Wrong tool for the job. RCD (the test button is giveaway) protect against current imbalance. T2 SPD works in 8/20microseconds.T2 SPD is always standby 24/7 with nothing to do for the user, no buttons to press, no switches to flip. Only inspect once in awhile there is still enough "life" in the window.
Example of three phase Type 2 SPD:
Whole house Type2 SPD (indirect strike) is usually what you will need.
Proper ones like Hager SPM240E/440E or ABB OVR-T2 or Schneider iPRD is supposed to be installed in the DB box, AFTER whole house MCB and BEFORE whole house RCD.
30 dollar china made unknown brand "toys" may not work well.
Generally, a good T2 SPD for single phase about 200-230 bucks, 3 phase 400-500 bucks
50cm rule of total max cable length apply for installation of T2 SPD.
QUOTE
RCD should only trip if there is an imbalance between the phase and neutral on the circuits/rings that are connected. The only way that it would trip in a thunderstorm were if a surge voltage due to lightning were to be induced on either the phase or neutral thus causing an imbalance. -
per https://www2.theiet.org/forums/forum/messag...&threadid=50221
Further reading on SPD..start with https://www.electrical-installation.org/enw...on_Device_(SPD)