Is it appropriate to use a 3C 40x00076 flexible cable for 1 HP and 1.5 HP inverters, and a 3C 70x00076 flexible cable for a 2.5 HP inverter?
Shouldn't the standard at least require a 2.5 mm² cable? These two types of flexible cables do not appear to be equivalent to a 2.5 mm² cable.
There is no Malaysia Standard for the wiring size between the Outdoor and Indoor unit, only the installed wires that feeds the a/cond. The wiring between ODU and IDU is considered wiring internal to the unit and is specified in the installation manual by the manufacturer.Shouldn't the standard at least require a 2.5 mm² cable? These two types of flexible cables do not appear to be equivalent to a 2.5 mm² cable.
Sample of specifications from Daikin

40 x 0.0076 = nominal diameter 1.1 mm²
70 x 0.0076 = nominal diameter 2.0 mm²
Looks like 40 x 0.0076 should not be used as I have never seen an installation manual that allows less than 1.5 mm² between the ODU and IDU. For the 70 strand you need to check for your specific unit if it is appropriate.