Actually ST requirements are 100mA for lighting and 30mA for plug points (power points for equipment easily accessible by hand). In this case, 100mA main RCDs are acceptable, provided that you have 30mA to cover the plug points in addition to the main RCD. If there is only main RCD it has to be a maximum of 30mA, but ST doesn't really recommend 1 RCD for the whole DB.
Of course, this is in addition to water heater circuits which are required to be protected by 10mA RCD (dedicated).
Adding a 10mA RCD in cascade with a 30mA/100mA is not an issue. The device is meant to trip the power due to safety reasons, what may happen is that both may trip at the same time if there is a problem, which is more preferable to it not tripping when the problem occurs.
Doing it "flat" is of course preferable but will involve alot of work at the DB, which is dangerous if not done properly.
Both may still trip, due to tolerances of the device itself especially when 10mA and 30mA are quite close in rating. There is a proper way to do discrimination of tripping for the devices, but even without the discrimination it's still preferable to put them in cascade rather than not having sufficient protection.
Hi Kytz, thanks a lot for your reply.Of course, this is in addition to water heater circuits which are required to be protected by 10mA RCD (dedicated).
Adding a 10mA RCD in cascade with a 30mA/100mA is not an issue. The device is meant to trip the power due to safety reasons, what may happen is that both may trip at the same time if there is a problem, which is more preferable to it not tripping when the problem occurs.
Doing it "flat" is of course preferable but will involve alot of work at the DB, which is dangerous if not done properly.
Both may still trip, due to tolerances of the device itself especially when 10mA and 30mA are quite close in rating. There is a proper way to do discrimination of tripping for the devices, but even without the discrimination it's still preferable to put them in cascade rather than not having sufficient protection.
For my RCDs, my electrician just daisy chain them from one RCD input to another RCD input. Ended up quite a long chain cause I've multiple RCDs. Is that dangerous?

As for discriminate tripping, I think this one really need proper sifu. I think 99% street sifu don't know this. Mine also don't know.