> izzit safe to add additional unit aircond at home Chat

views
     
jAkUn
post Dec 27 2016, 10:29 PM

Casual
***
Junior Member
326 posts

Joined: Jan 2005
From: Damansara

QUOTE(Richard @ Dec 27 2016, 10:21 PM)
Just to be clear ..

For single phase residential loads..

Your maximum load is limited to the size of the electrical conductor supplied into your home..

The general max size is usually 2x25mm2 Aluminium Overhead cable which gives you a maximum 60A single phase..

This is also why you must not replace the 60A HRC fuse to 100A because that fuse will not blow before the cable starts to burn..

If you need more load then pull in another wire which will give you an additional 60A..

No a 3 Phase kWH meter will cost you more than double the price of a single phase kWH meter and it uses additional cable..

You only pull in another wire if you exceed the existing ..
*
i see..
its because i see lots of comments, 3 phase save tnb bills a lot when using a number of airconds.
TSdarien99
post Jan 9 2017, 05:31 PM

Casual
***
Junior Member
449 posts

Joined: Dec 2009


thanks guise, additional aircond running without problem thumbup.gif
hollyweed
post Jan 9 2017, 05:33 PM

Getting Started
**
Junior Member
67 posts

Joined: May 2015

QUOTE(darien99 @ Dec 25 2016, 08:27 PM)
here u go
*
ini machiem 1 phase. takut trip. better dont.
hollyweed
post Jan 9 2017, 05:34 PM

Getting Started
**
Junior Member
67 posts

Joined: May 2015

QUOTE(darien99 @ Jan 9 2017, 05:31 PM)
thanks guise, additional aircond running without problem  thumbup.gif
*
oh dah install ke. haha ok ignore my previous reply rclxms.gif
Zot
post Jan 9 2017, 05:44 PM

Look at all my stars!!
*******
Senior Member
7,938 posts

Joined: Mar 2014
QUOTE(hollyweed @ Jan 9 2017, 05:34 PM)
oh dah install ke. haha ok ignore my previous reply  rclxms.gif
*
Normal 3 pin plug can be used run 1HP air-con without problem. Higher power need to use 15A socket.

If not mistaken a 20A MCB is used for 2x13A sockets. 1HP aircon is using no more than 1kW. So, each MCB can support 2 x 1HP aircon without problem. If you need to add 1 more 1HP aircon, just make sure the power is taken from another MCB, i.e. using 3-pin socket on separate circuit.

As long as total current usage is less than 63A (power rating for 1 phase), there is no need to use 3-phase supply.