 Multimeter recommend, Learning the Basic now

views
     
SUSceo684
post Oct 17 2021, 03:41 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(okuribito @ Oct 16 2021, 09:05 PM)
» Click to show Spoiler - click again to hide... «

Thanks ceo684

Yeah I appreciate the need for some extra length of wire in there as well as not too much; else cannot close the box LOL Still, i think a longer section with narrow insulation between the barrier/finger guard & the tip will speed up work

Btw, I was learning about RCDs and I think I found a use case for current measurement. Since they work on residual current, one might want to find out how much that residual current is.

My friend had a RCCB that just wouldn't reset after a thunderstorm. The electrician said RCCB damaged by surge & recommended to instal a new one. So my friend did that himself; turned off the Main circuit breaker after the meter & took out the old RCCB & put in a new one, ensuring the Line & Neutral were inserted correctly and tightly

Before he turned the main circuit breaker back on, he pushed the RCCB's switch back on; but it wouldn't engage  ohmy.gif   He also had a good look at the old one (not connected at all) and tried to push the switch back on AND he could! So he took out the new one and connected the old one back in the DB.  LOL the switch wouldn't engage in the ON position hahaha

He then reconfirmed that the main CB was OFF & removed one of the Neutral wire from the RCCB; tried to push the switch up again - it engaged & stayed up!

We think there's current in the Neutral but none in the Line - that's why the RCCB wouldn't allow the switch to stay up. I'm waiting for my new Kyoritsu to arrive & I plan to go over to measure the amps across the In & Out Neutral poles on the RCCB (mains off) to test our suspicion. What do you think?
*
Whatever current went IN on hot(s) did not return OUT on N is causing RCD tripping, or rather, even TWO RCD tripping means you (DEFINITELY) have a leaking device/melted socket/plug /wires incorrectly wired are touching earth (lately this miswiring issues are very common - not sure intentional sabotage or just pure noob workers wiring power strips and plugs incorrectly) etc.

Need to troubleshoot by isolating circuits - off all and turn on one by one until you identify the problem. The RCD should be able to hold up with 0 final-circuit MCBs turned on.

The problem with desktop DMM amp measurement is you need to run current in series - i.e. through the meter itself to measure amps - safer with clamp.
The touch at in and out N will not work for current because you're measuring in parallel. shakehead.gif
Running current through the meter directly produce a lot of heat. sweat.gif

This post has been edited by ceo684: Oct 17 2021, 03:53 AM
okuribito
post Oct 17 2021, 01:11 PM

Regular
******
Senior Member
1,021 posts

Joined: Mar 2010
» Click to show Spoiler - click again to hide... «


QUOTE
The touch at in and out N will not work for current because you're measuring in parallelshakehead.gif
Running current through the meter directly produce a lot of heat.  sweat.gif


ummmmmm the thing is that the RCCB refuse to engage in ON position... ie there's a break in the circuit because the RCCB refuse to close the circuit ....so if "touch at in and out N" it is in series.... Isn't it?

Only IF the RCCB is in ON position will "touch at in and out N" be in parallel IMHO haha I wasn't sleeping in form five physics class tongue.gif Am I mistaken? hehe double check


thanks for that practical tip about stressing the meter thumbsup.gif

This post has been edited by okuribito: Oct 17 2021, 01:11 PM
stormer.lyn
post Oct 17 2021, 05:56 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(okuribito @ Oct 16 2021, 09:05 PM)
Before he turned the main circuit breaker back on, he pushed the RCCB's switch back on; but it wouldn't engage  ohmy.gif  He also had a good look at the old one (not connected at all) and tried to push the switch back on AND he could! So he took out the new one and connected the old one back in the DB.  LOL the switch wouldn't engage in the ON position hahaha

He then reconfirmed that the main CB was OFF & removed one of the Neutral wire from the RCCB; tried to push the switch up again - it engaged & stayed up!
*
If the Incoming breaker/Isolation switch is OFF, the RCCB will not have energy to trip. This is the way it must work. Please double, then triple check, then call an experienced electrician, because the way you describe your circuit is not how it is supposed to work.

QUOTE(okuribito @ Oct 17 2021, 01:11 PM)
ummmmmm the thing is that the RCCB refuse to engage in ON position... ie there's a break in the circuit because the RCCB refuse to close the circuit ....so if "touch at in and out N" it is in series.... Isn't it?

Only IF the RCCB is in ON position will "touch at in and out N" be in parallel IMHO haha I wasn't sleeping in form five physics class  tongue.gif  Am I mistaken? hehe double check
thanks for that practical tip about stressing the meter  thumbsup.gif
*
You are trying to sound like you know what you are doing. Please don't; your safety is at risk.

The (2 units) RCCB is already tripping, there is no need to know how much current by measuring at the in-and-out. To measure at the in-and-out Neutral, you will have to short the in-and-out Live, effectively taking the RCCB out of the circuit. You are trying to somewhat measure the leakage current which is unnecessary to solve your problem, but increases your risk.

Just so you know, there are specific instances where leakage current would need to be measured, where the RCCB is shorted out (bypassed) from the circuit. But this leakage current is typically measured using a very sensitive clamp meter.
sevenor
post Nov 26 2021, 01:05 PM

Getting Started
**
Junior Member
185 posts

Joined: Jun 2006
From: Bandar Utama, PJ
QUOTE(ceo684 @ Oct 17 2021, 03:41 AM)
…..wires incorrectly wired are touching earth (lately this miswiring issues are very common - not sure intentional sabotage or just pure noob workers wiring power strips and plugs incorrectly) etc.
*
Cant agree with you more. Recently while installing a simple water filter next to my washing machine, I received a mild electric shock* when my elbow accidentally touched the side panel of the washing machine. When tested with a Philip test pen on the metal drum n metal door hinges of the washer, to my horror, the pen lit up! I suspected during house renovation more than 15 years ago an inexperienced electrical contractor worker must have wired the wires wrongly. My suspicion was proven right when I checked it with a power outlet/socket tester (see pic below). It showed that there was no Earth! 😅 After dismantling the wall socket, I found out that the PVC insulation of Earth cable was not peeled off enough and the tightening screw was actually screwing onto the PVC insulation only instead of on the copper wire! Imagine if there had been a short circuit during the 15+ odd years, you guys wouldn’t be hearing this from me already unless…. 😂😂😂

*Talking about mild electric shock, I had also experienced the same with my MacBook but I had already check the power outlet it’s connected to and the L, N and E were in order. Wonder what could be the reason…🤔

user posted image

This post has been edited by sevenor: Nov 26 2021, 04:04 PM
sevenor
post Nov 26 2021, 02:09 PM

Getting Started
**
Junior Member
185 posts

Joined: Jun 2006
From: Bandar Utama, PJ
.

This post has been edited by sevenor: Nov 26 2021, 09:38 PM
SUSceo684
post Nov 26 2021, 08:11 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(sevenor @ Nov 26 2021, 01:05 PM)
Cant agree with you more. Recently while installing a simple water filter next to my washing machine, I received a mild electric shock* when my elbow accidentally touched the side panel of the washing machine. When tested with a Philip test pen on the metal drum n metal door hinges of the washer, to my horror, the pen lit up! I suspected during house renovation more than 15 years ago an inexperienced electrical contractor worker must have wired the wires wrongly. My suspicion was proven right when I checked it with a power outlet/socket tester (see pic below). It showed that there was no Earth! 😅 After dismantling the wall socket, I found out that the PVC insulation of Earth cable was not peeled off enough and the tightening screw was actually screwing onto the PVC insulation only instead of on the copper wire! Imagine if there had been a short circuit during the 15+ odd years, you guys wouldn’t be hearing this from me already unless…. 😂😂😂

*Talking about mild electric shock, I had also experienced the same with my MacBook but I had already check the power outlet it’s connected to and the L, N and E were in order. Wonder what could be the reason…🤔

user posted image
*
IKR. Look at this idiota's work!
Nowadays buy new home really need to tear down every switch and every socket just to ensure that they are all wired correctly.

Some customer place the wires are not even screwed in at the terminal. They just popped out once I open the socket up laugh.gif

This post has been edited by ceo684: Nov 26 2021, 08:12 PM


Attached thumbnail(s)
Attached Image
sevenor
post Nov 26 2021, 09:39 PM

Getting Started
**
Junior Member
185 posts

Joined: Jun 2006
From: Bandar Utama, PJ
QUOTE(ceo684 @ Nov 26 2021, 08:11 PM)
IKR. Look at this idiota's work!
Nowadays buy new home really need to tear down every switch and every socket just to ensure that they are all wired correctly.

Some customer place the wires are not even screwed in at the terminal. They just popped out once I open the socket up laugh.gif
*
OMG!!! 🤦‍♂️

In fact, I had gone to the length of checking all my house power outlets with the outlet tester to make sure that they were wired properly. I don’t know how I could have missed the power outlet of the washer despite being so meticulous! 😂 I had also labeled all the outlets to avoid overloading any particular circuit but in spite of that, recently a 3-pin plug and the wall socket melted! It must have happened over years. Good thing the ELCB had tripped eventually else… The mistake was in connecting a 2400W kettle and a fridge in parallel in the same circuit AND most probably the use of a 3-core flexible cable which was lower than the required rating. Notice that the PVC insulation of the Live wire inside the plug and parts of the plug melted.

This post has been edited by sevenor: Nov 26 2021, 10:07 PM


Attached thumbnail(s)
Attached Image Attached Image Attached Image
SUSceo684
post Nov 27 2021, 03:09 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(sevenor @ Nov 26 2021, 09:39 PM)
OMG!!! 🤦‍♂️

In fact, I had gone to the length of checking all my house power outlets with the outlet tester to make sure that they were wired properly. I don’t know how I could have missed the power outlet of the washer despite being so meticulous! 😂 I had also labeled all the outlets to avoid overloading any particular circuit but in spite of that, recently a 3-pin plug and the wall socket melted! It must have happened over years. Good thing the ELCB had tripped eventually else… The mistake was in connecting a 2400W kettle and a fridge in parallel in the same circuit AND most probably the use of a 3-core flexible cable which was lower than the required rating. Notice that the PVC insulation of the Live wire inside the plug and parts of the plug melted.
*
This plug seems like it didn't even get a Sirim sticker laugh.gif
But yeah, in the market there's barely passing and better made plug tops and sockets.
I recommend MK. Good stuff and technically not super expensive.

Sockets E2757 or S2757 about rm4.50-5, diff is whether u want frameless or picture frame flush type.

Plug top for high draw device use MK650 duraplug. About 5.50 ea only.

There's subtle diff in tolerances - like the plug top fuse holder grips like hell vs weakling fuse holder from other ciplak plug tops. Loose connections cause fires. It is also important to cut the wire lengths and strip to the correct mm as the cardboard template to achieve a "perfect fit" in the plug top. I had a similar plug top meltdown coz idiota installed it all 3 wires equal length, 1st problem. Led to 2nd problem, it pulled down the fuse holder and created airgap arcing.

This post has been edited by ceo684: Nov 27 2021, 03:12 AM


Attached thumbnail(s)
Attached Image Attached Image
sevenor
post Nov 27 2021, 09:50 AM

Getting Started
**
Junior Member
185 posts

Joined: Jun 2006
From: Bandar Utama, PJ
QUOTE(ceo684 @ Nov 27 2021, 03:09 AM)
This plug seems like it didn't even get a Sirim sticker laugh.gif

I recommend MK. Good stuff and technically not super expensive.

*
Normally I do not pay much attention to whether a product has SIRIM sticker or not. Now I know better! 😅

Yeah, usually if I were buying 3-pin plug, socket or switches, i would go for MK or Schneider-Clipsal. This burnt plug was happened to be on hand when I needed one and I didn’t think much of it. Most likely it came with another product I bought earlier but which had went kaput.

stormer.lyn
post Nov 28 2021, 02:54 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(sevenor @ Nov 27 2021, 09:50 AM)
Normally I do not pay much attention to whether a product has SIRIM sticker or not. Now I know better! 😅

Yeah, usually if I were buying 3-pin plug, socket or switches, i would go for MK or Schneider-Clipsal. This burnt plug was happened to be on hand when I needed one and I didn’t think much of it. Most likely it came with another product I bought earlier but which had went kaput.
*
You are making the association that the plug burnt because of the SIRIM status. While this may be somewhat true due to the quality of the plug that can pass SIRIM, it is not always true.

A fuse inserted into a circuit is a weak point for high resistance, as the connection depends on the spring tension and the fuse contacting its socket on both ends. That is why you see burning failure at the fuse - for sockets, for house incoming fuses, for equipment fuses, etc - the contacts go high resistance due to oxidisation over time or losing spring tension. And when something is high resistance, it begins to heat up, maybe to the point of failure.

All my high current extension sockets have the plug fuse bypassed, and overcurrent protection is provided by a MCB. I also wirebrush the socket pins from oxidisation to ensure a good contact within the socket.
user posted image

On a side note, SIRIM will certify a product for any specifications; for example "this roll of cable is 100 m long ± 1 mm" and SIRIM will pass it if all your cable meets this length. So technically, this roll of cable has a SIRIM certificate. But of course you actually want a roll of cable with a SIRIM certificate to MS2112-3 for electrical specifications to be sure of the electrical characteristics.


sevenor
post Nov 28 2021, 04:10 PM

Getting Started
**
Junior Member
185 posts

Joined: Jun 2006
From: Bandar Utama, PJ

QUOTE(stormer.lyn @ Nov 28 2021, 02:54 PM)
You are making the association that the plug burnt because of the SIRIM status. While this may be somewhat true due to the quality of the plug that can pass SIRIM, it is not always true.

A fuse inserted into a circuit is a weak point for high resistance, as the connection depends on the spring tension and the fuse contacting its socket on both ends. That is why you see burning failure at the fuse - for sockets, for house incoming fuses, for equipment fuses, etc - the contacts go high resistance due to oxidisation over time or losing spring tension. And when something is high resistance, it begins to heat up, maybe to the point of failure.

All my high current extension sockets have the plug fuse bypassed, and overcurrent protection is provided by a MCB. I also wirebrush the socket pins from oxidisation to ensure a good contact within the socket.
user posted image

On a side note, SIRIM will certify a product for any specifications; for example "this roll of cable is 100 m long ± 1 mm" and SIRIM will pass it if all your cable meets this length. So technically, this roll of cable has a SIRIM certificate. But of course you actually want a roll of cable with a SIRIM certificate to MS2112-3 for electrical specifications to be sure of the electrical characteristics.
*
Bro, you have misunderstood me. What I meant was, I didn’t take SIRIM’s approval seriously. In order words, I didn’t care whether a product was SIRIM approved or not.

Never crossed my mind that the fuse in the plug top could be the weak link. Learn something! 👍

All your high current extension sockets have the plug fuse bypassed? Wow, very brave of you! What happens if your MCB fails to trip cos MCBs do fail sometimes.

Wirebrush the socket pins? I wonder how many people care enough to do that. I certainly don’t. Never thought of doing it in fact although I have wirebrushes! 😂
stormer.lyn
post Nov 28 2021, 04:39 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(sevenor @ Nov 28 2021, 04:10 PM)
All your high current extension sockets have the plug fuse bypassed? Wow, very brave of you! What happens if your MCB fails to trip cos MCBs do fail sometimes.
*
Actually not really brave. I make my own high current extensions, so I include a 16A MCB at the metal clad socket extension itself. So 2 MCBs (one at the DB, another at my socket) need to fail at the same time for a failure to trip. Don't forget the item plugged into the extension still has their fuse in the plug.

I also have a 10 mA RCCB mounted with a short lead and a socket, just in case I need to use power tools and work in damp areas.

See, actually NOT brave, and take a lot of extra precautions. Actually, now that I'm talking about it, I think I should change all of them to 10 mA RCBOs. After all, I can only die once, and I don't want to use that card too soon.
sevenor
post Nov 28 2021, 08:13 PM

Getting Started
**
Junior Member
185 posts

Joined: Jun 2006
From: Bandar Utama, PJ
QUOTE(stormer.lyn @ Nov 28 2021, 04:39 PM)
Actually not really brave. I make my own high current extensions, so I include a 16A MCB at the metal clad socket extension itself. So 2 MCBs (one at the DB, another at my socket) need to fail at the same time for a failure to trip. Don't forget the item plugged into the extension still has their fuse in the plug.

I also have a 10 mA RCCB mounted with a short lead and a socket, just in case I need to use power tools and work in damp areas.

See, actually NOT brave, and take a lot of extra precautions. Actually, now that I'm talking about it, I think I should change all of them to 10 mA RCBOs. After all, I can only die once, and I don't want to use that card too soon.
*
MCB or RCCB at the wall socket? I’m curious to learn how you do it. Mind share a picture of it? TIA

stormer.lyn
post Nov 28 2021, 09:55 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(sevenor @ Nov 28 2021, 08:13 PM)
MCB or RCCB at the wall socket? I’m curious to learn how you do it. Mind share a picture of it? TIA
*
Sure. Just do something like this. Since the fuse in my 3-pin plug for my extension is bypassed, then the board is installed with a MCB for protection. This picture is from Sh*pee, mine is in the car, lazy to go and take. But I hope you get the idea.

user posted image

This post has been edited by stormer.lyn: Nov 28 2021, 09:57 PM
sevenor
post Nov 30 2021, 12:23 AM

Getting Started
**
Junior Member
185 posts

Joined: Jun 2006
From: Bandar Utama, PJ
QUOTE(stormer.lyn @ Nov 28 2021, 09:55 PM)
Sure. Just do something like this. Since the fuse in my 3-pin plug for my extension is bypassed, then the board is installed with a MCB for protection. This picture is from Sh*pee, mine is in the car, lazy to go and take. But I hope you get the idea.

user posted image
*
Oh this is the extension you meant. I believe I’ve seen it used by electrical contractor during my house renovation many years ago. I didn’t pay much attention to it then.

To wirebrush the metal parts of all the plug tops and wall sockets around the house will require crazy amount of work! 😅Instead, I think I’ll just wirebrush (with cordless drill) only the plug tops only of those power-hungry appliances and maybe smear a thin coat of Vaseline on them after that. 😀

This post has been edited by sevenor: Nov 30 2021, 04:04 AM
tspannai P
post Nov 30 2021, 12:55 AM

New Member
*
Probation
11 posts

Joined: Aug 2020
QUOTE(ceo684 @ May 4 2021, 09:47 AM)
RM125 SANWA DIGITAL MULTIMETER CD800A - 600V/0.4 A/Ω/100 μF capacitance
RM130 FLUKE 101 - 600V/NO A/Ω/100 μF capacitance
RM120 Kyoritsu KEW1018H  - 600V/NO A/Ω/200 μF capacitance
RM150 Kyoritsu 1009 - 600V/10 A/Ω/100 μF capacitance  thumbup.gif
RM170 Kyoritsu KEW1021R  - 600V/10 A/Ω/1000 μF capacitance  thumbup.gif
*
Ayam uses Fluke 101. From price list above, just like last time, most multimeter are almost the same price range (RM100–200). Ayam choose Fluke because it is branded and would probably last longer. The Fluke seems easy to use with no range selection. There is also no current measurement, so you will never have to worry about burning your fuse.

Same as ts, ayam brought the multimeter for basic stuff like measuring battery and sockets.

Not to say i want to say but ayam used to use Keysight multimeter at wok brows.gif . Those came with lots of accessories hooks and probes.
The Fluke comes with zero accessories and the basic crappy probes. You will need to buy a clip or hook for the negative end.
sevenor
post Nov 30 2021, 02:30 PM

Getting Started
**
Junior Member
185 posts

Joined: Jun 2006
From: Bandar Utama, PJ
QUOTE(stormer.lyn @ Nov 28 2021, 09:55 PM)
Sure. Just do something like this. Since the fuse in my 3-pin plug for my extension is bypassed, then the board is installed with a MCB for protection. This picture is from Sh*pee, mine is in the car, lazy to go and take. But I hope you get the idea.

user posted image
*
These are actually what I want thumbup.gif but the prices... cry.gif

user posted image

user posted image
stormer.lyn
post Nov 30 2021, 02:39 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(sevenor @ Nov 30 2021, 02:30 PM)
These are actually what I want  thumbup.gif but the prices...  cry.gif

» Click to show Spoiler - click again to hide... «

*
Those prices are one thing to consider. But I prefer making my own units as I have control over the parts I use and can replace in case there is a fault. Imagine something drops on the switch and it breaks. I for sure don't want to spend money another time. But in my self-built unit, I can change the metal clad socket by itself. If you can do the replacing/servicing yourself, then it may be something to consider when you buy items.
sevenor
post Nov 30 2021, 02:59 PM

Getting Started
**
Junior Member
185 posts

Joined: Jun 2006
From: Bandar Utama, PJ
QUOTE(stormer.lyn @ Nov 30 2021, 02:39 PM)
Those prices are one thing to consider. But I prefer making my own units as I have control over the parts I use and can replace in case there is a fault. Imagine something drops on the switch and it breaks. I for sure don't want to spend money another time. But in my self-built unit, I can change the metal clad socket by itself. If you can do the replacing/servicing yourself, then it may be something to consider when you buy items.
*
Actually, I'm capable of making the wooden extension myself. It's true. The one we make ourselves, if using all quality parts, will be much better and safer than the ready made one sold in the shops. What I'm looking for is a wall socket with RCD and not an extension.

This MK Electric 2 Gang RCD Socket will be nice to have. Having said that, I think it's not really necessary if RCDs are already installed at the DB box, unless like you, the fuse in the plug tops are bypassed. Furthermore, if possible, to inspect the plug tops, maybe once a year, to make sure that they are not oxidized.

user posted image




Lurker
post Nov 30 2021, 03:11 PM

L U R K I N G
Group Icon
Elite
4,420 posts

Joined: Jan 2003
good tip on cleaning the 3 prongs for oxidation...

i believe they are copper? can use brasso?