QUOTE(LaiN87 @ Dec 26 2016, 08:25 PM)
Our loads are all single phase. Very rarely you will have 3 phase air con for residential.
Let's say we 1ph.
Means 63A max like someone said.
(Also depending on cable sizing they did when they wire the house)
If you have 3ph, u theoretically can have 3x the loads.
This means that 63A x 3 = 189A total since what they do is they alternate the loads on 3 diff Electrical lines.
Is like having a 1 lane road vs a 3 lane highway.
But current always flow 2 ways. The neutral line have to be oversized properly too. So in the end might not be 3x max.
ok..Let's say we 1ph.
Means 63A max like someone said.
(Also depending on cable sizing they did when they wire the house)
If you have 3ph, u theoretically can have 3x the loads.
This means that 63A x 3 = 189A total since what they do is they alternate the loads on 3 diff Electrical lines.
Is like having a 1 lane road vs a 3 lane highway.
But current always flow 2 ways. The neutral line have to be oversized properly too. So in the end might not be 3x max.
3 phase supply properly balanced across each phase means no current flows through the Neutral.. The neutral only returns the unbalance current across the phases..
11KV transmission lines is only 3 wires.. It is distributed in Delta with all phase current balanced.. Only when step down by transformer from Delta 11kV/433V Star is where the neutral is introduced where the Neutral is earthed..
From Transformer it goes to a Feeder pillar where there will be an Earth fault protection device before it gets distributed to residential properties where is must also be earthed at the DB.. This is known as a T-T (Terra-Terra) system..
The usual tail into a residential landed property is only 2x25mm(60A) or 2x16mm2(40A) Aluminium cable which only provides you the fuse rated max demand load which is a slow blow high rupture capacity fuse..
This maximum demand can easily be exceeded by the high inrush starting current of inductive motors (your aircon motor)..
3 Phase is the name of an electrical supply.. It can be 3 wire (2 phase lines plus Neutral) or 4 wire (3 Phase lines Plus Neutral) supply..
Single Phase is the name of a electricity supply of a 2 wire (one phase plus Neutral) supply..
If in doubt please get a competent electrical contractor to verify the existing maximum demand to check that your wiring can handle the electrical load..
You can easily overload (think electrical fire) your existing wiring if you change your protection fuse to a higher rating without knowing your maximum demand..
What I am saying is basic electrical common knowledge to all electricians..
If you don't understand what I'm saying please talk to an electrical person who knows something about maximum demand and how to use a clamp on ammeter..
Electricity is not your friend .. It is a known killer held in a copper prison just waiting to kill you..