QUOTE(Richard @ Dec 26 2016, 09:27 PM)
ok..
3 phase supply properly balanced across each phase means no current flows through the Neutral.. The neutral only returns the unbalance current across the phases..
11KV transmission lines is only 3 wires.. It is distributed in Delta with all phase current balanced.. Only when step down by transformer from Delta 11kV/433V Star is where the neutral is introduced where the Neutral is earthed..
From Transformer it goes to a Feeder pillar where there will be an Earth fault protection device before it gets distributed to residential properties where is must also be earthed at the DB.. This is known as a T-T (Terra-Terra) system..
The usual tail into a residential landed property is only 2x25mm(60A) or 2x16mm2(40A) Aluminium cable which only provides you the fuse rated max demand load which is a slow blow high rupture capacity fuse..
This maximum demand can easily be exceeded by the high inrush starting current of inductive motors (your aircon motor)..
3 Phase is the name of an electrical supply.. It can be 3 wire (2 phase lines plus Neutral) or 4 wire (3 Phase lines Plus Neutral) supply..
Single Phase is the name of a electricity supply of a 2 wire (one phase plus Neutral) supply..
If in doubt please get a competent electrical contractor to verify the existing maximum demand to check that your wiring can handle the electrical load..
You can easily overload (think electrical fire) your existing wiring if you change your protection fuse to a higher rating without knowing your maximum demand..
What I am saying is basic electrical common knowledge to all electricians..
If you don't understand what I'm saying please talk to an electrical person who knows something about maximum demand and how to use a clamp on ammeter..
Electricity is not your friend .. It is a known killer held in a copper prison just waiting to kill you..
3 phase supply properly balanced across each phase means no current flows through the Neutral.. The neutral only returns the unbalance current across the phases..You can try to balance all the feeders you want but in the house it will never be balanced.
This maximum demand can easily be exceeded by the high inrush starting current of inductive motors (your aircon motor)..That's why I am saying. Unless all aircons are turning on at the same exact time, it's not going to burn anything.
It's back to the question I'm telling that doesn't mean if you have 6 air-cons you would need to immediately convert into 3 phase supply.
Especially now with inverter based air-con, it will not only be 0-1 (off-on) which contributes to the high inrush.
In the end, the electrical contractor might just want money and ask you to convert and doesn't think in your best interest.
3 Phase is the name of an electrical supply.. It can be 3 wire (2 phase lines plus Neutral) or 4 wire (3 Phase lines Plus Neutral) supply..I don't think you know your basic electrical common knowledge as well. My fundamental might be flawed cos might gave back some to the Uni but I don't think you're right either.
3 phase can only mean 3 phase. It can only mean 3 phase 3 wire (3 phase without neutral) or 3 phase 4 wire (3 phase with neutral).
Electricity is not your friend .. It is a known killer held in a copper prison just waiting to kill you..Agreed.
Some readings for others:
http://www.renorepairs.my/library/electric...d-single-phase/This post has been edited by LaiN87: Dec 27 2016, 08:52 PM