2 Poles MCB Incoming TNB Power
|
SUSceo684
|
Aug 12 2024, 02:01 AM
|
|
QUOTE(13aby @ Jul 26 2024, 11:41 PM)  here is the photo of the incoming (Bottom Left) to two RCCB It’s already sized correctly. Don’t waste money What I would suggest is to redo the pigtails as there is a minimum bend radius (don't hard turn 90 degrees), keep the cable curved gently. Nanti patah inside and create hotspot. This post has been edited by ceo684: Aug 12 2024, 02:12 AM
|
|
|
|
|
|
SUSceo684
|
Aug 12 2024, 02:02 AM
|
|
QUOTE(13aby @ Jul 30 2024, 12:04 PM)  Bought from two different place , why color different? Make sure buy from proper seller. Many recon ABB and Hager from Singapore HIP refurbishing land in MY. Plus why don’t you get 6kA withstand model instead of the 4.5kA. ABB not expensive for 6kA This post has been edited by ceo684: Aug 12 2024, 02:04 AM
|
|
|
|
|
|
SUSceo684
|
Aug 12 2024, 02:06 AM
|
|
QUOTE(13aby @ Jul 25 2024, 07:41 PM) Dont la like this bro i not sure i clamp wrong or it really so low , 2 Airconds 2 WH this two is the biggest power eater i guess . Cuckoo , Air Fryer , Washine Machine and Fridge all On . Or i just follow back Developer 63A  because i planning to change all to HAGER . and mayb the 10mm to 16mm Advice please  Your clamp meter not true RMS is it. One unit WH running from cold already take 14-16A easily. The 16mm one you can buy Mega Kabel meter loose cut in the correct colours (red and black) as necessary, but if your supply (from meter) is 10mm then no point lah. Also, not much use for the 100mA RCD when the 30mA RCD is capable for whole house sockets and lights. There is little point in using the 100mA RCD in modern day without fluorescent tube lights.This post has been edited by ceo684: Aug 12 2024, 02:09 AM
|
|
|
|
|
|
SUSceo684
|
Aug 12 2024, 08:11 PM
|
|
QUOTE(13aby @ Aug 12 2024, 04:33 PM) Sent , but no reply from them since ever haha Yes i bought from Authorised Reseller / Distributor shop (Pentapower(M) Sdn Bhd (Puchong) & (CPE Electrical Supplier via Shopee). But they say use 4.5k is enough . Or should i change all to 6k as developer provide? Ya i redo the reading correct already , 1 WH running around 14A .... Incoming is 16mm from meter but thn 10mm to both RCCB (100mA & 30mA) For my WH , Developer no give RCCB / RCBO i added myself for safety . Forget the 100mA RCD (buang), rerun with 16mm inside the DB. That 10mm is only good for ard 40A and can create a hotspot which is unprotected because it is supposed to be 16mm throughout.
|
|
|
|
|
|
SUSceo684
|
Aug 12 2024, 10:18 PM
|
|
QUOTE(13aby @ Aug 12 2024, 09:07 PM) means only use 1nos 30mA whole whole house? The empty space is 2 nos RCCB 0.01 .. not yet install when snap this  Yes. According to MS1979 COP it is allowed. And safer too for changing lights.
|
|
|
|
|
|
SUSceo684
|
Aug 13 2024, 02:50 AM
|
|
QUOTE(13aby @ Aug 12 2024, 10:41 PM) My neutral bar is separated by two sides , can i connect both side by tapping a wire? or need to replace a longer bar Common neutral, use a 16mm Mega Kabel pigtail.
|
|
|
|
|
|
SUSceo684
|
Aug 13 2024, 10:07 AM
|
|
QUOTE(13aby @ Aug 13 2024, 10:02 AM) U mean connect with a 16mm cable like photo ? 10mm boleh?  Beli lah one meter of 16mm. Less than 10 bucks per meter only. 10mm not good enough. https://s.lazada.com.my/s.PTisA
|
|
|
|
|
|
SUSceo684
|
Aug 14 2024, 05:14 AM
|
|
QUOTE(13aby @ Aug 13 2024, 11:22 AM) 16mm i got spare , so i just tap the wire to connect the both bar ya Yes, do a smooth horseshoe shape
|
|
|
|
|
|
SUSceo684
|
Aug 15 2024, 09:27 AM
|
|
QUOTE(13aby @ Aug 14 2024, 05:52 PM) just notice i dont have cutter size to cut 16mm haha , any recommendations for the cutter? MTC-45 or 47 cutters. (the biggest one) This post has been edited by ceo684: Aug 15 2024, 09:28 AM
|
|
|
|
|
|
SUSceo684
|
Aug 21 2024, 12:32 PM
|
|
QUOTE(13aby @ Aug 17 2024, 02:31 PM) 100mA removed and all now using 30mA RCCB  The MCBs should ideally use the same brand so they're the same height. Attached thumbnail(s)
|
|
|
|
|
|
SUSceo684
|
Aug 23 2024, 08:14 PM
|
|
QUOTE(prophecus @ Aug 22 2024, 09:27 AM) Developers have to comply to wiring regulation by Suruhanjaya Tenaga. 10 mA for water heater and wet area. 30 mA for sockets. 100mA for lighting and AC. Dei. Read back MS1979 COP on the RCDs and ER1994 regulation. Especially the highlighted word.QUOTE(prophecus @ Aug 22 2024, 09:27 AM) in the UK they have moved on to RCBO. No more RCCB as it is included in each circuit. So if there is leakage only individual circuit would trip not the whole house. In Malaysia RCBO is available for Water heater (20A, 10mA trip), the rest not widely available yet or price too expensive. Not economical to use RCBO for every circuit. Even for WH they do not carry the correct size of 20A/10mA. Most of the common RCBO is still 25A/10mA which is incorrect for the 2.5mm cut corner cables commonly installed. This post has been edited by ceo684: Aug 23 2024, 08:26 PM Attached thumbnail(s)
Attached File(s)
ms.1979.2007.pdf ( 1.25mb )
Number of downloads: 2
SuruhanjayaTenagaGuidelinesForElectricalWiringInResidentialBuildings.pdf ( 427.2k )
Number of downloads: 3
|
|
|
|
|