual
***
Junior Member
409 posts

Joined: Apr 2019
QUOTE(ceo684 @ Mar 17 2021, 01:52 PM)
That can be checked by an electrician with a clamp meter. As this is done "hot" while electricity is still running.

Generally if the oven is below 3000W then should be no problem.
But if the oven has signs saying "requires permanent installation" or the likes, OR if power exceed 3000W then you still have to pull new wiring as the standard 13A socket is NOT sufficient.
*
Thanks! I'll get an electrician to check it.
SUSslimey
post Mar 17 2021, 02:11 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(focusrite @ Mar 17 2021, 10:16 AM)
My parents want to start a small home baking business and are planning on getting a commercial oven. Would you guys recommend that we change to three phase?

We have a lot of aircons in the house but pretty much never on them all at the same time. At most 2 on at the same time.
*
i think should be ok.

if it trips the breaker then you know then there is an issue


focusrite
post Mar 17 2021, 03:01 PM

Casual
***
Junior Member
409 posts

Joined: Apr 2019
QUOTE(slimey @ Mar 17 2021, 02:11 PM)
i think should be ok.

if it trips the breaker then you know then there is an issue
*
yeah, can consider just use first to see if there are any problems.

can save money if no problems tongue.gif
SUSceo684
post Mar 17 2021, 09:35 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(focusrite @ Mar 17 2021, 03:01 PM)
yeah, can consider just use first to see if there are any problems.

can save money if no problems  tongue.gif
*
I'll add on - if the oven came with a 13A standard plug will not have issues.

If the oven doesn't come ready-to-use with a plug or requires 415V (three phase), then it will be the first sign of "requires professional installation". Some commercial oven use 415V.

focusrite
post Mar 17 2021, 10:22 PM

Casual
***
Junior Member
409 posts

Joined: Apr 2019
QUOTE(ceo684 @ Mar 17 2021, 09:35 PM)
I'll add on - if the oven came with a 13A standard plug will not have issues.

If the oven doesn't come ready-to-use with a plug or requires 415V (three phase), then it will be the first sign of "requires professional installation". Some commercial oven use 415V.
*
Good to know thanks
Pain4UrsinZ
post Mar 18 2021, 06:55 PM

Regular
******
Senior Member
1,856 posts

Joined: Dec 2008
From: In The HELL FIRE



Hi guys, in Malaysia or Strata any rules saying that we cannot run concealed wiring without pvc conduit?

What wires should I use for concealed wiring 1.5mm for light and fan?

Other than double pvc what is other options? is it necessary to use double pvc ?

This post has been edited by Pain4UrsinZ: Mar 18 2021, 08:19 PM
SUSceo684
post Mar 18 2021, 07:04 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(Pain4UrsinZ @ Mar 18 2021, 06:55 PM)
Hi guys, in Malaysia or Strata any rules saying that we cannot run concealed wiring without pvc conduit?

What wires should I use for concealed wiring 1.5mm for light and fan?

Other than double pvc what is other options?
*
Generally you can see CHAPTER 5 CABLE SELECTION in "ST GUIDELINES FOR ELECTRICAL WIRING IN RESIDENTIAL BUILDINGS 2008". PDF available online.

You are pulling new wire from DB box or connecting to existing point?


This post has been edited by ceo684: Mar 18 2021, 07:11 PM
Pain4UrsinZ
post Mar 18 2021, 07:12 PM

Regular
******
Senior Member
1,856 posts

Joined: Dec 2008
From: In The HELL FIRE



QUOTE(ceo684 @ Mar 18 2021, 07:04 PM)
Generally you can see CHAPTER 5 CABLE SELECTION in "ST GUIDELINES FOR ELECTRICAL WIRING IN RESIDENTIAL BUILDINGS 2008". PDF available online.

You are pulling new wire from DB box or connecting to existing point?
*
from Both also because DB slot limited

This post has been edited by Pain4UrsinZ: Mar 18 2021, 07:13 PM