It adds on in the
main DB box. Refer 3:11 for the general diagram
https://youtu.be/oa_a4HTVqoQ?t=191Depending on what supply (1 phase or 3 phase), you need some room in the DB box (of either 2 modules width, or 4 modules width).
To create room, this may require moving around some MCB's; or if the DB box is full, a new bigger box preferably with similar layout need to be installed.
Similar layout meaning if currently u are using a 12x2 row (24 slot)
----------
----------
expand to something like a 16x2 row (or 16x3 row).
-------------
-------------
If you expand to a 27x 1 row format
---------------------
---------yes, it give u 3 more slots space as 27>24
but the problem is I dont think your existing wiring lengths can stretchhhhh that much (mostly it is just nice only, no slack).
Hence if its 12x2 row in the beginning then u need to get something that follows along the same format as the old box.
The SPD still need a bit of kung fu to do properly although its install location is confined to within the DB box.
Technically the connection is the easy part but
that's assuming the customer DB box has sufficient space else need to upgrade bigger box and/or remove unused MCB to fit and move out existing MCB as the "wong wai" is closest possible to the main MCB [50cm max = shortest bestest].
https://library.e.abb.com/public/76853add5a...olutions_EN.pdfpages 19, 21, 22, 23, 30 (see TNS/TT system diagram, Malaysia use TT).
Back-up protection dedicated to the SPD = At bare minimum, SPD must be behind at least the main MCB (for indirect strike/T2).
It is recommended to have another MCB dedicated just for the SPD alone (whilst the main MCB will take care of shorts, but additional one MCB still not expensive to implement) in case the SPD totally failed due to damage (and created a short circuit) after kena too many strikes.
Thanks for the info.
My DB doesn't have enough space to install another 4P SDP. If I pull all the 4 wires (3L + N) from (after the main MCB but before the RCCB) out of the main DB, into another small db box so I can install a new MCB (dedicated for SDP)+ the 4P SPD, does the 50cm rule apply from where I pull the 4 cables out, or from the 2nd MCB?
Saw these on Shopee; will this work? The length of those cables (3L + N + E) definitely exceeds 50cm already, unless you measure from that 2nd MCB on the right