 RCCB/ELCB 100mA still nuisance trip!, during lightning storms

views
     
SUSsupersound
post Jun 14 2015, 12:52 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(wodenus @ Jun 14 2015, 12:51 PM)
In homes the outdoor rod is buried in the ground I think smile.gif
*
Yes, indeed it is buried in the ground.
That's why we need to do a visual check.
wodenus
post Jun 14 2015, 01:06 PM

Tree Octopus
********
All Stars
14,990 posts

Joined: Jan 2003
QUOTE(supersound @ Jun 14 2015, 12:52 PM)
Yes, indeed it is buried in the ground.
That's why we need to do a visual check.
*
Don't you have to dig it out or something? smile.gif
SUSsupersound
post Jun 14 2015, 01:07 PM

10k Club
********
Senior Member
11,554 posts

Joined: Aug 2009
QUOTE(wodenus @ Jun 14 2015, 01:06 PM)
Don't you have to dig it out or something? smile.gif
*
If it is something needs to be done, it has to be done. Doing some dirty digging works is tedious or getting a house burnt down is tedious?
wodenus
post Jun 14 2015, 01:10 PM

Tree Octopus
********
All Stars
14,990 posts

Joined: Jan 2003
QUOTE(supersound @ Jun 14 2015, 01:07 PM)
If it is something needs to be done, it has to be done. Doing some dirty digging works is tedious or getting a house burnt down is tedious?
*
We just switched everything electric over to electronic. Seems to have solved the problem. Also I have been electrocuted before, it's no big deal smile.gif

Fazab
post Jun 20 2015, 12:54 AM

On my way
****
Senior Member
519 posts

Joined: Jun 2011


Hi sifus

My new house RCCB 63A 0.1A tripping randomly.
Did the usual diagnosis and trace the problem to one line supplying the front lights.
When the MCB (6A) for this in ON, cannot reset the RCCB, trips immediately.
When I OFF this MCB, then only can reset the RCCB.
After sometime however can reset back with that MCB ON.

The problem is transient, sekejap ada, sekejap OK.

The faulty line has a timer switch, which I thought was causing the problem, so call back the wireman.

He checked and found that the one line is carrying 33 light points (including 16 T5s and 10 mLED downlights) and 1 fan. rclxub.gif rclxub.gif rclxub.gif
But I very seldom on everything. usually max 7-10 lights only.

He thinks it overload, and 'partition' some load over to the nearby 20A MCB. Don't know what it means.

But the RCCB still trips randomly. Although now can reset.

Any ideas how to approach? I suspect some wire are overheating, that why after a while cooling down the problem goes away, only to happen again later.
ozak
post Jun 20 2015, 03:55 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(Fazab @ Jun 20 2015, 12:54 AM)
Hi sifus

My new house RCCB 63A 0.1A  tripping randomly.
Did the usual diagnosis and trace the problem to one line supplying the front lights.
When the MCB (6A) for this in ON, cannot reset the RCCB, trips immediately.
When I OFF this MCB, then only can reset the RCCB. 
After sometime however can reset back with that MCB ON.

The problem is transient, sekejap ada, sekejap OK.

The faulty line has a timer switch, which I thought was causing the problem, so call back the wireman.

He checked and found that the one line is carrying 33 light points (including 16 T5s and 10 mLED downlights) and 1 fan.  rclxub.gif  rclxub.gif  rclxub.gif
But I very seldom on everything. usually max 7-10 lights only.

He thinks it overload, and 'partition' some load over to the nearby 20A MCB. Don't know what it means.

But the RCCB still trips randomly. Although now can reset.

Any ideas how to approach?  I suspect some wire are overheating, that why after a while cooling down the problem goes away, only to happen again later.
*
RCCB trip is telling you that something is shortcircuit. But not overload. If it overload, the MCB through that line will trip.

Since you able to isolate the problem and only that line cause the trip, it is much more easy to troubleshoot. But your electrician diagnose wrongly. Since all the light and electrical thing able to ON without cause the MCB trip, that mean there is no overload on that line.

For the shortcircuit, you have to look at the lighting, timer, fan, etc on that line. There is something faulty there. But which 1. So you need to further isolated those thing to 1 by 1 or by the switching group. ON 1 switch at a time and see will it trip. If no, than OFF it and proceed another switch ON. Till you find that cause tripping.

If this group of light cause tripping, than need to further isolate which light is cause the trip. You need to disconnect the light 1 by 1 and try to ON to find that spoil 1 that cause the trip.
DMegaMall
post Jul 6 2015, 12:25 PM

New Member
*
Newbie
2 posts

Joined: Oct 2012
From: Tropicana City Mall, Petaling Jaya.


Hi, my house is having the the same issue during thunderstom, my RCCB will always trip even on a minor "lightning", thinking of changing the RCCB, should I change to 30mA/100mA or 300mA? Which one is less sensitive to lightning?
Kiding
post Jul 6 2015, 09:45 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(DMegaMall @ Jul 6 2015, 12:25 PM)
Hi, my house is having the the same issue during thunderstom, my RCCB will always trip even on a minor "lightning", thinking of changing the RCCB, should I change to 30mA/100mA or 300mA? Which one is less sensitive to lightning?
*
Start reading from post #97 onward !
gagak_84
post Dec 13 2015, 10:26 PM

Getting Started
**
Junior Member
132 posts

Joined: Dec 2008
From: Seremban, Port Dickson


guys.. need some help..

my new house RCCB always trip during raining.

incomer from TNB goes to this
R,Y,B = 32A,415V and 10kA
looks like SPD but no earthing pole from this one

outgoing goes to RCCB in which the specs is
63A 415V 100mA

im thinking to change the RCCB with good brand such as ABB with same specs.
if the same thing happen i would install new SPD with earthing pole

another thing is my neutral terminal at DB box doesnt jump to earting terminal, i saw some videos and most of it jumped together.


gagak_84
post Dec 13 2015, 11:13 PM

Getting Started
**
Junior Member
132 posts

Joined: Dec 2008
From: Seremban, Port Dickson


Attached Image

is it normal 32A fuse for each phase goes to 63A RCCB? why dont used 63A fuse instead

This post has been edited by gagak_84: Dec 14 2015, 02:42 PM
ozak
post Dec 14 2015, 10:39 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(gagak_84 @ Dec 13 2015, 10:26 PM)
guys.. need some help..

my new house RCCB always trip during raining.

incomer from TNB goes to this
R,Y,B = 32A,415V and 10kA
looks like SPD but no earthing pole from this one

outgoing goes to RCCB in which the specs is
63A 415V 100mA

im thinking to change the RCCB with good brand such as ABB with same specs.
if the same thing happen i would install new SPD with earthing pole

another thing is my neutral terminal at DB box doesnt jump to earting terminal, i saw some videos and most of it jumped together.
*
RCCB is not the problem. It work fine. RCCB is not using earth to trip cause it is not a ELCB.

You have 3 choice to reduce the trip.

1) change the RCCB to less sensitive to 300mA or 0.3A. But will delay the trip if any short circuit.
2) Install a surge protector to absorb the surge voltage. It will channel the surge to earth. So your earth rod need to be good.
3) Check the earth rod infront your garden. The checking is in Ohm which less ohm is better. (below 100ohm)


weikee
post Dec 14 2015, 11:27 PM

10k Club
********
All Stars
12,019 posts

Joined: Jan 2003
If your RCCB trip, mean you have leakage.

During rainy day water may have enter some wiring and water conduct electric, so the electric current are leak thought the water.
jackbanner
post Dec 15 2015, 10:56 AM

On my way
****
Senior Member
660 posts

Joined: Jun 2009
Wher did u buy the Sine Tamer?


QUOTE(macgy @ Oct 18 2013, 12:44 PM)
I am searching to increase the sensitivity of my RCCD to induce more frequent tripping and saw this forum...totally opposite of what i m looking for but here is my comment...Increasing RCCD beyond 100mA is dangerous, please avoid doing so, RCCD is installed to save lifes.
If it is due to lightning, a good surge protection device (SPD/TVSS) will be able to solve the problem, increase in surge will be absorb by the device, look for 1 with 10 modes protection if tripping is too frequent, otherwise 7 modes protection device is sufficient for a house and choose 1 with the longest warranty (rules of thumb..length of warranty=quality), my problem was sorted out...using an american brand, Sine Tamer. thumbup.gif
*
jackbanner
post Dec 15 2015, 12:29 PM

On my way
****
Senior Member
660 posts

Joined: Jun 2009
Have u solved this problem?
If u have, how did u do it?


QUOTE(Fazab @ Jun 20 2015, 12:54 AM)
Hi sifus

My new house RCCB 63A 0.1A  tripping randomly.
Did the usual diagnosis and trace the problem to one line supplying the front lights.
When the MCB (6A) for this in ON, cannot reset the RCCB, trips immediately.
When I OFF this MCB, then only can reset the RCCB. 
After sometime however can reset back with that MCB ON.

The problem is transient, sekejap ada, sekejap OK.

The faulty line has a timer switch, which I thought was causing the problem, so call back the wireman.

He checked and found that the one line is carrying 33 light points (including 16 T5s and 10 mLED downlights) and 1 fan.  rclxub.gif  rclxub.gif  rclxub.gif
But I very seldom on everything. usually max 7-10 lights only.

He thinks it overload, and 'partition' some load over to the nearby 20A MCB. Don't know what it means.

But the RCCB still trips randomly. Although now can reset.

Any ideas how to approach?  I suspect some wire are overheating, that why after a while cooling down the problem goes away, only to happen again later.
*
gagak_84
post Dec 15 2015, 03:46 PM

Getting Started
**
Junior Member
132 posts

Joined: Dec 2008
From: Seremban, Port Dickson


QUOTE(ozak @ Dec 14 2015, 10:39 PM)
RCCB is not the problem. It work fine. RCCB is not using earth to trip cause it is not a ELCB.

You have 3 choice to reduce the trip.

1) change the RCCB to less sensitive to 300mA or 0.3A. But will delay the trip if any short circuit.
2) Install a surge protector to absorb the surge voltage. It will channel the surge to earth. So your earth rod need to be good.
3) Check the earth rod infront your garden. The checking is in Ohm which less ohm is better. (below 100ohm)
*
on no 3, how to check the ohm on the rod i saw someone said Hager and schneider RCCB equipped by anti-storm protection.. is that true??

Thinking of to change my current RCCB with this one

user posted image

This post has been edited by gagak_84: Dec 15 2015, 03:59 PM
ozak
post Dec 15 2015, 04:09 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(gagak_84 @ Dec 15 2015, 03:46 PM)
on no 3, how to check the ohm on the rod i saw someone said Hager and schneider RCCB equipped by anti-storm protection.. is that true??

Thinking of to change my current RCCB with this one

user posted image
*
The earth rod only can be check with earth meter. Which some electrician have.

You can try to change. But the 0.1A is sensitive. It still will trip. But lesser.
gagak_84
post Dec 15 2015, 04:28 PM

Getting Started
**
Junior Member
132 posts

Joined: Dec 2008
From: Seremban, Port Dickson


can i check whether my equipment have earth leakage at DB box..
which i check whether earthing din-rail has live current using test pen
ozak
post Dec 15 2015, 04:39 PM

10k Club
********
All Stars
17,021 posts

Joined: Jan 2005


QUOTE(gagak_84 @ Dec 15 2015, 04:28 PM)
can i check whether my equipment have earth leakage at DB box..
which i check whether earthing din-rail has live current using test pen
*
Leave it to the electrician to check if you not experience.

Electric can kill. Don't touch if you really not sure.

Your house is running 3P. Phase to phase is 415V. It is dangerous.
Kiding
post Dec 26 2015, 12:18 AM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


I'm interesting in this ABB OVR T2 SPD (http://new.abb.com/products/ABB2CTB802341R8000), planing to install it in the DB

user posted image

I'm wondering will it reduce the frequent RCCB trip when lighting hit nearby my house, I stay at the hill top, whenever lightning hit nearby, it is very high chance the RCCB will trip!
sonerin
post Dec 26 2015, 08:07 AM

Look at all my stars!!
*******
Senior Member
8,739 posts

Joined: Aug 2009
QUOTE(Kiding @ Dec 26 2015, 12:18 AM)
I'm interesting in this ABB OVR T2 SPD (http://new.abb.com/products/ABB2CTB802341R8000), planing to install it in the DB

user posted image

I'm wondering will it reduce the frequent RCCB trip when lighting hit nearby my house, I stay at the hill top, whenever lightning hit nearby, it is very high chance the RCCB will trip!
*
Is better to go for hager brand on lighting surge protector