 Got an electric shock from steel shower head!

views
     
TSsubaiku
post Jun 30 2022, 04:10 PM, updated 4y ago

Casual
***
Junior Member
445 posts

Joined: Oct 2008
Literally got shocked last night when I was using the shower. Mine is a steel shower set type. Got zapped when I touched it!

Tested with one of those electricity meters, definitely got current. WTF. Anybody else had this problem before? I've got a Joven water heater installed above the ceiling. Is it caused by the heater or something else? Don't know if it's related or not but a few days ago switching on another water heater keep tripping the whole house (also the same model JH25).


Attached thumbnail(s)
Attached Image
H3artBreakKid
post Jun 30 2022, 04:13 PM

💔💔💔
***
Junior Member
454 posts

Joined: Jun 2012


high rise or landed?
TSsubaiku
post Jun 30 2022, 04:15 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(H3artBreakKid @ Jun 30 2022, 04:13 PM)
high rise or landed?
*
Well, condo but mine's only 6 floors, I'm on the ground floor.
Aftermaths
post Jun 30 2022, 04:16 PM

On my way
****
Junior Member
601 posts

Joined: Apr 2012


QUOTE(H3artBreakKid @ Jun 30 2022, 04:13 PM)
high rise or landed?
*
I believe is landed with central water heater.

Personally I'll suggest TS to change into wall type for each toilet.

dawho
post Jun 30 2022, 04:17 PM

Enthusiast
*****
Senior Member
782 posts

Joined: Oct 2009



this means got some leak in your wiring....
jessicakoh
post Jun 30 2022, 04:31 PM

Getting Started
**
Junior Member
51 posts

Joined: Jan 2007
ELCB test button ok?
TSsubaiku
post Jun 30 2022, 04:52 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(jessicakoh @ Jun 30 2022, 04:31 PM)
ELCB test button ok?
*
Errr, mine got no ELCB button like those wall mounted type.

» Click to show Spoiler - click again to hide... «

nihility
post Jul 2 2022, 08:11 PM

Regular
******
Senior Member
1,595 posts

Joined: Sep 2021


You are fortunate that you are still alive. Go get licensed wiremen to check the wiring & compliance to ST guide for the water heater installation.
davidlow7
post Jul 4 2022, 10:17 AM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(nihility @ Jul 2 2022, 08:11 PM)
You are fortunate that you are still alive. Go get licensed wiremen to check the wiring & compliance to ST guide for the water heater installation.
*
There is a leak in your wiring.

Hopefully you have had a 10mA dedicated RCCB with its dedicated wiring installed for the water heater only, as it is crucial in saving lives.

ELCB from your heater will not detect leakage OUTSIDE the WH so the RCCB is important.
TSsubaiku
post Jul 4 2022, 05:34 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(nihility @ Jul 2 2022, 08:11 PM)
You are fortunate that you are still alive. Go get licensed wiremen to check the wiring & compliance to ST guide for the water heater installation.
*
Thanks for the input, have first asked the Joven technician to come take a look. Then will ask an electrician to double check. Got a phobia now touching anything metal that's connected to an electrical connection. sad.gif

Sorry, a bit of a noob re: electrical stuff, what's this ST guide you mentioned?
TSsubaiku
post Jul 4 2022, 05:35 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(davidlow7 @ Jul 4 2022, 10:17 AM)
There is a leak in your wiring.

Hopefully you have had a 10mA dedicated RCCB with its dedicated wiring installed for the water heater only, as it is crucial in saving lives.

ELCB from your heater will not detect leakage OUTSIDE the WH so the RCCB is important.
*
Thanks for the input! Will definitely look into this. Found a thread that seems to be talking about what you're suggesting..

https://forum.lowyat.net/index.php?showtopic=4938749&st=
davidlow7
post Jul 4 2022, 10:41 PM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(subaiku @ Jul 4 2022, 05:35 PM)
Thanks for the input! Will definitely look into this. Found a thread that seems to be talking about what you're suggesting..

https://forum.lowyat.net/index.php?showtopic=4938749&st=
*
There's a latest guideline from ST
https://www.st.gov.my/en/contents/files/dow...N_DOMESTIK1.pdf
rjmsfire
post Jul 16 2022, 10:13 PM

Getting Started
**
Junior Member
77 posts

Joined: Apr 2011
https://www.todayonline.com/singapore/elder...-heater-1841166

You are lucky didn't get electrocuted to death. This news article of a case in Singapore has some technical explanations of how it can happen.
TSsubaiku
post Jul 18 2022, 04:15 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(rjmsfire @ Jul 16 2022, 10:13 PM)
https://www.todayonline.com/singapore/elder...-heater-1841166

You are lucky didn't get electrocuted to death. This news article of a case in Singapore has some technical explanations of how it can happen.
*
Thanks for the link. Yes, lucky indeed.. read the article, although slightly different from my case, but the thing to take note is this:

user posted image
TSsubaiku
post Jul 18 2022, 04:43 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
Ok guys, really thanks for all the input, just wanted to update for everybody's future reference because this was scary AF. So this is what actually happened.

Got the Joven technician to come over and check, turns out it is the heater element that was spoilt. But usually if this happens, turning on the water heater would have tripped the current box. However it did not, instead the current was running through the copper piping then into the steel shower head. F*ck.

So, got heater element fixed and then got my electrician to come take a look to find out why it didn't trip as it should have. Turns out the ground wire for the water heater was not connected to anything! shocking.gif This one is probably due to my previous crappy contractor who did my reno who also installed the water heaters. Was a vomit blood experience but that's another story.

What the electrician did then was to connect the ground wire from my nearby air ventilator to the water heater's ground wire so in future should trip if anything goes wrong. He says should be safe enough. But can also do further precaution by installing RCBO for the water heater at the current box.

Sorry if I have wrongly described anything as my electrical knowledge is nil. Anyways I'm considering getting these RCBO models, all got various prices... any advice?

https://shopee.com.my/%F0%9F%86%9ACHINT-NXB...77-d1d65bb4a703

https://shopee.com.my/MAXGUARD-20A-32A-2P-1...b3-07b2a2953144

This one is the cheapest, but... is it any good? sweat.gif
https://shopee.com.my/CNC-YCB9NL-40-230V-RC...fb-5b0e8b96535e
gobiomani
post Jul 19 2022, 12:21 PM

Enthusiast
*****
Junior Member
707 posts

Joined: Jun 2019

QUOTE(subaiku @ Jul 18 2022, 04:43 PM)
Ok guys, really thanks for all the input, just wanted to update for everybody's future reference because this was scary AF. So this is what actually happened.

Got the Joven technician to come over and check, turns out it is the heater element that was spoilt. But usually if this happens, turning on the water heater would have tripped the current box. However it did not, instead the current was running through the copper piping then into the steel shower head. F*ck.

So, got heater element fixed and then got my electrician to come take a look to find out why it didn't trip as it should have. Turns out the ground wire for the water heater was not connected to anything!  shocking.gif This one is probably due to my previous crappy contractor who did my reno who also installed the water heaters. Was a vomit blood experience but that's another story.

What the electrician did then was to connect the ground wire from my nearby air ventilator to the water heater's ground wire so in future should trip if anything goes wrong. He says should be safe enough. But can also do further precaution by installing RCBO for the water heater at the current box.

Sorry if I have wrongly described anything as my electrical knowledge is nil. Anyways I'm considering getting these RCBO models, all got various prices... any advice?

https://shopee.com.my/%F0%9F%86%9ACHINT-NXB...77-d1d65bb4a703

https://shopee.com.my/MAXGUARD-20A-32A-2P-1...b3-07b2a2953144

This one is the cheapest, but... is it any good?  sweat.gif
https://shopee.com.my/CNC-YCB9NL-40-230V-RC...fb-5b0e8b96535e
*
If going for RCBO get the Schneider one - around RM130. Better still if your DB box has sufficient space, get RCCB 10mA from ABB or Hager, its around RM150 for ABB and RM190 for Hager. If using RCCB, you still need a MCB.
Don't cheap out on breakers and RCDs.
stormer.lyn
post Jul 19 2022, 02:17 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(subaiku @ Jul 18 2022, 04:43 PM)
Only the middle one, Maxguard, is the correct specifications for a water heater at a sensitivity of 10 mA or 0.01 A
katijar
post Jul 19 2022, 05:15 PM

Look at all my stars!!
*******
Senior Member
2,294 posts

Joined: Sep 2011
i think the shower head and hose cant use metal one ...

need change to plastic/rubber
Kiding
post Jul 19 2022, 07:13 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(gobiomani @ Jul 19 2022, 12:21 PM)
If going for RCBO get the Schneider one - around RM130. Better still if your DB box has sufficient space, get RCCB 10mA from ABB or Hager, its around RM150 for ABB and RM190 for Hager. If using RCCB, you still need a MCB.
Don't cheap out on breakers and RCDs.
*
Fully agreed, all water heater must install along with RCCB or RCBO, this is to add second protection measure, if the first protection failed like TS said, then second protection will save your life. a good quality RCCB with installation just cost less than RM500, your life is definitely worth more than RM500.

TSsubaiku
post Jul 20 2022, 10:47 AM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(gobiomani @ Jul 19 2022, 12:21 PM)
If going for RCBO get the Schneider one - around RM130. Better still if your DB box has sufficient space, get RCCB 10mA from ABB or Hager, its around RM150 for ABB and RM190 for Hager. If using RCCB, you still need a MCB.
Don't cheap out on breakers and RCDs.
*
Ok, thanks! Will look into the Schneider ones... sorry noob question, not sure if I have a MCB? This is my DB box currently...

Attached Image Attached Image

This post has been edited by subaiku: Jul 20 2022, 10:47 AM