QUOTE(zodiacyi @ Jun 14 2022, 03:45 PM)
I think it's time for me to get a certified electrician to get the job done. He has no idea what I'm talking about when I asked him to perform a test circuit to confirm if the RCD is indeed faulty. He even suggested for me to buy a new RCD that is less sensitive (300mA) just like the spare RCD he has installed for me. I do not want to be killed 6 times over so I just brushed him off. Thanks again for your reply.
Most welcome. Sorry late reply.
QUOTE(davidlow7 @ Jun 14 2022, 11:15 PM)
I got headache with most electricians nowadays and I don't know where to find someone competent now to install ab RCD/RCBO 10mA for me.
The
electrician that someone recommended does not know what is RCBO and tell me this is not for Malaysia one 🤦♂️. He further insisted that I'll need to rewiring everything when I install one.
Really headache and I don't know where to get someone competent. I've not used the water heater for months now.
Got one, but you need to dig in FB "Chargeman & Wireman" group.
QUOTE(judesh @ Jan 6 2023, 08:03 AM)
Hi Guys, after reading the comments here I decided to check what's in my house. It's a 2 storey house in Melaka with 3 phase supply. 1 WH connected to dB downstairs which I will replace with 10mA RCCB. Will also replace the main 4P 100mA RCCB with 30mA from ABB.
Upstairs DB will also replace main 100mA RCCB to 30mA.... But all slots full so can't change to RCCB for each WH so looking at options...
1. Change 14way to 18way DB?
2. Replace with 10mA RCBO for the 2 WH...is this PnP or need also to identify the N and connect accordingly?
3. Maxguard or any other Sirim approved 10mA RCBO ok or recommended Schneider only?
4. All the WH are connected by plug socket in wall above inside bathroom. Will also replace this with splash proof socket as recommended... Can I connect the 10mA RCCB above this socket instead ? Or above switch outside bathroom?
Thanks
1) is always possible, I run 48 way for my small apartment; RCBO is space saving as it can replace existing MCB slot (1-to-1).
2) need to identify the return N for that specific circuit. bit mafan. but doable, and its a necessary step for proper installation.
3)
Your life insurance provider. Personally if best-of-the-best, ABB or Hager has technical advantage being VI (voltage independent) in such that even if the voltage to RCD dips below certain V, the RCD still will operate even at 0 voltage. It is pure current imbalance detection. Whereas "for any other commonly available brand that is cheaper" they are highly likely to be the VD type RCD (voltage dependent). Nevertheless, understand that ABB/Hager 10mA costs upwards of RM150 each, I would recommend at least getting a Schneider 10mA.
4) Plug and socket is illegal because almost all WH already exceed 15A nominal. Change to splash proof centon connector.
4.1)
The 10mA ideally should be at the DB box area for ease of maintenance but if there is no other better way, keep it OUTSIDE of the wet area (outside of bathroom) and
before the 20A switch (i.e. RCD must always be powered).
QUOTE(lowyat101 @ Jan 6 2023, 10:50 AM)
» Click to show Spoiler - click again to hide... «
just curious, why you want to use the 30mA for the mains?sorry ignore the questions above, just found out that my house also having the 30mA

30mA offers a "seatbelt" to cut power
before your heart goes out of order "ventricular fillibration" at 50mA.
Since 100mA or 300mA is gonna cut power AFTER your heart goes out of order "ventricular fillibration" at 50mA... in short, it means bye bye
There is no mention of 300mA for domestic installation in the MS1979 COP at all.
--Yes this is old version @ 2007 but the 2015 one didn't change much.