Renovations 3-phase wiring

views
     
SUSceo684
post Apr 22 2021, 10:53 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(bobowyc @ Apr 22 2021, 09:17 AM)
Update: I contacted one tnb contractor from their list, they quoted my client 4.8k for laying the new GI pipe, rewire, new board, new outgoing wire into the DB and necessary works. I think its a reasonable pricing. 😅 what do you think?
*
Sounds good all in all, being a TNB panel things will generally be smoother brows.gif
bobowyc
post Apr 22 2021, 11:42 PM

You are who you are.
******
Senior Member
1,921 posts

Joined: Apr 2013
From: Petaling Jaya


QUOTE(ceo684 @ Apr 22 2021, 10:53 PM)
Sounds good all in all, being a TNB panel things will generally be smoother brows.gif
*
Yeah. They said the cable is enough long for the new meter board. so no worries there. xD Hopefully all works out good next week! xD Thanks again for your assist!
gilabola
post Nov 20 2021, 12:34 PM

On my way
****
Senior Member
669 posts

Joined: Jan 2005


Duplicate post. Sorry

This post has been edited by gilabola: Nov 20 2021, 12:39 PM
gilabola
post Nov 20 2021, 12:34 PM

On my way
****
Senior Member
669 posts

Joined: Jan 2005


Duplicate post. Sorry

This post has been edited by gilabola: Nov 20 2021, 12:39 PM
gilabola
post Nov 20 2021, 12:35 PM

On my way
****
Senior Member
669 posts

Joined: Jan 2005


Duplicate post. Sorry

This post has been edited by gilabola: Nov 20 2021, 12:48 PM
gilabola
post Nov 20 2021, 12:35 PM

On my way
****
Senior Member
669 posts

Joined: Jan 2005


While renovating my house, my contractor said the 3 phase DB Box had sparks. He recommends replacing the part circled at a cost of RM500. I'm wondering if the contractor is trying to pull a fast one

Any advise if the cost is reasonable

This post has been edited by gilabola: Nov 20 2021, 12:51 PM


Attached thumbnail(s)
Attached Image
stormer.lyn
post Nov 20 2021, 01:55 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(gilabola @ Nov 20 2021, 12:35 PM)
While renovating my house, my contractor said the 3 phase DB Box had sparks. He recommends replacing the part  circled at a cost of RM500. I'm wondering if the contractor is trying to pull a fast one

Any advise if the cost is reasonable
*
Nope, doesn't sound right that the Neutral busbar needs to be replaced. If it is sparking why not just redo and tighten back the screw terminals? If an individual screw terminal is damaged, why not just move the slot, as you have so many empty ones?
(FYI I am not an end user just giving my so called "opinion", but a tech in the industry)
gilabola
post Nov 20 2021, 03:44 PM

On my way
****
Senior Member
669 posts

Joined: Jan 2005


QUOTE(stormer.lyn @ Nov 20 2021, 01:55 PM)
Nope, doesn't sound right that the Neutral busbar needs to be replaced. If it is sparking why not just redo and tighten back the screw terminals? If an individual screw terminal is damaged, why not just move the slot, as you have so many empty ones?
(FYI I am not an end user just giving my so called "opinion", but a tech in the industry)
*
Many thanks, stormer.lyn. notworthy.gif

Even if the contractor needed to replace it, the busbar costs less than RM50 (see link below). No way it would cost RM500

https://shopee.com.my/THREE-Phase-MCB-Coppe...0951.4233122116

This post has been edited by gilabola: Nov 20 2021, 03:45 PM
SUSceo684
post Nov 20 2021, 06:31 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(stormer.lyn @ Nov 20 2021, 01:55 PM)
Nope, doesn't sound right that the Neutral busbar needs to be replaced. If it is sparking why not just redo and tighten back the screw terminals? If an individual screw terminal is damaged, why not just move the slot, as you have so many empty ones?
(FYI I am not an end user just giving my so called "opinion", but a tech in the industry)
*
Sparking is just a symptom of loose connection.
lopo90
post Nov 21 2021, 02:38 PM

On my way
****
Junior Member
695 posts

Joined: Nov 2010


Hi guys, anyone familiar with electrical wiring. Hope someone can help out..

I got an oven from China , rated 220v with power output 3200watts.

plan to change the oven's default plug (250v/16a) rating to the standard 250v/13a so that it can fit into the wall socket


Given we are using the standard 240v, that means this oven will be running on 13.3 amps. Which is higher than the 13amps rating

Is it ok if I were to run the oven slightly above the rated amps?

Or should I change it to the 15amp plug

Reason for asking is because I've noticed similar oven (3200w) sold on shopee using the standard 13amps plug

This post has been edited by lopo90: Nov 21 2021, 02:43 PM
SUSceo684
post Nov 22 2021, 03:46 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(lopo90 @ Nov 21 2021, 02:38 PM)
Hi guys, anyone familiar with electrical wiring. Hope someone can help out..

I got an oven from China , rated 220v with power output 3200watts.

plan to change the oven's default plug (250v/16a) rating to the standard 250v/13a so that it can fit into the wall socket
Given we are using the standard 240v, that means this oven will be running on 13.3 amps. Which is higher than the 13amps rating

Is it ok if I were to run the oven slightly above the rated amps?

Or should I change it to the 15amp plug

Reason for asking is because I've noticed similar oven (3200w) sold on shopee using the standard 13amps plug
*
We are using 230V. So anyhow also exceeded 13A. Means cannot use 13A.

You have to use a 15A UNFUSED plug with a 16A MCB,

OR hardwire using at least a 20A CU (connection unit) more commonly known as isolator like https://www.lazada.com.my/products/schneide...2655030922.html with a 16A MCB, better buy 35A rated isolator since few bucks more.

OR use a 16A commando plug and socket https://www.lazada.com.my/products/quality-...0884196990.html AND switch with 25A isolator switch like this https://www.lazada.com.my/products/quality-...0884196990.html (U need to mount in PVC box, nett effect is like this https://www.lazada.com.my/products/taian-tj...211221209.html) with a 16A MCB.

The 16A MCB is important as all options are UNFUSED.
lopo90
post Nov 22 2021, 05:26 PM

On my way
****
Junior Member
695 posts

Joined: Nov 2010


QUOTE(ceo684 @ Nov 22 2021, 03:46 AM)
We are using 230V. So anyhow also exceeded 13A. Means cannot use 13A.

You have to use a 15A UNFUSED plug with a 16A MCB,

OR hardwire using at least a 20A CU (connection unit) more commonly known as isolator like https://www.lazada.com.my/products/schneide...2655030922.html with a 16A MCB, better buy 35A rated isolator since few bucks more.

OR use a 16A commando plug and socket https://www.lazada.com.my/products/quality-...0884196990.html AND switch with 25A isolator switch like this https://www.lazada.com.my/products/quality-...0884196990.html (U need to mount in PVC box, nett effect is like this https://www.lazada.com.my/products/taian-tj...211221209.html) with a 16A MCB.

The 16A MCB is important as all options are UNFUSED.
*
Hi. Thanks for the explanation

Never knew about the commando plug, that looks promising for my oven.

Appreciate the help
mavistan89
post Jan 23 2022, 04:36 PM

On my way
****
Junior Member
500 posts

Joined: Aug 2014
Hi for a old teres house old meter upgrade to 3 phase how much does it cost? My tnb person quote me rm5000

He said
Rm2500 tnb
Rm1000 tnb form
Rm1500 wiring from meter board

This reasonable?
SUSceo684
post Jan 23 2022, 10:28 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(mavistan89 @ Jan 23 2022, 04:36 PM)
Hi for a old teres house old meter upgrade to 3 phase how much does it cost? My tnb person quote me rm5000

He said
Rm2500 tnb
Rm1000 tnb form
Rm1500 wiring from meter board

This reasonable?
*
Include DB refresh? Existing 40A or 63A?
mavistan89
post Jan 24 2022, 12:46 AM

On my way
****
Junior Member
500 posts

Joined: Aug 2014
QUOTE(ceo684 @ Jan 23 2022, 10:28 PM)
Include DB refresh? Existing 40A or 63A?
*
A 40+ years old house, not sure 40A or 63A ... they will change the meter thing.. is it DB?
IMF2025
post Jan 24 2022, 11:21 AM

Getting Started
**
Junior Member
202 posts

Joined: Mar 2020


QUOTE(mavistan89 @ Jan 23 2022, 04:36 PM)
Hi for a old teres house old meter upgrade to 3 phase how much does it cost? My tnb person quote me rm5000

He said
Rm2500 tnb
Rm1000 tnb form
Rm1500 wiring from meter board

This reasonable?
*
1. What is the 2.5k tnb fee for? Usually this is around 1.7k.sound on the high side. Check with tnb to confirm.
2. Tnb form ie runner fee to help u fill up and submit. Price is ok. Although sometimes u can get 600-800 bucks if u look hard enough.
3. 1.5k for wiring from meter board to your house DB. Need to know the spec and does this include good grounding works since u r upgrading from single phase to 3 phase.

Also is your new DB board 3 phase ready?
SUSceo684
post Jan 24 2022, 12:07 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(mavistan89 @ Jan 24 2022, 12:46 AM)
A 40+ years old house, not sure 40A or 63A ... they will change the meter thing.. is it DB?
*
Should make sure, because if supply already 63A it is very unlikely you need more than that (hence no point in going 3 phase).
shinn911
post Feb 8 2022, 12:08 AM

Getting Started
**
Junior Member
118 posts

Joined: Nov 2006


I currently applied to upgrade my hse from single to 3 phase...anyone got a rough idea how long I need to wait for Tunggu Nanti Buat (TNB)??
enduser
post Feb 8 2022, 10:20 AM

Regular
******
Senior Member
1,280 posts

Joined: Jan 2003
QUOTE(shinn911 @ Feb 8 2022, 12:08 AM)
I currently applied to upgrade my hse from single to 3 phase...anyone got a rough idea how long I need to wait for Tunggu Nanti Buat (TNB)??
*
U login at mytnb, chk under ' i want to check my application status'
Follow up from there
imation1314
post Mar 9 2022, 12:27 AM

Getting Started
**
Junior Member
159 posts

Joined: Sep 2010
Anyone know how to to check the max load on TNB meter ? Is this means single phase with max load 100A ?


user posted image