QUOTE(Momo33 @ Oct 20 2022, 08:09 AM)
yes , one can try use 30mA RCCB at the DB box.
the issue will be more power trips . as in Msia we do have many lightning storms . and if you are not home
the food in the fridge will go bad.
the thing about 30mA for 13 A SSO really how many house implement this . even in todays new houses majority
dont have.
so how did they pass the tnb inspection /CF and is it really necessary . i dont really know.
Not many - its common in retrofitted and new build in SG
But in MY.. new builds got put but mainly China brands to save cost
Rarely you will get Schneider nowadays even for half million dollar place
QUOTE(pmaxv @ Oct 20 2022, 09:45 AM)
Hi ceo. I've got a question on point 3 of yours. How do you add the 10ma RCD under the 30ma/100ma RCD? my electrician told me if I do a hierarchy level that will cause side effects. eg. they trip each other off. so he told me to install flat level instead. eg. the rcds are totally isolated.
30mA RCD, whole house (sum of all L - sum of all N return = acceptable losses)
Branches out from here to a bunch of little MCBs.
The 10mA is just for WH's own single L and single N. Input=output = acceptable losses and won't trip. IF the WH N is shared that means:
1) Installation is wrong in the first place
2) Useless for purpose of RCD, forever trip.
3) Most likely because it is not a dedicated LNE run from DB box to the WH unit.
Impossible they will trip each other off
unless the WH circuit is shared neutral.QUOTE(Momo33 @ Oct 20 2022, 10:32 AM)
they will not trip each other off.
example if there is leakage of 20mA in the WH , only the 10 mA RCD will trip.
Correct.
And if there's a leakage of 20mA in a socket or light outlet unrelated to WH circuit, the 10mA will not trip.
QUOTE(pmaxv @ Oct 20 2022, 01:30 PM)
Hi Kytz, thanks a lot for your reply.
For my RCDs, my electrician just daisy chain them from one RCD input to another RCD input. Ended up quite a long chain cause I've multiple RCDs. Is that dangerous?

As for discriminate tripping, I think this one really need proper sifu. I think 99% street sifu don't know this. Mine also don't know.
No, this is acceptable.
QUOTE(Kytz @ Oct 20 2022, 02:21 PM)
Actually devices that can cause safety hazards like water heaters already come with built in RCD nowadays, so it's not necessary to cascade multiple RCDs (as long as all DB circuits are properly protected already with the correct ratings).
Rather, it's recommended (and also more important) to test the RCD regularly instead to ensure that protection is intact. Some water heaters even allow you to test their RCD.
Because like what ceo684 has mentioned, the RCD will fail someday, and the only way to find out is by testing them.
Mana ada WH with built-in RCD.
ELCB got lah.
RCD is god tier protection (think of it as modern airbags)
ELCB is antiquated retired era stuff because "what if leakage don't leak nicely through Earth" aka leak elsewhere e.g. humans = don't t