views
     
ozak
post Dec 1 2012, 12:11 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Kiding @ Dec 1 2012, 11:01 AM)
If using 30mA then I expect the nuisance trip will even worst!

Actually the 100mA is good enough, it trip yesterday when the aircon installer accidentally touch the wire.

I think most house in Malaysia use 100mA by default.
*
Not true. I been using 30mA for many many yrs. Last time I always have this nuisance tripping. Go to electrical shop and ask for the solution from the bos. Told me to change to a better 1 and abit expensive. Brand hager and cost rm120. Change it and now less trip.

Use a better way to solve the problem and not downgrade the safety. You still have a solution like earthing and surge protector.
ozak
post Dec 1 2012, 01:11 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Kiding @ Dec 1 2012, 12:55 PM)
Thanks for the advice, I will give it a try, Where can I get Hager brand in Klang Valley area? Can I get it at Jalan Pasar?
*
The original RCCB from the house developer is 100mA. Trip like hell. Change it to better brand Hager 30mA. Less trip.

So it doesn't logic to me that 100mA give less problem. And compromise the safety.

You can get it at any electrical shop. It is not branded item now.
ozak
post Dec 1 2012, 05:56 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


Here are some information and understanding about RCCB.

Attached File  RCD_The_Best_Way_To_Guarantee_Electrical_Safety_At_Home1.pdf ( 60.29k ) Number of downloads: 939
Attached File  RCD_The_Best_Way_To_Guarantee_Electrical_Safety_At_Home.pdf ( 129.5k ) Number of downloads: 840


Why nuisance trip, what happen and some solution without compromise the safety.

Attached File  Solution.pdf ( 171.31k ) Number of downloads: 1641


This post has been edited by ozak: Dec 1 2012, 05:58 PM
ozak
post Dec 1 2012, 11:27 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(JinXXX @ Dec 1 2012, 10:13 PM)
can we buy and fix the RCCD ourself to replace my told ELCB ? 15 years no touch/change it..

or its better to recommend an "ëlectrician" to fix it ?
*
Can it trip? Press the test button to try it.

You can change it yourself. Not difficult. Just makesure OFF the main MCB or takeout the fuse. 2 wire in and 2 wire out. Some maybe have direction of incoming and outgoing. Some don't.

If no confident, buy the RCCB and ask the bos change it for you. Pay some fee.
ozak
post Dec 2 2012, 01:45 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Kiding @ Dec 2 2012, 12:36 AM)
Asking Hager 30mA RCCB around 5 shops in Puchong and Serdang, none of them carry 30mA, so just get the 100mA for RM80

I'm planing to install 30mA sensitivity RCBO to replace the MCB for the electric shower heater, is it better than install 30mA at the main switch?
*
Beside hager, you can get the ABB anti nuisance trip 30mA RCCB. Read the pdf file above.

RCBO is a good idea too. It have extra protection than RCCB. It use after the main RCCB.

I m using RCD+fuse 30mA for heater, kitchen and fountain. Install inside toilet nearer to heater.

user posted image
ozak
post Apr 26 2013, 03:07 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(jialitrading @ Apr 26 2013, 02:00 PM)
Dear Ozak,

Mine to share where you bought this item?

What is it called?? I want to fix them for my water heater too.

Thanks
*
It is a RCD. Brand MK. Don't think can get it here and not selling anymore. Order it from UK 13yrs ago.
ozak
post Dec 27 2013, 10:15 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 27 2013, 10:02 AM)
we all in the neighbourhood are told by dealer and local electrician that 300mA safer.

for my case i m monitoring current 100mA rccb and fuse switch after tightening. i update if there are updates.
*
You are mis inform. 300mA is not safer. You get short and the rccb is not easily trip. That's not call safer.

Lightning happen and the rccb not easily trip. That is call better.

100mA is more easily trip because it is more sensitive to detect minor fault. Which of course have problem with big bow of lightning. The easy and less cost way is just change it to 300mA. It still will trip but lesser.


ozak
post Dec 27 2013, 01:06 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 27 2013, 12:38 PM)
look like mass are misinformed. this make sense why those local electric shops had so much abundant stock of 300mA rccbs. the misinformed public in large perceive the solution was best way out. just like monkey see monkey do.

meaning the lesser the mA the better protection.

well I had my fuse switch replaced. as mention before due to loose contact with TNB L wire. the inner components are toasted but it had been working all while for years. here are the pictures. the connectors are all dark purple.
[attachmentid=3787797][attachmentid=3787799]
*
The meaning of the number like 100mA or 300mA is how much the current detect will trip the rccb. Lower figure is safer.

The purple color is the constant hot temperature at the contact surface surrounding side. After long period of hot temperature, the material will change color. That show ..
1) A high current is flowing without sufficient surface contact between. Create a bottle neck at that place. This cost resistance and hot temperature occur.
2) Loose connection cost the electron hard to flow over within 2 contact. Occasionally some spark will happen. Resistance and hot temperature occur.

If you can, change that fuse holder to mcb type. Outside your house beside the meter is already have the fuse protect. (black square box) You don't need another fuse in the DB box. That is for the developer cut cost. MCB have better switch surface contact.

Just my bullshit CSI. He....

ozak
post Dec 27 2013, 01:50 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 27 2013, 01:41 PM)
63A MCB? i had given thoughts about it. however my TNB L wire comes from bottom. Hence just nice to insert into INCOMING ONLY on the fuis switch from bottom up. while for MCB the L wire is not sufficient long to go on top of the incoming terminal. cause the wiring configuration is top down. which is reason i practically notice L wire shorter than N. cause the TNB N wire by defaults go to incoming N of RCCB from top which more longer.
*
Just put the MCB upside down. The look is same. Just the switch handle opposite.
ozak
post Dec 28 2013, 12:13 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 27 2013, 02:09 PM)
btw any comment which is best rccb to date with anti-nuisance tripping. currently using this rccb. anyone had any comments or experiences on this VL rccb product provided by developer.

[attachmentid=3787910]
*
I remember abb have some device that can prevent trip from lightning. It just install beside the mcb.

Your rccb is fine. So for easy solution, just change it to 300mA.
ozak
post Dec 28 2013, 11:49 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(toh2020 @ Dec 28 2013, 09:53 AM)
you mentioned before 100mA should be safer. btw which model of ABB which deem popular?
*
This --> "So for easy solution"

For proper way, that cost you a lot. Try check at ABB site.
ozak
post Dec 30 2013, 12:19 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(stevie8 @ Dec 29 2013, 09:48 PM)
By the way, if you suspect your koi pond is causing the trip, you better don't touch the water.
*
Ain't the fish already belly up?
ozak
post Jun 20 2015, 03:55 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Fazab @ Jun 20 2015, 12:54 AM)
Hi sifus

My new house RCCB 63A 0.1A  tripping randomly.
Did the usual diagnosis and trace the problem to one line supplying the front lights.
When the MCB (6A) for this in ON, cannot reset the RCCB, trips immediately.
When I OFF this MCB, then only can reset the RCCB. 
After sometime however can reset back with that MCB ON.

The problem is transient, sekejap ada, sekejap OK.

The faulty line has a timer switch, which I thought was causing the problem, so call back the wireman.

He checked and found that the one line is carrying 33 light points (including 16 T5s and 10 mLED downlights) and 1 fan.  rclxub.gif  rclxub.gif  rclxub.gif
But I very seldom on everything. usually max 7-10 lights only.

He thinks it overload, and 'partition' some load over to the nearby 20A MCB. Don't know what it means.

But the RCCB still trips randomly. Although now can reset.

Any ideas how to approach?  I suspect some wire are overheating, that why after a while cooling down the problem goes away, only to happen again later.
*
RCCB trip is telling you that something is shortcircuit. But not overload. If it overload, the MCB through that line will trip.

Since you able to isolate the problem and only that line cause the trip, it is much more easy to troubleshoot. But your electrician diagnose wrongly. Since all the light and electrical thing able to ON without cause the MCB trip, that mean there is no overload on that line.

For the shortcircuit, you have to look at the lighting, timer, fan, etc on that line. There is something faulty there. But which 1. So you need to further isolated those thing to 1 by 1 or by the switching group. ON 1 switch at a time and see will it trip. If no, than OFF it and proceed another switch ON. Till you find that cause tripping.

If this group of light cause tripping, than need to further isolate which light is cause the trip. You need to disconnect the light 1 by 1 and try to ON to find that spoil 1 that cause the trip.
ozak
post Dec 14 2015, 10:39 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(gagak_84 @ Dec 13 2015, 10:26 PM)
guys.. need some help..

my new house RCCB always trip during raining.

incomer from TNB goes to this
R,Y,B = 32A,415V and 10kA
looks like SPD but no earthing pole from this one

outgoing goes to RCCB in which the specs is
63A 415V 100mA

im thinking to change the RCCB with good brand such as ABB with same specs.
if the same thing happen i would install new SPD with earthing pole

another thing is my neutral terminal at DB box doesnt jump to earting terminal, i saw some videos and most of it jumped together.
*
RCCB is not the problem. It work fine. RCCB is not using earth to trip cause it is not a ELCB.

You have 3 choice to reduce the trip.

1) change the RCCB to less sensitive to 300mA or 0.3A. But will delay the trip if any short circuit.
2) Install a surge protector to absorb the surge voltage. It will channel the surge to earth. So your earth rod need to be good.
3) Check the earth rod infront your garden. The checking is in Ohm which less ohm is better. (below 100ohm)


ozak
post Dec 15 2015, 04:09 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(gagak_84 @ Dec 15 2015, 03:46 PM)
on no 3, how to check the ohm on the rod i saw someone said Hager and schneider RCCB equipped by anti-storm protection.. is that true??

Thinking of to change my current RCCB with this one

user posted image
*
The earth rod only can be check with earth meter. Which some electrician have.

You can try to change. But the 0.1A is sensitive. It still will trip. But lesser.
ozak
post Dec 15 2015, 04:39 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(gagak_84 @ Dec 15 2015, 04:28 PM)
can i check whether my equipment have earth leakage at DB box..
which i check whether earthing din-rail has live current using test pen
*
Leave it to the electrician to check if you not experience.

Electric can kill. Don't touch if you really not sure.

Your house is running 3P. Phase to phase is 415V. It is dangerous.
ozak
post May 28 2016, 06:32 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Jason @ May 28 2016, 12:40 AM)
Thank you for your input. Guess if its not broken, don't fix it. Cause apart from being more sensitive, nothing else is wrong.
*
It is sometime not cause by the elcb.

The surge go through the old wire and trip it. You can try to replace the elcb to new 1.

If problem still happen, time to change the wiring.
ozak
post Jun 28 2017, 09:59 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Octopuz @ Jun 28 2017, 09:09 AM)
another or replace current 100mA 40A RCD with 30mA sensitivity.

so as for the RCD current rate, i shouldn't change it to 63A type right? what's the gain of installing higher current rate (e.g. 100A)?

SPD is for nuisance trip prevention during raining season and proctect my computer stuffs.

Correct me if my understanding is wrong.
*
You can replace to a more sensitive RCD. But you probably will get nuisance trip more frequent.

You can change the RCD to 63A rate. 40A or 63A is a max load on the device.

Having SPD is good. But it is not 100% protected to all your device.

Lightning can be come from many way. From the main supply, wire around the wall, service provider network (Lan wire) etc.

Important is to check your earth is sufficient. And additional SPD nearer to your sensitive device. Lan network too.
ozak
post May 21 2018, 09:47 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(aeiou228 @ May 21 2018, 12:10 AM)
Yesterday's thunderstorm nuisance tripping forced me to cut short my out station trip to return home to switch the RCD back on in order to prevent refrigerator from foul smell.  Such pain !
Is there any device out there where I can turn on the RCD remotely without electricity and WiFi network?
*
So far non.

But there is a motorize auto reset device for RCD. It will auto reset few time before totally off. Don't recommend to use. Not safe.

What I do is, change the RCD. The nuisance trip prevent type. I m using ABB.

I plunge another ground rod at the right side of the house in the garden. Original ground rod and wired on the left. 3 pcs connected rod totally 6m. 6mm earth wire into the AV cabinet and distribute to others wall socket. The wall socket is inside the cabinet. So the earth wire cannot see. I confirm the earth wire is running good by the Belkin earth led light up. Before that, it either no light or fade blinking.

Doing this 2 thing solve my 80% of nuisance trip.

Remaining thing I would like to do is install SPD in the DB. Already brought but haven't install yet. Plan change all the MCB and install together. Distribute more new earth wire to others wall socket. If can, plunge another ground rod behind the house and more SPD far from DB.

The main goal is, shorten the earth wire into the ground.

What I always do for the fridge is, I freeze more ice in the bottle/container/gel before long holiday. In case it trip, extra ice prolong the cold. My experience is it last about 3days.
ozak
post May 21 2018, 09:56 AM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Kiding @ May 14 2016, 01:56 PM)
I bought it around RM430, local seller quote me RM800+, my.rs-online.com selling around RM680
*
So expensive the SPD ?

Local have many such SPD sell. Pretty common device. Sheineider, Hager, ABB etc

ABB cost RM275. Hager cheaper.