[quote=deadwiller,Dec 9 2019, 06:57 PM]
[quote=Fubar20,Dec 9 2019, 06:55 PM]
Any other appliances connected to that power point? Or that circuit?
Sometimes the wiring from the DB doesn't just go to that power point, maybe share with other switches.
This I’m really not too sure. If it does share with others, what are my options? Change the CB to a 20A? There is nothing connected to that power point.
[/quote]
Do not simply change the MCB to 20A.
The MCB to lighting points is normally 6A MCB. Standard looping is 6 lighting points for each loop. For the 3 pin sockets, a 20A MCB is used for every 2 x 3 pin sockets. Do note that the wire diameter for lighting and wall sockets are different sizes. If you change the 6A light MCB to 20A, you risk melting the wire insulator in the wall and possible fire. The lighting wire is not meant to carry high load.