QUOTE(DuitNow @ Mar 4 2019, 09:49 AM)
Ok the last test, when I switch on the aircon at the lowest speed setting after resting the aircon for 20-30mins, the fan did spin up then stop. This consider normal?
*
Is aircon in dry mode?
If it stop, try to use finger or some long object to flick the blower to move..... does it start?
SUSslimey
post Mar 4 2019, 12:02 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(DuitNow @ Mar 4 2019, 11:40 AM)
If I change fan setting to high mode or other mode, fan blower will start.

Its just that fan blower wind not strong, even if I set fan to high mode. Fan motor problem possible? Cost repair high?
*
Don’t know.... sounds weird with the blower stopping on its own after 20-30min.

I can’t pin point the problem. If pcb then it might not worth the repair.
SUSslimey
post Mar 4 2019, 03:02 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(voscar @ Mar 4 2019, 12:26 PM)
if everytime start-up need to use long object flick only the blower fan starts spinning, what's wrong is that? is it repairable and was it expensive to repair?
encountered this on some old aircond...
*
Capacitor.

The item to change cost only few bucks.
SUSslimey
post Mar 4 2019, 03:04 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(DuitNow @ Mar 4 2019, 01:24 PM)
If its fan blower motor then worth repairing?
*
If fan blower then it is an easy fix.

But I don’t think it is blower problem.
SUSslimey
post Mar 4 2019, 03:44 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(DesktopLimousine @ Mar 4 2019, 03:42 PM)
Need a recommendation for my 200sqf room. My nearest shop offer me RM1.3k for daikin r32/r410 non inverter for 1.5hp. Is this a good deal? Which one is more better r32 or r410? Or should i take the inverter aircon for rm1.6k (but the shop not recommend it since im living at housing far from a town which is not good in electricity production and may damage the inverter pcb board). Im gonna use it for about 12-18hrs a day cause im not working and only doing business in my own bedroom.
*
Lel.

Just go inverter r32.

It is not like your fridge or tv or computer ko often right?
SUSslimey
post Mar 4 2019, 03:52 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(DesktopLimousine @ Mar 4 2019, 03:48 PM)
So far no k.o laaa, just the fridge sometimes make toktok sound when the voltage drop in the night. Then I need to switch off then turn it on back. How much electric bill save for inverter compare to non inverter?
*
Weird fridge.

Anyway... how much it save depends on how you use.
Can be up to 30 percent easily.

Inverter is not only about saving electricity, it is also quieter and more comfortable.

If you really want peace of mind, ask for extended warranty at the shop
SUSslimey
post Mar 4 2019, 04:20 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(DuitNow @ Mar 4 2019, 04:18 PM)
The electrician that fix the aircon switch, did a simple check and told me the air fan blower motor is the main problem the room not cool enough.

So if I ask an aircon repairman to fix the air fan blower, how much would it cost? Or should I buy a new aircon better?
*
The blower motor cost rm 80 usually. The rest is labor.

I still think it is not motor problem.
SUSslimey
post Mar 5 2019, 10:21 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(toffeeman @ Mar 5 2019, 10:09 PM)
Hi I went on the shop at Harvey Norman.  The sales lady claimed that the Panasonic R32 air conditioners can be installed to replace the old R22 air conds without having to change the piping.

Can someone validate this is really the case?
*
haha.........

of course can be installed..........but...........
install wrongly or badly.........it will be endless repairs and troubleshooting

and i don't think panasonic will honor the warranty
SUSslimey
post Mar 5 2019, 10:22 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(zizheng @ Mar 5 2019, 09:45 PM)
York YWM09G-AMLBB
*
outdoor unit has no sensor.

if you know what you are doing, i suggest change the indoor room sensor and indoor coil sensor.
SUSslimey
post Mar 6 2019, 11:32 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(zizheng @ Mar 6 2019, 08:39 PM)
any idea how much does the  sensor cost?
when I turn on the AC, the compressor only runs after a while and it never stops. so, is the sensors which are giving problem?
*
the two sensor together should cost less than rm 30. likely room sensor is the one giving wrong information to the motherboard. but since you are opening it might as well change the coil sensor together.......
SUSslimey
post Mar 7 2019, 06:56 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(1tanmee @ Mar 7 2019, 05:24 PM)
Recommendatiom for portable aircon please. Weather so unberably hot nowadays!
*
All portable aircon are crap.

Sure you can get cold air blowing at you but the electric bill will be big.
SUSslimey
post Mar 7 2019, 08:52 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(ayamxxx @ Mar 7 2019, 08:41 PM)
Appreciate to know the brand n model?
First time heard indoor bocor, usually only the pipe leaking etc.
*
indoor coil leak is quite common.........especially at all the C joints at both sides of the evaporator coil.
SUSslimey
post Mar 8 2019, 09:20 AM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(DuitNow @ Mar 8 2019, 01:06 AM)
One more thing, I notice if I switch on the aircon for long duration, I will hear a knocking sound on the compresoor outside onceawhile. The knocking sound is quite loud.
*
Lol.
Many problem.
1. Your indoor coil could be very dirty and blocked. There is still liquid state gas that is being sucked into the compressor. If the suction line got frost on it then can confirm the indoor unit coil is blocked with dust.
2. The filter for the refrigerant might be blocked and faulty.

I suggest have a aircon guy clean the indoor and outdoor unit.
Maybe it is the blocked indoor unit that is causing the airflow to be bad. Hey if you hear sounds like fu fu fu when the cross fan is spinning then confirm block la.
SUSslimey
post Mar 8 2019, 12:54 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(DuitNow @ Mar 8 2019, 11:08 AM)
But the aircon just cleaned by aircon repairman a few weeks ago. sad.gif

The aircon repairman check say no problem at all. So how? Should I contact the official service centre? I dont know where the receipt gone, even the official aircon service centre namecard also thrown off.

After the cleaning, and using for a few weeks, it isnt as cool and its only cool when the whether damm cold.

Or just replace the aircon since quite old already over 5 years, should be 6-7 years since its 2019 now.
So if take 1.5hp, whether inverter or noninverter, will the electric bill be lower compare if I take 1.0hp inverter or noninverter?
*
Lol. Another crappy aircon guy.

Do whatever you want la. It is an old aircon anyway.
SUSslimey
post Mar 13 2019, 05:56 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(amco @ Mar 13 2019, 05:40 PM)
3 things to do :
INDOOR UNIT
1. Clean if dirty
2. Change capacitor (standard 1hp = 1uf, around RM 6-10)
3. Blower motor need to change

Follow the quide in sequence for cheapest repair.
*
Erm. Capacitor size depends on the blower motor. 1hp= 1uf might not be the case.
SUSslimey
post Mar 20 2019, 11:42 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(shebbycs @ Mar 20 2019, 11:34 PM)
Just talk with aircond specialist he said better avoid mitsubishi because problem with sensor

for daikin and panasonic suppose to be same but he suggest to take daikin because he said panasonic spare part is more expensive then daikin, is it true? how much different ? but when I asked bout warranty, he said both brand offer same warranty
*
Daikin is from oyl factory Malaysia. Expect part prices to be cheaper by rm 20-30

Panasonic has history of problem with sensor also.
Old York produced from oyl factory has lousy capacitor that fail quickly.....

Meh.

Each brand got their own problem.

This post has been edited by slimey: Mar 20 2019, 11:43 PM
SUSslimey
post Feb 6 2021, 04:12 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(adamw @ Feb 6 2021, 03:39 PM)
If Armaflex/insulator for the copper pipings already partialy damage due to aging is it necessary to replace with new insulation?
*
Depends on location.
Those inside wall don’t matter.
Those outdoor don’t matter much.
Those running horizontally across ceiling could be potential problem as condensation build up and drip, damaging the ceiling.
SUSslimey
post Feb 13 2021, 06:07 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(squidsquid @ Feb 13 2021, 09:31 AM)
Can anyone recommend reliable aircond (panasonic) repair service at shah alam? Can pls also PM me directly

There is power light near the switch but no power light on the aircond itself.

Thanks
*
2 possible reasons.......

1. defect of flexible cable connecting the switch to aircon. poor quality ones can break internally the connection of the wires.

2. blown fuse on the aircon pcb........usually only happen during operation then stop suddenly........requires further investigation if this is the case.

but, if you dont have electrical knowledge, better get a professional
SUSslimey
post Mar 10 2021, 06:04 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(chanmickey @ Mar 10 2021, 05:42 PM)
Hi everyone, want to share a problem with my Mitsubishi 1hp aircond inverter type. I have called 2 aircond service companies and both unable to help. The last one asked me to change the aircond. Basicallly it is not cold and the air that comes out like whooshing. One of the service men changed a part to test suspecting it to be the cause. Picture of part below. However after changing and running the aircond for quite awhile, he tested the temp of air coming out and it is still not cold enough. He gave up.
The air cond is about 6 years now, just past warranty. The repair man mentioned the compressor is not powerful enough?
Any Sifus here can give idea what to do next?
Or do you have any one to recommend to repair around Subang area?

Many thanks in advance

user posted image
*
have they tested the current in amps drawn by the compressor?

here's the basics :

1. 1hp aircon inverter type i assume current drawn during cooling phase is 3+ to 4 amps. usually around 3.5amp when running close to 100% power. check your own unit for more accurate figures.
2. also have to check gas pressure together with amount of amp drawn. i assume refrigerant is r410a for an aircon of that age. gas pressure at the suction line would be more than 100 psi and less than 140 psi during cooling phase.

scenario :

1. if amp drawn is low and refrigerant pressure is low......means you are low on refrigerant and having a refrigerant leak
2. if amp drawn is very low and refrigerant pressure is very high........,means that the compressor is not running
3. if amp drawn is high and refrigerant pressure is high, it could mean that the outdoor coil is dirty and possible outdoor fan malfunction
4. if amp drawn is normal and refrigerant pressure is low............it could mean indoor coil is dirty or indoor fan malfunction
5. if amp drawn is low and refrigerant pressure is normal/a bit higher than normal, it could mean compressor speed is slower than usual which could be caused by :1. compressor run capacitor dying, 2. signal sent by indoor to outdoor does not represent the actual condition......check indoor coil sensor/indoor room sensor.

for an aircon of 6 years.......i would check the health of the capacitor and sensor. that's my suspicion.
SUSslimey
post Mar 19 2021, 12:17 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(ceo684 @ Mar 19 2021, 11:21 AM)
At least one, for motor start. There may be one more smaller one for fan run capacitor.

Some designs combine two required ratings for both start/fan - this usually referred to dual capacitor (3-leg physical type).

The only hard part is whether the AC unit is safely accessible.

How to test caps:

*
One simple way to test is to clamp the wire to outdoor unit. Either the neutral or live can do.

Read the current draw.
If draws at least 0.2-0.3 , you know the outdoor fan is working. And hence outdoor fan cap is good.

In the case of bad compressor cap, it will fluctuate between that above number and some random big number for a fraction of a second, like 0.3 then suddenly 20 then back either to 0( indoor circuit board trip and will show error code) or back to 0.3( this will cycle a few times and aircon will not be cold). Reasoning for the big number like 20 amp is due to compressor not running and hence high load during static condition.

If after change cap(assuming cap is good and correctly wired) still the same , the compressor is dead

Just sharing some safe ways of testing without going to outdoor and to decide on next step based on the diagnosis.

This post has been edited by slimey: Mar 19 2021, 12:18 PM