 Problem with Panasonic air conditioner

views
     
TSkelvyn
post Dec 29 2011, 04:35 PM, updated 14y ago

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
Anyone know how to solve this problem?

I am having problem with one of the 1HP air conditioner unit from Panasonic. Problem started after about one month after installation.
It seems that it is noisy when the air swing is allow to swing.
Their technicians have made 5 attempts to rectify the problem and till now, the problem still persist. rclxub.gif
It seems that they are using trial & error method. Every time, when they come, just apply some grease onto the moving parts and the next time, come and change the air vent. After using for a few days, after the grease dries up, the noise comes back.
Now, the warranty is about to expire... sad.gif

Written to their Customer Care dept, then they called and want to try to apply grease and replace the air vent again. Really don't know when all these trial & error will end and problem solve.

Really regretted installing the Pana aircon. Some more went and installed 4 units. Include the older set (2 years ago), so, in total 5 units. sad.gif

tiensong
post Dec 29 2011, 04:42 PM

Look at all my stars!!
*******
Senior Member
2,237 posts

Joined: Jul 2011
Buying things sometimes depend on luck too..

So far no problem with pana air-con in my current house..

but for my new house, i plan to use york...
TSkelvyn
post Dec 29 2011, 05:03 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
My mum's house has using Panasonic air conditioner for so many years. No problem. A few friends also using panasonic air con, also did not hear them commenting. Have installed one unit of Pana 2 years ago. Also no problem.

But when installed the new model Panasonic, then encountered problem.
During one of their trips, one of their technician accidentally mentioned that they have encountered similar problem and have not managed to resolve them. So, if the problem still persist, then just do not allow the air vent to swing. Have to live with it.

So, I would say that the older model are reliable but not so for the newer model.
svage98
post Dec 29 2011, 07:23 PM

Casual
***
Junior Member
432 posts

Joined: Oct 2007
From: Nilai



QUOTE(kelvyn @ Dec 29 2011, 04:35 PM)
Anyone know how to solve this problem?

I am having problem with one of the 1HP air conditioner unit from Panasonic. Problem started after about one month after installation.
It seems that it is noisy when the air swing is allow to swing.
Their technicians have made 5 attempts to rectify the problem and till now, the problem still persist. rclxub.gif
It seems that they are using trial & error method. Every time, when they come, just apply some grease onto the moving parts and the next time, come and change the air vent. After using for a few days, after the grease dries up, the noise comes back.
Now, the warranty is about to expire... sad.gif

Written to their Customer Care dept, then they called and want to try to apply grease and replace the air vent again. Really don't know when all these trial & error will end and problem solve.

Really regretted installing the Pana aircon. Some more went and installed 4 units. Include the older set (2 years ago), so, in total 5 units.  sad.gif
*
So all 4 units noisy or just the one?
TSkelvyn
post Dec 30 2011, 11:14 AM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
The noisy problem from the air vent movements on 2 units have been solve (hopefully will be permanent) while the one in the bedroom is still not solve. Damn irritating since it is in the bedroom
ravemaster
post Apr 19 2012, 12:43 PM

Getting Started
**
Junior Member
139 posts

Joined: Jun 2006


i got a question here...it is about my panasonic 1hp inverter air cond installed last month. the problem is the nanoeg function like now not working fine (light turned off).
from complete shutdown, if i on the unit, the blue light of the nanoeg feature will turn on, but a couple of minutes, i will auto turn it off. pressing the button from the controller does not help. the thing is working for the 1st 1 month. any body got any idea? thanks
stevie8
post Apr 19 2012, 02:25 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(kelvyn @ Dec 30 2011, 11:14 AM)
The noisy problem from the air vent movements on 2 units have been solve (hopefully will be permanent) while the one in the bedroom is still not solve. Damn irritating since it is in the bedroom
*
SWAP
TSkelvyn
post Apr 19 2012, 02:46 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(ravemaster @ Apr 19 2012, 01:43 PM)
i got a question here...it is about my panasonic 1hp inverter air cond installed last month. the problem is the nanoeg function like now not working fine (light turned off).
from complete shutdown, if i on the unit, the blue light of the nanoeg feature will turn on, but a couple of minutes, i will auto turn it off. pressing the button from the controller does not help. the thing is working for the 1st 1 month. any body got any idea? thanks
*
Suggest that you lodge your complain with Panasonic. get the complain ref no. Keep calling them if no response.

QUOTE(stevie8 @ Apr 19 2012, 03:25 PM)
SWAP
*
Problem is that those are 1.5Hp while the one in the bedroom is 1HP.
Anyway, the noisy problem solved after replacing the indoor unit (CS-PC9MKH) with the newer modal (CS-C9NKH)
it seems that Panasonic's older model has some design fault with its air swing mechanism...
hkh_88
post Apr 19 2012, 03:39 PM

Casual
***
Junior Member
315 posts

Joined: Nov 2005
From: Puchong



QUOTE(kelvyn @ Apr 19 2012, 02:46 PM)
Suggest that you lodge your complain with Panasonic. get the complain ref no. Keep calling them if no response.
Problem is that those are 1.5Hp while the one in the bedroom is 1HP.
Anyway, the noisy problem solved after replacing the indoor unit (CS-PC9MKH) with the newer modal (CS-C9NKH)
it seems that Panasonic's older model has some design fault with its air swing mechanism...
*
1 and 1.5hp indoor unit can be swap de. last time 1.5hp indoor broke then put 1.0hp indoor unit, working fine. biggrin.gif
TSkelvyn
post Apr 19 2012, 04:14 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(hkh_88 @ Apr 19 2012, 04:39 PM)
1 and 1.5hp indoor unit can be swap de. last time 1.5hp indoor broke then put 1.0hp indoor unit, working fine. biggrin.gif
*
Maybe the indoor unit can be interchange... hmm.gif
But since they are under warranty, if pandai pandai go and interchange, then if happen to claim for warranty later, then problem. Usual la... when claim for warranty they will find reasons to get out of responsibility...
Since still under warranty, then let Panasonic rectify their product design fault.


boomber
post Apr 19 2012, 06:13 PM

Casual
***
Junior Member
447 posts

Joined: Jan 2009


My panasonic eco navi also noisy when it swing, somemore the unit under 1 year... expensive but lousy quality.

My study room using mitsubishi mr. slim, 3 years not a single noise from the air cond. My new house will be 100% mitsubishi.
etsy3699
post Apr 19 2012, 07:08 PM

Getting Started
**
Junior Member
60 posts

Joined: Mar 2011


QUOTE(boomber @ Apr 19 2012, 06:13 PM)
My panasonic eco navi also noisy when it swing, somemore the unit under 1 year... expensive but lousy quality.

My study room using mitsubishi mr. slim, 3 years not a single noise from the air cond. My new house will be 100% mitsubishi.
*
Ya Mitsubishi is good, York is depending on luck, and Panasonic Inverter in my bedroom quite noisy suddenly in the middle of the night! Expensive some more, gas also different than normal gas, need to add RM40-50 for inverter gas. Regret.
TSkelvyn
post Apr 19 2012, 08:17 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(boomber @ Apr 19 2012, 07:13 PM)
My panasonic eco navi also noisy when it swing, somemore the unit under 1 year... expensive but lousy quality.

My study room using mitsubishi mr. slim, 3 years not a single noise from the air cond. My new house will be 100% mitsubishi.
*
If still under warranty, just keep complaining to Panasonic. If you complain hard enough, they will replace it. hehehe
Also don't forget the consumer tribunal if they(Pana) do not act on your complains. There has been a few complains lodge by various purchaser of the product... The consumer tribunal is effective although as bit slow...but the message gets across to the rightful party.
boomber
post Apr 19 2012, 09:11 PM

Casual
***
Junior Member
447 posts

Joined: Jan 2009


QUOTE(etsy3699 @ Apr 19 2012, 07:08 PM)
Ya Mitsubishi is good, York is depending on luck, and Panasonic Inverter in my bedroom quite noisy suddenly in the middle of the night! Expensive some more, gas also different than normal gas, need to add RM40-50 for inverter gas. Regret.
*
Ya, my stupid econavi also will cause noise middle of the night, sound like raining but actually is the plastic and blower sound.
The thing is, panasonic econavi price is more or less similar to Mitsubishi Mr. Slim... I bought it cause I want to try different brand and everyone told me pana is quite good...

True that they can come and service but i dun think everyone so free to keep waiting for their engineer at home, its not once a year....more than that...

Conclusion, if can go for other brand, lol.
netcrawler
post Apr 19 2012, 10:52 PM

Regular
******
Senior Member
1,542 posts

Joined: Jan 2005
From: Seri Kembangan


I'm using Pana Econavi and it's okay so far smile.gif
TSkelvyn
post Apr 20 2012, 08:41 AM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(netcrawler @ Apr 19 2012, 11:52 PM)
I'm using Pana Econavi and it's okay so far smile.gif
*
Depending on which model you are having...
I believe on the latest model, they have changed the swing mechanism and hopefully solve the air swing noisy problem.. whistling.gif
moshei
post Apr 20 2012, 05:53 PM

New Member
*
Junior Member
8 posts

Joined: Apr 2012
From: New York


Why not ask them to replace the parts of your Panasonic air-con since its not working even there fixing the problem. I guess you can do that since they new about your problem.
hkh_88
post Apr 23 2012, 10:13 PM

Casual
***
Junior Member
315 posts

Joined: Nov 2005
From: Puchong



panasonic eco navi tat bad meh? Deng lo, just bought all unit for my 2.5 storey home. totally 8 sets doh.gif doh.gif
netcrawler
post Apr 23 2012, 10:39 PM

Regular
******
Senior Member
1,542 posts

Joined: Jan 2005
From: Seri Kembangan


QUOTE(hkh_88 @ Apr 23 2012, 10:13 PM)
panasonic eco navi tat bad meh? Deng lo, just bought all unit for my 2.5 storey home. totally 8 sets  doh.gif  doh.gif
*
My one is okay for econavi.
TSkelvyn
post Apr 24 2012, 08:04 AM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(hkh_88 @ Apr 23 2012, 11:13 PM)
panasonic eco navi tat bad meh? Deng lo, just bought all unit for my 2.5 storey home. totally 8 sets  doh.gif  doh.gif
*
If you are getting the latest model, should be OK as they have may have rectify the problem with their previous model's air swing mechanism.
faiz573
post Apr 24 2012, 09:06 AM

New Member
*
Junior Member
30 posts

Joined: Sep 2011


oh, shit i was planning to install panasonic ac for my unit....
can some one recommend other brand than PANA ???
TSkelvyn
post Apr 24 2012, 09:11 AM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
Try Daikin.. Frankly if I had not installed Pana, would have gone for Daikin
iamsobloodysick
post Apr 24 2012, 10:16 AM

Look at all my stars!!
*******
Senior Member
2,006 posts

Joined: Mar 2005
From: Truly Malaise
QUOTE(faiz573 @ Apr 24 2012, 09:06 AM)
oh, shit i was planning to install panasonic ac for my unit....
can some one recommend other brand than PANA ???
*
Daikin is absolutely pro in aircond, solid built quality and yet quiet operation.

#1 in Japan.


Added on April 24, 2012, 10:21 am
QUOTE(hkh_88 @ Apr 23 2012, 10:13 PM)
panasonic eco navi tat bad meh? Deng lo, just bought all unit for my 2.5 storey home. totally 8 sets  doh.gif  doh.gif
*
More high tech sensor in the blower, more unexpected problem from the blower. This is a logic situation.

Before buying, the Econ navi selling point is drooling among the customers. But most purchasers never bother the problem brought by the sensor.



This post has been edited by iamsobloodysick: Apr 24 2012, 10:21 AM
hkh_88
post Apr 24 2012, 01:52 PM

Casual
***
Junior Member
315 posts

Joined: Nov 2005
From: Puchong



QUOTE(kelvyn @ Apr 24 2012, 08:04 AM)
If you are getting the latest model, should be OK as they have may have rectify the problem with their previous model's air swing mechanism.
*
ya latest model. bought it this month. not yet install sweat.gif
teq
post Apr 24 2012, 03:13 PM

Casual
***
Junior Member
353 posts

Joined: Oct 2004


the latest model refers to S10NKH? old one is S10MKH? or something else? unsure.gif


Added on April 24, 2012, 3:17 pmwhat about standard model? which model number is new one?

This post has been edited by teq: Apr 24 2012, 03:17 PM
loumou
post Apr 24 2012, 04:08 PM

On my way
****
Senior Member
579 posts

Joined: Jan 2007
is daikin good?planning to install 1 for living hall, is that pricey?
faiz573
post Apr 24 2012, 04:51 PM

New Member
*
Junior Member
30 posts

Joined: Sep 2011


daikin ?? mahal ke bro ?
i got one quatation for pana inverter 1.5 KUDA RM1600 .....
PENING BIN VENING ALREADY BRO
TSkelvyn
post Apr 24 2012, 04:58 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
They are mostly around the same price region.. maybe different of RM30-50
Where are you located? Think you could try PM iamsobloodysick
He is selling Pana, Daikin, York, etc


Added on April 24, 2012, 5:04 pm
QUOTE(teq @ Apr 24 2012, 04:13 PM)
the latest model refers to S10NKH? old one is S10MKH? or something else? unsure.gif


Added on April 24, 2012, 3:17 pmwhat about standard model? which model number is new one?
*
If not mistaken, for the standard model, PC9MKH is the older model while C9NKH is the newer one

This post has been edited by kelvyn: Apr 24 2012, 05:04 PM
Mel2
post Apr 24 2012, 06:56 PM

Enthusiast
*****
Junior Member
861 posts

Joined: Mar 2012


i also regret choosing Pana air-cond.. i'm not using those econ navi series though..

but the previous ones..



i've been using them for the past 4 yrs...

all were ok, until they get noisy after regular services...


the noisiest ones are located in my bedroom and dining area.. rclxub.gif

those are the most used ones lah... both also 2.5HP


the others, smaller HP ones, still ok... not noisy YET... laugh.gif



for sure, the next time i want to buy, i'll choose another brand, either Daikin or York...

no more Panasonic ...
TSkelvyn
post Apr 24 2012, 08:40 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
Some people also mentioned that York is noisy.....
Mel2
post Apr 24 2012, 08:48 PM

Enthusiast
*****
Junior Member
861 posts

Joined: Mar 2012


Daikin then.. tongue.gif
skng03
post Apr 24 2012, 08:53 PM

Regular
******
Senior Member
1,450 posts

Joined: Oct 2008


QUOTE(Mel2 @ Apr 24 2012, 06:56 PM)
i also regret choosing Pana air-cond.. i'm not using those econ navi series though..

but the previous ones..
i've been using them for the past 4 yrs...

all were ok, until they get noisy after regular services...
the noisiest ones are located in my bedroom and dining area..  rclxub.gif

those are the most used ones lah... both also 2.5HP
the others, smaller HP ones, still ok... not noisy YET...  laugh.gif
for sure, the next time i want to buy, i'll choose another brand, either Daikin or York...

no more Panasonic ...
*
QUOTE(kelvyn @ Apr 24 2012, 08:40 PM)
Some people also mentioned that York is noisy.....

*
Yup, york indoor confirm noisy than other..esp 2hp n above. Now my only 1.5hp wall unit also aking noise when switch to sleep mode:(
One thing good about york is fast response on complaints , sure turn up at your door step the next day.


Mel2
post Apr 24 2012, 09:45 PM

Enthusiast
*****
Junior Member
861 posts

Joined: Mar 2012


there were two occasions we found ice-forms in our indoor blower unit... doh.gif

either we didnt clean it regular enough or it had been switched on for too long hours..


stevie8
post Apr 24 2012, 09:45 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
Go for Toshiba, Mitsubishi or Sharp. Sanyo and Pana ...errrr... having bad experience with noise with the outdoor units.
winochia
post Apr 24 2012, 10:55 PM

New Member
*
Junior Member
20 posts

Joined: Jan 2008
on the panasonic aircon just finish install 4 unit today by the aircon contractor, but funny story is that one compressor had writing on the top "sensor had issue" but still pack in the box, complain to TBM they willing to exchange another unit but the real story start here rather the unit being send back to the manufacture they simply clear up the writing on the top of the compressor and repack and sold again.

1st how come the compressor had issue pack and send to the customer
2nd are the retailer want to get more profit by selling issue compressor

SUSkimsim
post Apr 25 2012, 05:01 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(kelvyn @ Dec 29 2011, 04:35 PM)
Anyone know how to solve this problem?

I am having problem with one of the 1HP air conditioner unit from Panasonic. Problem started after about one month after installation.
It seems that it is noisy when the air swing is allow to swing.
Their technicians have made 5 attempts to rectify the problem and till now, the problem still persist. rclxub.gif
It seems that they are using trial & error method. Every time, when they come, just apply some grease onto the moving parts and the next time, come and change the air vent. After using for a few days, after the grease dries up, the noise comes back.
Now, the warranty is about to expire... sad.gif

Written to their Customer Care dept, then they called and want to try to apply grease and replace the air vent again. Really don't know when all these trial & error will end and problem solve.

Really regretted installing the Pana aircon. Some more went and installed 4 units. Include the older set (2 years ago), so, in total 5 units.  sad.gif
*
The solution is only change the swing motor,
All the rest to be solve up smile.gif
TSkelvyn
post Apr 25 2012, 05:29 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(kimsim @ Apr 25 2012, 06:01 PM)
The solution is only change the swing motor,
All the rest to be solve up smile.gif
*
Nope. Change the whole blower unit to the never model. Problem solved tongue.gif
adrianjc
post Apr 25 2012, 06:09 PM

Enthusiast
*****
Senior Member
898 posts

Joined: Jul 2011


QUOTE(kelvyn @ Apr 25 2012, 05:29 PM)
Nope. Change the whole blower unit to the never model. Problem solved  tongue.gif
*
Aiks... Just got Panasonic airconds installed for the whole house about a month back. blink.gif
Using a mix of the normal and EcoNavi models.... fingers crossed that everything works well.

Used Daikin aircond before at my parents place and that was one aircond that was forever giving me problems. From water leaks to air being not cold enough... it was a constant every couple of months nightmare. Had it changed to an older model Pana and used it a couple of years before i moved out of my parents place with no issues.

Aircond still going strong and cold even though i've not slept in that room in over a year. Maybe its a mix of the aircond manufacturers, the sellers and a lil bit of luck that determines a persons experience with a specific brand. hmm.gif
SUSkimsim
post Apr 25 2012, 06:30 PM

Let Me ❤️ You
*******
Senior Member
5,847 posts

Joined: Nov 2010
From: Malaysia 🇲🇾


QUOTE(adrianjc @ Apr 25 2012, 06:09 PM)
Aiks... Just got Panasonic airconds installed for the whole house about a month back.  blink.gif
Using a mix of the normal and EcoNavi models.... fingers crossed that everything works well.

Used Daikin aircond before at my parents place and that was one aircond that was forever giving me problems. From water leaks to air being not cold enough... it was a constant every couple of months nightmare. Had it changed to an older model Pana and used it a couple of years before i moved out of my parents place with no issues.

Aircond still going strong and cold even though i've not slept in that room in over a year. Maybe its a mix of the aircond manufacturers, the sellers and a lil bit of luck that determines a persons experience with a specific brand.  hmm.gif
*
Why not try the Mitsubishi starmex inverter.
Quiet and reliable @ 19db in supper quite mode and 1 fan level at only 21db.
Outdoor also quiet and bigger size design like 1.5hp and above.

iamsobloodysick
post Apr 25 2012, 08:25 PM

Look at all my stars!!
*******
Senior Member
2,006 posts

Joined: Mar 2005
From: Truly Malaise
QUOTE(adrianjc @ Apr 25 2012, 06:09 PM)
Aiks... Just got Panasonic airconds installed for the whole house about a month back.  blink.gif
Using a mix of the normal and EcoNavi models.... fingers crossed that everything works well.

Used Daikin aircond before at my parents place and that was one aircond that was forever giving me problems. From water leaks to air being not cold enough... it was a constant every couple of months nightmare. Had it changed to an older model Pana and used it a couple of years before i moved out of my parents place with no issues.

Aircond still going strong and cold even though i've not slept in that room in over a year. Maybe its a mix of the aircond manufacturers, the sellers and a lil bit of luck that determines a persons experience with a specific brand.  hmm.gif
*
the aircond water leakage (too dirty?) and the air is not cold (concealed piping?), it could be related to workmanship or product defect.


TSkelvyn
post Apr 26 2012, 08:55 AM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(adrianjc @ Apr 25 2012, 07:09 PM)
Aiks... Just got Panasonic airconds installed for the whole house about a month back.  blink.gif
Using a mix of the normal and EcoNavi models.... fingers crossed that everything works well.

Used Daikin aircond before at my parents place and that was one aircond that was forever giving me problems. From water leaks to air being not cold enough... it was a constant every couple of months nightmare. Had it changed to an older model Pana and used it a couple of years before i moved out of my parents place with no issues.

Aircond still going strong and cold even though i've not slept in that room in over a year. Maybe its a mix of the aircond manufacturers, the sellers and a lil bit of luck that determines a persons experience with a specific brand.  hmm.gif
*
I reckon that sometimes, buying products will depends on your luck. If you are unlucky, you happen to get those batch or model that were not properly designed, etc. Then you are in trouble. I would say that the previous Panasonic model sucks. Problem with their swing mechanism. This is confirmed by their own technical people. That's why they came out with the latest model so fast.

Their latest model is better. Not forgetting those earlier one are also OK. This is from my own personal experience. My mum's and some of my friends' and also the one that I installed more than 2 years ago. All Pana brand. They are OK. No complain at all.

Since you have installed them, just monitor. If there are any problem, quickly lodge your complain during the warranty period. What I did was to extend the warranty of the aircon since I do not have confidence in that particular model..just for the peace of mind... smile.gif
ozak
post Apr 26 2012, 09:38 AM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(adrianjc @ Apr 25 2012, 06:09 PM)
Aiks... Just got Panasonic airconds installed for the whole house about a month back.  blink.gif
Using a mix of the normal and EcoNavi models.... fingers crossed that everything works well.

Used Daikin aircond before at my parents place and that was one aircond that was forever giving me problems. From water leaks to air being not cold enough... it was a constant every couple of months nightmare. Had it changed to an older model Pana and used it a couple of years before i moved out of my parents place with no issues.

Aircond still going strong and cold even though i've not slept in that room in over a year. Maybe its a mix of the aircond manufacturers, the sellers and a lil bit of luck that determines a persons experience with a specific brand.  hmm.gif
*
Don't worry lah. I have been using panasonic aircon for over 14yrs. Change to 2nd set due to old age. Panasonic also.

Just becarefull with the installation and the servicing. This are the main cause that your aircon getting worst.
majorarmstrong
post May 20 2012, 09:40 PM

Look at all my stars!!
*******
Senior Member
2,239 posts

Joined: Aug 2009


anyone can intro a good and reliable aircond service guy. Need to service my panasonic already 1 years old. not cold now.
TSkelvyn
post May 20 2012, 09:58 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(majorarmstrong @ May 20 2012, 10:40 PM)
anyone can intro a good and reliable aircond service guy. Need to service my panasonic already 1 years old. not cold now.
*
If your new aircon is not cold after only one year, then these must be some thing wrong with it... Maybe you should claim for warranty. Or maybe there is gas leakage somewhere...
YJYYEE
post Jun 10 2012, 02:07 AM

Getting Started
**
Junior Member
145 posts

Joined: Feb 2011
From: Selangor


QUOTE(majorarmstrong @ May 20 2012, 09:40 PM)
anyone can intro a good and reliable aircond service guy. Need to service my panasonic already 1 years old. not cold now.
*
What model is ur air conditioner?...heavy usage?

QUOTE(kelvyn @ May 20 2012, 09:58 PM)
If your new aircon is not cold after only one year, then these must be some thing wrong with it... Maybe you should claim for warranty. Or maybe there is gas leakage somewhere...
*
Usually an air conditioner need to be serviced after how many years?...

This post has been edited by YJYYEE: Jun 10 2012, 12:20 PM
TSkelvyn
post Jun 11 2012, 08:47 AM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(YJYYEE @ Jun 10 2012, 03:07 AM)
Usually an air conditioner need to be serviced after how many years?...
*
For me, normally, I just clean the vent inside the blower unit. Just open the cover and clean the filter. The frequency will be dependent on the environment. If dirty and use frequently, then need to clean more frequent.

nicky1112001
post Jul 22 2012, 05:58 AM

Getting Started
**
Junior Member
219 posts

Joined: Feb 2007


If suddenly got ice flying out.. small Pierce ice flying when I sleep in midnight just now..Panasonic 1.0 inverter. Seem alot problem...I buying time after 1 month then problem come...aircond with fresh hot air coming out.. then they come fix and after few month now got ice come out..


Added on July 22, 2012, 5:58 amIf suddenly got ice flying out.. small Pierce ice flying when I sleep in midnight just now..Panasonic 1.0 inverter. Seem alot problem...I buying time after 1 month then problem come...aircond with fresh hot air coming out.. then they come fix and after few month now got ice come out..


This post has been edited by nicky1112001: Jul 22 2012, 05:58 AM
skng03
post Jul 22 2012, 07:26 AM

Regular
******
Senior Member
1,450 posts

Joined: Oct 2008


QUOTE(nicky1112001 @ Jul 22 2012, 05:58 AM)
If suddenly got ice flying out.. small Pierce ice flying when I sleep in midnight just now..Panasonic 1.0 inverter. Seem alot problem...I buying time after 1 month then problem come...aircond with fresh hot air coming out.. then they come fix and after few month now got ice come out..


Added on July 22, 2012, 5:58 amIf suddenly got ice flying out.. small Pierce ice flying when I sleep in midnight just now..Panasonic 1.0 inverter. Seem alot problem...I buying time after 1 month then problem come...aircond with fresh hot air coming out.. then they come fix and after few month now got ice come out..
*
Your ac need service already, have u ever clean the filter? Can make ice mean your ac still good just the dirt block the air circulation
nicky1112001
post Jul 22 2012, 07:46 AM

Getting Started
**
Junior Member
219 posts

Joined: Feb 2007


QUOTE(skng03 @ Jul 22 2012, 07:26 AM)
Your ac need service already, have u ever clean the filter? Can make ice mean your ac still good just the dirt block the air circulation
*
I just clean last week...and this model r410a inverter really give me alot problem....I I buy just 3 week then already spoil..now this Laguna geng. Got iced fly out..
lingleeyen
post Jul 22 2012, 09:44 AM

Regular
******
Senior Member
1,376 posts

Joined: Jan 2011
QUOTE(nicky1112001 @ Jul 22 2012, 07:46 AM)
I just clean last week...and this model r410a inverter really give me alot problem....I I buy just 3 week then already spoil..now this Laguna geng. Got iced fly out..
*
Check if you have enough refrigerant/ leakage. Check also if you have dirty indoor unit coil.
skng03
post Jul 22 2012, 10:31 AM

Regular
******
Senior Member
1,450 posts

Joined: Oct 2008


QUOTE(lingleeyen @ Jul 22 2012, 09:44 AM)
Check if you have enough refrigerant/ leakage. Check also if you have dirty indoor unit coil.
*
And check the blower fan …
Dennos
post Jul 22 2012, 09:37 PM

Look at all my stars!!
*******
Senior Member
2,736 posts

Joined: Dec 2006



QUOTE(nicky1112001 @ Jul 22 2012, 07:46 AM)
I just clean last week...and this model r410a inverter really give me alot problem....I I buy just 3 week then already spoil..now this Laguna geng. Got iced fly out..
*
+1, my coil changed for this. Sleep and kiss by sliced ice at nite. WTF !!!
TSkelvyn
post Jul 23 2012, 09:01 AM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(nicky1112001 @ Jul 22 2012, 08:46 AM)
I just clean last week...and this model r410a inverter really give me alot problem....I I buy just 3 week then already spoil..now this Laguna geng. Got iced fly out..
*
Since it is only 3 weeks old, bettter lodge your complain with Panasonic. get the complain ref no.
Ask them when they want to send their people over to rectify the problem. Follow up with an official complain letter. Keep records of all your complains to Panasonic. If you complain "hard enough" am sure they will act on your complain for sure.
nicky1112001
post Jul 23 2012, 03:50 PM

Getting Started
**
Junior Member
219 posts

Joined: Feb 2007


QUOTE(skng03 @ Jul 22 2012, 10:31 AM)
And check the blower fan …
*
may i know where the blower fan?can we open it and clean ourself?


Added on July 23, 2012, 3:53 pm
QUOTE(Dennos @ Jul 22 2012, 09:37 PM)
+1, my coil changed for this. Sleep and kiss by sliced ice at nite. WTF !!!
*
sick air cond....in midnight time suddenly got sound clong clong clong then fly out pieces peices of ice to my bed....really a sucks air cond...pay rm1450 get a ice making air cond to put my room...if like that..i better buy a peti sejuk to put my room...this my last time on this lousy panasonic air cond...next time if got free i also buang longkang on that..

This post has been edited by nicky1112001: Jul 23 2012, 03:53 PM
lingleeyen
post Jul 23 2012, 04:12 PM

Regular
******
Senior Member
1,376 posts

Joined: Jan 2011
QUOTE(nicky1112001 @ Jul 23 2012, 03:50 PM)
may i know where the blower fan?can we open it and clean ourself?


Added on July 23, 2012, 3:53 pm

sick air cond....in midnight time suddenly got sound clong clong clong then fly out pieces peices of ice to my bed....really a sucks air cond...pay rm1450 get a ice making air cond to put my room...if like that..i better buy a peti sejuk to put my room...this my last time on this lousy panasonic air cond...next time if got free i also buang longkang on that..
*
The entire system screwed up might be due to 2 factor. The unit itself or the installation.

Ice making AC might be caused by several factor.

1) Coil dirty
2) Refrigerant level low

Since you have just cleaned it, cause 1 is omitted. Cause 2 is more like it. Low refrigerant can be due to poor unit or poor installation. If the unit is damaged before or after installation, the leakage will be detected if the installer is running on a proper installation steps. If he is following the correct steps, things will not happen like what happened to you now. They will notify you on the fault and rectify it with or without charges.

What you should do now is to check for leakage. Get them to hold the pressure of the system, then the piping, then the indoor, then the outdoor.
nicky1112001
post Jul 25 2012, 05:52 PM

Getting Started
**
Junior Member
219 posts

Joined: Feb 2007


QUOTE(lingleeyen @ Jul 23 2012, 04:12 PM)
The entire system screwed up might be due to 2 factor. The unit itself or the installation.

Ice making AC might be caused by several factor.

1) Coil dirty
2) Refrigerant level low

Since you have just cleaned it, cause 1 is omitted. Cause 2 is more like it. Low refrigerant can be due to poor unit or poor installation. If the unit is damaged before or after installation, the leakage will be detected if the installer is running on a proper installation steps. If he is following the correct steps, things will not happen like what happened to you now. They will notify you on the fault and rectify it with or without charges.

What you should do now is to check for leakage. Get them to hold the pressure of the system, then the piping, then the indoor, then the outdoor.
*
finaly they coming to check....guess wat i get?all the gas inside gone....no gas...funny things...special thanks that installer...somemore still dare ask me pay rm50 service and rm80 to pam gas inside agains...
halcyon27
post Jul 25 2012, 05:59 PM

Look at all my stars!!
*******
Senior Member
2,140 posts

Joined: Nov 2010


QUOTE(nicky1112001 @ Jul 25 2012, 05:52 PM)
finaly they coming to check....guess wat i get?all the gas inside gone....no gas...funny things...special thanks that installer...somemore still dare ask me pay rm50 service and rm80 to pam gas inside agains...
*
sounds like a leak. even if pump gas it will still leak. best to reinstall piping or find and fix leak. A properly installed air cond shouldn't leak.

Places where leaks occur at:
fan coil - joint btw piping and blower
condenser - joint btw piping and compressor
piping - anywhere along piping

Barring aircond defect, problem lies with installation. If this air cond is inverter using R410a, it needs thicker piping (0.8mm). The old 0.6mm cannot handle the higher operating pressure of the R410a which is 1.6x higher than R22 meaning the thinner pipe will burst.

This post has been edited by halcyon27: Jul 25 2012, 06:01 PM
nicky1112001
post Jul 25 2012, 06:03 PM

Getting Started
**
Junior Member
219 posts

Joined: Feb 2007


i dunno wat they doing..jsut see they clean my air cond blower inside and then say gas leak...then check where leak and fix then pam back that gas..

patmos
post Jul 25 2012, 06:14 PM

Getting Started
**
Junior Member
118 posts

Joined: Jan 2009


Looks like it's more to installation problem instead of the air-cond itself.
halcyon27
post Jul 25 2012, 08:21 PM

Look at all my stars!!
*******
Senior Member
2,140 posts

Joined: Nov 2010


QUOTE(nicky1112001 @ Jul 22 2012, 05:58 AM)
If suddenly got ice flying out.. small Pierce ice flying when I sleep in midnight just now..Panasonic 1.0 inverter. Seem alot problem...I buying time after 1 month then problem come...aircond with fresh hot air coming out.. then they come fix and after few month now got ice come out..


Added on July 22, 2012, 5:58 amIf suddenly got ice flying out.. small Pierce ice flying when I sleep in midnight just now..Panasonic 1.0 inverter. Seem alot problem...I buying time after 1 month then problem come...aircond with fresh hot air coming out.. then they come fix and after few month now got ice come out..
*
I just re-read your post to confirm that since its R410a, it's good to get a second professional installer standby after two weeks.

R410a gas cost a bit cos it's a mixture of 50% gas a, 25% gas b and 25% gas c. It cannot be top up just like R22 which is only a single type. Since the gas is costly, my guess is that your first installer fudged on installation causing a leak.

Re-read my explanation up in post #57 for possible causes. My guess is there's a leak somewhere.

A worst case scenario is if the installers didn't realize that they are using 0.6mm pipes.

This post has been edited by halcyon27: Jul 25 2012, 08:31 PM
cherroy
post Jul 25 2012, 10:16 PM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


Aircond forming ice most of the time means gas is low.

Nothing to do with the air-cond itself generally.
Aircond is not manufactured to produce ice, rest assure. biggrin.gif


Added on July 25, 2012, 10:27 pm
QUOTE(halcyon27 @ Jul 25 2012, 08:21 PM)
A worst case scenario is if the installers didn't realize that they are using 0.6mm pipes.
*
I won't be surprise if it did happen.

Many condo and apartment nowadays has pre-fixed conceal piping for air-cond.
So ensure the spec of piping is suit to the air-cond needs before buying.

Last time, my house renovation contractor screw up the Astro conceal wiring, they loop the Astro cable like ordinary electricity looping, causing signal loss across all the point. doh.gif

This post has been edited by cherroy: Jul 25 2012, 10:28 PM
cherroy
post Jul 25 2012, 10:34 PM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


Workmanship is one area one always to look at and forget whenever there is issue on air-cond.

I have 4 Pana air-cond that being used for 4 years daily until now, none has issue (touch wood), until now.

But one poor workmanship in installation that not tilting enough, cause some minor water clog issue from time to time especially when dirty time.


halcyon27
post Jul 25 2012, 10:52 PM

Look at all my stars!!
*******
Senior Member
2,140 posts

Joined: Nov 2010


QUOTE(cherroy @ Jul 25 2012, 10:16 PM)

Added on July 25, 2012, 10:27 pm
Many condo and apartment nowadays has pre-fixed conceal piping for air-cond.
So ensure the spec of piping is suit to the air-cond needs before buying.
*
That's a clue and a very important question also which needs asking. New install over existing piping or with new piping? hmm.gif
lingleeyen
post Jul 26 2012, 09:14 AM

Regular
******
Senior Member
1,376 posts

Joined: Jan 2011
QUOTE(halcyon27 @ Jul 25 2012, 08:21 PM)
I just re-read your post to confirm that since its R410a, it's good to get a second professional installer standby after two weeks.

R410a gas cost a bit cos it's a mixture of 50% gas a, 25% gas b and 25% gas c. It cannot be top up just like R22 which is only a single type. Since the gas is costly, my guess is that your first installer fudged on installation causing a leak.
Re-read my explanation up in post #57 for possible causes. My guess is there's a leak somewhere.

A worst case scenario is if the installers didn't realize that they are using 0.6mm pipes.
*
On the bolded part, it is not entirely true but it is not wrong. R410a is a mixture with very very very very very very minimal temperature glitch as the boiling point of the mixture refrigerant is similar. As the boiling point is similar, the evaporation rate of each refrigerant is similar, hence there will be no one refrigerant is less in ratio than other. If there is leakage, top up on R410a is acceptable even if it is in 'commercial unit installation standard'.

However, it is often very hard to determine how much refrigerant is left in the unit. What installer will do in Malaysia is that they will measure the pressure of the system, using experience, they assume the remaining refrigerant quantity and add according to what they think is the balance. What Aussie will do is that they reclaim the refrigerant into a tank, weigh it, and top up according to spec, with the tank on a weighing machine. Before the recharge, they even do vacuum the system before re-charging. So if we are kiasi, we release the refrigerant (which is illegal), and recharge the full weight. Installer in Malaysia do not use the reclaim machine.

As for the piping thickness, some manufacturers specified 0.8mm because they kiasi and wanted to cover their own ass. I have experience in using 3/8 tubes with 0.38mmt and 1/2 tubes with 0.56mmt, with working pressure of 400psi, testing pressure 600psi. Operating pressure of these room air conditioners are lesser than 400psi. The worried point of why manufacturers wanted to use 0.8mmt tube is that they are concern about the flaring point crack, not the pipe burst. Poor flaring will result in a crack at the joining point hence leakage.
halcyon27
post Jul 26 2012, 11:47 AM

Look at all my stars!!
*******
Senior Member
2,140 posts

Joined: Nov 2010


QUOTE(lingleeyen @ Jul 26 2012, 09:14 AM)
On the bolded part, it is not entirely true but it is not wrong. R410a is a mixture with very very very very very very minimal temperature glitch as the boiling point of the mixture refrigerant is similar. As the boiling point is similar, the evaporation rate of each refrigerant is similar, hence there will be no one refrigerant is less in ratio than other. If there is leakage, top up on R410a is acceptable even if it is in 'commercial unit installation standard'.

However, it is often very hard to determine how much refrigerant is left in the unit. What installer will do in Malaysia is that they will measure the pressure of the system, using experience, they assume the remaining refrigerant quantity and add according to what they think is the balance. What Aussie will do is that they reclaim the refrigerant into a tank, weigh it, and top up according to spec, with the tank on a weighing machine. Before the recharge, they even do vacuum the system before re-charging. So if we are kiasi, we release the refrigerant (which is illegal), and recharge the full weight. Installer in Malaysia do not use the reclaim machine.

As for the piping thickness, some manufacturers specified 0.8mm because they kiasi and wanted to cover their own ass. I have experience in using 3/8 tubes with 0.38mmt and 1/2 tubes with 0.56mmt, with working pressure of 400psi, testing pressure 600psi. Operating pressure of these room air conditioners are lesser than 400psi. The worried point of why manufacturers wanted to use 0.8mmt tube is that they are concern about the flaring point crack, not the pipe burst. Poor flaring will result in a crack at the joining point hence leakage.
*
thks for enlightening! no wonder r410a so expensive.... it's also the labor involved. Is flaring point crack a common issue with many installations in the field?

This post has been edited by halcyon27: Jul 26 2012, 11:48 AM
lingleeyen
post Jul 26 2012, 12:25 PM

Regular
******
Senior Member
1,376 posts

Joined: Jan 2011
QUOTE(halcyon27 @ Jul 26 2012, 11:47 AM)
thks for enlightening! no wonder r410a so expensive.... it's also the labor involved. Is flaring point crack a common issue with many installations in the field?
*
I am not sure why R410a is more expensive but I believe it is because of the supply/ demand effect, Installers are actually doing the same thing be it with R22 or R410a. What they need is only need a different pressure gauge, different copper pipes, and a different refrigerant tank. They position, flare, bur, hook up, vacuum, open valve, on AC, touch, feel, pack things, done. They do nothing different from R22 units, so labour should not vary. But you know la, they bought special tool, they need to have ROI also ma.

Side note. If your AC's piping is not exceeding the standard pipe length, then additional refrigerant is not required. Check the spec of standard piping length and don't get conned.

Flaring crack at the tip can be very common. When they have poor installation skill or a poor tool, your flared end is not symetric. Looks odd and you will have visible or non visible crack. So after they joint it, you will have problem because that is the most vulnarable part to high pressure low ductality.
lolly8968
post Jul 26 2012, 06:25 PM

New Member
*
Junior Member
12 posts

Joined: Jul 2012
QUOTE(kelvyn @ Dec 29 2011, 04:35 PM)
Anyone know how to solve this problem?

I am having problem with one of the 1HP air conditioner unit from Panasonic. Problem started after about one month after installation.
It seems that it is noisy when the air swing is allow to swing.
Their technicians have made 5 attempts to rectify the problem and till now, the problem still persist. rclxub.gif
It seems that they are using trial & error method. Every time, when they come, just apply some grease onto the moving parts and the next time, come and change the air vent. After using for a few days, after the grease dries up, the noise comes back.
Now, the warranty is about to expire... sad.gif

Written to their Customer Care dept, then they called and want to try to apply grease and replace the air vent again. Really don't know when all these trial & error will end and problem solve.

Really regretted installing the Pana aircon. Some more went and installed 4 units. Include the older set (2 years ago), so, in total 5 units.  sad.gif
*
Same problem, newer Pana model. I'm not sure what the "sound" you have is, but for me (I don't reco this as a long-term shocking.gif solution ), a hard knock with my hand on the side (NOT the front) solved it, i.e. there was a loose or vibrating part somewhere. Grease won't help, get someone to check it part by part.

PS, a lot of people have the view that Panasonic products now are much lower in quality than they were many years ago. My old National fan, 20 years and still perfect working condition.
skng03
post Jul 26 2012, 09:14 PM

Regular
******
Senior Member
1,450 posts

Joined: Oct 2008


QUOTE(lolly8968 @ Jul 26 2012, 06:25 PM)
Same problem, newer Pana model. I'm not sure what the "sound" you have is, but for me (I don't reco this as a long-term  shocking.gif solution ), a hard knock with my hand on the side (NOT the front) solved it, i.e. there was a loose or vibrating part somewhere. Grease won't help, get someone to check it part by part.

PS, a lot of people have the view that Panasonic products now are much lower in quality than they were many years ago. My old National fan, 20 years and still perfect working condition.
*
Most…if no all brand now manufacture/OEM @ world factory-china, National/=Panasonic so don't compare smile.gif
halcyon27
post Jul 26 2012, 11:39 PM

Look at all my stars!!
*******
Senior Member
2,140 posts

Joined: Nov 2010


QUOTE(skng03 @ Jul 26 2012, 09:14 PM)
Most…if no all brand now manufacture/OEM @ world factory-china, National/=Panasonic so don't compare smile.gif
*
In the 50s-70s, the west used to scorn Jap product = low quality. Now they know better. Even recent BBC article in the UK, top 3 most reliable car makes are from Honda, Toyota and Lexus. The conti rank among the lowest with Range Rover among them.

Who knows that China (and Korea) might become the next Japan in terms of quality. Lots of Japanese now working in China. The migration of highly skilled labour in an increasingly stagnant economy now going to where the boom is. Not just there but in Thailand, German tech and know-how are diffusing there. Cotto (tiles, WC, bidet, bath,etc) and Pimatec are some examples. Pimatec makes Pimaflex which I hope comes here. It would make aircon brazening a thing of the past. On the contrary, it might increase incidence of aircond theft.

This post has been edited by halcyon27: Jul 26 2012, 11:44 PM
weikee
post Jul 27 2012, 08:57 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(halcyon27 @ Jul 26 2012, 11:39 PM)
In the 50s-70s, the west used to scorn Jap product = low quality. Now they know better. Even recent BBC article in the UK, top 3 most reliable car makes are from Honda, Toyota and Lexus. The conti rank among the lowest with Range Rover among them.

Who knows that China (and Korea) might become the next Japan in terms of quality. Lots of Japanese now working in China. The migration of highly skilled labour in an increasingly stagnant economy now going to where the boom is. Not just there but in Thailand, German tech and know-how are diffusing there. Cotto (tiles, WC, bidet, bath,etc) and Pimatec are some examples. Pimatec makes Pimaflex which I hope comes here. It would make aircon brazening a thing of the past. On the contrary, it might increase incidence of aircond theft.
*
There are still some skill set China even Taiwan find it hard to take on. Like car gearbox, how many do you see it manufacture from China? Mainly still come from Japan and Europe.

China is goods on manufacture because of cheap labor,soon they will lost the competitive. Take Malaysia for example we used to be good in manufacture same as Singapore and Taiwan. But we never evolved, now we can't compete with China for manufacture, and neither we can compete with Singapore and Taiwan for high tech manufacturing.

This post has been edited by weikee: Jul 27 2012, 08:59 AM
halcyon27
post Jul 27 2012, 10:01 AM

Look at all my stars!!
*******
Senior Member
2,140 posts

Joined: Nov 2010


QUOTE(weikee @ Jul 27 2012, 08:57 AM)
There are still some skill set China even Taiwan find it hard to take on. Like car gearbox, how many do you see it manufacture from China? Mainly still come from Japan and Europe.

China is goods on manufacture because of cheap labor,soon they will lost the competitive. Take Malaysia for example  we used to be good in manufacture  same as Singapore and Taiwan. But we never evolved, now we can't compete with China for manufacture, and neither we can compete with Singapore and Taiwan for high tech manufacturing.
*
Or Indonesia?
weikee
post Jul 27 2012, 10:14 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
I read an article about China. They are good in copying, but they only know how to copy the product and not the process. They copy the fast things the tangible things. They losing the own culture and value. They are just a production house now, and the real skill like handcraft are dying. They don't have many creative peoples. Not many artist, designer and skill people now.
This are the things and skill they need to copy to move to next stage. We Malaysia should too


craftsnknots
post Jul 27 2012, 10:24 AM

On my way
****
Senior Member
577 posts

Joined: Feb 2012
I thought that is Taiwan..Every year when my boss and my team go for New technology exhibition in Germany, they have a big sign at the entrance "We apologize but no Taiwanese allowed"

Because they always copy other's machines and sell it at a much much lower cost and cheaper change parts, but the quality/accuracy is not there
weikee
post Jul 27 2012, 10:36 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(craftsnknots @ Jul 27 2012, 10:24 AM)
I thought that is Taiwan..Every year when my boss and my team go for New technology exhibition in Germany, they have a big sign at the entrance "We apologize but no Taiwanese allowed"

Because they always copy other's machines and sell it at a much much lower cost and cheaper change parts, but the quality/accuracy is not there
*
If you notice, Taiwan and Malaysia have not been moving for some years.

My friend have a very good comment when he travel to Taiwan for holiday. Taiwan for holiday is good for Malaysia because they have not move much in the economy just like Malaysia so the afford level is like in Malaysia. Which I agree.
ozak
post Jul 27 2012, 10:46 AM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(craftsnknots @ Jul 27 2012, 10:24 AM)
I thought that is Taiwan..Every year when my boss and my team go for New technology exhibition in Germany, they have a big sign at the entrance "We apologize but no Taiwanese allowed"

Because they always copy other's machines and sell it at a much much lower cost and cheaper change parts, but the quality/accuracy is not there
*
Will the germany write for China too.
weikee
post Jul 27 2012, 10:48 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
China buy than reversed engineer it ;-)

Have you see the crv of China. Dam real from far.

ozak
post Jul 27 2012, 10:58 AM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(weikee @ Jul 27 2012, 10:48 AM)
China buy than reversed engineer it  ;-)

Have you see the crv of China. Dam real from far.
*
China commit so many copy crime. But nobody dare to sue it.
phoenix69
post Jul 28 2012, 11:58 AM

Regular
******
Senior Member
1,836 posts

Joined: Sep 2007


QUOTE(ozak @ Jul 27 2012, 10:58 AM)
China commit so many copy crime. But nobody dare to sue it.
*
With quantity comes quality.
China DVD used to last 1 month, Nowadays I switch on my China brand DVD machine on all the time hoping for it to rosak so i have excuse to change a new one ... still waiting after 4 years. doh.gif

With quantity comes innovation.
China converting machines used to be cheap and quite basic, Nowadays their prices are going up up up, and the new machines output, percision, range are increasing day by day, even the west is using China machines more and more.

With quantity comes power.
Companies initially complained about China copying and kept their technology under wraps whithin their oun countries, Nowadays they are opening plants and even sub contracting manufacturing to China. e.g. Iphone to Foxconn in China.

With quantity comes acceptance.
Countries used to target China as their main competitor, Nowadays they all want to sell to china.

The sleeping dragon has awakened. rclxm9.gif
ozak
post Jul 28 2012, 12:54 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(phoenix69 @ Jul 28 2012, 11:58 AM)
With quantity comes quality.
China DVD used to last 1 month, Nowadays I switch on my China brand DVD machine on all the time hoping for it to rosak so i have excuse to change a new one ... still waiting after 4 years.  doh.gif

With quantity comes innovation.
China converting machines used to be cheap and quite basic, Nowadays their prices are going up up up, and the new machines output, percision, range are increasing day by day, even the west is using China machines more and more.

With quantity comes power.
Companies initially complained about China copying and kept their technology under wraps whithin their oun countries, Nowadays they are opening plants and even sub contracting manufacturing to China. e.g. Iphone to Foxconn in China.

With quantity comes acceptance.
Countries used to target China as their main competitor, Nowadays they all want to sell to china.

The sleeping dragon has awakened.  rclxm9.gif
*
I m waiting some country to punish them. It seems like only US capable do that. Since they copy a lot of US product.


weikee
post Jul 28 2012, 02:03 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(ozak @ Jul 28 2012, 12:54 PM)
I m waiting some country to punish them. It seems like only US capable do that. Since they copy a lot of US product.
*
Us are afraid of them, because China is the largest US bonds hold. If they dump all the bonds US still go shock at least for few years. The money will be less than our boleh dollars.


Added on July 28, 2012, 2:07 pm
QUOTE(phoenix69 @ Jul 28 2012, 11:58 AM)
With quantity comes quality.
China DVD used to last 1 month, Nowadays I switch on my China brand DVD machine on all the time hoping for it to rosak so i have excuse to change a new one ... still waiting after 4 years.  doh.gif

With quantity comes innovation.
China converting machines used to be cheap and quite basic, Nowadays their prices are going up up up, and the new machines output, percision, range are increasing day by day, even the west is using China machines more and more.

With quantity comes power.
Companies initially complained about China copying and kept their technology under wraps whithin their oun countries, Nowadays they are opening plants and even sub contracting manufacturing to China. e.g. Iphone to Foxconn in China.

With quantity comes acceptance.
Countries used to target China as their main competitor, Nowadays they all want to sell to china.

The sleeping dragon has awakened.  rclxm9.gif
*
Quantity yes, quality maybe, innovative I will say close to non. If they are good, they will have more innovative product and application.

You should see their gen X people, many are spoiled.


This post has been edited by weikee: Jul 28 2012, 02:07 PM
ozak
post Jul 28 2012, 03:02 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(weikee @ Jul 28 2012, 02:03 PM)
Us are afraid of them, because China is the largest US bonds hold. If they dump all the bonds US still go shock at least for few years. The money will be less than our boleh dollars.


Added on July 28, 2012, 2:07 pm

Quantity yes, quality maybe, innovative I will say close to non. If they are good, they will have more innovative product and application. 

You should see their gen X people, many are spoiled.
*
Don't think the china that stupid. China will lost more than the US. Their money not their enemy.
weikee
post Jul 28 2012, 04:20 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(ozak @ Jul 28 2012, 03:02 PM)
Don't think the china that stupid. China will lost more than the US. Their money not their enemy.
*
Don't forget China is self sustain and also a communist country. They can do many things we think is not good.
Ah well way off topic.
wyxyz
post Aug 13 2012, 12:09 AM

Enthusiast
*****
Senior Member
730 posts

Joined: Mar 2005


Bought the panasonic inverter 1.0 model last November 2011. However, the funny thing happened was, halfway through (2-3hours after switched on), the 'cooling' was cut off, just normal wind blow. I've set the remote control manually instead of Auto. Any of you guys encountered such problem before? Or should I call panasonic again. The last week, the technician said it was because the gas was not enough. Troublesome betul.
cherroy
post Aug 13 2012, 10:51 AM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(wyxyz @ Aug 13 2012, 12:09 AM)
Bought the panasonic inverter 1.0 model last November 2011. However, the funny thing happened was, halfway through (2-3hours after switched on), the 'cooling' was cut off, just normal wind blow. I've set the remote control manually instead of Auto. Any of you guys encountered such problem before? Or should I call panasonic again. The last week, the technician said it was because the gas was not enough. Troublesome betul.
*
Gas not enough is not because of the air-cond itself is good or not good. (unless it is air-cond internal piping issue, which generally less likely occur)
Gas not enough can be caused by leaking in between the piping, which is more related to workmanship issue.

So it is not fair to blame the air-cond disregard whatever brand.


Added on August 13, 2012, 10:57 amThe reason I said so, because majority air-cond problem I encountered were more about or caused by workmanship/installation issue.

This post has been edited by cherroy: Aug 13 2012, 10:57 AM
wyxyz
post Aug 16 2012, 09:18 AM

Enthusiast
*****
Senior Member
730 posts

Joined: Mar 2005


QUOTE(cherroy @ Aug 13 2012, 10:51 AM)
Gas not enough is not because of the air-cond itself is good or not good. (unless it is air-cond internal piping issue, which generally less likely occur)
Gas not enough can be caused by leaking in between the piping, which is more related to workmanship issue.

So it is not fair to blame the air-cond disregard whatever brand.


Added on August 13, 2012, 10:57 amThe reason I said so, because majority air-cond problem I encountered were more about or caused by workmanship/installation issue.
*
i think i have to enlighten you on this. After panasonic sent their men over. Pumped in extra gas. Everything is good to go. Like what i told you earlier, 2-3 hours after the aircond was turned on, the cooling was completely cut off.

What i did later was to RESET the aircond via remote (pressing the AC next to the 'clock'). And the cooling gets kick back.

So, whether or not it is an installation issue. I'm not too sure.

t_rex3475
post Aug 18 2012, 01:50 PM

New Member
*
Newbie
1 posts

Joined: Aug 2012
same problem happened to me. Did you solve the problem?
they tell me it was because the contamination of the air quality was no longer. but I do not believe it. icon_question.gif


Added on August 18, 2012, 1:54 pm
QUOTE(ravemaster @ Apr 19 2012, 12:43 PM)
i got a question here...it is about my panasonic 1hp inverter air cond installed last month. the problem is the nanoeg function like now not working fine (light turned off).
from complete shutdown, if i on the unit, the blue light of the nanoeg feature will turn on, but a couple of minutes, i will auto turn it off. pressing the button from the controller does not help. the thing is working for the 1st 1 month. any body got any idea? thanks
*
same problem happened to me. Did you solve the problem?
they tell me it was because the contamination of the air quality was no longer. but I do not believe it. icon_question.gif

This post has been edited by t_rex3475: Aug 18 2012, 01:54 PM
dang!
post Aug 18 2012, 11:16 PM

New Member
*
Junior Member
20 posts

Joined: Sep 2011
Just an additional info.

I've had a Toshiba a/c for about 4 years now. And throughout these 4 years, I had to have a technician "pump in gas" for at least twice a year. Same problem, the a/c stopped blowing out cold air. Meanwhile, my National a/c in the other room has worked perfectly for 5 years and there isn't one day where this "no gas" problem has ever occurred.

But then, reading from the above posts, it seems like the "no gas" problem is caused by human error so..it all depends on your luck I guess.
weikee
post Aug 18 2012, 11:37 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Sometime is installation issue, sometime is copper hose issue, sometime is machine. Take time to identify.
wyxyz
post Aug 19 2012, 12:18 AM

Enthusiast
*****
Senior Member
730 posts

Joined: Mar 2005


QUOTE(wyxyz @ Aug 16 2012, 09:18 AM)
i think i have to enlighten you on this. After panasonic sent their men over. Pumped in extra gas. Everything is good to go. Like what i told you earlier, 2-3 hours after the aircond was turned on, the cooling was completely cut off.

What i did later was to RESET the aircond via remote (pressing the AC next to the 'clock'). And the cooling gets kick back.

So, whether or not it is an installation issue. I'm not too sure.
*
After several attempts, the technician managed to find out that it was the 'control board' (indoor unit) that created so much trouble. Half functioning half spoilt, that's why even troubleshooting also cannot detect.



cclim2011
post Oct 3 2012, 08:02 AM

Regular
******
Senior Member
1,701 posts

Joined: Feb 2011
QUOTE(wyxyz @ Aug 19 2012, 12:18 AM)
After several attempts, the technician managed to find out that it was the 'control board' (indoor unit) that created so much trouble. Half functioning half spoilt, that's why even troubleshooting also cannot detect.
*
I have this Sharp Plasmacluster Aircond, 2 units. Both of them giving crackling sound that I suspect it's from the plastic parts, expand and contract and it can be very very luod sometimes, till make me wake up frmo sleep! The technicians come and tried to fix, taking off the parts and putting them back and they still make the same noise. THey ordered replacement parts but have never come after 2, 3 months!

So frustrated. Anyone experiences this issue? The noise comes even a few minuets after the air cond is switched off!
sin99
post Nov 13 2012, 06:56 PM

New Member
*
Newbie
3 posts

Joined: May 2007
Does anyone know the reason why Panasonic aircond - EcoNavi timer blinks and unit just stop function...I am trying to on and off the aircond but after a while the timer blinks again and the aircond just stop functioning....Does anyone have the same problem and how to fix it?
tiger3555
post Nov 13 2012, 07:46 PM

Getting Started
**
Junior Member
169 posts

Joined: Feb 2011
QUOTE(sin99 @ Nov 13 2012, 06:56 PM)
Does anyone know the reason why Panasonic aircond - EcoNavi timer blinks and unit just stop function...I am trying to on and off the aircond but after a while the timer blinks again and the aircond just stop functioning....Does anyone have the same problem and how to fix it?
*
i got poblem same like u.I also using econavi type.After switch on air con then half n hours it suddenly "off" itself. I repeat "on" aircon again n again but still same turn off after half hours. timer will blink after 1st "off" n i never set timer but it also blink.

call panasonic service agent come to investigate. They say is the air con gas leaking (between pipe and nat no proper join togerther). They also say econavi type air con off itself is to protect the compressor when no enough gas inside the pipe. Old type air con dont have this type off function and the compressor will continue to operate and last will spoilt the compressor. They ask me to contact back person install air con unit (contractor).
sin99
post Nov 13 2012, 08:23 PM

New Member
*
Newbie
3 posts

Joined: May 2007
Tiger355, can't be leaking because my aircond with luck it function with cool air but most of the time...has the auto off and timer blinks faulty....I called the shop that i bought the aircond n they help me to log a report to panasonic. dunno whether they will come and check or not.

sad.gif huh have to call back the contractor to fix the issue? the Panasonic guy cannot fix? sad.gif

Did you problem solve after u had the contractor to fix it? Wat was the actual issue, did u ask the contractor?

This post has been edited by sin99: Nov 13 2012, 09:32 PM
cherroy
post Nov 13 2012, 09:34 PM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(sin99 @ Nov 13 2012, 08:23 PM)
Tiger355, can't be leaking because my aircond with luck it function with cool air but most of the time...has the auto off and timer blinks faulty....I called the shop that i bought the aircond n they help me to log a report to panasonic. dunno whether they will come and check or not.

sad.gif huh have to call back the contractor to fix the issue? the Panasonic guy cannot fix? sad.gif
*
Leaking also can give you cool air one.
It can result in freezing (not only cool biggrin.gif )! if there is no enough gas (due to leaking).

Generally,
If it is installation error (piping leaking) is about contractor issue.
If it is air-cond issue/faulty then it is manufacturer warranty responsible.

This post has been edited by cherroy: Nov 13 2012, 09:35 PM
arafat
post Nov 13 2012, 09:35 PM

ROCK ON!
******
Senior Member
1,747 posts

Joined: Nov 2004
From: serdang selangor

disable econavi cannot fix it?
sin99
post Nov 13 2012, 09:37 PM

New Member
*
Newbie
3 posts

Joined: May 2007
QUOTE(cherroy @ Nov 13 2012, 09:34 PM)
Leaking also can give you cool air one.
It can result in freezing (not only cool  biggrin.gif )! if there is no enough gas (due to leaking). 

Generally,
If it is installation error (piping leaking) is about contractor issue.
If it is air-cond issue/faulty then it is manufacturer warranty responsible.
*
Ok will ask the contractor to check it for me again coz this is the 2nd time sad.gif


Added on November 13, 2012, 9:39 pm
QUOTE(arafat @ Nov 13 2012, 09:35 PM)
disable econavi cannot fix it?
*
Nope...I din on it

This post has been edited by sin99: Nov 13 2012, 09:39 PM
cherroy
post Nov 13 2012, 09:56 PM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(sin99 @ Nov 13 2012, 09:37 PM)
Ok will ask the contractor to check it for me again coz this is the 2nd time sad.gif
*
You mean first time fixed already, and still happened?

Sometimes, it may better off to use third party or another experienced installer to check, as those installed one the unit one may not want to admit their mistake in installation (if there is),
or some lazy to check, (also they can't charge you if it is their fault in the first place, right?) ,as it may tedious and time consuming job to find out the leaking point.
Not meant installer is like that, as there are many good and responsible installer as well. Just speak with my experience before.

From my experience, (Had installed 3-4 brands before, and more than 20 unit in the past including Pana latest), seldom air-cond itself got problem, most of the time, if there is problem, very often come from installation issue/problem.

ozak
post Nov 13 2012, 11:30 PM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


My office just instal a 2hp york aircon. After a week, it getting not cold. Morning it cold and slowly getting hot in the afternoon.

Call the installer back and complain. After check, found out the gas pressure down (gas leaking). The compressor keep running till over heat and shutdown. The leaking is from the copper pipe coupling joint. (Lazy job) So ask them to use solder joint and not coupling.
tiger3555
post Nov 14 2012, 07:32 AM

Getting Started
**
Junior Member
169 posts

Joined: Feb 2011
QUOTE(sin99 @ Nov 13 2012, 08:23 PM)
Tiger355, can't be leaking because my aircond with luck it function with cool air but most of the time...has the auto off and timer blinks faulty....I called the shop that i bought the aircond n they help me to log a report to panasonic. dunno whether they will come and check or not.

sad.gif huh have to call back the contractor to fix the issue? the Panasonic guy cannot fix? sad.gif

Did you problem solve after u had the contractor to fix it? Wat was the actual issue, did u ask the contractor?
*
yes have to call back contractor.panasonic only investigate the problem of air con, if is the air con problem they will fix, if is piping problem they will ask u call u contractor. My air con so far so good after call contractor to fix. Actual problem i already mention from previous post. nod.gif
weikee
post Nov 14 2012, 08:01 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Actually you can tell if the AC is running with low gas, you hear some hissing sound at the blower unit when it start up for the first 5 to 10 min, most running at 1/2 gas full it still create such sound. Syne AC will even have this sound if only 2/3 full.

With this knowledge I call up Panasonic just few days before warranty expired, they came and check, true enough the AC gas was not enough. It take longer time to cool the room and making hissing sound. He found the problem is at the join/fitting at three compressor, ask my own contractor came and redo the fitting and vacuum and refill gas. New got to Waite another 6 months.

Learn this from an experience AC installer many years back.

This also apply to car a/c compressor.

I am a person who like cold, and very sensative to a/c, bit of a/c problem i will feel it.

This post has been edited by weikee: Nov 14 2012, 08:06 AM
Lushtree
post Nov 14 2012, 01:43 PM

Getting Started
**
Junior Member
103 posts

Joined: Aug 2012


QUOTE(weikee @ Nov 14 2012, 08:01 AM)
Actually you can tell if the AC is running with low gas, you hear some hissing sound at the blower unit when it start up for the first 5 to 10 min, most running at 1/2 gas full it still create such sound. Syne AC will even have this sound if only 2/3 full.

With this knowledge I call up Panasonic just few days before warranty expired, they came and check, true enough the AC gas was not enough. It take longer time to cool the room and making hissing sound. He found the problem is at the join/fitting at three compressor, ask my own contractor came and redo the fitting and vacuum and refill gas. New got to Waite another 6 months.

Learn this from an experience AC installer many years back.

This also apply to car a/c compressor.

I am a person who like cold, and very sensative to a/c, bit of a/c problem i will feel it.
*
Usually there is a trace of compressor oil at the place of gas leak, mineral oil for R-22 system and POE (synthetic oil) for R410A system btw, these oil can be easy wash away by water or rain, cover the copper join for rain if its expose. then you can check after a few day.

Btw is that a copper connector join or welding join the technician detect the leak?
weikee
post Nov 14 2012, 02:20 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
QUOTE(Lushtree @ Nov 14 2012, 01:43 PM)
Usually there is a trace of compressor oil at the place of gas leak, mineral oil for R-22 system and POE (synthetic oil) for R410A system btw, these oil can be easy wash away by water or rain, cover the copper join for rain if its expose. then you can check after a few day.

Btw is that a copper connector join or welding join the technician detect the leak?
*
very minor gas leak don't have oil, and take up to 6+ months the a/c fully out of gas.

Is the connector from copper to compressor valve. I have reserved if that was the case, First time it happen my contractor came and check every single connection and no leak. It could be piping or the indoor/outdoor unit have micro leak. If happen again I will change the a/c together with the piping..
sovietmah
post Nov 14 2012, 03:11 PM

Look at all my stars!!
*******
Senior Member
2,243 posts

Joined: Nov 2005
QUOTE(kelvyn @ Dec 29 2011, 04:35 PM)
Anyone know how to solve this problem?

I am having problem with one of the 1HP air conditioner unit from Panasonic. Problem started after about one month after installation.
It seems that it is noisy when the air swing is allow to swing.
Their technicians have made 5 attempts to rectify the problem and till now, the problem still persist. rclxub.gif
It seems that they are using trial & error method. Every time, when they come, just apply some grease onto the moving parts and the next time, come and change the air vent. After using for a few days, after the grease dries up, the noise comes back.
Now, the warranty is about to expire... sad.gif

Written to their Customer Care dept, then they called and want to try to apply grease and replace the air vent again. Really don't know when all these trial & error will end and problem solve.

Really regretted installing the Pana aircon. Some more went and installed 4 units. Include the older set (2 years ago), so, in total 5 units.  sad.gif
*
May i know the model?
lazzy_dogg
post Nov 15 2012, 06:49 PM

Enthusiast
*****
Senior Member
943 posts

Joined: Oct 2004
From: K.Lumpur, Subang



anyone faced with the nanoe-g light blinking? i am having that problem.... error code H00... anyone knows what is it?

xerox1234
post Nov 15 2012, 09:53 PM

Casual
***
Junior Member
334 posts

Joined: Nov 2005
My 1.5HP aircon take ages to get cool, abt 10 minutes, is this normal?
swgiant
post Nov 16 2012, 12:22 AM

Extravagance RUINS Your Life !!!
******
Senior Member
1,414 posts

Joined: Jan 2003
From: 47300


panasonic delux model too complicated then will it increase the chances of parts failure for a long term running, iam doubt that...
Titan_Gunners
post Nov 16 2012, 08:54 AM

Regular
******
Senior Member
1,573 posts

Joined: Sep 2010
QUOTE(xerox1234 @ Nov 15 2012, 09:53 PM)
My 1.5HP aircon take ages to get cool, abt 10 minutes, is this normal?
*
how many time do you expected, 1 min? I would say 10-15 min is standard time to cool the room.
xerox1234
post Nov 16 2012, 09:31 AM

Casual
***
Junior Member
334 posts

Joined: Nov 2005
QUOTE(Titan_Gunners @ Nov 16 2012, 08:54 AM)
how many time do you expected, 1 min? I would say 10-15 min is standard time to cool the room.
*
Mitshubishi only takes 5 minutes and the cool air started after the compressor running but NOT for Panasonic. This Econavi is really slow and I was told should be 3-5 minutes. Even after 10 minutes, it only start has some cool air and not really cool as compare with Mitshubishi. That's why I wonder if something wrong with this model. I had old model without Econavi and it works well.

TSkelvyn
post Nov 17 2012, 04:48 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
QUOTE(sovietmah @ Nov 14 2012, 04:11 PM)
May i know the model?
*
They now have the new model. I think the problem should be resolved by now....
bdcyl
post Dec 30 2012, 10:07 PM

Enthusiast
*****
Senior Member
874 posts

Joined: Aug 2006
QUOTE(kelvyn @ Dec 29 2011, 05:35 PM)
Anyone know how to solve this problem?

I am having problem with one of the 1HP air conditioner unit from Panasonic. Problem started after about one month after installation.
It seems that it is noisy when the air swing is allow to swing.
Their technicians have made 5 attempts to rectify the problem and till now, the problem still persist. rclxub.gif
It seems that they are using trial & error method. Every time, when they come, just apply some grease onto the moving parts and the next time, come and change the air vent. After using for a few days, after the grease dries up, the noise comes back.
Now, the warranty is about to expire... sad.gif

Written to their Customer Care dept, then they called and want to try to apply grease and replace the air vent again. Really don't know when all these trial & error will end and problem solve.

Really regretted installing the Pana aircon. Some more went and installed 4 units. Include the older set (2 years ago), so, in total 5 units.  sad.gif
*
same thing happen to me (I INSTALL 5) BUT NOT ALL UNIT HAPPEN THE CRACKING SOUND.... it i s because of the changes of the temp that cause the expansion / contraction of the unit... it happen to model C(NUM)MKH MODEL...
then the fix this prob and is not happen anymore on newer that NKH MODEL IS C(NUM)MKH MODEL... I BOUGHT 1 MKH MODEL AND IS NO PROB...


Added on December 30, 2012, 10:08 pmANYBODY KNOW WHERE I CAN DOWNLOAD CS-C9MKH QUICK GUIDE??? WANA REFER TO SOMETHING...

This post has been edited by bdcyl: Dec 30 2012, 10:08 PM
sam_moysfun
post Apr 19 2014, 05:05 PM

New Member
*
Newbie
3 posts

Joined: Oct 2013
Does anyone has Gree brand air-conditioner at home? Need to seek help how to set sleep mode on the remote control. Thanks.
cdspins
post Apr 19 2014, 11:34 PM

Look at all my stars!!
*******
Senior Member
2,714 posts

Joined: May 2008


QUOTE(xerox1234 @ Nov 16 2012, 09:31 AM)
Mitshubishi only takes 5 minutes and the cool air started after the compressor running but NOT for Panasonic. This Econavi is really slow and I was told should be 3-5 minutes. Even after 10 minutes, it only start has some cool air and not really cool as compare with Mitshubishi. That's why I wonder if something wrong with this model. I had old model without Econavi and it works well.
*
Ya.... facing the same problem... I think this is how they achieve the 30% energy savings advertise on econavi model. My old panasonic also quite cold but this econavi doh.gif
SUSTXSim
post Jan 8 2016, 07:41 PM

TIME Fibre Assistant and Wi-Fi Router Assistant
*******
Senior Member
2,137 posts

Joined: Oct 2015


Hi, anyone facing problem with ECONAVI?
kksoon
post Jun 26 2016, 11:07 AM

Regular
******
Senior Member
1,498 posts

Joined: Oct 2006
Anyone know how to check the error code for Panasonic CS-PC18QKH using remote when the timer LED blinking & aircond auto off by it self?
SUSTXSim
post Jun 26 2016, 11:21 AM

TIME Fibre Assistant and Wi-Fi Router Assistant
*******
Senior Member
2,137 posts

Joined: Oct 2015


QUOTE(kksoon @ Jun 26 2016, 11:07 AM)
Anyone know how to check the error code for Panasonic CS-PC18QKH using remote when the timer LED blinking & aircond auto off by it self?
*
user posted image
idoblu
post Jan 18 2017, 07:58 AM

stars for sale
********
All Stars
11,308 posts

Joined: Feb 2008
my pana inverter (used for about 2 years) suddenly turned off. Turned back on but no more cold air.
Check error codes - give 95.

tech came found mainboard at compressor faulty - one of the caps blew
lucky still got warranty

user posted image
ozak
post Jan 18 2017, 09:20 AM

10k Club
********
All Stars
17,018 posts

Joined: Jan 2005


QUOTE(idoblu @ Jan 18 2017, 07:58 AM)
my pana inverter (used for about 2 years) suddenly turned off. Turned back on but no more cold air.
Check error codes - give 95.

tech came found mainboard at compressor faulty - one of the caps blew
lucky still got warranty

user posted image
*
Electronic component nowadays so unreliable.

Follow china way of manufacturing is bad.
Twins10
post Aug 2 2018, 10:10 AM

Enthusiast
*****
Junior Member
919 posts

Joined: Aug 2015
My pana 1 hp capacitor blew. What crap! Never buy pana again.
SUSslimey
post Aug 2 2018, 02:15 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(Twins10 @ Aug 2 2018, 10:10 AM)
My pana 1 hp capacitor blew.  What crap!  Never buy pana again.
*
A common fault.

Either the cap for the indoor blower usually rated at 1 or 1.5 micro farad
Or the outdoor unit cap for the compressor usually rated at 30 micro farad
Twins10
post Aug 2 2018, 03:33 PM

Enthusiast
*****
Junior Member
919 posts

Joined: Aug 2015
Rm130 to clean n rm100 for capacitor.
SUSslimey
post Aug 2 2018, 05:02 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(Twins10 @ Aug 2 2018, 03:33 PM)
Rm130 to clean n rm100 for capacitor.
*
Lel. Can diy.
The capacitor only cost rm20 for the 30uf and rm3 for the 1uf.
Cleaning can be done easily if you have a garden sprayer.

If the outdoor unit gets water during a rain it should self clean so no need clean outdoor unit usually.

 

Change to: