Not many - its common in retrofitted and new build in SG
But in MY.. new builds got put but mainly China brands to save cost
Rarely you will get Schneider nowadays even for half million dollar place
30mA RCD, whole house (sum of all L - sum of all N return = acceptable losses)
Branches out from here to a bunch of little MCBs.
The 10mA is just for WH's own single L and single N. Input=output = acceptable losses and won't trip. IF the WH N is shared that means:
1) Installation is wrong in the first place
2) Useless for purpose of RCD, forever trip.
3) Most likely because it is not a dedicated LNE run from DB box to the WH unit.
Impossible they will trip each other off
unless the WH circuit is shared neutral.Correct.
And if there's a leakage of 20mA in a socket or light outlet unrelated to WH circuit, the 10mA will not trip.
No, this is acceptable.
Mana ada WH with built-in RCD.
ELCB got lah.
RCD is god tier protection (think of it as modern airbags)
ELCB is antiquated retired era stuff because "what if leakage don't leak nicely through Earth" aka leak elsewhere e.g. humans = don't t
Thanks for the explanation on RCD and neutral line. They are definitely very informative. I like how you explained the current going in and out must be balanced. Now I wonder if my neutral is shared. But that one got to ask my electrician. So far no tripping yet.