 RCCB/ELCB 100mA still nuisance trip!, during lightning storms

views
     
TSsocratesman
post Mar 15 2011, 12:29 PM, updated 10y ago

Regular
******
Senior Member
1,807 posts

Joined: Jan 2003
From: KL
Hi folks,

My family and I are living in a terrace house.
Recently my dad changed our 25-yr old voltage-based ELCB to a newer current-based RCCB (Wylex 2Pole 40A with 100mA sensitivity)

After that it start nuisance tripping a lot during storms, even if the lightning is far away. mad.gif
When no storm, everything is OK.

I was surprised even 100mA also trips a lot, if 30mA of course I can understand the tripping.

Any RCCB users here on 100mA sensitivity? Do yours trip frequently during storms? If yes, what did you do to mitigate the annoyance?

This post has been edited by socratesman: Mar 15 2011, 12:30 PM
PJusa
post Mar 15 2011, 02:00 PM

Look at all my stars!!
*******
Senior Member
2,031 posts

Joined: Jan 2003
From: PJ
disconnected mine for the same reason. 100mA provides no safety anyway to humans. neither does 30 mA - you would need max. of 10mA for that.
blibala
post Mar 16 2011, 12:31 AM

Regular
******
Senior Member
1,920 posts

Joined: Jan 2005
Probably fault happened to your earthing....nobody use 10mA sensitivity at home lar...
PJusa
post Mar 16 2011, 08:46 PM

Look at all my stars!!
*******
Senior Member
2,031 posts

Joined: Jan 2003
From: PJ
nope all is perfectly well. and 10 mA is the recommended trip threshold in europe. any higher and its deadly for humans anyway so there is little point in having the ELCB for the purpose of saving a life anyway.
TSsocratesman
post Mar 17 2011, 12:06 PM

Regular
******
Senior Member
1,807 posts

Joined: Jan 2003
From: KL
QUOTE(blibala @ Mar 16 2011, 12:31 AM)
Probably fault happened to your earthing....nobody use 10mA sensitivity at home lar...
*
ermm...i said 100mA wink.gif
blibala
post Mar 17 2011, 01:12 PM

Regular
******
Senior Member
1,920 posts

Joined: Jan 2005
change to better brand of ELCB/RCCB...GE, Hager....
SUSNew Klang
post Mar 23 2011, 02:54 PM

Look at all my stars!!
*******
Senior Member
4,998 posts

Joined: Dec 2010
QUOTE(blibala @ Mar 17 2011, 01:12 PM)
change to better brand of ELCB/RCCB...GE, Hager....
*
IEE now states RCD (previously ELCB/RCCB were used).

10mA - 30 mA. Trip within 30 ms for shocks to person.

Protection against fire- up to 100mA.

Should use surge arrestor to protect your home.
mikicun
post Mar 23 2011, 02:56 PM

Casual
***
Junior Member
444 posts

Joined: Nov 2006
From: somewhere i belong...
use 300mA la then...
less tripping
SUSNew Klang
post Mar 23 2011, 03:02 PM

Look at all my stars!!
*******
Senior Member
4,998 posts

Joined: Dec 2010
QUOTE(mikicun @ Mar 23 2011, 02:56 PM)
use 300mA la then...
less tripping
*
You can use 300mA for the main incomer however not necessary protect against lightning.
xa[V]ier
post Mar 24 2011, 09:19 AM

Getting Started
**
Junior Member
131 posts

Joined: Nov 2007


QUOTE(socratesman @ Mar 15 2011, 12:29 PM)
Hi folks,

My family and I are living in a terrace house.
Recently my dad changed our 25-yr old voltage-based ELCB to a newer current-based RCCB (Wylex 2Pole 40A with 100mA sensitivity)

After that it start nuisance tripping a lot during storms, even if the lightning is far away. mad.gif
When no storm, everything is OK.

I was surprised even 100mA also trips a lot, if 30mA of course I can understand the tripping.

Any RCCB users here on 100mA sensitivity? Do yours trip frequently during storms? If yes, what did you do to mitigate the annoyance?
*
Maybe there's something wrong with your wiring.. some leakage somewhere..
eMKs
post Mar 24 2011, 05:36 PM

On my way
****
Senior Member
647 posts

Joined: Jan 2010
From: Klang
Install auto reset ELCB smile.gif
helob
post Oct 30 2011, 11:40 AM

Getting Started
**
Junior Member
265 posts

Joined: Jan 2003
Hi,
Saw your msg above while searching for solution to frequent lighning power trip.
I encountered exactly the same problem using the same RCCB/ELCB from MEM.
Did you find a solution?
If so, would appreciate if you can share it with me.
Thank You
Have a nice day.

QUOTE(socratesman @ Mar 15 2011, 12:29 PM)
Hi folks,

My family and I are living in a terrace house.
Recently my dad changed our 25-yr old voltage-based ELCB to a newer current-based RCCB (Wylex 2Pole 40A with 100mA sensitivity)

After that it start nuisance tripping a lot during storms, even if the lightning is far away. mad.gif
When no storm, everything is OK.

I was surprised even 100mA also trips a lot, if 30mA of course I can understand the tripping.

Any RCCB users here on 100mA sensitivity? Do yours trip frequently during storms? If yes, what did you do to mitigate the annoyance?
*
SUSceo684
post Oct 30 2011, 02:25 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




instead of 40A type maybe try using the 63A type.
helob
post Oct 30 2011, 02:39 PM

Getting Started
**
Junior Member
265 posts

Joined: Jan 2003
QUOTE(ceo684 @ Oct 30 2011, 02:25 PM)
instead of 40A type maybe try using the 63A type.
*
Tks for the input.
I am already using the 63A type.
Here is the spec on my MEM RCCB

Manufacturer: MEM
Model:632ELMN
In=63A
Ioan=100ma
Un=240V~

Would it help if using Ioan of 300ma or 500ma?

Thank You

This post has been edited by helob: Oct 30 2011, 02:41 PM


Attached thumbnail(s)
Attached Image
pky
post Oct 31 2011, 07:39 PM

On my way
****
Senior Member
558 posts

Joined: Jan 2003
In = 40A / 63A indicates the Max carry amp of the RCCB. It means, if you install a 40A RCCB, but you are running 50A of load, it will trip. This protect from overload.

Ioan is the sensitivity of the RCCB. Ideally, Live + Neutral = 0, if Live + Neutral /= 0, leakage happen. But, there's no ideal in real life, so, comes the Ioan where it is the tolerance the device will accept before registering the leakage as a fault, in your case, 100mA.
Generally, for lighting circuit, 100mA is used, 30mA is used for power circuit and 300mA for Air-Con.

As for your problem, how old is your house, particularly, the electrical wiring? The older the wiring, the higher the probability of leakage through wires due to degration of the insulator.

Proper solution, do a complete insulation test to the whole house, or change all the wiring. Improve your house earthing system.

Cheap solution, which profesional do not agree, but client will usually do due to cost saving. Use higher tolerance RCCB or use ELCB instead.

No matter how do it, make sure other than the fuse, there's at least a protection device in place.
helob
post Nov 2 2011, 03:11 PM

Getting Started
**
Junior Member
265 posts

Joined: Jan 2003
Thanks for the very informative feedback.
My house is well over ten years as I bought it ten years ago.
You are most probably right that some wire insulation has degraded to a point where there is earth leakage during lightning which trip the RCCB.
My thought was to isolate certain area/wiring where leakage is suspected by selectively turn off the DPN MCB during lighning.
What is the best method of identifying the area/wiring other than doing a complete insulation test for the whole house?
Typically how long and the cost of doing a complete insulation test for a semi-D single storey house?
I thought RCCB is the current version of ELCB.
Pls elaborate on "use ELCB instead"
TQ and have a nice day.


QUOTE(pky @ Oct 31 2011, 07:39 PM)
In = 40A / 63A indicates the Max carry amp of the RCCB. It means, if you install a 40A RCCB, but you are running 50A of load, it will trip. This protect from overload.

Ioan is the sensitivity of the RCCB. Ideally, Live + Neutral = 0, if Live + Neutral /= 0, leakage happen. But, there's no ideal in real life, so, comes the Ioan where it is the tolerance the device will accept before registering the leakage as a fault, in your case, 100mA.
Generally, for lighting circuit, 100mA is used, 30mA is used for power circuit and 300mA for Air-Con.

As for your problem, how old is your house, particularly, the electrical wiring? The older the wiring, the higher the probability of leakage through wires due to degration of the insulator.

Proper solution, do a complete insulation test to the whole house, or change all the wiring. Improve your house earthing system.

Cheap solution, which profesional do not agree, but client will usually do due to cost saving. Use higher tolerance RCCB or use ELCB instead.

No matter how do it, make sure other than the fuse, there's at least a protection device in place.
*
zeese
post Nov 2 2011, 03:31 PM

Warning Level
******
Senior Member
1,818 posts

Joined: Jan 2005
From: Kuala Lumpur
why nobody mention about grounding.. there was a thread about this and most replies mentioned about improving the wire grounding..
TSsocratesman
post Nov 2 2011, 07:54 PM

Regular
******
Senior Member
1,807 posts

Joined: Jan 2003
From: KL
didn't realise helpful helob resurrected my thread lol

After some research, I suspect background leakage from the internal wiring (my house is 30+ yrs old).
Say, maybe about 60-70mA worth of background leakage between Live and Neutral.
So the tiniest of surges from lightning could be enough to send the Live-Neutral delta over 100mA => TRIP

damn, now must check all the circuits in the house..mafan
pky
post Nov 2 2011, 09:17 PM

On my way
****
Senior Member
558 posts

Joined: Jan 2003
QUOTE(helob @ Nov 2 2011, 03:11 PM)
Thanks for the very informative feedback.
My house is well over ten years as I bought it ten years ago.
You are most probably right that some wire insulation has degraded to a point where there is earth leakage during lightning which trip the RCCB.
My thought was to isolate certain area/wiring where leakage is suspected by selectively turn off the DPN MCB during lighning.
What is the best method of identifying  the area/wiring other than doing a complete insulation test for the whole house?
Typically how long and the cost of doing a complete insulation test for a semi-D single storey house?
I thought RCCB is the current version of ELCB.
Pls elaborate on "use ELCB instead"
TQ and have a nice day.
*
Insulation test is very tedious job. Have to dismantle all lighting and power point from its appliances, and it might damage your existing wirie insulation since during insulation test, 1kV(can set to 500V) will be injected to the circuit to stress the wiring. If your wire insulation "almost going to die" after the injection, most probably going to "die" for good. We only do insulation test if the house wiring is still new, or when we know which particular circuit giving the problem. Not to mention, i don't think your local neighbourhood electrician know what is "insulation test".

RCCB are replacing ELCB and both are two different thing with different protection method which you can easily google it up.

QUOTE(zeese @ Nov 2 2011, 03:31 PM)
why nobody mention about grounding.. there was a thread about this and most replies mentioned about improving the wire grounding..
*
One of my suggestion is to improve the earthing system as well. But it will involve lots of $$ especially lately where copper price are still at it high side.


QUOTE(socratesman @ Nov 2 2011, 07:54 PM)
didn't realise helpful helob resurrected my thread lol

After some research, I suspect background leakage from the internal wiring (my house is 30+ yrs old).
Say, maybe about 60-70mA worth of background leakage between Live and Neutral.
So the tiniest of surges from lightning could be enough to send the Live-Neutral delta over 100mA => TRIP

damn, now must check all the circuits in the house..mafan
*
As i suggested earlier to helob, either change the house wiring, use less sensitive RCCB, use back the primitive ELCB, improve your earthing system, or change to other protection system such as using adjustable ELR with a shunt trip coil, or just leave it as is, standby at the DB during thunder.

helob
post Nov 9 2011, 10:54 AM

Getting Started
**
Junior Member
265 posts

Joined: Jan 2003
QUOTE(socratesman @ Nov 2 2011, 07:54 PM)
didn't realise helpful helob resurrected my thread lol

After some research, I suspect background leakage from the internal wiring (my house is 30+ yrs old).
Say, maybe about 60-70mA worth of background leakage between Live and Neutral.
So the tiniest of surges from lightning could be enough to send the Live-Neutral delta over 100mA => TRIP

damn, now must check all the circuits in the house..mafan
*
What is your findings so far?
Care to share!
Tks
mytrader
post Nov 9 2011, 03:21 PM

Casual
***
Junior Member
451 posts

Joined: Feb 2008


Anyone heard of self reset-ing ELCB ?


kelvyn
post Nov 9 2011, 03:30 PM

Look at all my stars!!
*******
Senior Member
3,173 posts

Joined: May 2007
Am curious on how this resetting ELCB works. The ELCB is supposed to trip when there is a fault in the circuit. Auto resetting without establishing the fault first, would that be dangerous?
PJusa
post Nov 9 2011, 06:49 PM

Look at all my stars!!
*******
Senior Member
2,031 posts

Joined: Jan 2003
From: PJ
can be bought but they only reset three times before a manual reset is required. they are meant for unammned outstation places. if you want self resetting safe the money and just remove the existing one. safety wise its (almost) the same smile.gif
SUSceo684
post Nov 10 2011, 02:27 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




Maybe u try playing around with the little MCB switches and try to narrow down which circuit is causing the trip during lightning?
JinXXX
post Nov 10 2011, 09:35 AM

Look at all my stars!!
*******
Senior Member
2,516 posts

Joined: Feb 2007
From: Uarla Umpur



QUOTE(ceo684 @ Nov 10 2011, 02:27 AM)
Maybe u try playing around with the little MCB switches and try to narrow down which circuit is causing the trip during lightning?
*
is there a device that we can use to check and find out the problems ???


weikee
post Nov 10 2011, 09:38 AM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Yes, someone already mention it before.
Zestune
post Nov 11 2011, 12:58 AM

New Member
*
Junior Member
7 posts

Joined: Jul 2010
From: The Strand, Kota Damansara


Better check on your house earthing ... if trip during lightning ... Or you can try changing your RCCB to those like Hager RCCBs that is designed with an anti-nuisance tripping feature, which do not unnecessarily tripped unless there is a genuine earth fault.

This post has been edited by Zestune: Nov 11 2011, 01:36 AM
jimmylim85
post Nov 11 2011, 01:15 AM

iPhone world....
*******
Senior Member
7,826 posts

Joined: Jan 2003
From: Ipoh




There is also electronic selectable sensitivity to adjuct from 0.1A to 1A cut off.

Anyway having it trip during lightning isn't good as it try block surge from entering your electrical appliances.

Btw MCB is meant for overload cut off. It trips whenever the load (amperage) goes beyond the rated. Usually it trips when Live wire shorted to Neutral. ELCB trips whenever there is leakage on Neutral. For example, Live or Neutral wire is leak to the earth, it trips.

To test how good is your electrical grounding, get a MEGA tester or insulation tester. Calculation based on OHM.


JinXXX
post Nov 11 2011, 12:33 PM

Look at all my stars!!
*******
Senior Member
2,516 posts

Joined: Feb 2007
From: Uarla Umpur



QUOTE(jimmylim85 @ Nov 11 2011, 01:15 AM)
To test how good is your electrical grounding, get a MEGA tester or insulation tester. Calculation based on OHM.
*
OHM = ??

nvm found out its also ohm / resistance calculation smile.gif

This post has been edited by JinXXX: Nov 11 2011, 03:06 PM
pky
post Nov 11 2011, 02:18 PM

On my way
****
Senior Member
558 posts

Joined: Jan 2003
MCB detects overcurrent. Say, a 2.5HP aircon connected to 10A MCB, MCB will trip.
ELCB detects if any current running in the Earth conductor
RCCB detects residue current between L&N.

Earth Resistivity (Electrical Grounding) test using Earth Tester. Calculated in Ohm, the lower the ohm the better it is.

Insulation Tester (Mega Tester) is test the insulation capability of the cables. Measured in MOhm. The higher it is, the better.

Both Earth tester and insulation tester are not cheap at hundreds.
JinXXX
post Nov 11 2011, 03:06 PM

Look at all my stars!!
*******
Senior Member
2,516 posts

Joined: Feb 2007
From: Uarla Umpur



QUOTE(pky @ Nov 11 2011, 02:18 PM)
MCB detects overcurrent. Say, a 2.5HP aircon connected to 10A MCB, MCB will trip.
ELCB detects if any current running in the Earth conductor
RCCB detects residue current between L&N.

Earth Resistivity (Electrical Grounding) test using Earth Tester. Calculated in Ohm, the lower the ohm the better it is.

Insulation Tester (Mega Tester) is test the insulation capability of the cables. Measured in MOhm. The higher it is, the better.

Both Earth tester and insulation tester are not cheap at hundreds.
*
+1 smile.gif
liktin111
post Jun 7 2012, 04:21 PM

New Member
*
Newbie
1 posts

Joined: Mar 2012
QUOTE(socratesman @ Mar 15 2011, 12:29 PM)
Hi folks,

My family and I are living in a terrace house.
Recently my dad changed our 25-yr old voltage-based ELCB to a newer current-based RCCB (Wylex 2Pole 40A with 100mA sensitivity)

After that it start nuisance tripping a lot during storms, even if the lightning is far away. mad.gif
When no storm, everything is OK.

I was surprised even 100mA also trips a lot, if 30mA of course I can understand the tripping.

Any RCCB users here on 100mA sensitivity? Do yours trip frequently during storms? If yes, what did you do to mitigate the annoyance?
*
Hi,
As mention the ELCB for 100mA will trip frequently during storms is a norm. Its prove that your ELCB working. If the ELCB never trip at all, you are in trouble. ELCB is a safety device used in electrical installations with high earth impedance to prevent SHOCK and to protect your SENSITIVE equipment/home appliances.

The ELCB rating should be as low as possible to prevent shock; do you think that 100mA is safe enough for human and equipment? NO. IEC 60479 stated that human cannot take in more than 7mA of leakage current. More than that are critical level and may cause to DEATH. Unfortunately, the current ELCB lowest rating is 10mA whereby still a risk to human against SHOCK. If you choose to use 30mA at your main, you will complain that it trip more frequent as compare to your assisting one (100mA).

I have the solution where comply to IEC 60479 and eliminate nuisance trip… thumbup.gif

jack~daniel
post Oct 27 2012, 05:14 PM

Enthusiast
*****
Senior Member
834 posts

Joined: Jun 2012
From: ~Heaven~


QUOTE(socratesman @ Mar 15 2011, 12:29 PM)
Hi folks,

My family and I are living in a terrace house.
Recently my dad changed our 25-yr old voltage-based ELCB to a newer current-based RCCB (Wylex 2Pole 40A with 100mA sensitivity)

After that it start nuisance tripping a lot during storms, even if the lightning is far away. mad.gif
When no storm, everything is OK.

I was surprised even 100mA also trips a lot, if 30mA of course I can understand the tripping.

Any RCCB users here on 100mA sensitivity? Do yours trip frequently during storms? If yes, what did you do to mitigate the annoyance?
*
100ma is complusary for main switchboard.cant use more than that according to regulation.nuisance tripping occured during lightning strike due to current imbalance between live and neutral.so its pretty normal.lightning wave travel frm tnb cables to ur house.its not about the lightning is far...


Added on October 27, 2012, 5:17 pm
QUOTE(liktin111 @ Jun 7 2012, 04:21 PM)
Hi,
As mention the ELCB for 100mA will trip frequently during storms is a norm. Its prove that your ELCB working. If the ELCB never trip at all, you are in trouble.  ELCB is a safety device used in electrical installations with high earth impedance to prevent SHOCK and to protect your SENSITIVE equipment/home appliances.

The ELCB rating should be as low as possible to prevent shock; do you think that 100mA is safe enough for human and equipment? NO. IEC 60479 stated that human cannot take in more than 7mA of leakage current. More than that are critical level and may cause to DEATH. Unfortunately, the current ELCB lowest rating is 10mA whereby still a risk to human against SHOCK. If you choose to use 30mA at your main, you will complain that it trip more frequent as compare to your assisting one (100mA).

I have the solution where comply to IEC 60479 and eliminate nuisance trip… thumbup.gif
*
iec stated min is 30ma to prevent frm direct contact.not 7ma.100ma is for domestic application as per regulation.30ma is for final circuit or special location


Added on October 27, 2012, 5:23 pm
QUOTE(pky @ Nov 11 2011, 02:18 PM)
MCB detects overcurrent. Say, a 2.5HP aircon connected to 10A MCB, MCB will trip.
ELCB detects if any current running in the Earth conductor
RCCB detects residue current between L&N.

Earth Resistivity (Electrical Grounding) test using Earth Tester. Calculated in Ohm, the lower the ohm the better it is.

Insulation Tester (Mega Tester) is test the insulation capability of the cables. Measured in MOhm. The higher it is, the better.

Both Earth tester and insulation tester are not cheap at hundreds.
*
elcb and rccb serve same purpose..elcb is old term and has been raplaced with rccb


This post has been edited by jack~daniel: Oct 27 2012, 05:23 PM
Kiding
post Dec 1 2012, 12:42 AM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


My house also get nuisance trip during thunder storm, I plan to change the TBC 100mA RCCB to Hager 100mA RCCB, would it help? and where to get the Hager RCCB?
PJusa
post Dec 1 2012, 10:26 AM

Look at all my stars!!
*******
Senior Member
2,031 posts

Joined: Jan 2003
From: PJ
if your earth is good it *might* help. do note that in my personal opinion you dont need an ELCB at all if you decide to go higher than 30mA. Its no use. The ELCB is meant to save a humans life if they get into the circuit. If your cutoff level is already deadly why even bother with it? Either you do it properly or no need to do at all. If nobody gets inside the circuit you're pretty safe without an ELCB.
Kiding
post Dec 1 2012, 11:01 AM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(PJusa @ Dec 1 2012, 10:26 AM)
if your earth is good it *might* help. do note that in my personal opinion you dont need an ELCB at all if you decide to go higher than 30mA. Its no use. The ELCB is meant to save a humans life if they get into the circuit. If your cutoff level is already deadly why even bother with it? Either you do it properly or no need to do at all. If nobody gets inside the circuit you're pretty safe without an ELCB.
*
If using 30mA then I expect the nuisance trip will even worst!

Actually the 100mA is good enough, it trip yesterday when the aircon installer accidentally touch the wire.

I think most house in Malaysia use 100mA by default.
ozak
post Dec 1 2012, 12:11 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Kiding @ Dec 1 2012, 11:01 AM)
If using 30mA then I expect the nuisance trip will even worst!

Actually the 100mA is good enough, it trip yesterday when the aircon installer accidentally touch the wire.

I think most house in Malaysia use 100mA by default.
*
Not true. I been using 30mA for many many yrs. Last time I always have this nuisance tripping. Go to electrical shop and ask for the solution from the bos. Told me to change to a better 1 and abit expensive. Brand hager and cost rm120. Change it and now less trip.

Use a better way to solve the problem and not downgrade the safety. You still have a solution like earthing and surge protector.
Kiding
post Dec 1 2012, 12:55 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(ozak @ Dec 1 2012, 12:11 PM)
Not true. I been using 30mA for many many yrs. Last time I always have this nuisance tripping. Go to electrical shop and ask for the solution from the bos. Told me to change to a better 1 and abit expensive. Brand hager and cost rm120. Change it and now less trip.

Use a better way to solve the problem and not downgrade the safety. You still have a solution like earthing and surge protector.
*
Thanks for the advice, I will give it a try, Where can I get Hager brand in Klang Valley area? Can I get it at Jalan Pasar?
weikee
post Dec 1 2012, 12:56 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
Find the root cause of the problem. Keep increasing the tolerance must as well bypass ELCB run without safety.
ozak
post Dec 1 2012, 01:11 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Kiding @ Dec 1 2012, 12:55 PM)
Thanks for the advice, I will give it a try, Where can I get Hager brand in Klang Valley area? Can I get it at Jalan Pasar?
*
The original RCCB from the house developer is 100mA. Trip like hell. Change it to better brand Hager 30mA. Less trip.

So it doesn't logic to me that 100mA give less problem. And compromise the safety.

You can get it at any electrical shop. It is not branded item now.
ozak
post Dec 1 2012, 05:56 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


Here are some information and understanding about RCCB.

Attached File  RCD_The_Best_Way_To_Guarantee_Electrical_Safety_At_Home1.pdf ( 60.29k ) Number of downloads: 939
Attached File  RCD_The_Best_Way_To_Guarantee_Electrical_Safety_At_Home.pdf ( 129.5k ) Number of downloads: 840


Why nuisance trip, what happen and some solution without compromise the safety.

Attached File  Solution.pdf ( 171.31k ) Number of downloads: 1641


This post has been edited by ozak: Dec 1 2012, 05:58 PM
JinXXX
post Dec 1 2012, 10:13 PM

Look at all my stars!!
*******
Senior Member
2,516 posts

Joined: Feb 2007
From: Uarla Umpur



QUOTE(ozak @ Dec 1 2012, 01:11 PM)
The original RCCB from the house developer is 100mA. Trip like hell. Change it to better brand Hager 30mA. Less trip.

So it doesn't logic to me that 100mA give less problem. And compromise the safety.

You can get it at any electrical shop. It is not branded item now.
*
can we buy and fix the RCCD ourself to replace my told ELCB ? 15 years no touch/change it..

or its better to recommend an "ƫlectrician" to fix it ?
ozak
post Dec 1 2012, 11:27 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(JinXXX @ Dec 1 2012, 10:13 PM)
can we buy and fix the RCCD ourself to replace my told ELCB ? 15 years no touch/change it..

or its better to recommend an "ƫlectrician" to fix it ?
*
Can it trip? Press the test button to try it.

You can change it yourself. Not difficult. Just makesure OFF the main MCB or takeout the fuse. 2 wire in and 2 wire out. Some maybe have direction of incoming and outgoing. Some don't.

If no confident, buy the RCCB and ask the bos change it for you. Pay some fee.
Pennbattle
post Dec 2 2012, 12:19 AM

Casual
***
Junior Member
440 posts

Joined: Jul 2012


My parent house happen too only when got lighting. Without lighting everything o.k. The house only 7 years. Any solution for me?
Kiding
post Dec 2 2012, 12:36 AM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


Asking Hager 30mA RCCB around 5 shops in Puchong and Serdang, none of them carry 30mA, so just get the 100mA for RM80

I'm planing to install 30mA sensitivity RCBO to replace the MCB for the electric shower heater, is it better than install 30mA at the main switch?
ozak
post Dec 2 2012, 01:45 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Kiding @ Dec 2 2012, 12:36 AM)
Asking Hager 30mA RCCB around 5 shops in Puchong and Serdang, none of them carry 30mA, so just get the 100mA for RM80

I'm planing to install 30mA sensitivity RCBO to replace the MCB for the electric shower heater, is it better than install 30mA at the main switch?
*
Beside hager, you can get the ABB anti nuisance trip 30mA RCCB. Read the pdf file above.

RCBO is a good idea too. It have extra protection than RCCB. It use after the main RCCB.

I m using RCD+fuse 30mA for heater, kitchen and fountain. Install inside toilet nearer to heater.

user posted image
Dennis126
post Mar 14 2013, 09:36 AM

New Member
*
Newbie
1 posts

Joined: Mar 2013
has anybody used AOELEC Auto Reclosing (Resetting) RCCB before ?

How is the effectiveness ?

I understand it can auto rest 3 times and after the third time it has to be manually reset (for safety reason).
Can the resetting time be adjustable, ie to auto set after say 30 minutes it has tripped?

How much is the cost per unit ?

Thanks in advance.

dennis


Attached Image
jovial
post Mar 15 2013, 12:43 PM

carpe diem
*******
Senior Member
2,129 posts

Joined: Jan 2003
From: Somewhere only we know..

QUOTE(PJusa @ Mar 15 2011, 02:00 PM)
disconnected mine for the same reason. 100mA provides no safety anyway to humans. neither does 30 mA - you would need max. of 10mA for that.
*
Please don't be silly to disconnect it as it's for your own protection. Many times that my RCCB has tripped, it's due to some malfunction in my house electrical equipment. Sometimes there's a residual leak in your house that's tripping your ELCB/RCCB.
PJusa
post Mar 15 2013, 11:14 PM

Look at all my stars!!
*******
Senior Member
2,031 posts

Joined: Jan 2003
From: PJ
disconnecting an ELCB that cant by definition do what it should do because the threshold is too high is not silly. if the ELCB will only act AFTER its too late because its rating is too high what's the use? i can also place another spare on on top of my meter for the looks of it and it would have almost the same effect.
jack~daniel
post Mar 26 2013, 08:03 AM

Enthusiast
*****
Senior Member
834 posts

Joined: Jun 2012
From: ~Heaven~


QUOTE(Kiding @ Dec 1 2012, 12:42 AM)
My house also get nuisance trip during thunder storm, I plan to change the TBC 100mA RCCB to Hager 100mA RCCB, would it help? and where to get the Hager RCCB?
*
Its normal for RCCB to trip during lightning strike, its nothing to do with rccb sensitivity, rccb trip due to current imbalance between live n neutral, to avoid rccb from tripping during lightning strike, use S-Type RCCB/anti nuisance rccb.

U can get at any hardware electrical shop...
jack~daniel
post Mar 26 2013, 08:16 AM

Enthusiast
*****
Senior Member
834 posts

Joined: Jun 2012
From: ~Heaven~


QUOTE(PJusa @ Dec 1 2012, 10:26 AM)
if your earth is good it *might* help. do note that in my personal opinion you dont need an ELCB at all if you decide to go higher than 30mA. Its no use. The ELCB is meant to save a humans life if they get into the circuit. If your cutoff level is already deadly why even bother with it? Either you do it properly or no need to do at all. If nobody gets inside the circuit you're pretty safe without an ELCB.
*
its nothing to do with good earth, but rccb must be connected to the earth in order for rccb to trip. RCBB installation is compulsory according to Malaysia regulation and some of british colonial country, most of the low voltage system adapted TT system. 30mA sensitivity is used for handheld equipment such as socket outlet, according to malaysia law, all scoket outlet must be connected to 30mA. For the main RCCB must use max 100mA sensitivity.

The question is , does 100mA can save the human live?, the answer is yes...please refer to iec 60479 for more details. Please note that rccb main function is to protect human being/livestock from indirect electrical shock, not from direct electrical shock.
jack~daniel
post Mar 26 2013, 08:29 AM

Enthusiast
*****
Senior Member
834 posts

Joined: Jun 2012
From: ~Heaven~


QUOTE(JinXXX @ Dec 1 2012, 10:13 PM)
can we buy and fix the RCCD ourself to replace my told ELCB ? 15 years no touch/change it..

or its better to recommend an "ƫlectrician" to fix it ?
*
Rccb/elcb must be tested at least once for every 2 years. If ELCB/RCCB is voltage operated, its compulsory to change to current operated. All the electrical installation must be installed by competent person according to malaysia law.

jack~daniel
post Mar 26 2013, 08:32 AM

Enthusiast
*****
Senior Member
834 posts

Joined: Jun 2012
From: ~Heaven~


QUOTE(Pennbattle @ Dec 2 2012, 12:19 AM)
My parent house happen too only when got lighting. Without lighting everything o.k. The house only 7 years. Any solution for me?
*
use RCCB + Autoreset. U also can use S type RCCB, but im not sure about the regulation because they didnt stated either G type or S type.
jack~daniel
post Mar 26 2013, 08:43 AM

Enthusiast
*****
Senior Member
834 posts

Joined: Jun 2012
From: ~Heaven~


QUOTE(Kiding @ Dec 2 2012, 12:36 AM)
Asking Hager 30mA RCCB around 5 shops in Puchong and Serdang, none of them carry 30mA, so just get the 100mA for RM80

I'm planing to install 30mA sensitivity RCBO to replace the MCB for the electric shower heater, is it better than install 30mA at the main switch?
*
RCBO normally is used for final circuit, not intended to be used for main circuit,

According to Malaysia regulation, for shower heater u must use 10mA sensitivity, but most of shower heater nowadays equipped with 10mA rccb.

Its not advisable to use 30mA for main circuit, it may cause nuisance tripping, u have to consider the leakage from the inductance load such as freeze, lighting,computer,air cond...for the equipment with energy saver, most of it contribute to high leakage current such as inverter aircond, computer & etc.
jack~daniel
post Mar 26 2013, 08:50 AM

Enthusiast
*****
Senior Member
834 posts

Joined: Jun 2012
From: ~Heaven~


QUOTE(Dennis126 @ Mar 14 2013, 09:36 AM)
has anybody used AOELEC Auto Reclosing (Resetting) RCCB before ?

How is the effectiveness ?

I understand it can auto rest 3 times and after the third time it has to be manually reset (for safety reason).
Can the resetting time be adjustable, ie to auto set after say 30 minutes it has tripped?

How much is the cost per unit ?

Thanks in advance.

dennis
Attached Image
*
Auto reset usually is used for industrial application, not for domestic application, but it doesnt matter since its not stated in the law.

Most of autoreset will fall under permanent trips after 3 times tripping in certain period, but its not for safety reason, its to differentiate whether it is nuisance tripping or permanent tripping.

30 minutes is too long, standard practice is 1 min for Malaysia because the lightning strike is frequent, most for the europe country is 3 sec.

For the ABB the cost is around RM800, but not reliable....

i would recommend mikimoto brand, but the price is twice than abb and more reliable.
jack~daniel
post Mar 26 2013, 08:55 AM

Enthusiast
*****
Senior Member
834 posts

Joined: Jun 2012
From: ~Heaven~


QUOTE(PJusa @ Mar 15 2013, 11:14 PM)
disconnecting an ELCB that cant by definition do what it should do because the threshold is too high is not silly. if the ELCB will only act AFTER its too late because its rating is too high what's the use? i can also place another spare on on top of my meter for the looks of it and it would have almost the same effect.
*
Please be remind that rccb main function is to protect from indirect contact, not for direct contact, even 300mA sensitivity still can protect from electrical shock.Please read iec 60479 for more details, its depend on the time to disconnect from the current and the magnitude of leakage current. Yes 10mA and 30mA can protect from direct electrical shock, but its not practical to use for the main circuit...
jovial
post Mar 28 2013, 07:43 AM

carpe diem
*******
Senior Member
2,129 posts

Joined: Jan 2003
From: Somewhere only we know..

QUOTE(PJusa @ Mar 15 2013, 11:14 PM)
disconnecting an ELCB that cant by definition do what it should do because the threshold is too high is not silly. if the ELCB will only act AFTER its too late because its rating is too high what's the use? i can also place another spare on on top of my meter for the looks of it and it would have almost the same effect.
*
ok, scenario..There's a short/earth leakage in the kettle. ELCB/RCCB detects it and turns off power. If the ELCB didn't work, you could have touched the kettle and electrocuted yourself.

scenario 2.. You touch a live wire and current starts flowing through you. Since it's electricity, your muscles seize and you can't let go. RCCB detects it and cuts off the power. 10mA flows through you compared to 10000mA.

The amount of of mA that it takes to kill you is very subjective. It depends on the path to ground. Whether it goes thru your heart or not etc.

This post has been edited by jovial: Mar 28 2013, 07:50 AM
teq
post Apr 9 2013, 05:35 PM

Casual
***
Junior Member
353 posts

Joined: Oct 2004


hi, I am facing rccb tripping during lightning.. currently using TBC 63A 100mA rccb..

I would like to try the Hager Anti Nuisance rccb.. may I know which model have the "Anti Nuisance" feature? or any Hager rccb are equipped with this feature?

Thank you.. smile.gif
ozak
post Apr 26 2013, 03:07 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(jialitrading @ Apr 26 2013, 02:00 PM)
Dear Ozak,

Mine to share where you bought this item?

What is it called?? I want to fix them for my water heater too.

Thanks
*
It is a RCD. Brand MK. Don't think can get it here and not selling anymore. Order it from UK 13yrs ago.
macgy
post Oct 18 2013, 12:44 PM

New Member
*
Junior Member
6 posts

Joined: Nov 2009
I am searching to increase the sensitivity of my RCCD to induce more frequent tripping and saw this forum...totally opposite of what i m looking for but here is my comment...Increasing RCCD beyond 100mA is dangerous, please avoid doing so, RCCD is installed to save lifes.
If it is due to lightning, a good surge protection device (SPD/TVSS) will be able to solve the problem, increase in surge will be absorb by the device, look for 1 with 10 modes protection if tripping is too frequent, otherwise 7 modes protection device is sufficient for a house and choose 1 with the longest warranty (rules of thumb..length of warranty=quality), my problem was sorted out...using an american brand, Sine Tamer. thumbup.gif
toh2020
post Dec 25 2013, 07:40 AM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
my rccd VL brande 100mA 63A provided by my developer keeps tripping especially lightning times.

i did a check on the life terminal to fuse switch 63A. I notice the incoming from TNB. the terminal is lose. u can slide up and down the life wire with slight force. when i dismantle the fuse switch. i saw inside connector clamp all purple. i presume this was bad installation from developer.

will this be the reason it cause the rccb to trip. if i tighten the wire connection will the prob solve.

thanks and appreciate the advice.
toh2020
post Dec 25 2013, 07:45 AM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
i check the tnb copper wire slightly darker. there are no arching marks on the wire and terminal of fuse switch. just the connectors on fuse switch turns purple. i sand paper life the tnb wire with protective glove to prevent electric shock. i already retighten the connection. i am currently monitor the situation.

under normal operating condition all appliances and lighting works perfectly fine for years. the tripping on rccb is only during lightnings. so long none of mcb trips at all.

anyone had observation this prob in nature cause rccb trips?

This post has been edited by toh2020: Dec 25 2013, 07:57 AM
stevie8
post Dec 25 2013, 10:28 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(toh2020 @ Dec 25 2013, 07:45 AM)
i check the tnb copper wire slightly darker. there are no arching marks on the wire and terminal of fuse switch. just the connectors on fuse switch turns purple. i sand paper life the tnb wire with protective glove to prevent electric shock. i already retighten the connection. i am currently monitor the situation.

under normal operating condition all appliances and lighting works perfectly fine for years. the tripping on rccb is only during lightnings. so long none of mcb trips at all.

anyone had observation this prob in nature cause rccb trips?
*
You are playing with high voltage live wires. This is the job for TNB, not even the developer. Wearing protective gloves is not enough, you should also wear rubber boots and a plastic or wooden stool/ladder on dry floor.

Loose cable can cause rccb to trip I had similar experience but I called TNB and they fixed it for free.
toh2020
post Dec 26 2013, 12:09 AM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
rubber shoes on top of wooden chair with rubber cushion on dry floor. forgot to mention that.
sovietmah
post Dec 26 2013, 03:06 PM

Look at all my stars!!
*******
Senior Member
2,243 posts

Joined: Nov 2005
my house at USJ 11 area.
always tripped when got thunderstorm.
i am using Hager ELCB 0.1mA.
Any idea if somethg that can reset back?
I am worry bout long holiday because i need electricity for my cctv and fridge.
toh2020
post Dec 26 2013, 04:50 PM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
what is the model of your ELCB? I presume should be RCCB for newer houses.
stevie8
post Dec 26 2013, 10:07 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(sovietmah @ Dec 26 2013, 03:06 PM)
my house at USJ 11 area.
always tripped when got thunderstorm.
i am using Hager ELCB 0.1mA.
Any idea if somethg that can reset back?
I am worry bout long holiday because i need electricity for my cctv and fridge.
*
Sometimes by changing to a new RCCD will solve the problem even with same brand and made. Even thunderstorm is far away it can affect the RCD to trip. if that is the case get it changed.

There are other causes like loose connection that increase and decrease the resistance and sometimes due to live or neutral wires touching some metal that linked the house like the plaster ceiling metal trusses that are usually connected to earth via the downlight reflector holder. Even if you call an electrician to check it will hell of a puzzle. But never change to higher rating even if being advised to lessen the sensitivity.
toh2020
post Dec 26 2013, 11:17 PM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
QUOTE(stevie8 @ Dec 26 2013, 10:07 PM)
Sometimes by changing to a new RCCD will solve the problem even with same brand and made. Even thunderstorm is far away it can affect the RCD to trip. if that is the case get it changed.

There are other causes like loose connection that increase and decrease the resistance and sometimes due to live or neutral wires touching some metal that linked the house like the plaster ceiling metal trusses that are usually connected to earth via the downlight reflector holder. Even if you call an electrician to check it will hell of a puzzle. But never change to higher rating even if being advised to lessen the sensitivity.
*
even big pure electrical shop nearby my area hardly can hardly get any 100mA rccb. due to demand and supply from the neighbourhood 300mA are selling like hot cakes. they said change your original from 100mA to 300mA solve your problems. most of my neighbours did that and they had no tripping problem especially lightnings.
stevie8
post Dec 27 2013, 01:44 AM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(toh2020 @ Dec 26 2013, 11:17 PM)
even big pure electrical shop nearby my area hardly can hardly get any 100mA rccb. due to demand and supply from the neighbourhood 300mA are selling like hot cakes. they said change your original from 100mA to 300mA solve your problems. most of my neighbours did that and they had no tripping problem especially lightnings.
*
No trip no protection, Already with 100ma you could be half dead. then don't use at all if tripping is the real problem, afterall it serves no real protection. There are many 30ma around not only 0.1ma except that it is more expensive. I am not being sarcastic, just that you mislead other people and it is an advice you ought to take.
toh2020
post Dec 27 2013, 10:02 AM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
QUOTE(stevie8 @ Dec 27 2013, 01:44 AM)
No trip no protection, Already with 100ma you could be half dead. then don't use at all if tripping is the real problem, afterall it serves no real protection. There are many 30ma around not only 0.1ma except that it is more expensive. I am not being sarcastic, just that you mislead other people and it is an advice you ought to take.
*
we all in the neighbourhood are told by dealer and local electrician that 300mA safer.

for my case i m monitoring current 100mA rccb and fuse switch after tightening. i update if there are updates.
ozak
post Dec 27 2013, 10:15 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 27 2013, 10:02 AM)
we all in the neighbourhood are told by dealer and local electrician that 300mA safer.

for my case i m monitoring current 100mA rccb and fuse switch after tightening. i update if there are updates.
*
You are mis inform. 300mA is not safer. You get short and the rccb is not easily trip. That's not call safer.

Lightning happen and the rccb not easily trip. That is call better.

100mA is more easily trip because it is more sensitive to detect minor fault. Which of course have problem with big bow of lightning. The easy and less cost way is just change it to 300mA. It still will trip but lesser.


toh2020
post Dec 27 2013, 12:38 PM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
QUOTE(ozak @ Dec 27 2013, 10:15 AM)
You are mis inform. 300mA is not safer. You get short and the rccb is not easily trip. That's not call safer.

Lightning happen and the rccb not easily trip. That is call better.

100mA is more easily trip because it is more sensitive to detect minor fault. Which of course have problem with big bow of lightning. The easy and less cost way is just change it to 300mA. It still will trip but lesser.
*
look like mass are misinformed. this make sense why those local electric shops had so much abundant stock of 300mA rccbs. the misinformed public in large perceive the solution was best way out. just like monkey see monkey do.

meaning the lesser the mA the better protection.

well I had my fuse switch replaced. as mention before due to loose contact with TNB L wire. the inner components are toasted but it had been working all while for years. here are the pictures. the connectors are all dark purple.


Attached Image Attached Image
ozak
post Dec 27 2013, 01:06 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 27 2013, 12:38 PM)
look like mass are misinformed. this make sense why those local electric shops had so much abundant stock of 300mA rccbs. the misinformed public in large perceive the solution was best way out. just like monkey see monkey do.

meaning the lesser the mA the better protection.

well I had my fuse switch replaced. as mention before due to loose contact with TNB L wire. the inner components are toasted but it had been working all while for years. here are the pictures. the connectors are all dark purple.
Attached Image Attached Image
*
The meaning of the number like 100mA or 300mA is how much the current detect will trip the rccb. Lower figure is safer.

The purple color is the constant hot temperature at the contact surface surrounding side. After long period of hot temperature, the material will change color. That show ..
1) A high current is flowing without sufficient surface contact between. Create a bottle neck at that place. This cost resistance and hot temperature occur.
2) Loose connection cost the electron hard to flow over within 2 contact. Occasionally some spark will happen. Resistance and hot temperature occur.

If you can, change that fuse holder to mcb type. Outside your house beside the meter is already have the fuse protect. (black square box) You don't need another fuse in the DB box. That is for the developer cut cost. MCB have better switch surface contact.

Just my bullshit CSI. He....

toh2020
post Dec 27 2013, 01:41 PM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
QUOTE(ozak @ Dec 27 2013, 01:06 PM)
The meaning of the number like 100mA or 300mA is how much the current detect will trip the rccb. Lower figure is safer.

The purple color is the constant hot temperature at the contact surface surrounding side. After long period of hot temperature, the material will change color. That show ..
1) A high current is flowing without sufficient surface contact between. Create a bottle neck at that place. This cost resistance and hot temperature occur.
2) Loose connection cost the electron hard to flow over within 2 contact. Occasionally some spark will happen. Resistance and hot temperature occur.

If you can, change that fuse holder to mcb type. Outside your house beside the meter is already have the fuse protect. (black square box) You don't need another fuse in the DB box. That is for the developer cut cost. MCB have better switch surface contact.

Just my bullshit CSI. He....
*
63A MCB? i had given thoughts about it. however my TNB L wire comes from bottom. Hence just nice to insert into INCOMING ONLY on the fuis switch from bottom up. while for MCB the L wire is not sufficient long to go on top of the incoming terminal. cause the wiring configuration is top down. which is reason i practically notice L wire shorter than N. cause the TNB N wire by defaults go to incoming N of RCCB from top which more longer.
ozak
post Dec 27 2013, 01:50 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 27 2013, 01:41 PM)
63A MCB? i had given thoughts about it. however my TNB L wire comes from bottom. Hence just nice to insert into INCOMING ONLY on the fuis switch from bottom up. while for MCB the L wire is not sufficient long to go on top of the incoming terminal. cause the wiring configuration is top down. which is reason i practically notice L wire shorter than N. cause the TNB N wire by defaults go to incoming N of RCCB from top which more longer.
*
Just put the MCB upside down. The look is same. Just the switch handle opposite.
toh2020
post Dec 27 2013, 02:06 PM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
QUOTE(ozak @ Dec 27 2013, 01:50 PM)
Just put the MCB upside down. The look is same. Just the switch handle opposite.
*
good suggestion.. biggrin.gif

since I already installed replaced the new fuse switch. might as well monitor till next thunderstorm.

I do believe there is loss of energy due to heat built up on old fuse switch. which causes in-balance in 2 way current all while. which why during lightings the tolerance no longer there.


toh2020
post Dec 27 2013, 02:09 PM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
btw any comment which is best rccb to date with anti-nuisance tripping. currently using this rccb. anyone had any comments or experiences on this VL rccb product provided by developer.

Attached Image
ycs
post Dec 27 2013, 02:55 PM

MEMBER
*******
Senior Member
4,232 posts

Joined: Jan 2003
From: Selangor



i also got tripping during lightning even far away

using ABB RCCB 100mA

This post has been edited by ycs: Dec 27 2013, 02:56 PM
stevie8
post Dec 27 2013, 08:47 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
I hv two. One 100ma for whole house, one 30ma for my koi pond. No tripping problem
ycs
post Dec 27 2013, 11:33 PM

MEMBER
*******
Senior Member
4,232 posts

Joined: Jan 2003
From: Selangor



QUOTE(stevie8 @ Dec 27 2013, 08:47 PM)
I hv two. One 100ma for whole house, one 30ma for my koi pond. No tripping problem
*
any particular reason in isolating the pond circuit?

i also happen to have a koi pond in the garden. could that be causing the tripping?
ozak
post Dec 28 2013, 12:13 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 27 2013, 02:09 PM)
btw any comment which is best rccb to date with anti-nuisance tripping. currently using this rccb. anyone had any comments or experiences on this VL rccb product provided by developer.

Attached Image
*
I remember abb have some device that can prevent trip from lightning. It just install beside the mcb.

Your rccb is fine. So for easy solution, just change it to 300mA.
stevie8
post Dec 28 2013, 12:48 AM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(ycs @ Dec 27 2013, 11:33 PM)
any particular reason in isolating the pond circuit?

i also happen to have a koi pond in the garden. could that be causing the tripping?
*
I did say no tripping problem, didn't I?

According to Fengshui, fire and water do not get along well. Electricity running the water pump being fire and pond is water it means danger. To double protect I added the 30ma RCD to the pond circuit.

When you have a pond you should have it protected with another RCD. Few years back there was news kid(s) killed playing water of a fountain but no further news on that what cause the electrocution. You see, without a sensitive RCD I will not dare touching the pond water. It is just like having a seat belt plus airbag driving. It is not if but when accident will happen.
toh2020
post Dec 28 2013, 09:53 AM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
QUOTE(ozak @ Dec 28 2013, 12:13 AM)
I remember abb have some device that can prevent trip from lightning. It just install beside the mcb.

Your rccb is fine. So for easy solution, just change it to 300mA.
*
you mentioned before 100mA should be safer. btw which model of ABB which deem popular?
ozak
post Dec 28 2013, 11:49 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 28 2013, 09:53 AM)
you mentioned before 100mA should be safer. btw which model of ABB which deem popular?
*
This --> "So for easy solution"

For proper way, that cost you a lot. Try check at ABB site.
stevie8
post Dec 29 2013, 09:48 PM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(ycs @ Dec 27 2013, 11:33 PM)
any particular reason in isolating the pond circuit?

i also happen to have a koi pond in the garden. could that be causing the tripping?
*
By the way, if you suspect your koi pond is causing the trip, you better don't touch the water.
ozak
post Dec 30 2013, 12:19 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(stevie8 @ Dec 29 2013, 09:48 PM)
By the way, if you suspect your koi pond is causing the trip, you better don't touch the water.
*
Ain't the fish already belly up?
stevie8
post Dec 30 2013, 12:39 AM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
QUOTE(ozak @ Dec 30 2013, 12:19 AM)
Ain't the fish already belly up?
*
It will not unless there is a connection/leaked to earth. The pond water is contained or isolated in the pond so when there is no earth (current got nowhere to go) it is not passing any bodies just like birds sitting on overhead live wires and dont die and fall.

You can put a bulb in a glass water tank and a +ve live wire, the bulb wont light up. You use a test pen tip touching a house live wire and your finger at the other end of the test pen (like you used to test for live current) and you are wearing rubber shoes, the test pen hard to get light up becuase there is no proper connection to earth but when you touch something like a concrete wall the test pen lights up without hesitation brows.gif Dont play play
stevie8
post Dec 30 2013, 02:15 AM

Regular
******
Senior Member
1,365 posts

Joined: Jun 2009
The word is dont touch the water. You can jump into the water and still live. Touch die, jump no die.
toh2020
post Dec 30 2013, 12:42 PM

Casual
***
Junior Member
493 posts

Joined: Apr 2011
QUOTE(ozak @ Dec 28 2013, 11:49 AM)
This --> "So for easy solution"

For proper way, that cost you a lot. Try check at ABB site.
*
how much will they cost me. Care to share with me reference price tag? Whereabouts to get great deals at reasonable prices.
biatche
post Aug 13 2014, 10:10 PM

Regular
******
Senior Member
1,649 posts

Joined: Jan 2003
Hello good people, am reviving an old thread.

user posted image

We've had this for 15 years. Whenever there's lightning, even in the far distance (a thunder as loud as a silent fart), a trip can happen. Can't quite remember anymore if this has been happening since the very beginning or if it's gradual. One thing that's for sure is I'm pretty tired of it.

So if we do have wiring leakage, by changing 'technologies' (some modern RCD?) will it help? Or irregardless of what circuit breaker we use, is it advisable to fix leaks anyway? My imagination tells me that trying to figure out where leaks are is no sane task.

What's the current contemporary recommended ELCB/ELCB-like device?

I've also posted in: http://cr4.globalspec.com/thread/97138

This post has been edited by biatche: Aug 13 2014, 10:30 PM
babie
post Oct 22 2014, 09:58 AM

New Member
*
Junior Member
46 posts

Joined: Apr 2006
anyone know where to get a rccb auto recloser that can be set to 10 minutes or more?
SUSsupersound
post Oct 22 2014, 02:29 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(babie @ Oct 22 2014, 09:58 AM)
anyone know where to get a rccb auto recloser that can be set to 10 minutes or more?
*
Usually I will prefer manual reset ELCB, as when ELCB trips, it show something wrong. Is better to make sure all appliance are intact before reset. This is for safety.
cherroy
post Oct 22 2014, 02:32 PM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(babie @ Oct 22 2014, 09:58 AM)
anyone know where to get a rccb auto recloser that can be set to 10 minutes or more?
*
Whenever RCCB/ELCB trips, it means something is not right in the circuit, and may require manual attention.

Auto-closed reset is defying the safety purpose of RCCB/ELCB.
Sawamura
post Oct 22 2014, 08:59 PM

Casual
***
Junior Member
323 posts

Joined: Aug 2005
From: KL



I dont understand why people feel tripping is a nuisance..

Its for protection, and tripping actually proves your protection works.

Could be from the surge also..

Since 100A would also trip, then change back to 30A..

With regards to koi pond using 30A, I believe (apart from fengshui POV) it is to protect your pump motor..


keyz
post Nov 2 2014, 04:25 PM

Regular
Group Icon
VIP
1,271 posts

Joined: Jan 2003
From: Terengganu


QUOTE(babie @ Oct 22 2014, 09:58 AM)
anyone know where to get a rccb auto recloser that can be set to 10 minutes or more?
*
Get DUVALĀ® Motorised Multi Auto Recloser with Type "AI" RCCB (DAR 330)

DUVALĀ® Motorised Multi Auto Recloser with Type "AI" RCCB - See more at: http://www.cornerstone.com.my/lvcontrol/in...h.whlu1Xtz.dpuf

Info taken from this 2012 thread:

Auto Power Reset and Surge Protector Review

You can see the test video here:

RCCB auto reset video
keyz
post Jun 14 2015, 11:09 AM

Regular
Group Icon
VIP
1,271 posts

Joined: Jan 2003
From: Terengganu


I bump this thread because I have similar problem & sharing the info might give benefit to others.

I made a research & I came across suggestion to use less sensitive RCCB. To use RCCB with "HI" type - i.e. High Immunity.

So..I bought one from forumer here, brand HAGER. Installed in Nov 2014.

As this year, no thunderstorm observed. Only 2 days back I considered very significant & can cause my RCCB to trip using the previous type.

I can conclude it does it job very well, as designed to do so.

user posted image
SUSsupersound
post Jun 14 2015, 12:36 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(keyz @ Jun 14 2015, 11:09 AM)
I bump this thread because I have similar problem & sharing the info might give benefit to others.

I made a research & I came across suggestion to use less sensitive RCCB. To use RCCB with "HI" type - i.e. High Immunity.

So..I bought one from forumer here, brand HAGER. Installed in Nov 2014.

As this year, no thunderstorm observed. Only 2 days back I considered very significant & can cause my RCCB to trip using the previous type.

I can conclude it does it job very well, as designed to do so.

user posted image
*
When you have your ELCB tripped, you need to start do some basic troubleshooting.
And not directly changing it to less sensitive type. What if you really have an appliance that having problem?
keyz
post Jun 14 2015, 12:46 PM

Regular
Group Icon
VIP
1,271 posts

Joined: Jan 2003
From: Terengganu


QUOTE(supersound @ Jun 14 2015, 12:36 PM)
When you have your ELCB tripped, you need to start do some basic troubleshooting.
And not directly changing it to less sensitive type. What if you really have an appliance that having problem?
*
Troubleshooting already done. Disconnect all electrical appliances & observe still tripping. So, no electrical appliance problem. Them call electrician to check. He verified all connection & safety protection, earth cable in good shape. He said in one area, not all house will trip at the same time. As electrician he observe similar case. Details explained to me but I don't understand.
SUSsupersound
post Jun 14 2015, 12:48 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(keyz @ Jun 14 2015, 12:46 PM)
Troubleshooting already done. Disconnect all electrical appliances & observe still tripping. So, no electrical appliance problem. Them call electrician to check. He verified all connection & safety protection, earth cable in good shape. He said in one area, not all house will trip at the same time. As electrician he observe similar case. Details explained to me but I don't understand.
*
Interesting. But how long you stay in this house?
BTW, there's something we never do all the time, which is taking out that outdoor rod and have a check on it sweat.gif
Like last time I work in O&G company, they have schedule to to a test on the copper rod.

This post has been edited by supersound: Jun 14 2015, 12:49 PM
wodenus
post Jun 14 2015, 12:51 PM

Tree Octopus
********
All Stars
14,990 posts

Joined: Jan 2003
QUOTE(supersound @ Jun 14 2015, 12:48 PM)
Interesting. But how long you stay in this house?
BTW, there's something we never do all the time, which is taking out that outdoor rod and have a check on it sweat.gif
Like last time I work in O&G company, they have schedule to to a test on the copper rod.
*
In homes the outdoor rod is buried in the ground I think smile.gif
SUSsupersound
post Jun 14 2015, 12:52 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(wodenus @ Jun 14 2015, 12:51 PM)
In homes the outdoor rod is buried in the ground I think smile.gif
*
Yes, indeed it is buried in the ground.
That's why we need to do a visual check.
wodenus
post Jun 14 2015, 01:06 PM

Tree Octopus
********
All Stars
14,990 posts

Joined: Jan 2003
QUOTE(supersound @ Jun 14 2015, 12:52 PM)
Yes, indeed it is buried in the ground.
That's why we need to do a visual check.
*
Don't you have to dig it out or something? smile.gif
SUSsupersound
post Jun 14 2015, 01:07 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(wodenus @ Jun 14 2015, 01:06 PM)
Don't you have to dig it out or something? smile.gif
*
If it is something needs to be done, it has to be done. Doing some dirty digging works is tedious or getting a house burnt down is tedious?
wodenus
post Jun 14 2015, 01:10 PM

Tree Octopus
********
All Stars
14,990 posts

Joined: Jan 2003
QUOTE(supersound @ Jun 14 2015, 01:07 PM)
If it is something needs to be done, it has to be done. Doing some dirty digging works is tedious or getting a house burnt down is tedious?
*
We just switched everything electric over to electronic. Seems to have solved the problem. Also I have been electrocuted before, it's no big deal smile.gif

Fazab
post Jun 20 2015, 12:54 AM

On my way
****
Senior Member
519 posts

Joined: Jun 2011


Hi sifus

My new house RCCB 63A 0.1A tripping randomly.
Did the usual diagnosis and trace the problem to one line supplying the front lights.
When the MCB (6A) for this in ON, cannot reset the RCCB, trips immediately.
When I OFF this MCB, then only can reset the RCCB.
After sometime however can reset back with that MCB ON.

The problem is transient, sekejap ada, sekejap OK.

The faulty line has a timer switch, which I thought was causing the problem, so call back the wireman.

He checked and found that the one line is carrying 33 light points (including 16 T5s and 10 mLED downlights) and 1 fan. rclxub.gif rclxub.gif rclxub.gif
But I very seldom on everything. usually max 7-10 lights only.

He thinks it overload, and 'partition' some load over to the nearby 20A MCB. Don't know what it means.

But the RCCB still trips randomly. Although now can reset.

Any ideas how to approach? I suspect some wire are overheating, that why after a while cooling down the problem goes away, only to happen again later.
ozak
post Jun 20 2015, 03:55 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Fazab @ Jun 20 2015, 12:54 AM)
Hi sifus

My new house RCCB 63A 0.1A  tripping randomly.
Did the usual diagnosis and trace the problem to one line supplying the front lights.
When the MCB (6A) for this in ON, cannot reset the RCCB, trips immediately.
When I OFF this MCB, then only can reset the RCCB. 
After sometime however can reset back with that MCB ON.

The problem is transient, sekejap ada, sekejap OK.

The faulty line has a timer switch, which I thought was causing the problem, so call back the wireman.

He checked and found that the one line is carrying 33 light points (including 16 T5s and 10 mLED downlights) and 1 fan.  rclxub.gif  rclxub.gif  rclxub.gif
But I very seldom on everything. usually max 7-10 lights only.

He thinks it overload, and 'partition' some load over to the nearby 20A MCB. Don't know what it means.

But the RCCB still trips randomly. Although now can reset.

Any ideas how to approach?  I suspect some wire are overheating, that why after a while cooling down the problem goes away, only to happen again later.
*
RCCB trip is telling you that something is shortcircuit. But not overload. If it overload, the MCB through that line will trip.

Since you able to isolate the problem and only that line cause the trip, it is much more easy to troubleshoot. But your electrician diagnose wrongly. Since all the light and electrical thing able to ON without cause the MCB trip, that mean there is no overload on that line.

For the shortcircuit, you have to look at the lighting, timer, fan, etc on that line. There is something faulty there. But which 1. So you need to further isolated those thing to 1 by 1 or by the switching group. ON 1 switch at a time and see will it trip. If no, than OFF it and proceed another switch ON. Till you find that cause tripping.

If this group of light cause tripping, than need to further isolate which light is cause the trip. You need to disconnect the light 1 by 1 and try to ON to find that spoil 1 that cause the trip.
DMegaMall
post Jul 6 2015, 12:25 PM

New Member
*
Newbie
2 posts

Joined: Oct 2012
From: Tropicana City Mall, Petaling Jaya.


Hi, my house is having the the same issue during thunderstom, my RCCB will always trip even on a minor "lightning", thinking of changing the RCCB, should I change to 30mA/100mA or 300mA? Which one is less sensitive to lightning?
Kiding
post Jul 6 2015, 09:45 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(DMegaMall @ Jul 6 2015, 12:25 PM)
Hi, my house is having the the same issue during thunderstom, my RCCB will always trip even on a minor "lightning", thinking of changing the RCCB, should I change to 30mA/100mA or 300mA? Which one is less sensitive to lightning?
*
Start reading from post #97 onward !
gagak_84
post Dec 13 2015, 10:26 PM

Getting Started
**
Junior Member
132 posts

Joined: Dec 2008
From: Seremban, Port Dickson


guys.. need some help..

my new house RCCB always trip during raining.

incomer from TNB goes to this
R,Y,B = 32A,415V and 10kA
looks like SPD but no earthing pole from this one

outgoing goes to RCCB in which the specs is
63A 415V 100mA

im thinking to change the RCCB with good brand such as ABB with same specs.
if the same thing happen i would install new SPD with earthing pole

another thing is my neutral terminal at DB box doesnt jump to earting terminal, i saw some videos and most of it jumped together.


gagak_84
post Dec 13 2015, 11:13 PM

Getting Started
**
Junior Member
132 posts

Joined: Dec 2008
From: Seremban, Port Dickson


Attached Image

is it normal 32A fuse for each phase goes to 63A RCCB? why dont used 63A fuse instead

This post has been edited by gagak_84: Dec 14 2015, 02:42 PM
ozak
post Dec 14 2015, 10:39 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(gagak_84 @ Dec 13 2015, 10:26 PM)
guys.. need some help..

my new house RCCB always trip during raining.

incomer from TNB goes to this
R,Y,B = 32A,415V and 10kA
looks like SPD but no earthing pole from this one

outgoing goes to RCCB in which the specs is
63A 415V 100mA

im thinking to change the RCCB with good brand such as ABB with same specs.
if the same thing happen i would install new SPD with earthing pole

another thing is my neutral terminal at DB box doesnt jump to earting terminal, i saw some videos and most of it jumped together.
*
RCCB is not the problem. It work fine. RCCB is not using earth to trip cause it is not a ELCB.

You have 3 choice to reduce the trip.

1) change the RCCB to less sensitive to 300mA or 0.3A. But will delay the trip if any short circuit.
2) Install a surge protector to absorb the surge voltage. It will channel the surge to earth. So your earth rod need to be good.
3) Check the earth rod infront your garden. The checking is in Ohm which less ohm is better. (below 100ohm)


weikee
post Dec 14 2015, 11:27 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
If your RCCB trip, mean you have leakage.

During rainy day water may have enter some wiring and water conduct electric, so the electric current are leak thought the water.
jackbanner
post Dec 15 2015, 10:56 AM

On my way
****
Senior Member
660 posts

Joined: Jun 2009
Wher did u buy the Sine Tamer?


QUOTE(macgy @ Oct 18 2013, 12:44 PM)
I am searching to increase the sensitivity of my RCCD to induce more frequent tripping and saw this forum...totally opposite of what i m looking for but here is my comment...Increasing RCCD beyond 100mA is dangerous, please avoid doing so, RCCD is installed to save lifes.
If it is due to lightning, a good surge protection device (SPD/TVSS) will be able to solve the problem, increase in surge will be absorb by the device, look for 1 with 10 modes protection if tripping is too frequent, otherwise 7 modes protection device is sufficient for a house and choose 1 with the longest warranty (rules of thumb..length of warranty=quality), my problem was sorted out...using an american brand, Sine Tamer. thumbup.gif
*
jackbanner
post Dec 15 2015, 12:29 PM

On my way
****
Senior Member
660 posts

Joined: Jun 2009
Have u solved this problem?
If u have, how did u do it?


QUOTE(Fazab @ Jun 20 2015, 12:54 AM)
Hi sifus

My new house RCCB 63A 0.1A  tripping randomly.
Did the usual diagnosis and trace the problem to one line supplying the front lights.
When the MCB (6A) for this in ON, cannot reset the RCCB, trips immediately.
When I OFF this MCB, then only can reset the RCCB. 
After sometime however can reset back with that MCB ON.

The problem is transient, sekejap ada, sekejap OK.

The faulty line has a timer switch, which I thought was causing the problem, so call back the wireman.

He checked and found that the one line is carrying 33 light points (including 16 T5s and 10 mLED downlights) and 1 fan.  rclxub.gif  rclxub.gif  rclxub.gif
But I very seldom on everything. usually max 7-10 lights only.

He thinks it overload, and 'partition' some load over to the nearby 20A MCB. Don't know what it means.

But the RCCB still trips randomly. Although now can reset.

Any ideas how to approach?  I suspect some wire are overheating, that why after a while cooling down the problem goes away, only to happen again later.
*
gagak_84
post Dec 15 2015, 03:46 PM

Getting Started
**
Junior Member
132 posts

Joined: Dec 2008
From: Seremban, Port Dickson


QUOTE(ozak @ Dec 14 2015, 10:39 PM)
RCCB is not the problem. It work fine. RCCB is not using earth to trip cause it is not a ELCB.

You have 3 choice to reduce the trip.

1) change the RCCB to less sensitive to 300mA or 0.3A. But will delay the trip if any short circuit.
2) Install a surge protector to absorb the surge voltage. It will channel the surge to earth. So your earth rod need to be good.
3) Check the earth rod infront your garden. The checking is in Ohm which less ohm is better. (below 100ohm)
*
on no 3, how to check the ohm on the rod i saw someone said Hager and schneider RCCB equipped by anti-storm protection.. is that true??

Thinking of to change my current RCCB with this one

user posted image

This post has been edited by gagak_84: Dec 15 2015, 03:59 PM
ozak
post Dec 15 2015, 04:09 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(gagak_84 @ Dec 15 2015, 03:46 PM)
on no 3, how to check the ohm on the rod i saw someone said Hager and schneider RCCB equipped by anti-storm protection.. is that true??

Thinking of to change my current RCCB with this one

user posted image
*
The earth rod only can be check with earth meter. Which some electrician have.

You can try to change. But the 0.1A is sensitive. It still will trip. But lesser.
gagak_84
post Dec 15 2015, 04:28 PM

Getting Started
**
Junior Member
132 posts

Joined: Dec 2008
From: Seremban, Port Dickson


can i check whether my equipment have earth leakage at DB box..
which i check whether earthing din-rail has live current using test pen
ozak
post Dec 15 2015, 04:39 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(gagak_84 @ Dec 15 2015, 04:28 PM)
can i check whether my equipment have earth leakage at DB box..
which i check whether earthing din-rail has live current using test pen
*
Leave it to the electrician to check if you not experience.

Electric can kill. Don't touch if you really not sure.

Your house is running 3P. Phase to phase is 415V. It is dangerous.
Kiding
post Dec 26 2015, 12:18 AM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


I'm interesting in this ABB OVR T2 SPD (http://new.abb.com/products/ABB2CTB802341R8000), planing to install it in the DB

user posted image

I'm wondering will it reduce the frequent RCCB trip when lighting hit nearby my house, I stay at the hill top, whenever lightning hit nearby, it is very high chance the RCCB will trip!
sonerin
post Dec 26 2015, 08:07 AM

Look at all my stars!!
*******
Senior Member
8,739 posts

Joined: Aug 2009
QUOTE(Kiding @ Dec 26 2015, 12:18 AM)
I'm interesting in this ABB OVR T2 SPD (http://new.abb.com/products/ABB2CTB802341R8000), planing to install it in the DB

user posted image

I'm wondering will it reduce the frequent RCCB trip when lighting hit nearby my house, I stay at the hill top, whenever lightning hit nearby, it is very high chance the RCCB will trip!
*
Is better to go for hager brand on lighting surge protector
keyz
post Jan 6 2016, 01:31 PM

Regular
Group Icon
VIP
1,271 posts

Joined: Jan 2003
From: Terengganu


QUOTE(Kiding @ Dec 26 2015, 12:18 AM)
I'm interesting in this ABB OVR T2 SPD (http://new.abb.com/products/ABB2CTB802341R8000), planing to install it in the DB

I'm wondering will it reduce the frequent RCCB trip when lighting hit nearby my house, I stay at the hill top, whenever lightning hit nearby, it is very high chance the RCCB will trip!
*
Mine also installed with SPD (installed 2015-09-19). Ever since, Only one time there is quite heavy lightning strike as reported by my wife but RCCB didn't trip.

user posted image


Kiding
post Jan 6 2016, 07:49 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(keyz @ Jan 6 2016, 01:31 PM)
Mine also installed with SPD (installed 2015-09-19). Ever since, Only one time there is quite heavy lightning strike as reported by my wife but RCCB didn't trip.

user posted image
*
How much you paid for the SPD devices and installation? I'm tired of the nuisance trip, it has been 3 times for last 30 days cry.gif
keyz
post Jan 6 2016, 08:11 PM

Regular
Group Icon
VIP
1,271 posts

Joined: Jan 2003
From: Terengganu


QUOTE(Kiding @ Jan 6 2016, 07:49 PM)
How much you paid for the SPD devices and installation? I'm tired of the nuisance trip, it has been 3 times for last 30 days  cry.gif
*
SPD Class 2 (for 3 phase) - RM477 incl. GST
Installation RM150 - local electrician. This installation cost include SPD & auto Reset RCCB.
macgy
post May 13 2016, 05:55 PM

New Member
*
Junior Member
6 posts

Joined: Nov 2009
Didn't realised this topic is still alive! i have recommended the use of SPD more than 2 years ago, now that another person has recommended to installed SPD, TAKE HIS ADVICE, THAT WILL RESOLVE THE TRIPPING PROBLEM provided if tripping is caused by LIGHTNING!, I have never experience anymore tripping since 2 years ago even during heavy thunder storm.
when install the SPD ..must ask the installer to install before the RCCB, if they say cannot, don't buy!
mine comes with 15 year unlimited warranty but they r more expensive but definitely worth it knowing that i won't encounter smelly and rotten food in my fridge when i come back from outstation because of the nuisance tripping!
clickNsnap
post May 13 2016, 11:40 PM

On my way
****
Junior Member
541 posts

Joined: Jun 2006


QUOTE(keyz @ Jan 6 2016, 09:11 PM)
SPD Class 2 (for 3 phase) - RM477 incl. GST
Installation RM150 - local electrician. This installation cost include SPD & auto Reset RCCB.
*
Hi,

Can please provide me the installer/electrician phone number and may I know where did you buy the SPD & auto Reset RCCB?

Btw, my house uses 1 phase only.

Thanks in advance! thumbup.gif

This post has been edited by clickNsnap: May 13 2016, 11:40 PM
keyz
post May 14 2016, 12:12 AM

Regular
Group Icon
VIP
1,271 posts

Joined: Jan 2003
From: Terengganu


QUOTE(clickNsnap @ May 13 2016, 11:40 PM)
Hi,

Can please provide me the installer/electrician phone number and may I know where did you buy the SPD & auto Reset RCCB?

Btw, my house uses 1 phase only.

Thanks in advance!  thumbup.gif
*
For electrician phone you can get from local shop which supply electrical part for contractor, not shop which selling electrical appliances. They do leave the business card number.

For SPD & auto RCCB I bought from L.V Control Technologies SB. 03-80112999. Mr. Alan Chua (alan@lvcontrol.com.my)

L.V.CONTROL TECHNOLOGIES SDN.BHD
No.3, Twin Park
Jalan Subang 7/1
Taman Perindustrian Subang USJ 1
47600 Subang Jaya
clickNsnap
post May 14 2016, 12:23 AM

On my way
****
Junior Member
541 posts

Joined: Jun 2006


QUOTE(keyz @ May 14 2016, 01:12 AM)
For electrician phone you can get from local shop which supply electrical part for contractor, not shop which selling electrical appliances. They do leave the business card number.

For SPD & auto RCCB I bought from L.V Control Technologies SB. 03-80112999. Mr. Alan Chua (alan@lvcontrol.com.my)

L.V.CONTROL TECHNOLOGIES SDN.BHD
No.3, Twin Park
Jalan Subang 7/1
Taman Perindustrian Subang USJ 1
47600 Subang Jaya
*
Thanks a million!

My house will trip, if heavy rain with loud thunder storm... hope install the SPD & auto RCCB will helps.
Kiding
post May 14 2016, 12:54 AM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


ABB OVR T2 SPD ordered from Taobao finally arrived, surprisingly it is imported from France, I though it is made in China blink.gif

Just install it myself at the location before RCCB and after the main switch, hopefully it will prevent the RCCB to trip during lightning.
Richard
post May 14 2016, 10:31 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Kiding @ May 14 2016, 12:54 AM)
ABB OVR T2 SPD ordered from Taobao finally arrived, surprisingly it is imported from France, I though it is made in China  blink.gif

Just install it myself at the location before RCCB and after the main switch, hopefully it will prevent the RCCB to trip during lightning.
*
Can you take a photo of your Surge Protection Device (SPD) and the installation..

I can help you confirm if it is correct..


Kiding
post May 14 2016, 11:30 AM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(Richard @ May 14 2016, 10:31 AM)
Can you take a photo of your Surge Protection Device (SPD) and the installation..

I can help you confirm if it is correct..
*
Hager is the RCCB, ABB is the SPD

Attached Image
Coconut
post May 14 2016, 01:29 PM

Regular
******
Senior Member
1,268 posts

Joined: Jan 2003


Yes abb spd still made in France. How much you bought from taobao? A lot of savings compare to buy local?
Kiding
post May 14 2016, 01:56 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(Coconut @ May 14 2016, 01:29 PM)
Yes abb spd still made in France. How much you bought from taobao? A lot of savings compare to buy local?
*
I bought it around RM430, local seller quote me RM800+, my.rs-online.com selling around RM680
Richard
post May 14 2016, 03:46 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Kiding @ May 14 2016, 11:30 AM)
Hager is the RCCB, ABB is the SPD

Attached Image
*
Yes.. Except you should be using black(N) from RCD to the neutral bar, grn/yellow(E) from SPD to Earth bar..

All the main cables size looks to be 10mm2 or larger so it's all good.. A bit of cable management would help make things look a lot better too..

This post has been edited by Richard: May 14 2016, 04:00 PM
Kiding
post May 14 2016, 06:04 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(Richard @ May 14 2016, 03:46 PM)
Yes.. Except you should be using black(N) from RCD to the neutral bar, grn/yellow(E) from SPD to Earth bar..

All the main cables size looks to be 10mm2 or larger so it's all good.. A bit of cable management would help make things look a lot better too..
*
Yes, I know it does not follow proper wire color codes, because I went to three electrical shops, only one shop selling 10 mm^2 and 16 mm^2 by meter, and only black color is available, the RCD wiring was done by developer, I can see they didn't follow the color code either in some place at my house.

Actually I tried to use 16 mm^2 but I realized I couldn't use it as it is too big to fit in, so only 10 mm^2 wires are used.
Richard
post May 14 2016, 07:34 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Kiding @ May 14 2016, 06:04 PM)
Yes, I know it does not follow proper wire color codes, because I went to three electrical shops, only one shop selling 10 mm^2 and 16 mm^2 by meter, and only black color is available, the RCD wiring was done by developer, I can see they didn't follow the color code either in some place at my house.

Actually I tried to use 16 mm^2 but I realized I couldn't use it as it is too big to fit in, so only 10 mm^2 wires are used.
*
ok.. but i would replace both 63A DP isolator/RCD with 40A if you're really looking for thermal protection the 10mm2..
clickNsnap
post May 20 2016, 03:03 PM

On my way
****
Junior Member
541 posts

Joined: Jun 2006


QUOTE(Richard @ May 14 2016, 08:34 PM)
ok.. but i would replace both 63A DP isolator/RCD with 40A if you're really looking for thermal protection the 10mm2..
*
Hi, My DB seem a bit small, any possible to add SPD? Thanks.

This post has been edited by clickNsnap: May 20 2016, 03:05 PM


Attached thumbnail(s)
Attached Image Attached Image
Kiding
post May 20 2016, 11:32 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(clickNsnap @ May 20 2016, 03:03 PM)
Hi, My DB seem a bit small, any possible to add SPD? Thanks.
*
It looks like running out of space, may need to change the DB box and add additional trail.
clickNsnap
post May 21 2016, 01:20 AM

On my way
****
Junior Member
541 posts

Joined: Jun 2006


QUOTE(Kiding @ May 21 2016, 12:32 AM)
It looks like running out of space, may need to change the DB box and add additional trail.
*
Change to a bigger DB and add SPD... redo all the wires... cost a lot? moneyflies.gif moneyflies.gif moneyflies.gif Can the SPD installed "outside" next to the old DB with a separate small DB or box? hmm.gif

This post has been edited by clickNsnap: May 21 2016, 01:20 AM
keyz
post May 21 2016, 10:31 AM

Regular
Group Icon
VIP
1,271 posts

Joined: Jan 2003
From: Terengganu


QUOTE(clickNsnap @ May 20 2016, 03:03 PM)
Hi, My DB seem a bit small, any possible to add SPD? Thanks.
*
Use 2ndary board with distance less than 50cm . Like this example:

Attached Image


Richard
post May 24 2016, 09:04 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(clickNsnap @ May 20 2016, 03:03 PM)
Hi, My DB seem a bit small, any possible to add SPD? Thanks.
*
The function of a surge protection device is to prevent a sudden Surge of Voltage from damaging your electronics by providing a path of least resistance to ground.. a protection against lightning strikes to overhead electrical lines and or from bad earth rods (which picks from impact zones and carries the voltage surges to your box) .

Only if this is the case then you can install it anywhere from your kwh meter cables to your distribution box.. A common practice is to install inside the DB but its not the only way to have it installed..

You can have it installed in its own enclosure after the kwh meter at any point before the DB (thus the equipment to be protected)... connect all phase/neutral cables to the SPD and connect SPD to a known good ground. (Ground rod reading below One Ohm)..


clickNsnap
post May 25 2016, 08:59 PM

On my way
****
Junior Member
541 posts

Joined: Jun 2006


QUOTE(keyz @ May 21 2016, 11:31 AM)
Use 2ndary board with distance less than 50cm . Like this example:

Attached Image
*
Thanks! keyz. Most likely I will having the same set-up as your picture.

QUOTE(Richard @ May 24 2016, 10:04 PM)
The function of a surge protection device is to prevent a sudden Surge of Voltage from damaging your electronics by providing a path of least resistance to ground.. a protection against lightning strikes to overhead electrical lines and or from bad earth rods (which picks from impactĀ  zones and carries the voltage surges to your box) .

Only if this is the case then you can install it anywhere from your kwh meter cables to your distribution box.. A common practice is to install inside the DB but its not the only way to have it installed..

You can have it installed in its own enclosure after the kwh meter at any point before the DB (thus the equipment to be protected)... connect all phase/neutral cables to the SPD and connect SPD to a known good ground. (Ground rod reading below One Ohm)..
*
Thanks! Richard. I will ask electrician to install the SPD for me and help to check my house has good grounding or not hmm.gif (I don't think I can install it myself, you are good and able to fix it yourself thumbsup.gif )

Btw, I snapped a picture when my contract installing the ground rob in front of the garden, the copper rod was about 10 feet long, with diameter of 1.0 - 1.5 cm.

This post has been edited by clickNsnap: May 25 2016, 09:02 PM


Attached thumbnail(s)
Attached Image
Jason
post May 26 2016, 09:07 PM

Look at all my stars!!
*******
Senior Member
6,355 posts

Joined: Jan 2003
Seems many experts here, maybe I can get some insight from you guys.

My terrace house is ~30 years old, and it always trip at the slightest lightning strikes. Even when my neighbour right next door don't trip. How do I reduce this?

The house got this installed, and as you can see its very old, I assume its an ELCB. Would upgrading this to a RCCB help? Or would it become more sensitive over time (deteriorating components inside).

user posted image
Richard
post May 27 2016, 07:37 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Jason @ May 26 2016, 09:07 PM)
Seems many experts here, maybe I can get some insight from you guys.

My terrace house is ~30 years old, and it always trip at the slightest lightning strikes. Even when my neighbour right next door don't trip. How do I reduce this?

The house got this installed, and as you can see its very old, I assume its an ELCB. Would upgrading this to a RCCB help? Or would it become more sensitive over time (deteriorating components inside).

user posted image
*
First off.. Please be aware you are expected to rewire your house after 20-30 years..

The main reason is the wire pvc insulation degrades as it gets older and if pvc is exposed to heat it degrades even faster.. Old pvc becomes brittle and its insulation property changes from being an insulator to becoming partly conductive..

So once you mention 30 year old house, any wireman will automatically go hmm old wire.. many shorts.. many trips better ask him rewire his house..

So if you ask me..

I 'll say hmm.. 30 years old house, old pvc wire => bad insulation everywhere +> sure many tripping..

Nothing wrong with your elcb (even if its old, but I would change it anyway), but the newer standard is rcd (residual current device) eg. rccb or rcbo they work the same..
Jason
post May 28 2016, 12:40 AM

Look at all my stars!!
*******
Senior Member
6,355 posts

Joined: Jan 2003
Thank you for your input. Guess if its not broken, don't fix it. Cause apart from being more sensitive, nothing else is wrong.
ozak
post May 28 2016, 06:32 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Jason @ May 28 2016, 12:40 AM)
Thank you for your input. Guess if its not broken, don't fix it. Cause apart from being more sensitive, nothing else is wrong.
*
It is sometime not cause by the elcb.

The surge go through the old wire and trip it. You can try to replace the elcb to new 1.

If problem still happen, time to change the wiring.
Richard
post May 28 2016, 07:24 PM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Jason @ May 28 2016, 12:40 AM)
Thank you for your input. Guess if its not broken, don't fix it. Cause apart from being more sensitive, nothing else is wrong.
*
oops .. if i wasn't clear I mean check your house wiring ..

It's an old house thus maybe you have old pvc wiring leaking ac currents making the elcb trip..

The elcb doesn't get more sensitive, its the old wiring that is leaking curent to earth making the elcb trip..

The elcb is probably less sensitive not more sensitive (its old it gets worse never better), you have bad wiring..

Please bro.. get it checked..
enduser
post May 28 2016, 09:56 PM

Regular
******
Senior Member
1,280 posts

Joined: Jan 2003
QUOTE(Jason @ May 26 2016, 09:07 PM)
Seems many experts here, maybe I can get some insight from you guys.

My terrace house is ~30 years old, and it always trip at the slightest lightning strikes. Even when my neighbour right next door don't trip. How do I reduce this?

The house got this installed, and as you can see its very old, I assume its an ELCB. Would upgrading this to a RCCB help? Or would it become more sensitive over time (deteriorating components inside).

user posted image
*
Better change to rccd for better protection as mention by EC here & to comply with the regulation

http://www.st.gov.my/index.php/policies/ci...stabilizer.html
macgy
post Jun 20 2016, 11:51 AM

New Member
*
Junior Member
6 posts

Joined: Nov 2009
Get a good Surge protection device and install b4 the RCCB / in your case B4 ELCB,
I install the American Brand more than 2 yrs ago, has never trip since, best part is their long unlimited warranty of more than 15 years, 1 to 1 exchange, i think Sine Tamer.
unfortunately, i loss the no. of contractor who install for me.
cherroy
post Jun 20 2016, 12:04 PM

20k VIP Club
Group Icon
Staff
25,802 posts

Joined: Jan 2003
From: Penang


QUOTE(macgy @ Jun 20 2016, 11:51 AM)
Get a good Surge protection device and install b4 the RCCB / in your case B4 ELCB,
I install the American Brand more than 2 yrs ago, has never trip since, best part is their long unlimited warranty of more than 15 years, 1 to 1 exchange, i think Sine Tamer.
unfortunately, i loss the no. of contractor who install for me.
*
errr...
Surge protection and RCCB/ELCB are 2 different issue. sweat.gif

RCCB/ELCB trip is good thing to have actually (except malfunction of RCCB/ELCB, due to aging etc), which just show that it is function properly to indicate there is a problem in the wire system or electrical appliances, which prompt user to rectify it.

maxilife1
post Jun 20 2016, 12:44 PM

On my way
****
Senior Member
536 posts

Joined: Aug 2009
From: Seri Kembangan


QUOTE(keyz @ Jan 6 2016, 01:31 PM)
Mine also installed with SPD (installed 2015-09-19). Ever since, Only one time there is quite heavy lightning strike as reported by my wife but RCCB didn't trip.

user posted image
*
QUOTE(keyz @ May 14 2016, 12:12 AM)
For electrician phone you can get from local shop which supply electrical part for contractor, not shop which selling electrical appliances. They do leave the business card number.

For SPD & auto RCCB I bought from L.V Control Technologies SB. 03-80112999. Mr. Alan Chua (alan@lvcontrol.com.my)

L.V.CONTROL TECHNOLOGIES SDN.BHD
No.3, Twin Park
Jalan Subang 7/1
Taman Perindustrian Subang USJ 1
47600 Subang Jaya
*
QUOTE(Richard @ May 24 2016, 09:04 PM)
The function of a surge protection device is to prevent a sudden Surge of Voltage from damaging your electronics by providing a path of least resistance to ground.. a protection against lightning strikes to overhead electrical lines and or from bad earth rods (which picks from impact  zones and carries the voltage surges to your box) .

Only if this is the case then you can install it anywhere from your kwh meter cables to your distribution box.. A common practice is to install inside the DB but its not the only way to have it installed..

You can have it installed in its own enclosure after the kwh meter at any point before the DB (thus the equipment to be protected)... connect all phase/neutral cables to the SPD and connect SPD to a known good ground. (Ground rod reading below One Ohm)..
*
all good info!

thanks rclxms.gif
Kiding
post Jun 20 2016, 03:50 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(cherroy @ Jun 20 2016, 12:04 PM)
errr...
Surge protection and RCCB/ELCB are 2 different issue.  sweat.gif

RCCB/ELCB trip is good thing to have actually (except malfunction of RCCB/ELCB, due to aging etc), which just show that it is function properly to indicate there is a problem in the wire system or electrical appliances, which prompt user to rectify it.
*
Agreed on surge protection and RCCB are protecting different scenario, RCCB protects human life from current leak, and SPD protects lightning strike damages.

But, RCCB often very sensitive to detect any current imbalance caused by lightning strike, thus, cause nuisance trip!

My ABB SPD have been installed for 1 month, there was a close lightning stroke my house nearby, my house alarm was triggered due to vibration, neighbor cars alarm was screaming! but this time, no power trip anymore ! rclxms.gif I'd say SPD really effective to reduce or eliminate power trip caused by lightning strike!
clickNsnap
post Aug 25 2016, 01:45 PM

On my way
****
Junior Member
541 posts

Joined: Jun 2006


Just would like to update, after replaced the Max Guard RCCB to Hager RCCB for two months, no more trip when there was heavy thunder storm & lightning smile.gif
TSsocratesman
post Aug 25 2016, 08:11 PM

Regular
******
Senior Member
1,807 posts

Joined: Jan 2003
From: KL
QUOTE(clickNsnap @ Aug 25 2016, 01:45 PM)
Just would like to update, after replaced the Max Guard RCCB to Hager RCCB for two months, no more trip when there was heavy thunder storm & lightning smile.gif
*
Omg I'm the TS and forgot to update mine lol.
We Replaced RCCB with similar specs but diff brand (hager) and no more thunderstorms trip since.
clickNsnap
post Aug 26 2016, 02:14 AM

On my way
****
Junior Member
541 posts

Joined: Jun 2006


QUOTE(socratesman @ Aug 25 2016, 09:11 PM)
Omg I'm the TS and forgot to update mine lol.
We Replaced RCCB with similar specs but diff brand (hager) and no more thunderstorms trip since.
*
thumbsup.gif look like replacing the old RCCB to a new Hager RCCB is the answer!
Kiding
post Aug 26 2016, 10:37 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(clickNsnap @ Aug 26 2016, 02:14 AM)
thumbsup.gif  look like replacing the old RCCB to a new Hager RCCB is the answer!
*
Not really, I replaced my old RCCB with Hager RCCB, it still trip, just lesser, now I have installed the ABB SPD, so far it is already 4 months and not a single trip.
clickNsnap
post Aug 26 2016, 11:57 PM

On my way
****
Junior Member
541 posts

Joined: Jun 2006


QUOTE(Kiding @ Aug 26 2016, 11:37 PM)
Not really, I replaced my old RCCB with Hager RCCB, it still trip, just lesser, now I have installed the ABB SPD, so far it is already 4 months and not a single trip.
*
Oh... I see, glad you've solved your issue. So far, I didn't have any trip after replaced with Hager RCCB smile.gif

Octopuz
post Jun 27 2017, 11:02 PM

Getting Started
**
Junior Member
61 posts

Joined: Jun 2006
hi guys,

i'm seeking advice on my upcoming DB replacement & SPD upgrade to more reliable Hager parts (for electric trip reduction).
Read most of the posts here and but i'm still not clear if it is okay to use RCCB 40A rate?

My current setup (not sure why 63A isolator is used by the developer):
Attached Image

thanks thanks

This post has been edited by Octopuz: Jun 27 2017, 11:02 PM
Richard
post Jun 28 2017, 03:34 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Octopuz @ Jun 27 2017, 11:02 PM)
hi guys,

i'm seeking advice on my upcoming DB replacement & SPD upgrade to more reliable Hager parts (for electric trip reduction).
Read most of the posts here and but i'm still not clear if it is okay to use RCCB 40A rate?

My current setup (not sure why 63A isolator is used by the developer):
Attached Image

thanks thanks
*
with respect to the guidelines set by ST..

- you should have another 30mA RCD strictly for the 13A 3 pin sockets (to be on a 20A mcb circuit)

- the 63A isolator is ok .. its function is only to switch on and off..

Why are you thinking to install an SPD?

This post has been edited by Richard: Jun 28 2017, 09:06 AM
Octopuz
post Jun 28 2017, 09:09 AM

Getting Started
**
Junior Member
61 posts

Joined: Jun 2006
QUOTE(Richard @ Jun 28 2017, 03:34 AM)
with respect to the guidelines set by ST..

- you should have another 30mA RCD strictly for the 13A 3 pin sockets (to be on a 20A mcb circuit)

- the 63A isolator is ok for 16mm2 intercabling but a 40A is preferable to use 10mm2 cables.. Its easier to install..

Why are you thinking to install an SPD?
*
another or replace current 100mA 40A RCD with 30mA sensitivity.

so as for the RCD current rate, i shouldn't change it to 63A type right? what's the gain of installing higher current rate (e.g. 100A)?

SPD is for nuisance trip prevention during raining season and proctect my computer stuffs.

Correct me if my understanding is wrong.

This post has been edited by Octopuz: Jun 28 2017, 09:16 AM
Richard
post Jun 28 2017, 09:19 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(Octopuz @ Jun 28 2017, 09:09 AM)
another or replace current 100mA 40A RCD with 30mA sensitivity.

SPD is for nuisance trip prevention during raining season and proctect my computer stuffs.

Correct me if my understanding is wrong.
*
Based on ST..

Protection sequence is fuse - (kwh meter) - isolator - 100mA RCD ( mcb's for light, aircon, fans etc), 10mA rcbo for water heater - 30mA RCD (mcb's for 13A sockets)

SPD is to ground surge voltages thus protecting sensitive equipment ..

This post has been edited by Richard: Jun 28 2017, 09:21 AM
ozak
post Jun 28 2017, 09:59 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Octopuz @ Jun 28 2017, 09:09 AM)
another or replace current 100mA 40A RCD with 30mA sensitivity.

so as for the RCD current rate, i shouldn't change it to 63A type right? what's the gain of installing higher current rate (e.g. 100A)?

SPD is for nuisance trip prevention during raining season and proctect my computer stuffs.

Correct me if my understanding is wrong.
*
You can replace to a more sensitive RCD. But you probably will get nuisance trip more frequent.

You can change the RCD to 63A rate. 40A or 63A is a max load on the device.

Having SPD is good. But it is not 100% protected to all your device.

Lightning can be come from many way. From the main supply, wire around the wall, service provider network (Lan wire) etc.

Important is to check your earth is sufficient. And additional SPD nearer to your sensitive device. Lan network too.
Kiding
post Jun 28 2017, 03:43 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


There are type 1, 2, 3 SPD,

Type 1 SPD protects from the directly lightning strike to your power supply line.
Type 2 SPD protects from indirectly lightning strike, this type of SPD is the one you install at your DB, it has less discharge current rating
Type 3 SPD protects sensitive equipment such as computer, AV equipments or electronic devices, type 3 SPD must install nearby your electronic devices.

In Malaysia, you will need type 3 SPD, if you stay at high ground or frequently lightning strike area, you will need type 2 SPD, if the power line is hanging in the air and connect to your house and your house is at the highest point, you better get type 1 SPD.
halcyon27
post Jun 28 2017, 03:51 PM

Look at all my stars!!
*******
Senior Member
2,140 posts

Joined: Nov 2010


QUOTE(Kiding @ Jun 28 2017, 03:43 PM)
There are type 1, 2, 3 SPD,

Type 1 SPD protects from the directly lightning strike to your power supply line.
Type 2 SPD protects from indirectly lightning strike, this type of SPD is the one you install at your DB, it has less discharge current rating
Type 3 SPD protects sensitive equipment such as computer, AV equipments or electronic devices, type 3 SPD must install nearby your electronic devices.

In Malaysia, you will need type 3 SPD, if you stay at high ground or frequently lightning strike area, you will need type 2 SPD, if the power line is hanging in the air and connect to your house and your house is at the highest point, you better get type 1 SPD.
*
Good tip
Octopuz
post Jun 30 2017, 10:46 PM

Getting Started
**
Junior Member
61 posts

Joined: Jun 2006
Richard, ozak and Kiding,

thanks for the inputs...
aeiou228
post May 21 2018, 12:10 AM

Look at all my stars!!
*******
Senior Member
5,867 posts

Joined: Feb 2006
Yesterday's thunderstorm nuisance tripping forced me to cut short my out station trip to return home to switch the RCD back on in order to prevent refrigerator from foul smell. Such pain !
Is there any device out there where I can turn on the RCD remotely without electricity and WiFi network?
Richard
post May 21 2018, 01:16 AM

Regular
******
Senior Member
1,083 posts

Joined: Jan 2003
From: Kota Kinabalu


QUOTE(aeiou228 @ May 21 2018, 12:10 AM)
Yesterday's thunderstorm nuisance tripping forced me to cut short my out station trip to return home to switch the RCD back on in order to prevent refrigerator from foul smell.  Such pain !
Is there any device out there where I can turn on the RCD remotely without electricity and WiFi network?
*
The residual current device (RCD) trips to tell you there is a problem with your wiring. Somewhere in the house one or more circuit wires Live or N insulation is damaged (bitten by rats, cut or too old) leaking a residual electric current.

If you imagine that water pipes are the electric wires and water is electricity than the lighting storm is a higher voltage(think higher pressure) forcing a leak in the water pipe.
I am not very good at explaining but I will advice you get a wireman to do an insulation testing on all Live and Neutral circuits in your electrical DB to find out which circuit has the damaged wiring.

Do not ignore the RCD tripping as damaged wires cause many electric fires. Please pay the wireman and get an insulation test done soonest and rewire that damaged circuit.

Be safe.
ozak
post May 21 2018, 09:47 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(aeiou228 @ May 21 2018, 12:10 AM)
Yesterday's thunderstorm nuisance tripping forced me to cut short my out station trip to return home to switch the RCD back on in order to prevent refrigerator from foul smell.  Such pain !
Is there any device out there where I can turn on the RCD remotely without electricity and WiFi network?
*
So far non.

But there is a motorize auto reset device for RCD. It will auto reset few time before totally off. Don't recommend to use. Not safe.

What I do is, change the RCD. The nuisance trip prevent type. I m using ABB.

I plunge another ground rod at the right side of the house in the garden. Original ground rod and wired on the left. 3 pcs connected rod totally 6m. 6mm earth wire into the AV cabinet and distribute to others wall socket. The wall socket is inside the cabinet. So the earth wire cannot see. I confirm the earth wire is running good by the Belkin earth led light up. Before that, it either no light or fade blinking.

Doing this 2 thing solve my 80% of nuisance trip.

Remaining thing I would like to do is install SPD in the DB. Already brought but haven't install yet. Plan change all the MCB and install together. Distribute more new earth wire to others wall socket. If can, plunge another ground rod behind the house and more SPD far from DB.

The main goal is, shorten the earth wire into the ground.

What I always do for the fridge is, I freeze more ice in the bottle/container/gel before long holiday. In case it trip, extra ice prolong the cold. My experience is it last about 3days.
ozak
post May 21 2018, 09:56 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Kiding @ May 14 2016, 01:56 PM)
I bought it around RM430, local seller quote me RM800+, my.rs-online.com selling around RM680
*
So expensive the SPD ?

Local have many such SPD sell. Pretty common device. Sheineider, Hager, ABB etc

ABB cost RM275. Hager cheaper.
FrankieSiow
post Oct 17 2018, 10:40 AM

Getting Started
**
Junior Member
51 posts

Joined: May 2012
QUOTE(keyz @ Jan 6 2016, 08:11 PM)
SPD Class 2 (for 3 phase) - RM477 incl. GST
Installation RM150 - local electrician. This installation cost include SPD & auto Reset RCCB.
*
Hello, may I know what brand and model of SPD that you using?
keyz
post Oct 25 2018, 08:23 AM

Regular
Group Icon
VIP
1,271 posts

Joined: Jan 2003
From: Terengganu


QUOTE(FrankieSiow @ Oct 17 2018, 10:40 AM)
Hello, may I know what brand and model of SPD that you using?
*
DuvalĀ® Class 2 Surge Protection Device (DUVAL D40C-275/3 + NPE)
FrankieSiow
post Oct 25 2018, 09:41 AM

Getting Started
**
Junior Member
51 posts

Joined: May 2012
QUOTE(keyz @ Oct 25 2018, 08:23 AM)
DuvalĀ® Class 2 Surge Protection Device (DUVAL D40C-275/3 + NPE)
*
Thank you for the info. biggrin.gif
hisashi84
post Feb 8 2019, 10:13 AM

New Member
*
Newbie
3 posts

Joined: Jun 2016
i saw "Maxguard 40kA 4P Surge Protection Device " from lazada.. about rm262. what is the different btw 40kA 4P and 40kA 2P?
sonerin
post Feb 8 2019, 12:29 PM

Look at all my stars!!
*******
Senior Member
8,739 posts

Joined: Aug 2009
QUOTE(hisashi84 @ Feb 8 2019, 10:13 AM)
i saw "Maxguard 40kA 4P Surge Protection Device " from lazada.. about rm262. what is the different btw 40kA 4P and 40kA 2P?
*
4P = 4 polarity and 2P= 2 polarity
SUSslimey
post Feb 8 2019, 12:30 PM


*******
Senior Member
6,914 posts

Joined: Apr 2007
QUOTE(hisashi84 @ Feb 8 2019, 10:13 AM)
i saw "Maxguard 40kA 4P Surge Protection Device " from lazada.. about rm262. what is the different btw 40kA 4P and 40kA 2P?
*
4p for 3 phase electric: red, yellow, blue, neutral.
2p for single phase: phase, neutral.
macgy
post Feb 20 2019, 12:17 PM

New Member
*
Junior Member
6 posts

Joined: Nov 2009
The Max Guard SPD is only a 4 modes protection SPD, go for at least 7 modes protection SPD, there are a few brands in the market, I installed a 10 modes protection SPD. probelm solved
ajizaimi
post May 21 2019, 07:35 AM

New Member
*
Newbie
9 posts

Joined: Apr 2012


QUOTE(Kiding @ May 14 2016, 11:30 AM)
Hager is the RCCB, ABB is the SPD

Attached Image
*
Boleh ke guna kabel 10mm dari main switch ke spd, spd ke rccb. Kabel asal 16mm. Kalau guna 16mm tak muat untuk looping di spd. Rumah saya 3 fasa 63A

user posted image
wordplay
post Mar 16 2022, 06:55 AM

Getting Started
**
Junior Member
142 posts

Joined: May 2008


QUOTE(macgy @ Feb 20 2019, 12:17 PM)
The Max Guard SPD is only a 4 modes protection SPD, go for at least 7 modes protection SPD, there are a few brands in the market, I installed a 10 modes protection SPD. probelm solved
*
What brand is it the 10 mode protection SPD?
jchong
post Jun 11 2022, 06:16 PM

****************
*******
Senior Member
5,989 posts

Joined: Nov 2005
QUOTE(wordplay @ Mar 16 2022, 06:55 AM)
What brand is it the 10 mode protection SPD?
*
He mentioned it was Sine Tamer brand.
wordplay
post Jun 11 2022, 10:49 PM

Getting Started
**
Junior Member
142 posts

Joined: May 2008


QUOTE(jchong @ Jun 11 2022, 06:16 PM)
He mentioned it was Sine Tamer brand.
*

Thanks For The reply Chong.

Maras Power Surge Protector also can be considers . Its Local made & price wise its quite expensive .

 

Change to: