QUOTE(babybaby1988 @ Jun 11 2021, 12:42 AM)
Hmm already buried all the wires into wall can the electrician uncle just pull the cable out without hacking?
I was thinking about 30mA RCD too but when he tried to install a 10mA RCD at the water heater plug downstairs, it keeps tripping. The plug point has looping (to another 4 sockets which i am not using except for a socket for a hood) which causes the tripping according to him. So to be safe i thought just used back the original 100mA since no tripping issue.
The electrician also install new DB upstairs (as attached). Anything i should ask him to change besides to change the 10mm to 16mm? The water heater cable he is using 2.5mm instead and he said trust him no issue one even after i show him the ST guidelines, i suppose should be ok right since my water heater is only 15amp. Not an easy uncle to deal with, even after i bought 10mA RCD and asked him to install, he refuses saying ppl will laugh at me. Only agreed after i showed him the Electricity Regulations.

Personally 30mA whole house will be fine since total amps IN = total amps OUT regardless how it is looped after that.
I run 30mA whole house myself no issue.
My parent's place also had this same problem where the WH circuit was shared with other things and its NOT dedicated. 10mA always trip. Resolved by running dedicated LNE circuit to the WH.
The difference is that the
SINGLE circuit 10mA RCD had "unexplainable and unaccounted for amps from other devices" that the 10mA cannot account for = trip first talk later, save life more important.
Whereas for WHOLE HOUSE 30mA.. as long as total amps IN = total amps OUT (since there's only one IN and one OUT cable back to TNB meter) it will be fine, even high sensitivity 30mA also OK.Anyway, congrats for putting in the 10mA RCDs for better electrical safety.
The difference is in 10mA WH circuit:
Even in cases where the WH circuit is actually shared neutral and trips the 10mA (because the neutral also contain other appliances' return so its imbalance with the incoming amp), this will not affect the whole house RCD.
This one can be solved by (a) correct way i.e. running a dedicated LNE circuit to that WH itself, as per code, without looping or
(b) use dirty trick (not so code compliant but likely to work without extensive hacking all over) is to install RCD as a spur i.e. AFTER the 20A switch (load side) and BEFORE the WH, so only that particular line going to the WH is balanced amps between incoming and outgoing.
Regarding the 63A MCB used on 10mm wire..
Changing the 10mm to 16mm will be expensive. In this situation, since your 63A will never trip before the 10mm cable is overloaded, the TNB cutout fuse will be your Plan Z overcurrent protection (between TNB meter to DB box) since that should still be on original 40A fuse.
The difference with MCB vs fuse, one can be reset in case of overload (just flip the MCB back on) whereas a fuse once blow already it need someone to buy a replacement, and
that replacement fuse will not be available fast if the electrical supply store is closed.
Regarding 2.5mm cable used for WH circuits;
Should be OK-lah with 2.5mm for WH if its just 15-16A load, within spec of the cable, as long as its all 3kW class heater (3xxx W). You cannot install those highlands model with 4800W using 2.5mm cable.
2.5mm can withstand 21A safely.
That uncle cannot explain why these happened leh..
nobody is laughingQUOTE
September 2013 – Japanese man electrocuted while holding shower head of water heater. Wife electrocuted trying to save husband.
https://www.thestar.com.my/news/nation/2013...death-apartmentAugust 2014 – Pharmacist (lady) found electrocuted while still clutching shower head of water heater.
https://www.thestar.com.my/news/nation/2014...-clutching-showJuly 2016 -
https://www.straitstimes.com/asia/se-asia/m...e-having-showerAugust 2020
https://www.thestar.com.my/news/nation/2020...ted-in-bathroomSingapore- using plug to connect WH
https://www.straitstimes.com/singapore/impr...while-showeringSince 2009; seven reported cases of death by electrocution on heated appliances, safety for electrical household appliances, SIRIM) (as of 2015)
7 Examples of WH Failure (Malaysia)
https://www.st.gov.my/en/contents/presentat...er%20Heater.pdfon heated appliances, safety for electrical household appliances, SIRIM):
-- Four cases involved water heaters
-- Three cases involved storage water heaters
-- Most cases RCCB (main) not working-- In one case earth and live cables melted (found to be undersized).
-- In ALL cases, victim died while still holding onto metallic shower head.
This post has been edited by ceo684: Jun 11 2021, 01:33 AM