So how do I know which cable being used for my WH? Cables come in standard size for the most part.
The CSA (cross sectional area) is calculated from "one strand diameter" x "total nos of strands".
We'll assume ur talking about the solid stranded (stiff cable) not flexicord (the soft n flexible stuff used in appliances/extension cord).
2.5mm² is made of 0.67mm dia per strand x 7 strands.
4.0mm² is made up of 0.85mm dia per strand x 7 strands.
If its labelled on the cable, u can read the size from the cable.
If its not clearly labelled, still can cross check:
Using either a
micrometer or vernier caliper to measure a strand, roughly u shud get the 0.67 value if 2.5mm² cable. Plus minus a little maybe 0.65 or 0.68, but if its grossly smaller like 0.5 on every strand of a supposedly 2.5mm² cable, then u know the cable is elcheapo substandard cable.
Weighing cables is inaccurate as the total weight also contain the insulation. Some substandard cable their insulation made thicker and copper made thinner, plastic is cheap ma.
QUOTE
And lets say if I wanted to change from 2.5 mm2 to 4 to support higher kW WH, does it mean have to rewire from the toilet all the way to the DB? Will it be very expensive? Since now copper price is expensive and also I think hacking has to be done? Anyone know roughly how much for this?
4mm top tier cables go for ~RM180-185/100m roll nowadays. Was RM136 in March. Top tier e.g. Mega Kabel, Caramay, or MCMA cartel members.
You will need LNE (3 rolls).
Loose cut only worth if its short distance.. like below 15-20meter otherwise the loose cut premium is also expensive (can be 50-60% or more) depending on where you source em.
Yes you need to rewire from DB for the most part.
Specifically "DB to WH switch, then switch to WH" for L & N. And DB direct flight to the WH (unbroken earth).
Copper went up ~1st Apr, luckily manage to secure full roll for my needs.
As for the hacking.. at a very minimum (starting from WH) you need to hack the line out from WH up to the ceiling. then horizontal run from there to the DB box ceiling part. Then drop down into DB box. (ending at DB). Ask the electrician don't hangman (cut the wire ends so tight in the DB that you cannot move the MCB later on).. can pusing pusing the extra length ("extra tolerance") around the side of the DB box so that next time want to relocate/replace DB box life is easier...
if hangman "cut exactly" really challenging to fit everything in place in future when everything else also 0 tolerance. Since the wire also already paid for and they will have no use for that few inches or 1 feet extra..but leaving "a bit of slack for the next guy" really helps.
It may be easier if you have plaster ceiling so only two main parts (start and end) to conceal, and minor hole to pass the cable thru beams or walls as necessary.
Concealing cost money because of the hacking. There is no harm in installing exposed PVC pipe conduit first, if money is a concern.. aesthetic wise when financially comfortable can conceal later.