QUOTE(chiehlim @ Jan 4 2011, 10:42 PM)
Hi Shazzac,
You got confused when I mentioned the fuse. It is not the fuse to my home supply (else indoor unit and all my lights will be off). I mean the fuse inside the external unit (the compressor).
My aircon technician checked the connections and piping and all ok (no leaking, electric supply is there to the input of the compressor). He suggested me to call up Daikin support. I did and now waiting for them to respond. However, just want to check with this forum to see if anyone has the same experience and what is the root cause. I don't want to get conned or given lame excuse by Daikin ppl.
Regards
Lim
If thats the case, i can only think of :
1) Your compressor capacitor need to be replaced. Without the capacitor's help, the compressor dont have enough "juice" to start up even though there is a supply flowing into it.
2) Ask your technician to check whether the compressor is really running by using ampere clamp meter and clamp the live wire to see if there are any amperage. If the ampere value is below 1 to 0.1, that mean your compressor doesnt run. If the ampere goes high such as >15 Ampere, that mean your compressor already jammed. There is 1 more thing, the "thermal relay" on your compressor already spoiled. This relay acted up as overheat protection to the compressor. It the compressor overheat, it will cut off the power to the compressor. You can try to bypass this relay if there are any.
P/s : there is a label/sticker on the ourdoor unit that stated model, running ampere and more. Check the running ampere value, ask your technician to bring ampere clamp meter to check if the value on the meter are the same as the sticker/label. Perfect running unit should give almost identical value
This post has been edited by Erza Scarlet: Jan 7 2011, 11:02 AM