QUOTE(stormer.lyn @ Jul 19 2022, 02:17 PM)
Only the middle one, Maxguard, is the correct specifications for a water heater at a sensitivity of 10 mA or 0.01 A
Ah thanks! What do you think about this brand? Recommended by the electrician...Got an electric shock from steel shower head!
|
|
Jul 20 2022, 10:49 AM
Show posts by this member only | IPv6 | Post
#21
|
![]() ![]() ![]()
Junior Member
445 posts Joined: Oct 2008 |
|
|
|
|
|
|
Jul 20 2022, 10:52 AM
Show posts by this member only | IPv6 | Post
#22
|
![]() ![]()
Junior Member
141 posts Joined: Dec 2010 |
QUOTE(subaiku @ Jun 30 2022, 04:10 PM) Literally got shocked last night when I was using the shower. Mine is a steel shower set type. Got zapped when I touched it! JOVEx again haha. BTW, I dont believe any build in electronics ELCB.Tested with one of those electricity meters, definitely got current. WTF. Anybody else had this problem before? I've got a Joven water heater installed above the ceiling. Is it caused by the heater or something else? Don't know if it's related or not but a few days ago switching on another water heater keep tripping the whole house (also the same model JH25). Only 2 brands I found is using Electro-Magnetic. ELCB. YET to me is not enough and by the rules regardless whether the unit comes with built in, they must have an exter RCCB, RCB, RCBO 10mA. And probably 99.99% user ignore |
|
|
Jul 20 2022, 01:36 PM
Show posts by this member only | IPv6 | Post
#23
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,132 posts Joined: Apr 2014 From: Shah Alam, Selangor |
QUOTE(subaiku @ Jul 20 2022, 10:49 AM) Sorry, never used before. There's something you must realise which unfortunately is this: Contractors don't recommend something based on your best interest. They recommend something because it is easy to purchase, or that is what they have in stock, or it has a large profit margin, etc.You also cannot trust something simply because it has a SIRIM sticker. You must get something that has a SIRIM sticker that has passed electrical specifications. A company could very well get a SIRIM sticker on the claimed weight of the item. That being said, if funds are limited, then go for Maxguard, EPS or Himel branded RCBO with these specs : 20 A overcurrent, 10 mA trip. All have SIRIM and are JKR approved*, meaning they have at least been electrically tested by someone independently. If you go for an RCCB instead of RCBO, then get 25 A, 10 mA trip. The 25A is because there will be an additional MCB for the water heater. NOTE: these specs are if your WH is below, say, 4500 W, which it probably is. Please review if the WH happens to be above this wattage. I can tell you that the store "Combi Electric" online delivers very fast, and price is fair. Now, saying that "Contractors don't recommend something based on your best interest" why should you trust me? I have absolutely no connection to the store just stated, I am not making money off you, and I am only recommending this based on your safety, because I can't get anything else from you! Disclaimer: * last time I checked |
|
|
Jul 20 2022, 04:36 PM
|
![]() ![]()
Junior Member
149 posts Joined: Feb 2021 |
QUOTE(subaiku @ Jul 18 2022, 04:43 PM) Ok guys, really thanks for all the input, just wanted to update for everybody's future reference because this was scary AF. So this is what actually happened. Just to clarify, you are using a storage water heater correct? Not an instant water heater.Got the Joven technician to come over and check, turns out it is the heater element that was spoilt. But usually if this happens, turning on the water heater would have tripped the current box. However it did not, instead the current was running through the copper piping then into the steel shower head. F*ck. So, got heater element fixed and then got my electrician to come take a look to find out why it didn't trip as it should have. Turns out the ground wire for the water heater was not connected to anything! What the electrician did then was to connect the ground wire from my nearby air ventilator to the water heater's ground wire so in future should trip if anything goes wrong. He says should be safe enough. But can also do further precaution by installing RCBO for the water heater at the current box. Sorry if I have wrongly described anything as my electrical knowledge is nil. Anyways I'm considering getting these RCBO models, all got various prices... any advice? https://shopee.com.my/%F0%9F%86%9ACHINT-NXB...77-d1d65bb4a703 https://shopee.com.my/MAXGUARD-20A-32A-2P-1...b3-07b2a2953144 This one is the cheapest, but... is it any good? https://shopee.com.my/CNC-YCB9NL-40-230V-RC...fb-5b0e8b96535e If it is a storage water heater, then FYI storage water heaters do not have a built-in circuit breaker like instant water heaters. So they have to rely on the DB box circuit breaker. BUT if your storage water heater is not grounded / no earth connection, no matter how good quality your circuit breaker is, the circuit breaker will not trip when there is a current leakage, and u will be electrocuted. Hence why SIRIM / Suruhanjaya Tenaga now set a new guideline for storage water heaters to come with Isolation Barriers placed at both the storage water heaters' inlet and outlet water connection. Most SIRIM certified storage water heater brands already complied to this guideline, and some brands even took the extra safety effort to pre-install the isolation barriers on the heater, such as CENTON, which is extra good, considering some inexperienced installers will missed out installing the Isolation Barriers if they are not pre-installed on the heater out-of-the-box. Isolation Barriers are simple devices that elongate any current flow from the storage water heater to users, so any current flow (if there is) will barely reach the users. So in your case where there is an unfortunate current leakage because of the lack of earthing, if your storage water heater is pre-installed with Isolation Barriers, the Isolation Barriers will protect u from electrocution to a certain extend. But every device has a lifespan as well, so u will probably be protected until the lifespan of the Isolation Barriers ended. So don't just rely on the Isolation Barriers to protect u. Installation and earthing connection has to be correct in the first place. Basically just a safety tip for u, if your storage water heater do not have Isolation Barriers pre-installed, u are advised to install them. |
|
|
Jul 21 2022, 09:39 AM
Show posts by this member only | IPv6 | Post
#25
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,132 posts Joined: Apr 2014 From: Shah Alam, Selangor |
QUOTE(Selene Yeo @ Jul 20 2022, 04:36 PM) If it is a storage water heater, then FYI storage water heaters do not have a built-in circuit breaker like instant water heaters. So they have to rely on the DB box circuit breaker. BUT if your storage water heater is not grounded / no earth connection, no matter how good quality your circuit breaker is, the circuit breaker will not trip when there is a current leakage, and u will be electrocuted. This is the reason a 10 mA RCCB/RCBO is specified for water heaters, either instant or storage, whether your heater is Grounded/Earthed or not. You become the Ground/Earth point, and the RCCB/RCBO trips before a fatal current electrocutes you.QUOTE Isolation Barriers are simple devices that elongate any current flow from the storage water heater to users, so any current flow (if there is) will barely reach the users.... As for this, you should absolutely also use isolation barriers (basically, a section of non-conductive pipe to break the path of the hot water copper pipe), or use PP-R or PB pipes for hot water.ElectroBOOM shows the effects of even a small gap of water on electrical conductivity on YouTube https://www.youtube.com/watch?v=dcrY59nGxBg&t=93s |
|
|
Jul 21 2022, 10:18 AM
Show posts by this member only | IPv6 | Post
#26
|
![]() ![]() ![]()
Junior Member
445 posts Joined: Oct 2008 |
QUOTE(stormer.lyn @ Jul 20 2022, 01:36 PM) Sorry, never used before. There's something you must realise which unfortunately is this: Contractors don't recommend something based on your best interest. They recommend something because it is easy to purchase, or that is what they have in stock, or it has a large profit margin, etc. "Contractors don't recommend something based on your best interest." Wise words. You also cannot trust something simply because it has a SIRIM sticker. You must get something that has a SIRIM sticker that has passed electrical specifications. A company could very well get a SIRIM sticker on the claimed weight of the item. That being said, if funds are limited, then go for Maxguard, EPS or Himel branded RCBO with these specs : 20 A overcurrent, 10 mA trip. All have SIRIM and are JKR approved*, meaning they have at least been electrically tested by someone independently. If you go for an RCCB instead of RCBO, then get 25 A, 10 mA trip. The 25A is because there will be an additional MCB for the water heater. NOTE: these specs are if your WH is below, say, 4500 W, which it probably is. Please review if the WH happens to be above this wattage. I can tell you that the store "Combi Electric" online delivers very fast, and price is fair. Now, saying that "Contractors don't recommend something based on your best interest" why should you trust me? I have absolutely no connection to the store just stated, I am not making money off you, and I am only recommending this based on your safety, because I can't get anything else from you! Disclaimer: * last time I checked Ok, thanks for the recommendations! Found these, these are the right ones right, as long as you get the 20A, 10ma versions? They all don't seem to have the earth fault indicator though which I read is important. Worth getting one with that in your opinion? https://shopee.com.my/MAXGUARD-20A-2P10MA-T...9b-d362c89e75bc https://shopee.com.my/Himel-HDB9PLEN40C-RCB...98-32ff6290e643 https://shopee.com.my/EPS-20A-25A-2P-10mA-6...fe-bfcd8624b2e9 Also, curious, how do you find out a product is JKR approved? |
|
|
|
|
|
Jul 21 2022, 10:38 AM
Show posts by this member only | IPv6 | Post
#27
|
![]() ![]() ![]()
Junior Member
445 posts Joined: Oct 2008 |
QUOTE(Selene Yeo @ Jul 20 2022, 04:36 PM) Just to clarify, you are using a storage water heater correct? Not an instant water heater. Yes, it's a storage water heater, the type that's installed up in the ceiling. Joven, model JH25.If it is a storage water heater, then FYI storage water heaters do not have a built-in circuit breaker like instant water heaters. So they have to rely on the DB box circuit breaker. BUT if your storage water heater is not grounded / no earth connection, no matter how good quality your circuit breaker is, the circuit breaker will not trip when there is a current leakage, and u will be electrocuted. Hence why SIRIM / Suruhanjaya Tenaga now set a new guideline for storage water heaters to come with Isolation Barriers placed at both the storage water heaters' inlet and outlet water connection. Most SIRIM certified storage water heater brands already complied to this guideline, and some brands even took the extra safety effort to pre-install the isolation barriers on the heater, such as CENTON, which is extra good, considering some inexperienced installers will missed out installing the Isolation Barriers if they are not pre-installed on the heater out-of-the-box. Isolation Barriers are simple devices that elongate any current flow from the storage water heater to users, so any current flow (if there is) will barely reach the users. So in your case where there is an unfortunate current leakage because of the lack of earthing, if your storage water heater is pre-installed with Isolation Barriers, the Isolation Barriers will protect u from electrocution to a certain extend. But every device has a lifespan as well, so u will probably be protected until the lifespan of the Isolation Barriers ended. So don't just rely on the Isolation Barriers to protect u. Installation and earthing connection has to be correct in the first place. Basically just a safety tip for u, if your storage water heater do not have Isolation Barriers pre-installed, u are advised to install them. Thanks for the tip about Isolation Barriers! So yeah, quite freaked about this whole affair. Went up and took a look, definitely no isolation barriers, copper piping all the way... second pic shows it going into concrete and connecting to my steel shower. And these were installed only 4 years ago. |
|
|
Jul 21 2022, 10:41 AM
|
![]() ![]() ![]() ![]() ![]()
Junior Member
709 posts Joined: Jun 2019 |
QUOTE(subaiku @ Jul 20 2022, 10:47 AM) Ok, thanks! Will look into the Schneider ones... sorry noob question, not sure if I have a MCB? This is my DB box currently... All those C20, C32, etc are MCBs.[attachmentid=11202996][attachmentid=11202997] Your DB box is using Hager components, better for you to buy Hager RCCBs as they will fit perfectly when you cover the enclosure. The enclosure tolerance is tight, if use other brands may not be able to close back, may need to trim the window on the enclosure cover if want to use cheaper brands. Take note that I am not talking about the outer cover, I'm talking about the cover where the stickers (main switch, danger, etc) are on. On another note, your DB box should not be having those C32 MCBs unless there are ring circuits in your house (which is very unlikely). Check what those MCBs are for and replace them with more appropriately sized MCBs. You must also change your main RCCB which is using 300mA sensitivity to 30mA (0.03A). 300mA house burn down also RCD will not trip. This post has been edited by gobiomani: Jul 21 2022, 10:45 AM |
|
|
Jul 21 2022, 10:45 AM
Show posts by this member only | IPv6 | Post
#29
|
![]() ![]() ![]()
Junior Member
445 posts Joined: Oct 2008 |
QUOTE(candidman78 @ Jul 20 2022, 10:52 AM) JOVEx again haha. BTW, I dont believe any build in electronics ELCB. "JOVEx again haha."Only 2 brands I found is using Electro-Magnetic. ELCB. YET to me is not enough and by the rules regardless whether the unit comes with built in, they must have an exter RCCB, RCB, RCBO 10mA. And probably 99.99% user ignore Why? You had similar experience with Joven? Actually I had two Joven water heaters spoilt within a week of each other, this one and the other one suddenly trip the whole house when I tried to switch it on. Both were because of the heater element. Both also just reached 4 years old. Makes me wonder what kind of quality the WH are and here I thought Joven was a reputable brand. |
|
|
Jul 21 2022, 10:59 AM
Show posts by this member only | IPv6 | Post
#30
|
![]() ![]() ![]()
Junior Member
455 posts Joined: Mar 2020 |
QUOTE(subaiku @ Jun 30 2022, 04:52 PM) Errr, mine got no ELCB button like those wall mounted type. Yours is the water heater tank types, not the regular one.» Click to show Spoiler - click again to hide... « You have current on the tap head - possible causes is you have some wiring work done and neutral and earth wiring got connected wrongly or wiring have issues. Better get a technician to check it ASAP. Edit : Saw TS found the root cause at post #15. I replied immediately because of the severity of the issue. Glad that you found it. This post has been edited by AbbyCom: Jul 21 2022, 11:09 AM subaiku liked this post
|
|
|
Jul 21 2022, 12:30 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,135 posts Joined: Jan 2003 From: Seri Kembangan |
Water heater safety guides from the electrical and electronics association of Malaysia https://www.st.gov.my/en/contents/presentat...-%20Updated.pdf maxguy liked this post
|
|
|
Jul 21 2022, 02:37 PM
Show posts by this member only | IPv6 | Post
#32
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,132 posts Joined: Apr 2014 From: Shah Alam, Selangor |
QUOTE(Kiding @ Jul 21 2022, 12:30 PM) Water heater safety guides from the electrical and electronics association of Malaysia Sorry to be a bit pedantic, but I have to point out...https://www.st.gov.my/en/contents/presentat...-%20Updated.pdf ST = Suruhanjaya Tenaga = Energy Commission = can make rules that must be followed electrical and electronics association of Malaysia = guidelines, no legal standing gobiomani liked this post
|
|
|
Jul 22 2022, 12:50 AM
Show posts by this member only | IPv6 | Post
#33
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(subaiku @ Jul 18 2022, 04:43 PM) Ok guys, really thanks for all the input, just wanted to update for everybody's future reference because this was scary AF. So this is what actually happened. Is not whether can or cannot. Its mandatory under the Electricity Regulations 1994 to have 10mA RCD fitted for wet floor appliances.Got the Joven technician to come over and check, turns out it is the heater element that was spoilt. But usually if this happens, turning on the water heater would have tripped the current box. However it did not, instead the current was running through the copper piping then into the steel shower head. F*ck. So, got heater element fixed and then got my electrician to come take a look to find out why it didn't trip as it should have. Turns out the ground wire for the water heater was not connected to anything! What the electrician did then was to connect the ground wire from my nearby air ventilator to the water heater's ground wire so in future should trip if anything goes wrong. He says should be safe enough. But can also do further precaution by installing RCBO for the water heater at the current box. Sorry if I have wrongly described anything as my electrical knowledge is nil. Anyways I'm considering getting these RCBO models, all got various prices... any advice? 1. You trust your life insurance to cheapo china brand? 2. Want to do, do properly. ABB or Hager 10mA RCD. Also like mentioned above, the 3 phase 0.3A = 300mA RCD is useless and against the law, cos of it all your 13A sockets are illegal and unprotected. You need to change to 30mA (0.03A) RCD. This will cost the good part of RM300-ish for the barang alone. This post has been edited by ceo684: Jul 22 2022, 12:54 AM |
|
|
|
|
|
Jul 26 2022, 10:24 PM
Show posts by this member only | IPv6 | Post
#34
|
![]() ![]() ![]()
Junior Member
445 posts Joined: Oct 2008 |
QUOTE(gobiomani @ Jul 21 2022, 10:41 AM) All those C20, C32, etc are MCBs. Hey thanks for all the tips! Did not notice that about my RCCB if you hadn't mentioned it! Will get my electrician to look into those C32 MCBs that you mentioned.Your DB box is using Hager components, better for you to buy Hager RCCBs as they will fit perfectly when you cover the enclosure. The enclosure tolerance is tight, if use other brands may not be able to close back, may need to trim the window on the enclosure cover if want to use cheaper brands. Take note that I am not talking about the outer cover, I'm talking about the cover where the stickers (main switch, danger, etc) are on. On another note, your DB box should not be having those C32 MCBs unless there are ring circuits in your house (which is very unlikely). Check what those MCBs are for and replace them with more appropriately sized MCBs. You must also change your main RCCB which is using 300mA sensitivity to 30mA (0.03A). 300mA house burn down also RCD will not trip. |
|
|
Jul 26 2022, 10:27 PM
Show posts by this member only | IPv6 | Post
#35
|
![]() ![]() ![]()
Junior Member
445 posts Joined: Oct 2008 |
QUOTE(AbbyCom @ Jul 21 2022, 10:59 AM) Yours is the water heater tank types, not the regular one. Heheh... thanks for the concern. You have current on the tap head - possible causes is you have some wiring work done and neutral and earth wiring got connected wrongly or wiring have issues. Better get a technician to check it ASAP. Edit : Saw TS found the root cause at post #15. I replied immediately because of the severity of the issue. Glad that you found it. |
|
|
Jul 26 2022, 10:52 PM
Show posts by this member only | IPv6 | Post
#36
|
![]() ![]() ![]()
Junior Member
445 posts Joined: Oct 2008 |
QUOTE(ceo684 @ Jul 22 2022, 12:50 AM) Is not whether can or cannot. Its mandatory under the Electricity Regulations 1994 to have 10mA RCD fitted for wet floor appliances. Sorry lah boss, didn't know better then 1. You trust your life insurance to cheapo china brand? 2. Want to do, do properly. ABB or Hager 10mA RCD. Also like mentioned above, the 3 phase 0.3A = 300mA RCD is useless and against the law, cos of it all your 13A sockets are illegal and unprotected. You need to change to 30mA (0.03A) RCD. This will cost the good part of RM300-ish for the barang alone. Appreciate the input. This post has been edited by subaiku: Jul 28 2022, 07:58 AM ceo684 liked this post
|
|
|
Jul 27 2022, 02:00 AM
Show posts by this member only | IPv6 | Post
#37
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,413 posts Joined: Jan 2008 From: KL - Cardiff - Subang - Sydney |
looking at how TS's electrician installed the water heater and the errors with the DB box.... I'm wondering how many other houses out there are done the same way by the same guy with the same mistake as well? basically all ticking time bomb.....
This post has been edited by ZeneticX: Jul 27 2022, 02:01 AM |
|
|
Jul 27 2022, 10:23 AM
|
![]() ![]() ![]() ![]() ![]()
Junior Member
709 posts Joined: Jun 2019 |
QUOTE(ZeneticX @ Jul 27 2022, 02:00 AM) looking at how TS's electrician installed the water heater and the errors with the DB box.... I'm wondering how many other houses out there are done the same way by the same guy with the same mistake as well? basically all ticking time bomb..... This kind of thing is unfortunately very common in Malaysia. Most so called electricians in Malaysia don't know what they are doing or want to get it done with minimum work for them. The attitude of most Malaysians where they are not willing to pay for good quality and knowledgeable electrician is also a very big contributing factor to such poor quality work. |
|
|
Jul 27 2022, 10:32 AM
|
![]() ![]() ![]() ![]()
Junior Member
501 posts Joined: Jul 2005 |
Nice thread.. I've learned a lot from you guys... tq and stay safe subaiku liked this post
|
|
|
Jul 28 2022, 08:37 AM
Show posts by this member only | IPv6 | Post
#40
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(ZeneticX @ Jul 27 2022, 02:00 AM) looking at how TS's electrician installed the water heater and the errors with the DB box.... I'm wondering how many other houses out there are done the same way by the same guy with the same mistake as well? basically all ticking time bomb..... An overwhelming majority - sad to say. |