and after the 2 Pole 63A incoming MCB , the outgoing Cable is using 10mm not 16mm
This post has been edited by 13aby: Jul 25 2024, 07:06 PM
2 Poles MCB Incoming TNB Power
|
|
Jul 25 2024, 07:05 PM, updated 2y ago
Show posts by this member only | Post
#1
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
My house all Eletrical on to max Test incoming Power only around 10A . Means i can change to 2Pole 32A MCB? Developer give now all 63A (1 x 2Pole MCB , 1x 100mA and 30mA) All 63A macam too much .
and after the 2 Pole 63A incoming MCB , the outgoing Cable is using 10mm not 16mm This post has been edited by 13aby: Jul 25 2024, 07:06 PM |
|
|
|
|
|
Jul 25 2024, 07:29 PM
Show posts by this member only | Post
#2
|
![]()
Newbie
44 posts Joined: Nov 2011 |
what?
|
|
|
Jul 25 2024, 07:41 PM
Show posts by this member only | Post
#3
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
QUOTE(syaifau @ Jul 25 2024, 07:29 PM) Dont la like this bro i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On . Or i just follow back Developer 63A Advice please |
|
|
Jul 25 2024, 09:53 PM
Show posts by this member only | Post
#4
|
![]()
Newbie
44 posts Joined: Nov 2011 |
My knowledge in electrical is so vastly impaired, i cant even advise myself.
All the best with your investigation, @13aby |
|
|
Jul 26 2024, 12:42 AM
Show posts by this member only | IPv6 | Post
#5
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(13aby @ Jul 25 2024, 08:41 PM) Dont la like this bro 2 AC , 2 WH on already is about 20 A .i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On . Or i just follow back Developer 63A Advice please |
|
|
Jul 26 2024, 01:14 AM
Show posts by this member only | IPv6 | Post
#6
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(13aby @ Jul 25 2024, 08:05 PM) My house all Eletrical on to max Test incoming Power only around 10A . Means i can change to 2Pole 32A MCB? Developer give now all 63A (1 x 2Pole MCB , 1x 100mA and 30mA) All 63A macam too much . use MCB 20 A for AC, WH , 4 mm cable and after the 2 Pole 63A incoming MCB , the outgoing Cable is using 10mm not 16mm MCB 6A for lightning. 1.5mm MCB 16 A for 3 pin socket . 2.5mm for RCCB 63A , 100mA for mains ,25mm cable RCCB 63A , 30mA for the 3 pin sockets , 2.5mm cable RCCB 63A , 10mA for WH , 4mm post a pix of your DB box better to advise you. gobiomani liked this post
|
|
|
|
|
|
Jul 26 2024, 09:46 PM
Show posts by this member only | Post
#7
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Jul 26 2024, 09:48 PM
Show posts by this member only | Post
#8
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
QUOTE(Momo33 @ Jul 26 2024, 01:14 AM) use MCB 20 A for AC, WH , 4 mm cable Using 63A incoming 2 Pole MCB and others 2 Main RCCB 63A also no problem? both is 100mA and 30mA now . Cable to 100mA and 30mA Developer give 10mm but the incoming TNB is 16mm . for the cable size min is 16mm for 63AMCB 6A for lightning. 1.5mm MCB 16 A for 3 pin socket . 2.5mm for RCCB 63A , 100mA for mains ,25mm cable RCCB 63A , 30mA for the 3 pin sockets , 2.5mm cable RCCB 63A , 10mA for WH , 4mm post a pix of your DB box better to advise you. My is High Rise Property This post has been edited by 13aby: Jul 26 2024, 09:48 PM |
|
|
Jul 26 2024, 11:41 PM
Show posts by this member only | Post
#9
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Jul 27 2024, 12:26 AM
Show posts by this member only | IPv6 | Post
#10
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(13aby @ Jul 26 2024, 10:48 PM) Using 63A incoming 2 Pole MCB and others 2 Main RCCB 63A also no problem? both is 100mA and 30mA now . Cable to 100mA and 30mA Developer give 10mm but the incoming TNB is 16mm . for the cable size min is 16mm for 63A looks fine . pix too. My is High Rise Property This post has been edited by Momo33: Jul 27 2024, 12:27 AM |
|
|
Jul 27 2024, 06:32 PM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
Jul 27 2024, 08:01 PM
Show posts by this member only | IPv6 | Post
#12
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(13aby @ Jul 27 2024, 07:32 PM) change over to Hager is better cos hager products good quality hence bit price higher. the items your developer use i also never see this brand before.... maybe unknown china product no sirim too . gobiomani liked this post
|
|
|
Jul 30 2024, 12:04 PM
|
![]() ![]() ![]() ![]() ![]()
Senior Member
975 posts Joined: Jan 2009 |
|
|
|
|
|
|
Jul 30 2024, 01:37 PM
|
![]() ![]()
Junior Member
128 posts Joined: Jun 2011 |
I think you can check the authenticity at https://hager.com/_en/check
|
|
|
Aug 10 2024, 01:52 PM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
4,950 posts Joined: Jul 2010 |
QUOTE(Momo33 @ Jul 26 2024, 01:14 AM) use MCB 20 A for AC, WH , 4 mm cable May I know why you use 63A RCCB instead of 25A RCCB for WH since there should be a 20A MCB for WH to protect the RCCB?MCB 6A for lightning. 1.5mm MCB 16 A for 3 pin socket . 2.5mm for RCCB 63A , 100mA for mains ,25mm cable RCCB 63A , 30mA for the 3 pin sockets , 2.5mm cable RCCB 63A , 10mA for WH , 4mm post a pix of your DB box better to advise you. |
|
|
Aug 10 2024, 02:28 PM
Show posts by this member only | IPv6 | Post
#16
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
QUOTE(mushigen @ Aug 10 2024, 02:52 PM) May I know why you use 63A RCCB instead of 25A RCCB for WH since there should be a 20A MCB for WH to protect the RCCB? if you know your WH amp rating then chose accordingly .yes can use rccb 25A, 10mA for those instant WH / 4kW type. 63A one can handle a heavy current rccb do not trip on over current . mushigen liked this post
|
|
|
Aug 10 2024, 02:32 PM
Show posts by this member only | IPv6 | Post
#17
|
![]() ![]() ![]() ![]() ![]() ![]()
Senior Member
1,448 posts Joined: Oct 2019 |
|
|
|
Aug 12 2024, 02:01 AM
Show posts by this member only | IPv6 | Post
#18
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(13aby @ Jul 26 2024, 11:41 PM) It’s already sized correctly. Don’t waste moneyWhat I would suggest is to redo the pigtails as there is a minimum bend radius (don't hard turn 90 degrees), keep the cable curved gently. Nanti patah inside and create hotspot. This post has been edited by ceo684: Aug 12 2024, 02:12 AM |
|
|
Aug 12 2024, 02:02 AM
Show posts by this member only | IPv6 | Post
#19
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(13aby @ Jul 30 2024, 12:04 PM) Make sure buy from proper seller. Many recon ABB and Hager from Singapore HIP refurbishing land in MY. Plus why don’t you get 6kA withstand model instead of the 4.5kA. ABB not expensive for 6kAThis post has been edited by ceo684: Aug 12 2024, 02:04 AM |
|
|
Aug 12 2024, 02:06 AM
|
![]() ![]() ![]() ![]() ![]() ![]() ![]() ![]()
All Stars
11,667 posts Joined: Jan 2003 From: Klang/Subang |
QUOTE(13aby @ Jul 25 2024, 07:41 PM) Dont la like this bro Your clamp meter not true RMS is it.i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On . Or i just follow back Developer 63A Advice please One unit WH running from cold already take 14-16A easily. The 16mm one you can buy Mega Kabel meter loose cut in the correct colours (red and black) as necessary, but if your supply (from meter) is 10mm then no point lah. Also, not much use for the 100mA RCD when the 30mA RCD is capable for whole house sockets and lights. There is little point in using the 100mA RCD in modern day without fluorescent tube lights. This post has been edited by ceo684: Aug 12 2024, 02:09 AM |
| Change to: | 0.0232sec
0.32