TSsubaiku
post Jun 30 2022, 04:10 PM, updated 4y ago

Casual
***
Junior Member
445 posts

Joined: Oct 2008
Literally got shocked last night when I was using the shower. Mine is a steel shower set type. Got zapped when I touched it!

Tested with one of those electricity meters, definitely got current. WTF. Anybody else had this problem before? I've got a Joven water heater installed above the ceiling. Is it caused by the heater or something else? Don't know if it's related or not but a few days ago switching on another water heater keep tripping the whole house (also the same model JH25).


Attached thumbnail(s)
Attached Image
H3artBreakKid
post Jun 30 2022, 04:13 PM

๐Ÿ’”๐Ÿ’”๐Ÿ’”
***
Junior Member
454 posts

Joined: Jun 2012


high rise or landed?
TSsubaiku
post Jun 30 2022, 04:15 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(H3artBreakKid @ Jun 30 2022, 04:13 PM)
high rise or landed?
*
Well, condo but mine's only 6 floors, I'm on the ground floor.
Aftermaths
post Jun 30 2022, 04:16 PM

On my way
****
Junior Member
601 posts

Joined: Apr 2012


QUOTE(H3artBreakKid @ Jun 30 2022, 04:13 PM)
high rise or landed?
*
I believe is landed with central water heater.

Personally I'll suggest TS to change into wall type for each toilet.

dawho
post Jun 30 2022, 04:17 PM

Enthusiast
*****
Senior Member
782 posts

Joined: Oct 2009



this means got some leak in your wiring....
jessicakoh
post Jun 30 2022, 04:31 PM

Getting Started
**
Junior Member
51 posts

Joined: Jan 2007
ELCB test button ok?
TSsubaiku
post Jun 30 2022, 04:52 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(jessicakoh @ Jun 30 2022, 04:31 PM)
ELCB test button ok?
*
Errr, mine got no ELCB button like those wall mounted type.

» Click to show Spoiler - click again to hide... «

nihility
post Jul 2 2022, 08:11 PM

Regular
******
Senior Member
1,596 posts

Joined: Sep 2021


You are fortunate that you are still alive. Go get licensed wiremen to check the wiring & compliance to ST guide for the water heater installation.
davidlow7
post Jul 4 2022, 10:17 AM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(nihility @ Jul 2 2022, 08:11 PM)
You are fortunate that you are still alive. Go get licensed wiremen to check the wiring & compliance to ST guide for the water heater installation.
*
There is a leak in your wiring.

Hopefully you have had a 10mA dedicated RCCB with its dedicated wiring installed for the water heater only, as it is crucial in saving lives.

ELCB from your heater will not detect leakage OUTSIDE the WH so the RCCB is important.
TSsubaiku
post Jul 4 2022, 05:34 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(nihility @ Jul 2 2022, 08:11 PM)
You are fortunate that you are still alive. Go get licensed wiremen to check the wiring & compliance to ST guide for the water heater installation.
*
Thanks for the input, have first asked the Joven technician to come take a look. Then will ask an electrician to double check. Got a phobia now touching anything metal that's connected to an electrical connection. sad.gif

Sorry, a bit of a noob re: electrical stuff, what's this ST guide you mentioned?
TSsubaiku
post Jul 4 2022, 05:35 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(davidlow7 @ Jul 4 2022, 10:17 AM)
There is a leak in your wiring.

Hopefully you have had a 10mA dedicated RCCB with its dedicated wiring installed for the water heater only, as it is crucial in saving lives.

ELCB from your heater will not detect leakage OUTSIDE the WH so the RCCB is important.
*
Thanks for the input! Will definitely look into this. Found a thread that seems to be talking about what you're suggesting..

https://forum.lowyat.net/index.php?showtopic=4938749&st=
davidlow7
post Jul 4 2022, 10:41 PM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(subaiku @ Jul 4 2022, 05:35 PM)
Thanks for the input! Will definitely look into this. Found a thread that seems to be talking about what you're suggesting..

https://forum.lowyat.net/index.php?showtopic=4938749&st=
*
There's a latest guideline from ST
https://www.st.gov.my/en/contents/files/dow...N_DOMESTIK1.pdf
rjmsfire
post Jul 16 2022, 10:13 PM

Getting Started
**
Junior Member
77 posts

Joined: Apr 2011
https://www.todayonline.com/singapore/elder...-heater-1841166

You are lucky didn't get electrocuted to death. This news article of a case in Singapore has some technical explanations of how it can happen.
TSsubaiku
post Jul 18 2022, 04:15 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(rjmsfire @ Jul 16 2022, 10:13 PM)
https://www.todayonline.com/singapore/elder...-heater-1841166

You are lucky didn't get electrocuted to death. This news article of a case in Singapore has some technical explanations of how it can happen.
*
Thanks for the link. Yes, lucky indeed.. read the article, although slightly different from my case, but the thing to take note is this:

user posted image
TSsubaiku
post Jul 18 2022, 04:43 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
Ok guys, really thanks for all the input, just wanted to update for everybody's future reference because this was scary AF. So this is what actually happened.

Got the Joven technician to come over and check, turns out it is the heater element that was spoilt. But usually if this happens, turning on the water heater would have tripped the current box. However it did not, instead the current was running through the copper piping then into the steel shower head. F*ck.

So, got heater element fixed and then got my electrician to come take a look to find out why it didn't trip as it should have. Turns out the ground wire for the water heater was not connected to anything! shocking.gif This one is probably due to my previous crappy contractor who did my reno who also installed the water heaters. Was a vomit blood experience but that's another story.

What the electrician did then was to connect the ground wire from my nearby air ventilator to the water heater's ground wire so in future should trip if anything goes wrong. He says should be safe enough. But can also do further precaution by installing RCBO for the water heater at the current box.

Sorry if I have wrongly described anything as my electrical knowledge is nil. Anyways I'm considering getting these RCBO models, all got various prices... any advice?

https://shopee.com.my/%F0%9F%86%9ACHINT-NXB...77-d1d65bb4a703

https://shopee.com.my/MAXGUARD-20A-32A-2P-1...b3-07b2a2953144

This one is the cheapest, but... is it any good? sweat.gif
https://shopee.com.my/CNC-YCB9NL-40-230V-RC...fb-5b0e8b96535e
gobiomani
post Jul 19 2022, 12:21 PM

Enthusiast
*****
Junior Member
709 posts

Joined: Jun 2019

QUOTE(subaiku @ Jul 18 2022, 04:43 PM)
Ok guys, really thanks for all the input, just wanted to update for everybody's future reference because this was scary AF. So this is what actually happened.

Got the Joven technician to come over and check, turns out it is the heater element that was spoilt. But usually if this happens, turning on the water heater would have tripped the current box. However it did not, instead the current was running through the copper piping then into the steel shower head. F*ck.

So, got heater element fixed and then got my electrician to come take a look to find out why it didn't trip as it should have. Turns out the ground wire for the water heater was not connected to anything!  shocking.gif This one is probably due to my previous crappy contractor who did my reno who also installed the water heaters. Was a vomit blood experience but that's another story.

What the electrician did then was to connect the ground wire from my nearby air ventilator to the water heater's ground wire so in future should trip if anything goes wrong. He says should be safe enough. But can also do further precaution by installing RCBO for the water heater at the current box.

Sorry if I have wrongly described anything as my electrical knowledge is nil. Anyways I'm considering getting these RCBO models, all got various prices... any advice?

https://shopee.com.my/%F0%9F%86%9ACHINT-NXB...77-d1d65bb4a703

https://shopee.com.my/MAXGUARD-20A-32A-2P-1...b3-07b2a2953144

This one is the cheapest, but... is it any good?  sweat.gif
https://shopee.com.my/CNC-YCB9NL-40-230V-RC...fb-5b0e8b96535e
*
If going for RCBO get the Schneider one - around RM130. Better still if your DB box has sufficient space, get RCCB 10mA from ABB or Hager, its around RM150 for ABB and RM190 for Hager. If using RCCB, you still need a MCB.
Don't cheap out on breakers and RCDs.
stormer.lyn
post Jul 19 2022, 02:17 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(subaiku @ Jul 18 2022, 04:43 PM)
Only the middle one, Maxguard, is the correct specifications for a water heater at a sensitivity of 10 mA or 0.01 A
katijar
post Jul 19 2022, 05:15 PM

Look at all my stars!!
*******
Senior Member
2,294 posts

Joined: Sep 2011
i think the shower head and hose cant use metal one ...

need change to plastic/rubber
Kiding
post Jul 19 2022, 07:13 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


QUOTE(gobiomani @ Jul 19 2022, 12:21 PM)
If going for RCBO get the Schneider one - around RM130. Better still if your DB box has sufficient space, get RCCB 10mA from ABB or Hager, its around RM150 for ABB and RM190 for Hager. If using RCCB, you still need a MCB.
Don't cheap out on breakers and RCDs.
*
Fully agreed, all water heater must install along with RCCB or RCBO, this is to add second protection measure, if the first protection failed like TS said, then second protection will save your life. a good quality RCCB with installation just cost less than RM500, your life is definitely worth more than RM500.

TSsubaiku
post Jul 20 2022, 10:47 AM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(gobiomani @ Jul 19 2022, 12:21 PM)
If going for RCBO get the Schneider one - around RM130. Better still if your DB box has sufficient space, get RCCB 10mA from ABB or Hager, its around RM150 for ABB and RM190 for Hager. If using RCCB, you still need a MCB.
Don't cheap out on breakers and RCDs.
*
Ok, thanks! Will look into the Schneider ones... sorry noob question, not sure if I have a MCB? This is my DB box currently...

Attached Image Attached Image

This post has been edited by subaiku: Jul 20 2022, 10:47 AM
TSsubaiku
post Jul 20 2022, 10:49 AM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(stormer.lyn @ Jul 19 2022, 02:17 PM)
Only the middle one, Maxguard, is the correct specifications for a water heater at a sensitivity of 10 mA or 0.01 A
*
Ah thanks! What do you think about this brand? Recommended by the electrician...

Attached Image
candidman78
post Jul 20 2022, 10:52 AM

Getting Started
**
Junior Member
141 posts

Joined: Dec 2010


QUOTE(subaiku @ Jun 30 2022, 04:10 PM)
Literally got shocked last night when I was using the shower. Mine is a steel shower set type. Got zapped when I touched it!

Tested with one of those electricity meters, definitely got current. WTF. Anybody else had this problem before? I've got a Joven water heater installed above the ceiling. Is it caused by the heater or something else? Don't know if it's related or not but a few days ago switching on another water heater keep tripping the whole house (also the same model JH25).
*
JOVEx again haha. BTW, I dont believe any build in electronics ELCB.
Only 2 brands I found is using Electro-Magnetic. ELCB.

YET to me is not enough and by the rules regardless whether the unit comes with built in, they must have an exter RCCB, RCB, RCBO 10mA.

And probably 99.99% user ignore
stormer.lyn
post Jul 20 2022, 01:36 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(subaiku @ Jul 20 2022, 10:49 AM)
Ah thanks! What do you think about this brand? Recommended by the electrician...

Attached Image
*
Sorry, never used before. There's something you must realise which unfortunately is this: Contractors don't recommend something based on your best interest. They recommend something because it is easy to purchase, or that is what they have in stock, or it has a large profit margin, etc.

You also cannot trust something simply because it has a SIRIM sticker. You must get something that has a SIRIM sticker that has passed electrical specifications. A company could very well get a SIRIM sticker on the claimed weight of the item.

That being said, if funds are limited, then go for Maxguard, EPS or Himel branded RCBO with these specs : 20 A overcurrent, 10 mA trip. All have SIRIM and are JKR approved*, meaning they have at least been electrically tested by someone independently. If you go for an RCCB instead of RCBO, then get 25 A, 10 mA trip. The 25A is because there will be an additional MCB for the water heater. NOTE: these specs are if your WH is below, say, 4500 W, which it probably is. Please review if the WH happens to be above this wattage.

I can tell you that the store "Combi Electric" online delivers very fast, and price is fair. Now, saying that "Contractors don't recommend something based on your best interest" why should you trust me? I have absolutely no connection to the store just stated, I am not making money off you, and I am only recommending this based on your safety, because I can't get anything else from you!

Disclaimer: * last time I checked
Selene Yeo
post Jul 20 2022, 04:36 PM

Getting Started
**
Junior Member
149 posts

Joined: Feb 2021


QUOTE(subaiku @ Jul 18 2022, 04:43 PM)
Ok guys, really thanks for all the input, just wanted to update for everybody's future reference because this was scary AF. So this is what actually happened.

Got the Joven technician to come over and check, turns out it is the heater element that was spoilt. But usually if this happens, turning on the water heater would have tripped the current box. However it did not, instead the current was running through the copper piping then into the steel shower head. F*ck.

So, got heater element fixed and then got my electrician to come take a look to find out why it didn't trip as it should have. Turns out the ground wire for the water heater was not connected to anything!  shocking.gif This one is probably due to my previous crappy contractor who did my reno who also installed the water heaters. Was a vomit blood experience but that's another story.

What the electrician did then was to connect the ground wire from my nearby air ventilator to the water heater's ground wire so in future should trip if anything goes wrong. He says should be safe enough. But can also do further precaution by installing RCBO for the water heater at the current box.

Sorry if I have wrongly described anything as my electrical knowledge is nil. Anyways I'm considering getting these RCBO models, all got various prices... any advice?

https://shopee.com.my/%F0%9F%86%9ACHINT-NXB...77-d1d65bb4a703

https://shopee.com.my/MAXGUARD-20A-32A-2P-1...b3-07b2a2953144

This one is the cheapest, but... is it any good?  sweat.gif
https://shopee.com.my/CNC-YCB9NL-40-230V-RC...fb-5b0e8b96535e
*
Just to clarify, you are using a storage water heater correct? Not an instant water heater.

If it is a storage water heater, then FYI storage water heaters do not have a built-in circuit breaker like instant water heaters. So they have to rely on the DB box circuit breaker. BUT if your storage water heater is not grounded / no earth connection, no matter how good quality your circuit breaker is, the circuit breaker will not trip when there is a current leakage, and u will be electrocuted.

Hence why SIRIM / Suruhanjaya Tenaga now set a new guideline for storage water heaters to come with Isolation Barriers placed at both the storage water heaters' inlet and outlet water connection. Most SIRIM certified storage water heater brands already complied to this guideline, and some brands even took the extra safety effort to pre-install the isolation barriers on the heater, such as CENTON, which is extra good, considering some inexperienced installers will missed out installing the Isolation Barriers if they are not pre-installed on the heater out-of-the-box.

Isolation Barriers are simple devices that elongate any current flow from the storage water heater to users, so any current flow (if there is) will barely reach the users. So in your case where there is an unfortunate current leakage because of the lack of earthing, if your storage water heater is pre-installed with Isolation Barriers, the Isolation Barriers will protect u from electrocution to a certain extend. But every device has a lifespan as well, so u will probably be protected until the lifespan of the Isolation Barriers ended. So don't just rely on the Isolation Barriers to protect u. Installation and earthing connection has to be correct in the first place.

Basically just a safety tip for u, if your storage water heater do not have Isolation Barriers pre-installed, u are advised to install them.
stormer.lyn
post Jul 21 2022, 09:39 AM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(Selene Yeo @ Jul 20 2022, 04:36 PM)
If it is a storage water heater, then FYI storage water heaters do not have a built-in circuit breaker like instant water heaters. So they have to rely on the DB box circuit breaker. BUT if your storage water heater is not grounded / no earth connection, no matter how good quality your circuit breaker is, the circuit breaker will not trip when there is a current leakage, and u will be electrocuted.
*
This is the reason a 10 mA RCCB/RCBO is specified for water heaters, either instant or storage, whether your heater is Grounded/Earthed or not. You become the Ground/Earth point, and the RCCB/RCBO trips before a fatal current electrocutes you.
QUOTE
Isolation Barriers are simple devices that elongate any current flow from the storage water heater to users, so any current flow (if there is) will barely reach the users....
As for this, you should absolutely also use isolation barriers (basically, a section of non-conductive pipe to break the path of the hot water copper pipe), or use PP-R or PB pipes for hot water.

ElectroBOOM shows the effects of even a small gap of water on electrical conductivity on YouTube https://www.youtube.com/watch?v=dcrY59nGxBg&t=93s
TSsubaiku
post Jul 21 2022, 10:18 AM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(stormer.lyn @ Jul 20 2022, 01:36 PM)
Sorry, never used before. There's something you must realise which unfortunately is this: Contractors don't recommend something based on your best interest. They recommend something because it is easy to purchase, or that is what they have in stock, or it has a large profit margin, etc.

You also cannot trust something simply because it has a SIRIM sticker. You must get something that has a SIRIM sticker that has passed electrical specifications. A company could very well get a SIRIM sticker on the claimed weight of the item.

That being said, if funds are limited, then go for Maxguard, EPS or Himel branded RCBO with these specs : 20 A overcurrent, 10 mA trip. All have SIRIM and are JKR approved*, meaning they have at least been electrically tested by someone independently. If you go for an RCCB instead of RCBO, then get 25 A, 10 mA trip. The 25A is because there will be an additional MCB for the water heater. NOTE: these specs are if your WH is below, say, 4500 W, which it probably is. Please review if the WH happens to be above this wattage.

I can tell you that the store "Combi Electric" online delivers very fast, and price is fair. Now, saying that "Contractors don't recommend something based on your best interest" why should you trust me? I have absolutely no connection to the store just stated, I am not making money off you, and I am only recommending this based on your safety, because I can't get anything else from you!

Disclaimer: * last time I checked
*
"Contractors don't recommend something based on your best interest." Wise words. tongue.gif

Ok, thanks for the recommendations! Found these, these are the right ones right, as long as you get the 20A, 10ma versions? They all don't seem to have the earth fault indicator though which I read is important. Worth getting one with that in your opinion?
https://shopee.com.my/MAXGUARD-20A-2P10MA-T...9b-d362c89e75bc

https://shopee.com.my/Himel-HDB9PLEN40C-RCB...98-32ff6290e643

https://shopee.com.my/EPS-20A-25A-2P-10mA-6...fe-bfcd8624b2e9

Also, curious, how do you find out a product is JKR approved?
TSsubaiku
post Jul 21 2022, 10:38 AM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(Selene Yeo @ Jul 20 2022, 04:36 PM)
Just to clarify, you are using a storage water heater correct? Not an instant water heater.

If it is a storage water heater, then FYI storage water heaters do not have a built-in circuit breaker like instant water heaters. So they have to rely on the DB box circuit breaker. BUT if your storage water heater is not grounded / no earth connection, no matter how good quality your circuit breaker is, the circuit breaker will not trip when there is a current leakage, and u will be electrocuted.

Hence why SIRIM / Suruhanjaya Tenaga now set a new guideline for storage water heaters to come with Isolation Barriers placed at both the storage water heaters' inlet and outlet water connection. Most SIRIM certified storage water heater brands already complied to this guideline, and some brands even took the extra safety effort to pre-install the isolation barriers on the heater, such as CENTON, which is extra good, considering some inexperienced installers will missed out installing the Isolation Barriers if they are not pre-installed on the heater out-of-the-box.

Isolation Barriers are simple devices that elongate any current flow from the storage water heater to users, so any current flow (if there is) will barely reach the users. So in your case where there is an unfortunate current leakage because of the lack of earthing, if your storage water heater is pre-installed with Isolation Barriers, the Isolation Barriers will protect u from electrocution to a certain extend. But every device has a lifespan as well, so u will probably be protected until the lifespan of the Isolation Barriers ended. So don't just rely on the Isolation Barriers to protect u. Installation and earthing connection has to be correct in the first place.

Basically just a safety tip for u, if your storage water heater do not have Isolation Barriers pre-installed, u are advised to install them.
*
Yes, it's a storage water heater, the type that's installed up in the ceiling. Joven, model JH25.

Thanks for the tip about Isolation Barriers! So yeah, quite freaked about this whole affair. Went up and took a look, definitely no isolation barriers, copper piping all the way... second pic shows it going into concrete and connecting to my steel shower. And these were installed only 4 years ago. shocking.gif

Attached Image Attached Image
gobiomani
post Jul 21 2022, 10:41 AM

Enthusiast
*****
Junior Member
709 posts

Joined: Jun 2019

QUOTE(subaiku @ Jul 20 2022, 10:47 AM)
Ok, thanks! Will look into the Schneider ones... sorry noob question, not sure if I have a MCB? This is my DB box currently...

Attached Image Attached Image
*
All those C20, C32, etc are MCBs.
Your DB box is using Hager components, better for you to buy Hager RCCBs as they will fit perfectly when you cover the enclosure. The enclosure tolerance is tight, if use other brands may not be able to close back, may need to trim the window on the enclosure cover if want to use cheaper brands. Take note that I am not talking about the outer cover, I'm talking about the cover where the stickers (main switch, danger, etc) are on.
On another note, your DB box should not be having those C32 MCBs unless there are ring circuits in your house (which is very unlikely). Check what those MCBs are for and replace them with more appropriately sized MCBs.
You must also change your main RCCB which is using 300mA sensitivity to 30mA (0.03A). 300mA house burn down also RCD will not trip.

This post has been edited by gobiomani: Jul 21 2022, 10:45 AM
TSsubaiku
post Jul 21 2022, 10:45 AM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(candidman78 @ Jul 20 2022, 10:52 AM)
JOVEx again haha. BTW, I dont believe any build in electronics ELCB.
Only 2 brands I found is using Electro-Magnetic. ELCB.

YET to me is not enough and by the rules regardless whether the unit comes with built in, they must have an exter RCCB, RCB, RCBO 10mA.

And probably 99.99% user ignore
*
"JOVEx again haha."

Why? You had similar experience with Joven? Actually I had two Joven water heaters spoilt within a week of each other, this one and the other one suddenly trip the whole house when I tried to switch it on. Both were because of the heater element. Both also just reached 4 years old. Makes me wonder what kind of quality the WH are and here I thought Joven was a reputable brand. dry.gif
AbbyCom
post Jul 21 2022, 10:59 AM

Casual
***
Junior Member
456 posts

Joined: Mar 2020
QUOTE(subaiku @ Jun 30 2022, 04:52 PM)
Errr, mine got no ELCB button like those wall mounted type.

» Click to show Spoiler - click again to hide... «

*
Yours is the water heater tank types, not the regular one.

You have current on the tap head - possible causes is you have some wiring work done and neutral and earth wiring got connected wrongly or wiring have issues. Better get a technician to check it ASAP.

Edit : Saw TS found the root cause at post #15. I replied immediately because of the severity of the issue. Glad that you found it.

This post has been edited by AbbyCom: Jul 21 2022, 11:09 AM
Kiding
post Jul 21 2022, 12:30 PM

Regular
******
Senior Member
1,135 posts

Joined: Jan 2003
From: Seri Kembangan


Water heater safety guides from the electrical and electronics association of Malaysia

https://www.st.gov.my/en/contents/presentat...-%20Updated.pdf
stormer.lyn
post Jul 21 2022, 02:37 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(Kiding @ Jul 21 2022, 12:30 PM)
Water heater safety guides  from the electrical and electronics association of Malaysia

https://www.st.gov.my/en/contents/presentat...-%20Updated.pdf
*
Sorry to be a bit pedantic, but I have to point out...
ST = Suruhanjaya Tenaga = Energy Commission = can make rules that must be followed
electrical and electronics association of Malaysia = guidelines, no legal standing
SUSceo684
post Jul 22 2022, 12:50 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(subaiku @ Jul 18 2022, 04:43 PM)
Ok guys, really thanks for all the input, just wanted to update for everybody's future reference because this was scary AF. So this is what actually happened.

Got the Joven technician to come over and check, turns out it is the heater element that was spoilt. But usually if this happens, turning on the water heater would have tripped the current box. However it did not, instead the current was running through the copper piping then into the steel shower head. F*ck.

So, got heater element fixed and then got my electrician to come take a look to find out why it didn't trip as it should have. Turns out the ground wire for the water heater was not connected to anything!ย  shocking.gif This one is probably due to my previous crappy contractor who did my reno who also installed the water heaters. Was a vomit blood experience but that's another story.

What the electrician did then was to connect the ground wire from my nearby air ventilator to the water heater's ground wire so in future should trip if anything goes wrong. He says should be safe enough. But can also do further precaution by installing RCBO for the water heater at the current box.

Sorry if I have wrongly described anything as my electrical knowledge is nil. Anyways I'm considering getting these RCBO models, all got various prices... any advice?
Is not whether can or cannot. Its mandatory under the Electricity Regulations 1994 to have 10mA RCD fitted for wet floor appliances.

1. You trust your life insurance to cheapo china brand? mega_shok.gif
2. Want to do, do properly. ABB or Hager 10mA RCD.

Also like mentioned above, the 3 phase 0.3A = 300mA RCD is useless and against the law, cos of it all your 13A sockets are illegal and unprotected.
You need to change to 30mA (0.03A) RCD. This will cost the good part of RM300-ish for the barang alone.

This post has been edited by ceo684: Jul 22 2022, 12:54 AM
TSsubaiku
post Jul 26 2022, 10:24 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(gobiomani @ Jul 21 2022, 10:41 AM)
All those C20, C32, etc are MCBs.
Your DB box is using Hager components, better for you to buy Hager RCCBs as they will fit perfectly when you cover the enclosure. The enclosure tolerance is tight, if use other brands may not be able to close back, may need to trim the window on the enclosure cover if want to use cheaper brands. Take note that I am not talking about the outer cover, I'm talking about the cover where the stickers (main switch, danger, etc) are on.
On another note, your DB box should not be having those C32 MCBs unless there are ring circuits in your house (which is very unlikely). Check what those MCBs are for and replace them with more appropriately sized MCBs.
You must also change your main RCCB which is using 300mA sensitivity to 30mA (0.03A). 300mA house burn down also RCD will not trip.
*
Hey thanks for all the tips! Did not notice that about my RCCB if you hadn't mentioned it! Will get my electrician to look into those C32 MCBs that you mentioned.
TSsubaiku
post Jul 26 2022, 10:27 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(AbbyCom @ Jul 21 2022, 10:59 AM)
Yours is the water heater tank types, not the regular one.

You have current on the tap head - possible causes is you have some wiring work done and neutral and earth wiring got connected wrongly or wiring have issues. Better get a technician to check it ASAP.

Edit : Saw TS found the root cause at post #15. I replied immediately because of the severity of the issue. Glad that you found it.
*
Heheh... thanks for the concern. smile.gif
TSsubaiku
post Jul 26 2022, 10:52 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(ceo684 @ Jul 22 2022, 12:50 AM)
Is not whether can or cannot. Its mandatory under the Electricity Regulations 1994 to have 10mA RCD fitted for wet floor appliances.

1. You trust your life insurance to cheapo china brand?ย  mega_shok.gif
2. Want to do, do properly. ABB or Hager 10mA RCD.

Also like mentioned above, the 3 phase 0.3A = 300mA RCD is useless and against the law, cos of it all your 13A sockets are illegal and unprotected.
You need to change to 30mA (0.03A) RCD. This will cost the good part of RM300-ish for the barang alone.
*
Sorry lah boss, didn't know better then tongue.gif . Learning by every new post. Didn't notice my RCCB was 300mA also, had thought it was 0.3A until gobiomani mentioned it.

Appreciate the input. smile.gif

This post has been edited by subaiku: Jul 28 2022, 07:58 AM
ZeneticX
post Jul 27 2022, 02:00 AM

stars for what
********
All Stars
12,413 posts

Joined: Jan 2008
From: KL - Cardiff - Subang - Sydney



looking at how TS's electrician installed the water heater and the errors with the DB box.... I'm wondering how many other houses out there are done the same way by the same guy with the same mistake as well? basically all ticking time bomb.....

This post has been edited by ZeneticX: Jul 27 2022, 02:01 AM
gobiomani
post Jul 27 2022, 10:23 AM

Enthusiast
*****
Junior Member
709 posts

Joined: Jun 2019

QUOTE(ZeneticX @ Jul 27 2022, 02:00 AM)
looking at how TS's electrician installed the water heater and the errors with the DB box.... I'm wondering how many other houses out there are done the same way by the same guy with the same mistake as well? basically all ticking time bomb.....
*
This kind of thing is unfortunately very common in Malaysia. Most so called electricians in Malaysia don't know what they are doing or want to get it done with minimum work for them. The attitude of most Malaysians where they are not willing to pay for good quality and knowledgeable electrician is also a very big contributing factor to such poor quality work.
mirzan007
post Jul 27 2022, 10:32 AM

On my way
****
Junior Member
501 posts

Joined: Jul 2005


Nice thread.. I've learned a lot from you guys... tq and stay safe


SUSceo684
post Jul 28 2022, 08:37 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(ZeneticX @ Jul 27 2022, 02:00 AM)
looking at how TS's electrician installed the water heater and the errors with the DB box.... I'm wondering how many other houses out there are done the same way by the same guy with the same mistake as well? basically all ticking time bomb.....
*
An overwhelming majority - sad to say.
TSsubaiku
post Aug 3 2022, 05:28 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(ZeneticX @ Jul 27 2022, 02:00 AM)
looking at how TS's electrician installed the water heater and the errors with the DB box.... I'm wondering how many other houses out there are done the same way by the same guy with the same mistake as well? basically all ticking time bomb.....
*
Yeah man, basically the contractor who did my place up was a nightmare to work with (but that's another story altogether). Using subpar subcontractors all the way, really should blacklist the f*cker. vmad.gif
TSsubaiku
post Aug 3 2022, 05:32 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(ceo684 @ Jul 28 2022, 08:37 AM)
An overwhelming majority - sad to say.
*
If you google "water heater electrocution" the results will really freak you out. sad.gif
TSsubaiku
post Aug 3 2022, 06:14 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(Selene Yeo @ Jul 20 2022, 04:36 PM)
Just to clarify, you are using a storage water heater correct? Not an instant water heater.

If it is a storage water heater, then FYI storage water heaters do not have a built-in circuit breaker like instant water heaters. So they have to rely on the DB box circuit breaker. BUT if your storage water heater is not grounded / no earth connection, no matter how good quality your circuit breaker is, the circuit breaker will not trip when there is a current leakage, and u will be electrocuted.

Hence why SIRIM / Suruhanjaya Tenaga now set a new guideline for storage water heaters to come with Isolation Barriers placed at both the storage water heaters' inlet and outlet water connection. Most SIRIM certified storage water heater brands already complied to this guideline, and some brands even took the extra safety effort to pre-install the isolation barriers on the heater, such as CENTON, which is extra good, considering some inexperienced installers will missed out installing the Isolation Barriers if they are not pre-installed on the heater out-of-the-box.

Isolation Barriers are simple devices that elongate any current flow from the storage water heater to users, so any current flow (if there is) will barely reach the users. So in your case where there is an unfortunate current leakage because of the lack of earthing, if your storage water heater is pre-installed with Isolation Barriers, the Isolation Barriers will protect u from electrocution to a certain extend. But every device has a lifespan as well, so u will probably be protected until the lifespan of the Isolation Barriers ended. So don't just rely on the Isolation Barriers to protect u. Installation and earthing connection has to be correct in the first place.

Basically just a safety tip for u, if your storage water heater do not have Isolation Barriers pre-installed, u are advised to install them.
*
Hey Selene, would you know of anybody who does the instalation of isolation barriers? Is it something any plumber can do? Tried google but not many results, they look something like this yeah?

user posted image
TSsubaiku
post Aug 3 2022, 07:51 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(gobiomani @ Jul 21 2022, 10:41 AM)
All those C20, C32, etc are MCBs.
Your DB box is using Hager components, better for you to buy Hager RCCBs as they will fit perfectly when you cover the enclosure. The enclosure tolerance is tight, if use other brands may not be able to close back, may need to trim the window on the enclosure cover if want to use cheaper brands. Take note that I am not talking about the outer cover, I'm talking about the cover where the stickers (main switch, danger, etc) are on.
On another note, your DB box should not be having those C32 MCBs unless there are ring circuits in your house (which is very unlikely). Check what those MCBs are for and replace them with more appropriately sized MCBs.
You must also change your main RCCB which is using 300mA sensitivity to 30mA (0.03A). 300mA house burn down also RCD will not trip.
*
Hey gobiomani, I've got another question, if my RCCB is 63A 300mA, is it neccesary to get the same 63A? As in a 63A 30mA RCCB?
SUSceo684
post Aug 4 2022, 08:41 AM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(subaiku @ Aug 3 2022, 07:51 PM)
Hey gobiomani, I've got another question, if my RCCB is 63A 300mA, is it neccesary to get the same 63A? As in a 63A 30mA RCCB?
*
To answer your question, yes you must get a 63A sustained rated to replace a 63A existing component.
Don't cheap out to get a 40A sustained rated part.

300mA tripping threshold is elcheapo protection for fire only.
Human already die when >50mA pass thru human body.
300mA tripping threshold is 6 times con-con-con-con-con-confirm die.
Or, rather, closing barn door after the horse left.

I put nothing more than 30mA tolerance RCDs for the places I can control.
Because that's the way. In SG and AU all use 30mA for domestic. In MY life is cheap.

This post has been edited by ceo684: Aug 4 2022, 08:43 AM
fireballs
post Aug 4 2022, 08:44 AM

10101
*******
Senior Member
5,650 posts

Joined: Mar 2012
QUOTE(subaiku @ Aug 3 2022, 06:14 PM)
Hey Selene, would you know of anybody who does the instalation of isolation barriers? Is it something any plumber can do? Tried google but not many results, they look something like this yeah?

user posted image
*
you can just buy from shopee, then ask plumber to install
gobiomani
post Aug 4 2022, 10:32 AM

Enthusiast
*****
Junior Member
709 posts

Joined: Jun 2019

QUOTE(subaiku @ Aug 3 2022, 07:51 PM)
Hey gobiomani, I've got another question, if my RCCB is 63A 300mA, is it neccesary to get the same 63A? As in a 63A 30mA RCCB?
*
Yes, must use back the same as sifu ceo684 said. I also learn so many things from her.
Skylinestar
post Aug 7 2022, 11:13 AM

Mega Duck
********
All Stars
10,477 posts

Joined: Jan 2003
From: Sarawak
QUOTE(nihility @ Jul 2 2022, 08:11 PM)
You are fortunate that you are still alive. Go get licensed wiremen to check the wiring & compliance to ST guide for the water heater installation.
*
where to find licensed wiremen? is there a directory or something?
nihility
post Aug 7 2022, 11:25 AM

Regular
******
Senior Member
1,596 posts

Joined: Sep 2021


QUOTE(Skylinestar @ Aug 7 2022, 11:13 AM)
where to find licensed wiremen? is there a directory or something?
*
https://ecos.st.gov.my/senarai-orang-kompet...aftar-elektrik-

You can search at the ST data base.
Selene Yeo
post Aug 8 2022, 12:07 AM

Getting Started
**
Junior Member
149 posts

Joined: Feb 2021


QUOTE(subaiku @ Aug 3 2022, 06:14 PM)
Hey Selene, would you know of anybody who does the instalation of isolation barriers? Is it something any plumber can do? Tried google but not many results, they look something like this yeah?

user posted image
*
Better get plumbers who know how to install storage water heaters to do it for u. At the inlet, u will need to connect it to the pressure relief valve too (water source piping > pressure relief valve > isolation barrier > storage water heater's inlet).

Yes it looks like the one in your picture, but better purchase from the storage water heater's brand distributor so that u get more assurance that it is a confirm fit.
TSsubaiku
post Aug 11 2022, 10:07 AM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(Selene Yeo @ Aug 8 2022, 12:07 AM)
Better get plumbers who know how to install storage water heaters to do it for u. At the inlet, u will need to connect it to the pressure relief valve too (water source piping > pressure relief valve > isolation barrier > storage water heater's inlet).

Yes it looks like the one in your picture, but better purchase from the storage water heater's brand distributor so that u get more assurance that it is a confirm fit.
*
Ok, thanks for that! Willdo! smile.gif
TSsubaiku
post Aug 11 2022, 10:18 AM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(ceo684 @ Aug 4 2022, 08:41 AM)
To answer your question, yes you must get a 63A sustained rated to replace a 63A existing component.
Don't cheap out to get a 40A sustained  rated part.

300mA tripping threshold is elcheapo protection for fire only.
Human already die when >50mA pass thru human body.
300mA tripping threshold is 6 times con-con-con-con-con-confirm die.
Or, rather, closing barn door after the horse left.

I put nothing more than 30mA tolerance RCDs for the places I can control.
Because that's the way. In SG and AU all use 30mA for domestic. In MY life is cheap.
*
Yes, thank you sifu! Re: 63A, just wanted to make sure since when I went to the shop, sale staff asked me and I also didn't know how to answer.

Which actually leads me to my next problem... when I was going to all the shops to source for the RCCBs and RCBOs nearly every shop staff gave me a funny look when I asked for 30mA tolerance RCCBs. They said it's too sensitive and will trip often and they recommended 100mA instead. (I know, I know, it's the law and 30mA is what all you guys have been recommending, and yes, 100mA still will con-con-con-con-confirm die tongue.gif)

So question for all those of you that actually have 30mA installed, does it actually trip easily? My worry is that I'm out of my condo for long periods of time often, if trip then things like the fridge might be a problem (with all the food rotting and all).
davidlow7
post Aug 11 2022, 02:04 PM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(nihility @ Aug 7 2022, 11:25 AM)
I used the same unfortunately those jobs seem to be subbed out to others, where sometimes I don't feel confident when they answered something incorrectly.
davidlow7
post Aug 11 2022, 02:10 PM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(subaiku @ Aug 11 2022, 10:18 AM)
Yes, thank you sifu! Re: 63A, just wanted to make sure since when I went to the shop, sale staff asked me and I also didn't know how to answer.

Which actually leads me to my next problem... when I was going to all the shops to source for the RCCBs and RCBOs nearly every shop staff gave me a funny look when I asked for 30mA tolerance RCCBs. They said it's too sensitive and will trip often and they recommended 100mA instead. (I know, I know, it's the law and 30mA is what all you guys have been recommending, and yes, 100mA still will con-con-con-con-confirm die tongue.gif)

So question for all those of you that actually have 30mA installed, does it actually trip easily? My worry is that I'm out of my condo for long periods of time often, if trip then things like the fridge might be a problem (with all the food rotting and all).
*
Well, same issue I faced..

They insisted water heater uses 30mA and when I said ST rule since 1994 is also there already he looked at me and insisted "no such thing ever!"

If you still worry of easily trip (despite the good brands like ABB, Hager won't unless it is a life-threatening leak) then you can continue with 100mA for your lighting and fan, since human are usually not exposed to it. Keep the 30mA maximum for your plug points, and 10mA for water heater.

Bear in mind, you should in fact ensure your steel roof/steel-type awnings are grounded as well (a green wire to connect to your DB busbar directly) for safety - otherwise ((when there is a leak) anyone who climbs the roof to fix/repair something might get electrocuted to death since your lighting/fan RCCB sensitivity is only at 100mA. This also ST requirement actually.
It would be a miracle if people who install awning at his house would get an electrician to help pull a green wire connect to your earth busbar, whilst the awning are fitted with wired lamps/fans.


nihility
post Aug 11 2022, 07:39 PM

Regular
******
Senior Member
1,596 posts

Joined: Sep 2021


QUOTE(davidlow7 @ Aug 11 2022, 02:04 PM)
I used the same unfortunately those jobs seem to be subbed out to others, where sometimes I don't feel confident when they answered something incorrectly.
*
If you want to prevent getting unregistered person to install , the least risky way if to ask the water heater retailer to recommend their electricians in their contact.
davidlow7
post Aug 11 2022, 08:08 PM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(nihility @ Aug 11 2022, 07:39 PM)
If you want to prevent getting unregistered person to install , the least risky way if to ask the water heater retailer to recommend their electricians in their contact.
*
I think the outcome is probably same in most cases - this is a known trend in Malaysia even by many main cons who do house renovation would tell the same that most of them on "shared" licenses.

This allows some of the licensed and good ones charging at superb high price, which might be ok from safety point of view but they are usually reluctant in taking a one-off job - they are more interested in big project like 50k for whole house wiring.
nihility
post Aug 11 2022, 09:21 PM

Regular
******
Senior Member
1,596 posts

Joined: Sep 2021


QUOTE(davidlow7 @ Aug 11 2022, 08:08 PM)
I think the outcome is probably same in most cases - this is a known trend in Malaysia even by many main cons who do house renovation would tell the same that most of them on "shared" licenses.

This allows some of the licensed and good ones charging at superb high price, which might be ok from safety point of view but they are usually reluctant in taking a one-off job - they are more interested in big project like 50k for whole house wiring.
*
It is true to certain extend on the license sharing. Usually they will target higher value task over smaller value task ( opportunity cost). Only the friendly electrical contractors can help you on this matter.
SUSceo684
post Aug 11 2022, 10:09 PM

Component Burner
********
All Stars
11,667 posts

Joined: Jan 2003
From: Klang/Subang




QUOTE(subaiku @ Aug 11 2022, 10:18 AM)
Yes, thank you sifu! Re: 63A, just wanted to make sure since when I went to the shop, sale staff asked me and I also didn't know how to answer.

Which actually leads me to my next problem... when I was going to all the shops to source for the RCCBs and RCBOs nearly every shop staff gave me a funny look when I asked for 30mA tolerance RCCBs. They said it's too sensitive and will trip often and they recommended 100mA instead. (I know, I know, it's the law and 30mA is what all you guys have been recommending, and yes, 100mA still will con-con-con-con-confirm die tongue.gif)

So question for all those of you that actually have 30mA installed, does it actually trip easily? My worry is that I'm out of my condo for long periods of time often, if trip then things like the fridge might be a problem (with all the food rotting and all).
*
It doesn't trip often if you buy a genuine ABB or Hager 30mA, current models.
Yes 30 years back models even 300mA also trip every other rain lah. The technology then and now improved a lot.

Nah I show you lah, I moved to SG and left my apartment fridge running.
Its protected with whole house 30mA, ABB.
Attached Image

QUOTE(davidlow7 @ Aug 11 2022, 02:10 PM)
Well, same issue I faced..

They insisted water heater uses 30mA and when I said ST rule since 1994 is also there already he looked at me and insisted "no such thing ever!"

If you still worry of easily trip (despite the good brands like ABB, Hager won't unless it is a life-threatening leak) then you can continue with 100mA for your lighting and fan, since human are usually not exposed to it. Keep the 30mA maximum for your plug points, and 10mA for water heater.

Bear in mind, you should in fact ensure your steel roof/steel-type awnings are grounded as well (a green wire to connect to your DB busbar directly) for safety - otherwise ((when there is a leak) anyone who climbs the roof to fix/repair something might get electrocuted to death since your lighting/fan RCCB sensitivity is only at 100mA. This also ST requirement actually.
It would be a miracle if people who install awning at his house would get an electrician to help pull a green wire connect to your earth busbar, whilst the awning are fitted with wired lamps/fans.
*
100mA for lights and fans?
You still use flourescent tube or halogen high-bay lamps at home??
seriously, 100mA?

Buy a good branded (read: ABB or Hager) 30mA whole house je lah. Dont waste money buying 100mA.

This post has been edited by ceo684: Aug 11 2022, 10:09 PM
davidlow7
post Aug 12 2022, 09:22 AM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(ceo684 @ Aug 11 2022, 10:09 PM)
You still use flourescent tube or halogen high-bay lamps at home??
seriously, 100mA?

Buy a good branded (read: ABB or Hager) 30mA whole house je lah. Dont waste money buying 100mA.
*
30mA RCCB should be the one to go for in replacing the 100mA, in fact I agree it should be for today's standard.
What I meant was the minimum is then to follow ST guideline, as last resort.

I think government had probably not enforcing this in the guideline because factoring the implementations nationwide would be a hassle due to lack of control and complexity but as user, we don't depend on government to protect ourselves.


stormer.lyn
post Aug 12 2022, 09:08 PM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(davidlow7 @ Aug 11 2022, 02:10 PM)
Bear in mind, you should in fact ensure your steel roof/steel-type awnings are grounded as well (a green wire to connect to your DB busbar directly) for safety - otherwise ((when there is a leak) anyone who climbs the roof to fix/repair something might get electrocuted to death since your lighting/fan RCCB sensitivity is only at 100mA. This also ST requirement actually.
It would be a miracle if people who install awning at his house would get an electrician to help pull a green wire connect to your earth busbar, whilst the awning are fitted with wired lamps/fans.
*
Are you saying ST lowest RCCB sensitivity for lights and fans is 100 mA, or are you saying ST requires metal awnings and metal roofs to be electrically grounded? The former is true, but I have never read the latter. Could you please cite a source if you mean the latter?
davidlow7
post Aug 12 2022, 10:10 PM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(stormer.lyn @ Aug 12 2022, 09:08 PM)
Are you saying ST lowest RCCB sensitivity for lights and fans is 100 mA, or are you saying ST requires metal awnings and metal roofs to be electrically grounded? The former is true, but I have never read the latter. Could you please cite a source if you mean the latter?
*
Here you go mate

https://www.st.gov.my/en/contents/files/dow...N_DOMESTIK1.pdf

user posted image

This post has been edited by davidlow7: Aug 12 2022, 10:20 PM
stormer.lyn
post Aug 13 2022, 08:35 AM

Regular
******
Senior Member
1,132 posts

Joined: Apr 2014
From: Shah Alam, Selangor
QUOTE(davidlow7 @ Aug 12 2022, 10:10 PM)
Thanks! Most appreciated!

Looks like ST has finally published an updated guidebook (Dated 1st December 2021) covering a lot more information. Lampiran III and V are particularly important (Pages 59 and 61) as it covers the current carrying capacity of wires, and is way more conservative than any manufacturer tables. From the ST table, 2.5 mmยฒ cables no longer are a 20 A MCB circuit....

user posted image
davidlow7
post Aug 13 2022, 10:07 AM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(stormer.lyn @ Aug 13 2022, 08:35 AM)
Thanks! Most appreciated!

Looks like ST has finally published an updated guidebook (Dated 1st December 2021) covering a lot more information. Lampiran III and V are particularly important (Pages 59 and 61) as it covers the current carrying capacity of wires, and is way more conservative than any manufacturer tables. From the ST table, 2.5 mmยฒ cables no longer are a 20 A MCB circuit....

user posted image
*
Yes but I think the issue we have in Malaysia is enforcement... You can see many electrical shops also selling DB box with 300mA rccb for domestic use. Wiremen taking contracts are mostly non-licensed whilst licensed ones simply charge with no control.

My house wireman luckily is really a knowledgeable person when I asked him to get ready earth wire connected to busbar for my future awning - he said "Singapore standard is like that" - by Singapore standard it does not mean just the guideline but also the enforcement!


TSsubaiku
post Aug 13 2022, 01:50 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(davidlow7 @ Aug 11 2022, 02:10 PM)
Well, same issue I faced..

They insisted water heater uses 30mA and when I said ST rule since 1994 is also there already he looked at me and insisted "no such thing ever!"

If you still worry of easily trip (despite the good brands like ABB, Hager won't unless it is a life-threatening leak) then you can continue with 100mA for your lighting and fan, since human are usually not exposed to it. Keep the 30mA maximum for your plug points, and 10mA for water heater.

Bear in mind, you should in fact ensure your steel roof/steel-type awnings are grounded as well (a green wire to connect to your DB busbar directly) for safety - otherwise ((when there is a leak) anyone who climbs the roof to fix/repair something might get electrocuted to death since your lighting/fan RCCB sensitivity is only at 100mA. This also ST requirement actually.
It would be a miracle if people who install awning at his house would get an electrician to help pull a green wire connect to your earth busbar, whilst the awning are fitted with wired lamps/fans.
*
Wah... the awning thing, I donโ€™t have that since I live in a condo but my parentโ€™s house has one. Another thing to look into. Thanks!
TSsubaiku
post Aug 13 2022, 01:54 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(ceo684 @ Aug 11 2022, 10:09 PM)
It doesn't trip often if you buy a genuine ABB or Hager 30mA, current models.
Yes 30 years back models even 300mA also trip every other rain lah. The technology then and now improved a lot.

Nah I show you lah, I moved to SG and left my apartment fridge running.
Its protected with whole house 30mA, ABB.
Attached Image
100mA for lights and fans?
You still use flourescent tube or halogen high-bay lamps at home??
seriously, 100mA?

Buy a good branded (read: ABB or Hager) 30mA whole house je lah. Dont waste money buying 100mA.
*
Thanks for that sifu! ๐Ÿ™๐Ÿป really gives me peace of mind! Ok, going ahead with Hager 63A, 30mA RCCB. ๐Ÿ˜Š

TSsubaiku
post Aug 13 2022, 02:02 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(davidlow7 @ Aug 13 2022, 10:07 AM)
Yes but I think the issue we have in Malaysia is enforcement... You can see many electrical shops also selling DB box with 300mA rccb for domestic use. Wiremen taking contracts are mostly non-licensed whilst licensed ones simply charge with no control.

My house wireman luckily is really a knowledgeable person when I asked him to get ready earth wire connected to busbar for my future awning - he said "Singapore standard is like that" - by Singapore standard it does not mean just the guideline but also the enforcement!
*
Heheh, mind sharing your wiremanโ€™s contact? I think anybody who reads through this thread will want his contact after this. ๐Ÿ˜
davidlow7
post Aug 13 2022, 06:13 PM

StageMaster
*******
Senior Member
8,306 posts

Joined: Jan 2003
From: Puchong Melaka Cyberjaya


QUOTE(subaiku @ Aug 13 2022, 02:02 PM)
Heheh, mind sharing your wiremanโ€™s contact? I think anybody who reads through this thread will want his contact after this. ๐Ÿ˜
*
I don't have his contact, but only my main con's contact so you might not be getting the 1st hand price.... I am also waiting for the chance to get his
TSsubaiku
post Aug 18 2022, 12:24 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(davidlow7 @ Aug 13 2022, 06:13 PM)
I don't have his contact, but only my main con's contact so you might not be getting the 1st hand price.... I am also waiting for the chance to get his
*
Hahaaaa... ok, ok.. share when you do. Thanks! smile.gif
TSsubaiku
post Aug 18 2022, 12:30 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(Selene Yeo @ Aug 8 2022, 12:07 AM)
Better get plumbers who know how to install storage water heaters to do it for u. At the inlet, u will need to connect it to the pressure relief valve too (water source piping > pressure relief valve > isolation barrier > storage water heater's inlet).

Yes it looks like the one in your picture, but better purchase from the storage water heater's brand distributor so that u get more assurance that it is a confirm fit.
*
Hey Selene, taking a look at my water heater outlets, the cold outlets seem to have a plastic/rubber barriers already, so I don't need to install them there right? Just the ones with the copper tubing?

user posted image

user posted image
maxguy
post Aug 18 2022, 12:52 PM

Enthusiast
*****
Senior Member
822 posts

Joined: Jan 2003


joven storage heater installation sample

https://images.app.goo.gl/h6zCNif8q7vJGr8b8

https://joven-electric.com/my/product/stora...my/jsh-my/jsh35

This post has been edited by maxguy: Aug 18 2022, 12:55 PM
TSsubaiku
post Aug 18 2022, 03:16 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(maxguy @ Aug 18 2022, 12:52 PM)
Thanks! Yup, I've seen those. But shop people says apparently the old model is prone to leaking.

This is the new model:
https://shopee.com.my/Joven-Isolation-Barri...3c-24c5996ca5f9

Still don't know why they cost so much for a plastic item. dry.gif
Selene Yeo
post Aug 25 2022, 01:56 AM

Getting Started
**
Junior Member
149 posts

Joined: Feb 2021


QUOTE(subaiku @ Aug 18 2022, 12:30 PM)
Hey Selene, taking a look at my water heater outlets, the cold outlets seem to have a plastic/rubber barriers already, so I don't need to install them there right? Just the ones with the copper tubing?

user posted image

user posted image
*
Suruhanjaya Tenaga recommends Isolation Barriers to be installed at both inlet and outlet. It is always better to be safe than sorry.
TSsubaiku
post Aug 26 2022, 04:13 PM

Casual
***
Junior Member
445 posts

Joined: Oct 2008
QUOTE(Selene Yeo @ Aug 25 2022, 01:56 AM)
Suruhanjaya Tenaga recommends Isolation Barriers to be installed at both inlet and outlet. It is always better to be safe than sorry.
*
Ok, thanks! thumbsup.gif

 