QUOTE(veron208 @ May 8 2024, 03:33 PM)
i have multiple old R22 ac and my ac installer told me that they just need to change the piping adapter for both ends.
the piping were all concealed in the wall.
weird when he said he will not use any special chemical or nitrogen to flush out
This is the copper pipe pressure data from Daikin

In theory the thinnest walled copper pipe (0.61 mm) can withstand the pressure in an R32 system. My data tables go until 400 psi for the high pressure side for R32, which is well under the bursting pressure limit. R410 and R32 systems run at similar pressures, so a R410 system should convert to R32 without issues.
Opinion: I believe the failure point when using thinner pipe is at the joints, not the actual bursting of the pipes. So I also use Nylog Blue on all the flares.You can use the incorrect pipe size for the a/cond, but the efficiency (both cooling and electrical) will drop. By how much I can't tell you.
Please note that brazing copper pipe will form copper oxides
on the inside if there is normal air inside the tube. You must flow a dry inert gas when brazing. The particles formed by bad brazing is bad for the system. (I use Argon not Nitrogen, because I do a bit of TIG welding, and already have the gas on hand. No need for the cost of additional N
2 gas and tank and flow meter, although Ar is more expensive)
You shouldn't mix lubricating oils. Some lubricating oils are incompatible with each other, for eg PAG and mineral oil. Wear and tear will increase or the compressor may jam. So the tubes
must be flushed with solvent before changing refrigeration gas systems. It is not necessary to purge the system with N
2 gas at this point, only during brazing.
And finally, you can't vacuum the system for too much or too long before charging the refrigeration gas.
Any of the above done/not done, will lead to a failure. Maybe in 3 months, maybe in 3 years, maybe in 30 years. I donno cannot say depends on luck, the star sign of the installer, and the phase of the moon.