Anyone heard of self reset-ing ELCB ?
RCCB/ELCB 100mA still nuisance trip!, during lightning storms
RCCB/ELCB 100mA still nuisance trip!, during lightning storms
|
|
Nov 9 2011, 03:21 PM
|
![]() ![]() ![]()
Junior Member
451 posts Joined: Feb 2008 |
Anyone heard of self reset-ing ELCB ?
|
|
|
|
|
|
Nov 9 2011, 03:30 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
3,173 posts Joined: May 2007 |
Am curious on how this resetting ELCB works. The ELCB is supposed to trip when there is a fault in the circuit. Auto resetting without establishing the fault first, would that be dangerous?
|
|
|
Nov 9 2011, 06:49 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,031 posts Joined: Jan 2003 From: PJ |
can be bought but they only reset three times before a manual reset is required. they are meant for unammned outstation places. if you want self resetting safe the money and just remove the existing one. safety wise its (almost) the same
|
|
|
Nov 10 2011, 02:27 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
Maybe u try playing around with the little MCB switches and try to narrow down which circuit is causing the trip during lightning?
|
|
|
Nov 10 2011, 09:35 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,516 posts Joined: Feb 2007 From: Uarla Umpur |
|
|
|
Nov 10 2011, 09:38 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
Yes, someone already mention it before.
|
|
|
|
|
|
Nov 11 2011, 12:58 AM
|
![]()
Junior Member
7 posts Joined: Jul 2010 From: The Strand, Kota Damansara |
Better check on your house earthing ... if trip during lightning ... Or you can try changing your RCCB to those like Hager RCCBs that is designed with an anti-nuisance tripping feature, which do not unnecessarily tripped unless there is a genuine earth fault.
This post has been edited by Zestune: Nov 11 2011, 01:36 AM |
|
|
Nov 11 2011, 01:15 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
7,826 posts Joined: Jan 2003 From: Ipoh |
There is also electronic selectable sensitivity to adjuct from 0.1A to 1A cut off.
Anyway having it trip during lightning isn't good as it try block surge from entering your electrical appliances. Btw MCB is meant for overload cut off. It trips whenever the load (amperage) goes beyond the rated. Usually it trips when Live wire shorted to Neutral. ELCB trips whenever there is leakage on Neutral. For example, Live or Neutral wire is leak to the earth, it trips. To test how good is your electrical grounding, get a MEGA tester or insulation tester. Calculation based on OHM. |
|
|
Nov 11 2011, 12:33 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,516 posts Joined: Feb 2007 From: Uarla Umpur |
|
|
|
Nov 11 2011, 02:18 PM
|
![]() ![]() ![]() ![]()
Senior Member
558 posts Joined: Jan 2003 |
MCB detects overcurrent. Say, a 2.5HP aircon connected to 10A MCB, MCB will trip.
ELCB detects if any current running in the Earth conductor RCCB detects residue current between L&N. Earth Resistivity (Electrical Grounding) test using Earth Tester. Calculated in Ohm, the lower the ohm the better it is. Insulation Tester (Mega Tester) is test the insulation capability of the cables. Measured in MOhm. The higher it is, the better. Both Earth tester and insulation tester are not cheap at hundreds. |
|
|
Nov 11 2011, 03:06 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,516 posts Joined: Feb 2007 From: Uarla Umpur |
QUOTE(pky @ Nov 11 2011, 02:18 PM) MCB detects overcurrent. Say, a 2.5HP aircon connected to 10A MCB, MCB will trip. +1 ELCB detects if any current running in the Earth conductor RCCB detects residue current between L&N. Earth Resistivity (Electrical Grounding) test using Earth Tester. Calculated in Ohm, the lower the ohm the better it is. Insulation Tester (Mega Tester) is test the insulation capability of the cables. Measured in MOhm. The higher it is, the better. Both Earth tester and insulation tester are not cheap at hundreds. |
|
|
Jun 7 2012, 04:21 PM
|
![]()
Newbie
1 posts Joined: Mar 2012 |
QUOTE(socratesman @ Mar 15 2011, 12:29 PM) Hi folks, Hi,My family and I are living in a terrace house. Recently my dad changed our 25-yr old voltage-based ELCB to a newer current-based RCCB (Wylex 2Pole 40A with 100mA sensitivity) After that it start nuisance tripping a lot during storms, even if the lightning is far away. When no storm, everything is OK. I was surprised even 100mA also trips a lot, if 30mA of course I can understand the tripping. Any RCCB users here on 100mA sensitivity? Do yours trip frequently during storms? If yes, what did you do to mitigate the annoyance? As mention the ELCB for 100mA will trip frequently during storms is a norm. Its prove that your ELCB working. If the ELCB never trip at all, you are in trouble. ELCB is a safety device used in electrical installations with high earth impedance to prevent SHOCK and to protect your SENSITIVE equipment/home appliances. The ELCB rating should be as low as possible to prevent shock; do you think that 100mA is safe enough for human and equipment? NO. IEC 60479 stated that human cannot take in more than 7mA of leakage current. More than that are critical level and may cause to DEATH. Unfortunately, the current ELCB lowest rating is 10mA whereby still a risk to human against SHOCK. If you choose to use 30mA at your main, you will complain that it trip more frequent as compare to your assisting one (100mA). I have the solution where comply to IEC 60479 and eliminate nuisance trip… |
|
|
Oct 27 2012, 05:14 PM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
834 posts Joined: Jun 2012 From: ~Heaven~ |
QUOTE(socratesman @ Mar 15 2011, 12:29 PM) Hi folks, 100ma is complusary for main switchboard.cant use more than that according to regulation.nuisance tripping occured during lightning strike due to current imbalance between live and neutral.so its pretty normal.lightning wave travel frm tnb cables to ur house.its not about the lightning is far...My family and I are living in a terrace house. Recently my dad changed our 25-yr old voltage-based ELCB to a newer current-based RCCB (Wylex 2Pole 40A with 100mA sensitivity) After that it start nuisance tripping a lot during storms, even if the lightning is far away. When no storm, everything is OK. I was surprised even 100mA also trips a lot, if 30mA of course I can understand the tripping. Any RCCB users here on 100mA sensitivity? Do yours trip frequently during storms? If yes, what did you do to mitigate the annoyance? Added on October 27, 2012, 5:17 pm QUOTE(liktin111 @ Jun 7 2012, 04:21 PM) Hi, iec stated min is 30ma to prevent frm direct contact.not 7ma.100ma is for domestic application as per regulation.30ma is for final circuit or special locationAs mention the ELCB for 100mA will trip frequently during storms is a norm. Its prove that your ELCB working. If the ELCB never trip at all, you are in trouble. ELCB is a safety device used in electrical installations with high earth impedance to prevent SHOCK and to protect your SENSITIVE equipment/home appliances. The ELCB rating should be as low as possible to prevent shock; do you think that 100mA is safe enough for human and equipment? NO. IEC 60479 stated that human cannot take in more than 7mA of leakage current. More than that are critical level and may cause to DEATH. Unfortunately, the current ELCB lowest rating is 10mA whereby still a risk to human against SHOCK. If you choose to use 30mA at your main, you will complain that it trip more frequent as compare to your assisting one (100mA). I have the solution where comply to IEC 60479 and eliminate nuisance trip… Added on October 27, 2012, 5:23 pm QUOTE(pky @ Nov 11 2011, 02:18 PM) MCB detects overcurrent. Say, a 2.5HP aircon connected to 10A MCB, MCB will trip. elcb and rccb serve same purpose..elcb is old term and has been raplaced with rccbELCB detects if any current running in the Earth conductor RCCB detects residue current between L&N. Earth Resistivity (Electrical Grounding) test using Earth Tester. Calculated in Ohm, the lower the ohm the better it is. Insulation Tester (Mega Tester) is test the insulation capability of the cables. Measured in MOhm. The higher it is, the better. Both Earth tester and insulation tester are not cheap at hundreds. This post has been edited by jack~daniel: Oct 27 2012, 05:23 PM |
|
|
|
|
|
Dec 1 2012, 12:42 AM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,135 posts Joined: Jan 2003 From: Seri Kembangan |
My house also get nuisance trip during thunder storm, I plan to change the TBC 100mA RCCB to Hager 100mA RCCB, would it help? and where to get the Hager RCCB?
|
|
|
Dec 1 2012, 10:26 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
2,031 posts Joined: Jan 2003 From: PJ |
if your earth is good it *might* help. do note that in my personal opinion you dont need an ELCB at all if you decide to go higher than 30mA. Its no use. The ELCB is meant to save a humans life if they get into the circuit. If your cutoff level is already deadly why even bother with it? Either you do it properly or no need to do at all. If nobody gets inside the circuit you're pretty safe without an ELCB. ceo684 liked this post
|
|
|
Dec 1 2012, 11:01 AM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,135 posts Joined: Jan 2003 From: Seri Kembangan |
QUOTE(PJusa @ Dec 1 2012, 10:26 AM) if your earth is good it *might* help. do note that in my personal opinion you dont need an ELCB at all if you decide to go higher than 30mA. Its no use. The ELCB is meant to save a humans life if they get into the circuit. If your cutoff level is already deadly why even bother with it? Either you do it properly or no need to do at all. If nobody gets inside the circuit you're pretty safe without an ELCB. If using 30mA then I expect the nuisance trip will even worst! Actually the 100mA is good enough, it trip yesterday when the aircon installer accidentally touch the wire. I think most house in Malaysia use 100mA by default. |
|
|
Dec 1 2012, 12:11 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
17,021 posts Joined: Jan 2005 |
QUOTE(Kiding @ Dec 1 2012, 11:01 AM) If using 30mA then I expect the nuisance trip will even worst! Not true. I been using 30mA for many many yrs. Last time I always have this nuisance tripping. Go to electrical shop and ask for the solution from the bos. Told me to change to a better 1 and abit expensive. Brand hager and cost rm120. Change it and now less trip. Actually the 100mA is good enough, it trip yesterday when the aircon installer accidentally touch the wire. I think most house in Malaysia use 100mA by default. Use a better way to solve the problem and not downgrade the safety. You still have a solution like earthing and surge protector. ceo684 liked this post
|
|
|
Dec 1 2012, 12:55 PM
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,135 posts Joined: Jan 2003 From: Seri Kembangan |
QUOTE(ozak @ Dec 1 2012, 12:11 PM) Not true. I been using 30mA for many many yrs. Last time I always have this nuisance tripping. Go to electrical shop and ask for the solution from the bos. Told me to change to a better 1 and abit expensive. Brand hager and cost rm120. Change it and now less trip. Thanks for the advice, I will give it a try, Where can I get Hager brand in Klang Valley area? Can I get it at Jalan Pasar?Use a better way to solve the problem and not downgrade the safety. You still have a solution like earthing and surge protector. |
|
|
Dec 1 2012, 12:56 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
12,019 posts Joined: Jan 2003 |
Find the root cause of the problem. Keep increasing the tolerance must as well bypass ELCB run without safety.
|
|
|
Dec 1 2012, 01:11 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
17,021 posts Joined: Jan 2005 |
QUOTE(Kiding @ Dec 1 2012, 12:55 PM) Thanks for the advice, I will give it a try, Where can I get Hager brand in Klang Valley area? Can I get it at Jalan Pasar? The original RCCB from the house developer is 100mA. Trip like hell. Change it to better brand Hager 30mA. Less trip. So it doesn't logic to me that 100mA give less problem. And compromise the safety. You can get it at any electrical shop. It is not branded item now. |